10-2 or 10-3 for dryer?

mrfixitusa | Posted in General Discussion on October 31, 2006 12:33pm

I’m moving a dryer from the basement up to the kitchen. 

Is it okay to use 10-2 for the dryer?

The dryer cord is a three prong.

If I use 10-2 the ground would have to serve as the neutral.  I guess that just doesn’t sound right.

Any recommendations?

Thanks for any input.

^^^^^^

 

S N A F U (Situation Normal: All Fouled Up)

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Scott | Oct 31, 2006 12:36am | #1

    ...if you have to ask...

    But anyway, dryers require 10-3 because there are 120V and 240V loads (the fan motor and heating coils respectively).

    Be careful.

    Scott.

    Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

  2. splintergroupie | Oct 31, 2006 12:38am | #2

    "Any recommendations?"

    You could always get some 10/3 w/ground and do it right. <rolls eyes>

    1. mrfixitusa | Oct 31, 2006 12:57am | #3

      I bought 10-3 and it's what I'm using I was just asking for opinions (rolls eyes).

      What is the purpose of 10-2 (rolls eyes) ?  I'm just curious and wanting to learn (rolls eyes)^^^^^^

       

      S N A F U (Situation Normal: All Fouled Up)

      1. BryanSayer | Oct 31, 2006 01:05am | #4

        10-2 is for things like A/C units, or maybe some large equipment that has no 120v accessories, where no seperate neutral is needed.You realize that you need to change to a 4 prong outlest and plug too, right? I actually have a brand new spare 4 prong plug and 6' cord laying around. If you want it, e-mail me your address.

      2. splintergroupie | Oct 31, 2006 01:21am | #5

        10/2 used in baseboard heaters, water heaters, runs too long for 12 ga....Mind you, i'm not an electrician, i only play one inside my own house.

        1. mrfixitusa | Oct 31, 2006 01:50am | #6

          I talked to an electrician while at home depot and he said he used 10-2 for "old work"

          He said he used 10-3 for "new work"  and for anything that had to be "up to code"

          He was buying 10-2 for a dryer while I was there.  He said he has done many this way.

          I'm going with the 10-3 and the new plug and new cord

          Thanks for all the responses!^^^^^^

           

          S N A F U (Situation Normal: All Fouled Up)

          1. DanH | Oct 31, 2006 02:11am | #8

            Yeah, he's wrong. If you're pulling new cable it should be 3+ground. Same for an electric range.
            Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi

          2. splintergroupie | Oct 31, 2006 02:25am | #9

            There's a guy across the road with a master electrician's license who told me my car battery wouldn't take a charge while sitting on my concrete floor.

          3. ponytl | Oct 31, 2006 02:32am | #10

            at one time long ago  that was true...  thats when auto batteries were tar & wood and "leaked"  since they started usuing plastic cases it's no longer true  but it's one of those old tales that won't die...  btw my master sparkey said the same thing...

            p

          4. splintergroupie | Oct 31, 2006 03:05am | #11

            I suppose i wouldn't have been so surprised to hear it coming from a layperson, but from a licensed electrician...a bit alarming.

          5. gb93433 | Nov 02, 2006 07:28am | #52

            Some places require little to get a license. In other places it is harder to get a contractor's license than to get a nationallly recognized certification.

          6. mrfixitusa | Nov 07, 2006 12:45am | #53

            Update:

            I ran 10-3 with ground from the breaker box to the new dryer location. 

            I installed a new four prong outlet/receptacle.

            I bought a new four prong cord to replace the old three prong dryer cord.

             

            Problem: The dryer is one year old.  It is made for only a three prong - three wire  dryer cord.

            The dryer has black and red terminals for both of the cord's hot wires.

            The dryer's third and only remaining terminal is for the neutral.

            I now have a fourth wire in the cord (green) and no place to attach it on the dryer. 

            Any suggestions?

            Thanks for any input.

             

             ^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          7. splintergroupie | Nov 07, 2006 12:59am | #54

            http://www.selfhelpandmore.com/switchoutlet/dryer/index.htm

          8. User avater
            BillHartmann | Nov 07, 2006 01:05am | #55

            "Problem: The dryer is one year old. It is made for only a three prong - three wire dryer cord."Don't believe that.Not if it is a UL approved appliance designed to be sold in the US.Look for a green screw. Or a stud with a ground symbol beside it.Is there anykind of wire or jump that is connected to the N terminal. It has to be removed.What is the brand and model number of the dryer?

