1 GROUND OR MORE? For multiple circuits

toolbear | Posted in Construction Techniques on December 18, 2004 03:17am

1 GROUND OR MORE? For multiple circuits in one conduit

Folks,

Situation:  Setting out to upgrade the garage electrical for workshop.  Meter main is on outside of wall, with space, so that is not an issue.  Plan surface mounted EMT with several circuits in it and 4″ J boxes on the walls:

2 – 20A, 12/3 WG, 120v  balanced circuits for the outlets on both sides

1 – 30A, 10/2 WG, 240v compressor/welder/whatever circuit for later (Got no compressor, got no welder – and I am not sure what amps they pull. Might have to increase wire size.

Question is:  with several circuits in one run, can they share a ground wire or should each circuit have it’s very own ground wire.

Please! Don’t make me read my obso 1996 copy of the code.  I though I spoke and wrote fluent English – until I started reading that.  It only seems to be written in English. 

The ToolBear

“Never met a man who couldn’t teach me something.” Anon.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. DaveRicheson | Dec 18, 2004 05:09pm | #1

    If you are running EMT, don't use 12/3 wg or any  type NM cable. Around here that would be a major code violation. Type NM cable is rated for heat by boyh the wire insulation and the outer sheating, both for how much it can witjstand, and how much heat it can shed. Enclosing it in conduite changes that rating to a lower value,

    If you are running EMT, pull in single conductors, in appropriate gauges for the fuse or breaker size. Pull a seperate ground for each circuit, not each device.

    My last shop garage/shop was wired as you described. I used  #12 THHN stranded wire in 1/2 EMT for the lighting runs and the receptical.  If you are not using spec. grade devices, stranded wire is a pain to land on terminals. It is also difficult to  push through anything other than short straight conduite runs. It is easier, however to pull with a fish tape. Using solid wire may be easier for you to both land on devices, and feed thru conduit by youself.

     

    Dave

    1. User avater
      BillHartmann | Dec 18, 2004 06:54pm | #2

      "If you are running EMT, pull in single conductors, in appropriate gauges for the fuse or breaker size. Pull a seperate ground for each circuit, not each device."Why a separate EGC for each circuit?In fact the EMT is qualified to be the EGC, but as been mentioned here many times lots of people thing that running a separate EGC is better practice.But only ONE should be enough, but sized for the largest circuit. And even if you ran multiple ones you would need to tie all of them together at each j-box. Sounds like making more work for nothing.

    2. toolbear | Dec 19, 2004 06:14pm | #3

      Dave,

      Glad you caught that so I can clarify.  I do tend to think in romex terms, but I was not planning on running the stuff in EMT.  

      All seperate conductors.  I am thinking of 3/4 EMT for the main run as I can do ten 10g THHN or 16 of the 12g - which means there is room for later additions.  Drop 1/2 legs  as needed.

      I use only commercial spec backwire outlets and put them in J boxes.  No 18CI handiboxes.  I like room.

      I am partial to flex after having stripped 6" of insulation off some solid as it ran across a liquidtight 90 fitting.  Is it naughty to use crimp down terminals on these?  Trying to get stranded under a screw is not on.  The ToolBear

      "Never met a man who couldn't teach me something." Anon.

      1. Stuart | Dec 19, 2004 06:43pm | #4

        "All seperate conductors.  I am thinking of 3/4 EMT for the main run as I can do ten 10g THHN or 16 of the 12g - which means there is room for later additions.  Drop 1/2 legs  as needed."

        Remember that if you run multiple conductors in a single conduit you may need to de-rate their current carrying capacity...the code allows up to three current carrying conductors without derating, 4 to 6 conductors you derate to 80%, 7 to 9 conductors derate to 70%, 10 to 20 conductors derate to 50%.  This applies to only the hot conductors.

        Edited to clarify: to match how this is described in the Code, "hot conductors" should be changed to "current carrying conductors."

        Edited 12/19/2004 7:39 pm ET by Stuart

        1. User avater
          SamT | Dec 19, 2004 08:53pm | #5

          >>the code allows up to three current carrying conductors without derating, 4 to 6 conductors you derate to 80%, 7 to 9 conductors derate to 70%, 10 to 20 conductors derate to 50%.  This applies to only the hot conductors.