          9. mrfixitusa | Nov 07, 2006 01:36am | #57

            Thank you for the excellent info !^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          10. splintergroupie | Nov 07, 2006 01:54am | #60

            I only google the stuff. The people who make the effort to put it on the Net...those folks deserve a round of applause!Happiness is a warm dryer. I've been laundering madly today, running the dryer into living space to get the humidity high enough that stroking the pets doesn't land us all in the ER. I'm also starting to suspect they put an addictive substance in Bounce dryer sheets...stuff's like catnip...

          11. mrfixitusa | Nov 07, 2006 05:22pm | #61

            I went to the website you provided and found the instructions for installing a four wire cord.The brass grounding strap (used for three wire cords) was removed easily and the four wire cord has been installed per the manufacturers instructions.Thanks again to everyone.^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          12. mrfixitusa | Nov 07, 2006 06:06pm | #62

            The next step in my project is installing two walls and a door to enclose the washer and dryer and put them in their own little "closet"The width of the closet will be about 6'6" so there's plenty of room as the washer and dryer width are only 5'.There will be room on one end (about 14" to 16") for vacuum cleaner, brooms, storage, etc. I will install a 6 ft sliding door.My question concerns the depth of the closet.I went to a friend's home yesterday and measured her closet. The inside dimensions were 40" for the DEPTH. Her home was built in the late 1980'sThrough careful planning and design I have been able to keep both the washer and dryer very close to the wall.I set the washer and dryer in place and they are only 2" or 3" from the wall due to my expertise and careful planning.The dryer will exhaust straight out the wall (exterior wall).This means I can make my closet only 30" or 31" deep and save valuable space in this kitchen. Are there any formal objections from anyone if I make the depth of the closet only 30" ?Tahnks for any input.^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          13. mrfixitusa | Nov 16, 2006 06:59pm | #63

            Job has been finished and just wanted to pass along some info to anyone who's interested.I moved a washer and dryer from a basement to a kitchen. In this particular house the kitchen has a crawl space under it. The home was built in 1976I removed a six foot sliding patio door and closed in the opening and then placed the washer and dryer in this area in the kitchen.I built a closet to put the washer and dryer in.I worked by myself and the job took about 100 hours and the cost of the materials was about %1,000.I ended up putting some unusual doors which were purchased at HD.The doors are heavy six foot sliding interior doors. They have a dark wood frame and the panel is frosted glass.^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          14. DanH | Nov 07, 2006 01:35am | #56

            See Mistress Splinter's reference. Remove the jumper between neutral and ground and route the ground wire to ground.

            People never lie so much as before an election, during a war, or after a hunt. --Otto von Bismarck

          15. mrfixitusa | Nov 07, 2006 01:38am | #58

            It is a GE dryer purchased one year ago for $229 at Sams Club.

            Model Number DX2300EE1WW

            Serial Number SH780902A

             

            Thanks!^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          16. User avater
            BillHartmann | Nov 07, 2006 01:52am | #59

            http://www.geappliances.com/You can do a search for Use and Care Manuals for that model number.
            They don't allow direct links.But since I already downloaded it I up upload the installation instructions. It shows you where the connection is and the strap to remove.

          17. Piffin | Oct 31, 2006 03:06am | #12

            I see why your screen name is fix it! You get you advice in the aisles of HD from questionable 'electricians' who don't worry about doing it to code? That guy is a hack who ought to have his license taaken away if he has onework like that will need somebody to fix it 

             

            Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

          18. mrfixitusa | Oct 31, 2006 03:28am | #13

            Thanks everyone ! I'll try to check codes next time before asking any silly questions !^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          19. DoRight | Oct 31, 2006 06:59pm | #24

            Let that be a lesson to you!  If you need or want a beating this is the place.  No question goes unpunished.  You need a thick skin here.  Other than that, it is a great place and you typcially get great help along this your bruise backside.  LOL!

          20. mrfixitusa | Oct 31, 2006 07:13pm | #25

            Lol, I love this place.^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          21. User avater
            BillHartmann | Oct 31, 2006 03:53am | #14

            "I talked to an electrician while at home depot and he said he used 10-2 for "old work"He said he used 10-3 for "new work" and for anything that had to be "up to code"He was buying 10-2 for a dryer while I was there. He said he has done many this way.I'm going with the 10-3 and the new plug and new cord"ACtually 10-2 is not legal for "old work".Here is what the code say in allow a 3 wire connection instead of 4 wire."The grounded conductor (aka the neutral) is INSULATED, or the counted conductor is uninsulated and part of a Type SE service entrance cable and the branch circuit originates at the serivce entrance."I but he was buying 10-2 NM (Romex) which has 2 insulated wires and a bare equipment ground conductor (aka "the ground") and not SE cable.What the code is saying is that you can use the neutral conductor to also ground the metal case in older dryer/stove installations.But you can NOT use the ground as the neutral.Edited 10/30/2006 8:55 pm by BillHartmann to add NOT.

            Edited 11/1/2006 9:40 am by BillHartmann

          22. mrfixitusa | Oct 31, 2006 04:45am | #15

            Thank you for the excellent info. ^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          23. User avater
            ToolFreakBlue | Oct 31, 2006 03:38pm | #16

            "What the code is saying is that you can use the neutral conductor to also ground the metal case in older dryer/stove installations."

            Good info Bill.

            Is it know at what point does an "older" installation become "new"? (other than 1996 or 1997 or whenever the 4 wire installation became code)

            Does that mean you could replace the outlet you can keep the 10-2 w ground?  What if you just shortened the run by moving the outlet to a wall closer to the panel, would it still be older work or new work?  

            Just curious.

             TFB (Bill)

          24. DanH | Oct 31, 2006 04:41pm | #17

            Basically an "older" installation becomes "new" when you install new wire.Or look at it this way: When pulling new wire for a dryer or range, why would you not use 3+ground, which is safe, vs 2+ground, which is unsafe?

            Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi

          25. DanH | Oct 31, 2006 04:43pm | #18

            Do not replace the 3-pin outlet with a 4-pin (without replacing the wire). That creates a false sense of security. Replace the pigtail if you must. (If you install a 3-pin pigtail on a unit that previously had a 4-pin pigtail, you must add a bonding jumper between the ground and neutral terminals.)
            Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi

          26. DanH | Oct 31, 2006 04:43pm | #19

            Four wires has been the standard since about 1980.
            Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi

          27. User avater
            BillHartmann | Oct 31, 2006 04:57pm | #20

            "Four wires has been the standard since about 1980."See my reply.

          28. mrfixitusa | Oct 31, 2006 05:10pm | #21

            I don't recommend this and I won't be doing it on my current project,
            but I have seen a free standing range-oven wired directly. In other words there was no cord and outlet - just the heavy wire coming up through the floor and connected to the oven with enough slack that you could slide the oven out to behind it.^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          29. User avater
            BillHartmann | Oct 31, 2006 05:30pm | #22

            I tried to word my reply so that it did not get into trying to define what is "old work" and what is "new work".What work you are allowed to do on an existing 3 wire installation would be upto the local inspector. Assuming that it does not have a bias on way or another it would probably be based on the difficulty of changing it.Replacing a receptacle "should" be OK (but see below*). And I would vote for allow moving it where you don't need to extend the cable.The NEC did not require the 4-wire installation until the 96 revision. But I believe that many local amendments did.Here are comments from the 2005 NEC Handbook (it is the code, plus additional comments and background)."Prior to the 1996 Code, use of the grounded circuit
            conductor as a grounding conductor was permitted for all installations. In many instances, the wiring method was
            service-entrance cable with an uninsulated neutral conductor covered by the cable jacket. Where Type SE cable was used
            to supply ranges and dryers, the branch circuit was required to originate at the service equipment to avoid neutral current
            from downstream panelboards on metal objects, such as pipes or ducts."*"In addition, a revision in this provision for the 2005 Code permits application of the exception only where the existing branch-circuit wiring method does not provide an equipment grounding conductor. There are many shall existing branch circuits in which nonmetallic sheath cable with three insulated circuit conductors and a bare equipment grounding conductor was used to supply a range or clothes
            dryer. The bare equipment grounding conductor was simply where an equipment grounding conductor is not present in not used because it was permitted to ground the equipment with the insulated neutral conductor of the NM cable. This "extra" conductor was on account of the fact that the bare conductor in a Type NM cable is to be used only as an circuit for these appliances shall be permitted to be grounded (neutral) conductor in the same manner mitted for an uninsulated conductor in the service entrance."