          Why only the hot? It seems to me that since the returns carry the same current and have the seam resistance, they would generate the same heat as the "hots".

          Ah wait, I see, since the current is limited by what the derated hot can carry, it effectively derates the returns.

          Doh!

          Of course, you wouldn't want to say "I gots 2 hots at 50%, so's I kin use a shared return at 100%."

          SamT

  2. fireball | Dec 19, 2004 11:20pm | #6

    Using EMT is the way to go.If you're just needing the two general use and one 240v dedicated circuit,3/4" pipe will be OK.If you're going to come anywhere close to 16 #12's you ought to bump it up to a 1" w/ 4 11/16" boxes.A lot of what the NEC says you can do is a serious PITA in real life.

    1. toolbear | Dec 19, 2004 11:55pm | #7

      I want to put in two 20A balanced circuits for the outlets and a 30a/240 for compressor.My ElectriCalc 96 says the limit in 12g THHN in 3/4 is 16, so I think I have room to spare, or do I.Can they all share one ground or does each circuit get a personal ground?The ToolBear

      "Never met a man who couldn't teach me something." Anon.

      1. fireball | Dec 20, 2004 12:30am | #8

        Each circuit does not need an individual ground.You would be packing the pipe with extra ground wires needlessly.For what you have said you need,pull a #10 ground and make joints at each point that you need to split off,remembering to add a ground tail to the box.I run conduit and pull wire every day, and I'm just trying to be helpful in saying that you don't want to pull the maximum number of conductors in a pipe that the NEC says you can.It's a lot of pi$$ing around if you have any number of boxes to pull through,and if you start splicing in them you'll end up with overloaded junction boxes.In laying out homeruns at work the most I ever want to go is 3 sets of three phase( 4 wires each) per 3/4 pipe.It's not hard for the wire count to creep up when you decide to put the garage door openers on their own circuit,and then there's three way switching for the lighting,etc....

        1. toolbear | Dec 20, 2004 08:52am | #12

          Barry,

          BTDT trying to deal with well-stuffed conduit and overstuffed boxes.  I like to oversize so there is room to pull, room to work and no question of a box fill violation. 

          So, I can put one 10g ground to share among a pair of 12g balanced circuits and one 10g 240 circuit. 

          Tap off the 10g. with the appro. gauge - 12g to the 120 stuff, 10g to the 240 stuff.

          Include each 4x4 J box with a pigtail.

          Should be fun.

           

           The ToolBear

          "Never met a man who couldn't teach me something." Anon.

  3. jrnbj | Dec 20, 2004 12:44am | #9

    For all us plain folk, would that be 1 black & 1 white for each circuit, but a single continuous green tapped into at each termination?

  4. pm22 | Dec 20, 2004 03:23am | #10

    This whole thread is slowly converging on truth. To begin with, the Code is poorly written because it is written by committees who pretend to be lawyers.

    For the grounding issue: EMT can serve as a ground but a real ground wire [green] is preferred. It is sized to the largest conductor; in your case it would be #10.

    You can run Romex [secret code name = non-metalic cable] in conduit but this is usually only done for protection.

    The derating applies to all the current carrying conductors which includes the neutrals. [Exception: balanced three phase circuit]

    You can terminate stranded wire with those crimp on terminals. You might want to use a larger conduit for future expansion and leave a pull string.

    ~Peter

    Martha Stewart is solicitating.
    Page two: Well, she is solicitating a donation of a wheelbarrow full of gold coins. The wheelbarrow must include a store receipt.

    1. toolbear | Dec 20, 2004 09:05am | #13

      Please tell me more about the derating and how to avoid it. 

      I will have two sets of 12g R,B, W for the balanced circuits.  One set of 10g R,B for the 240 and one 10g G for the common ground for all circuits. 

      I'll run the numbers again, but I think 3/4 EMT should handle that with room to spare.  Hope so, since my biggest bender is 3/4.

      Yes!  I should add a pull cord for Later. 

       The ToolBear

      "Never met a man who couldn't teach me something." Anon.

      1. DaveRicheson | Dec 20, 2004 02:03pm | #15

        Spent the Sat. night and all day Sun. at the hospital with my Dad.

        Looks like you got all the suggestions and answers you needed in this thread.