          30. mrfixitusa | Oct 31, 2006 06:27pm | #23

            Is the reason for using 10-3 rather than 10-2 based upon reducing shock hazard as the result of touching the metal dryer?^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          31. User avater
            BillHartmann | Oct 31, 2006 07:14pm | #26

            The whole concept, as developed over the years, is that you should have an EGC that does not normally carry current. Thus any equipment connected to or bonded to the egc is at the same potential.That is the reason that 4 wire is required for a sub-panel.With that kind of system then there will be no voltage difference between say the refigerator and the kitchen faucets.Now for some reasons of history (some say to save copper during WWII, but I am not sure of that) stoves and dryers where allowed to use only 3 wires. And in a 3 wire system the metal case of the equipment was bonded to the neutral.Now the neutral is a current carrying conductor and thus will have voltage drop and thus soem difference between it and other grounded equipment.However, the amount of neutral current is realatively small compared with the hots so the voltage drops will be miniumum. Also for something like a stove or dryer once installed properly the failure of the neutral connection is rare. But a failure of the neutral will put the case at 120 volts.But going to a 4-wire system eliminates even those small voltge differences and gets an independent system to ground the case even with a failure in the neutral system.

          32. DanH | Oct 31, 2006 08:24pm | #28

            To add to that, as a teen I remember getting shocks off of our electric range (3-pin plug). I investigated and found that the neutral/ground prong was not making very good connection. Normally this was not a problem, as everything in the range, including the timer, used 240V, so there was no neutral current.However, there was a "convenience outlet" on the stove (I don't even know if these are allowed anymore), and the toaster was plugged into that. Strangely the toaster wasn't working very well (because the neutral connection of the outlet was just tied to the range frame, and the entire range was at 120V, more or less, when the toaster was turned on).I removed the plug and spread the neutral pin a bit, fixing the problem, but it made me aware of the hazard and I've not been happy with the 3-pin range/dryer plugs (or range convenience outlets) since then.
            Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi

          33. mrfixitusa | Oct 31, 2006 08:49pm | #29

            Thanks for the excellent info. 

             ^^^^^^

             

            S N A F U (Situation Normal: All Fouled Up)

          34. User avater
            BillHartmann | Oct 31, 2006 08:58pm | #31

            "To add to that, as a teen I remember getting shocks off of our electric range (3-pin plug). I investigated and found that the neutral/ground prong was not making very good connection. Normally this was not a problem, as everything in the range, including the timer, used 240V, so there was no neutral current."Strange that the timer was 240.But are you sure that all of the buners where 240.But older stoves used burners with several segments (2 or 3?) along with a 5 or 7 position switch. It switched in different elements and in series and parallel and between 120 & 240.http://www.tpub.com/content/construction/14026/css/14026_215.htmI don't know when the infinit heat controls where started.When we moved we got a new GE stove with dual ovens (40"). One of the burners was constant tempature with a capulary tube on a springloaded button in the center of the burner. And a sliding tempature control. The other 3 burners had push button selectors for different power levels. I think that was 57.That control went out several times. The last time I replaced it they no longer made the consant temp system and the replacement was an infinit heat control. I am guessing mid 60's.

          35. DanH | Oct 31, 2006 09:56pm | #33

            Pretty sure (though my memory is of course suspect after about 40 years). I had the thing apart and recall being surprised that there was no connection to the neutral for other than the convenience outlet.
            Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi

          36. User avater
            ToolFreakBlue | Oct 31, 2006 07:58pm | #27

            Thanks Bill, Great information as usual.

             TFB (Bill)

          37. Stuart | Oct 31, 2006 08:52pm | #30

            "The NEC did not require the 4-wire installation until the 96 revision. But I believe that many local amendments did."

            Not to get too far off topic, but the other day I got a flyer here at the office from an electrical equipment distributor that has a map of the US showing which version of the NEC is used in which states.  Most of the country is using the 2005 revision, but there are still some states on the 2002 revision or even earlier - the map indicates that some parts of Hawaii are still using the 1993 revision!

          38. User avater
            BillHartmann | Oct 31, 2006 09:01pm | #32

            One small city in the Chicago area is using 1990, but it has the typical Chicago mods that require conduit. But other things like GFCI's are still at the 1990 level.And one near me has more current version. But they modified it to only require kitchen GFCI's next to the sink, I think that 1996 wording.

          39. tab1 | Nov 01, 2006 04:37pm | #37

            Bill,I thought I understood this thread until getting to your last line here:<I but he was buying 10-2 NM (Romex) which has 2 insulated wires and a bare equipment ground conductor (aka "the ground") and not SE cable.What the code is saying is that you can use the neutral conductor to also ground the metal case in older dryer/stove installations.But you can use the ground as the neutral.>Your saying, in that case, the 10-2 w/Gr Romex could be used for the dryer, with the ground wire as the neutral?Thanks.