        One other caution I'll add from experience.

        Attach all conduit runs and boxes as if you are going to hang stuff  on it....cause you will......eventually!

         

         

        Dave

        1. toolbear | Dec 20, 2004 05:20pm | #17

          Dave,

          You're right.  That conduit is great for hanging stuff. 

          I secure it with straps and deck screws to the studs.  You can chin yourself on it - at least once.  Twice...we'll see.The ToolBear

          "Never met a man who couldn't teach me something." Anon.

        2. DanH | Dec 20, 2004 09:44pm | #20

          Yeah, I was helping wire a TV studio where I worked, and I demanded that the conduit be attached well enough to support my weight, given that, while up on a ladder playing with lights, I might suddenly "desire" an additional handhold.

      2. User avater
        BillHartmann | Dec 20, 2004 08:36pm | #19

        "Please tell me more about the derating and how to avoid it. "First the requirement is based on "net" current carrying conductors.So a 240/120 circuit (2 hots and neutral) only count as 2 current carrying conductors. Because, at max load you either have full current on the 2 hots or one hot and a neutral. Now 2 "separate" 120v circuits would be 4 current carrying conductors. But if you run it as a multi wire circuit with a shared neutral then it is only 2 current carrying conductors. But in this case it does not matter as you will still be in the 4-6 count.But many people do not understand the actual current limits in the wiring charts.Using the 75 degree column and 90 degree column the acutal ampacity rating of wires are#14 20 25
        #12 25 30
        #10 35 40
        #8. 50 55Now if you use THHN/THHW (which is the common individual wire) then it ratd for upto 90 as is NM-B. But few terminals are rated for 90, most are rated for 75. But at 75 rates about you derate to 80% you have#14 16 amps
        #12 20 amps
        #10 28 amps
        #8 40 ampsWhich for the #14, 12, and #8 they are large enough for the nominal circuit ratings of 15, 20, and 40 amps.Now for the #10 I would stretch go ahead and use it for things like wood working equipment because of the low duty cycle. Also I know that I would have limited loads on the 120 at the sametime. This is ok for a home workshop, but not for a commerial establishment.In fact whenever I redo my shop I am going to run dual 20 amp 120 and a 20 240 circuit in a loop around the shop.But for air compressor and dust collector I am going to run separeate lines.

        1. toolbear | Dec 21, 2004 05:34am | #23

          Thanks, that helps make sense of 316. 

          Looks like for what I plan I will still have a working pair of 20a balanced circuits. 

          The 240 will get it's own conduit.The ToolBear

          "Never met a man who couldn't teach me something." Anon.

      3. pm22 | Dec 21, 2004 03:53am | #21

        "Please tell me more about the derating and how to avoid it."

        The Code is a confabulation of experience, distorted theory and backroom politics. Derating is a perverted attempt to keep wires from overheating, melting the insulation off and causing ensuing problems.

        Derating is based on the theory that each current carrying conductor releases heat in proportion to its resistance and the amount of amps it is conducting. The relevanent sections are Table 310-15(b)(2)(a) and good old 310-16.

        Here is a summary of 310-15:

        Number of conductors   % darating4-6                    80%7-9                    70%10-20                  50%

        Table 310-16 is what separates the professionals from the hacks. There are three columns: 60º C, 75Cº and 90º Centigrade. You never actually use the 90º column except for derating. Furthermore, according to 114c, you must use the 60º column for every thing less than 100 amps [exceptions exist but not here]. Here is a sumary of 316-16:

        AWG  60º  75º  90º14*  20   20   25 amps12*  25   25   3010*  30   35   40 8   40   50   55*240-3 says these sizes are to be protected at 15, 20 and 30 amps repectively. [This is for copper]

        At the bottom of the table are more derating tables for ambient temperature. Except for an attic in Phoenix, Arizona, these are a non-issue. 

        Assming that you are using THHN in your conduit, it is rated for 90º.  "two sets of 12g R,B, W for the balanced circuits.  One set of 10g R,B for the 240 " I get a total of SIX current carrying conductors.* This qualifies for 80% darating. Since this is THHN, you start with the 90º column. Your #12 could carry 30 amps X .80 = 24 amps and your #10 could carry 40 amps X .80 = 32 amps. But 114c says you must use the 60º column because the terminals of the breakers under 100 amps are only rated for 60º. So now your down to 25 and 30 amps -- or to be precise, 24 and 30 amps. But 240-3 limits these to 20 amps and 30 amps so this whole exercise is a lesson in futility.*310-15(4)(a).

        Hope this totally clarifies things and I didn't make any mistakes.

        ~Peter

  5. 4Lorn1 | Dec 20, 2004 03:54am | #11

    Those portions of the circuits run in conduit can operate with a single ground sized for the largest required ground. Watch the derates both for fill and ambient temperature.

    In other words if the largest required ground is a #8 all other circuits can be tapped into this ground conductor. The taps should be sizes for the circuit feeding the outlet. In your case matching the wire size of the hot feeding the outlet. IE: A receptacle fed with a #12 conductor has a #12 ground connected to the #8, as per the example above only.

    Those circuits or portions of circuits run in cable, Romex, have to each have a separate ground. The requirement is that all circuit conductors, including the ground, must be run together. Either within the cable or within the conduit.

    This has to do with the effects of impedance on circuit balancing, the timely functioning of breakers and how magnetic forces cancel each other out, or fail to, within circuits and surrounding materials.

    Circuits run in cables, multiconductor assemblies, Romex and sleeved in EMT for the purposes of localized mechanical protection also need separate grounds as there is no practical way to do it otherwise as splices have to be in an accessible and properly sized junction box or condulet. Here again you have to watch the pipe fill and derates.

    Note that the conductors within the cable, once removed from the jacket come under the rules for separate conductors, under their own ratings, within conduits. Sometimes this can be turned to your advantage but you have to know what the rules are to steer through the rocks.

  6. JetBoy2 | Dec 20, 2004 09:51am | #14

    Why not just run two or more sets of conduit? I suspect you'd be much happier with having more room to work in both the EMT and the boxes. And since this is a garge, won't those 120 circuits require a GFI receptacle in the first box for each 120 branch? Plus, you have the option of changing circuits down the road. If you pull 11 wires through a 3/4" EMT, I'd bet you are neither removing nor adding to that conduit in the future w/o removing all the wires. With the 120 and 240 circuits in separate runs, you have the option of changing the wiring in the future without interfering with other wires in the EMT. For me, the negligible higher cost of multiple conduit runs far outweighs the hassles of making connections and folding wires in tight spaces.

    1. toolbear | Dec 20, 2004 05:17pm | #16

      I can certainly see the advantages of a double run.  I hate working in stuffed spaces.

      I use 4" J boxes for wiggle room.The ToolBear

      "Never met a man who couldn't teach me something." Anon.

  7. daFarmerDave | Dec 20, 2004 05:21pm | #18

    The Lincon AC/DC stick welder at HD, $375, has a three conductor 50A plug on it. 

     

    Big Macs - 99 cents
    1. toolbear | Dec 21, 2004 05:29am | #22

      Thanks for the data.

      I was wondering about what those draw.  Better wire it like a stove.  Means it will have it's very own conduit.

      What does a tower compressor draw?The ToolBear

      "Never met a man who couldn't teach me something." Anon.

      1. daFarmerDave | Dec 22, 2004 06:17am | #24

        The 80 gallon 175 PSI jobs come in under thirty amps @ 240 V.  The do things right part of me thinks #8 or #6 to keep the volatge drop low.  I heard that makes motors last longer.Big Macs - 99 cents

        1. toolbear | Dec 22, 2004 02:20pm | #25

          Overwiring a size does help reduce voltage drop - depending on distance, load.  When in doubt, bump it up.  I think that there is a rule of thumb that after 75' of run, jump up one size.

          I use 10g cords for my saws.  HD was offering 100' of 10g with 3 outlet head for $62.  Bought one, cut in half, put a 20a GFCI in RT box on the other half.  50' of 10g then 50' of direct connect 12g cord to the saw. 

           The ToolBear

          "Never met a man who couldn't teach me something." Anon.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity

Learn about different approaches to making updates and repairs to older homes with historic charm.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring
  • FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity
  • Tools and Gear for the Moms Who Get it Done
  • An Easier Method for Mitered Head Casings

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 81%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data