          40. User avater
            BillHartmann | Nov 01, 2006 04:42pm | #38

            Sorry, I went back and edit it.A case of my mind "working" faster than I can type.It should read "But you can NOT use the ground as the neutral".

          41. tab1 | Nov 01, 2006 04:52pm | #39

            Thanks, makes sense.I've got a similar situation to the OP. Lots of extra 10-2 w/G around. Any reason I can't just run a single insulated #10, along with the 10-2? Would it need to be in conduit?Thanks.

          42. User avater
            BillHartmann | Nov 01, 2006 05:12pm | #40

            All wires for a circuit are to be in a single cable or raceway (conduit).Not sure how the an inspector would treat runing a cable and separate wire in a conduit.

          43. BryanSayer | Nov 01, 2006 05:16pm | #41

            If you are going to do conduit, strip the cables out of the sheath. There might be a question of how much is packed into the conduit and/or heat build up if you include the sheathing. And the inspector probably won't have a way to determine if it is ok or not. Easier to just remove them.

          44. User avater
            BillHartmann | Nov 01, 2006 05:42pm | #42

            Well that it technically incorrect also.First there is no problem with heat built up with cable in conduit. But it is a common misconception. Thus I would not be surprised to see an inspector question it.The real problem is that the conduit has to be sized as through the NM was single wire the diameter of the largest axis of the cable.But the wires in the cable are not marked for individual usage. Only the cable is marked.

          45. BryanSayer | Nov 01, 2006 11:58pm | #45

            That's interesting. Is wire mold treated differently than conduit, since you can (at least could) run romex to a junction point and then strip the sheathing away to run the individual conductors in the wire mold?

          46. User avater
            BillHartmann | Nov 02, 2006 12:11am | #46

            I think that the whole question gets down to the UL listing on each product and then it is up to inspect interpretations of "workmanship" and "following manufactures instructions".With Romex that is END is stripped and the wires runs several feet in wiremold you can still go back to the romex sheating and see the markings.But if you just have several wires that where stripped out of "nowhere" there is no way to show what the insulation, tempature rating, UL listing is.But in most cases no one will ever question it.

          47. BryanSayer | Nov 02, 2006 12:33am | #48

            I was figuring that, if you stuff the romex in the conduit, there is less air space to dissipate the heat, hence you would need larger conduit to be able to maintain the same heat level.But the labeling issue makes sense, though I hadn't thought of the individual conductors not being labeled. Seems like they should be.

          48. Dave45 | Nov 02, 2006 12:32am | #47

            I talked to an electrician while at home depot ..............

            Was this electrician wearing an orange apron? (giggle, snort, choke, gasp, wheeze, lmao)

  3. DanH | Oct 31, 2006 02:10am | #7

    If you run new cable, it should be 3 wires plus ground. Put a new 4-ping "pigtail" on the dryer. For existing wiring, the 3-pin plug is "grandfathered".

    Seven blunders of the world that lead to violence: wealth without work, pleasure without conscience, knowledge without character, commerce without morality, science without humanity, worship without sacrifice, politics without principle. --Mahatma Gandhi
  4. a92588 | Nov 01, 2006 02:07am | #34

    use that new 8-5 wire. you cant go wrong. its pink colored just remember to keep the exhaust short and clean

    1. User avater
      MarkH | Nov 01, 2006 03:00am | #35

      I like the stainless braided wire, with the anodized connectors.

      1. mrfixitusa | Nov 01, 2006 03:13am | #36

        Never heard of it. Sounds expensive^^^^^^

         

        S N A F U (Situation Normal: All Fouled Up)

  5. User avater
    IBEWChuck | Nov 01, 2006 11:38pm | #43

    I just gotta ask, where is your "area"?

    HINT: fill in your profile.

    I am amazed that four wire devices won't pass inspection, any where in the US.

  6. User avater
    BillHartmann | Nov 01, 2006 11:39pm | #44

    "In a lot of areas (like mine), 3 prong plugs are required, with a separate external ground that is hardwired to the chassis and a good ground."

    I want to know EXACTLY what area that is that has a such a modifications to the code.

    Certainly it is not a LOT of areas.

    "The argument for this arrangement is that the dryer is grounded even when the plug is not in the receptacle. "

    That is the most idiotic things that I have every heard of.

    Who cares if it grounded when it is not plugged in.

    I was at Sears last week and they had 50 dryers all lined up. And they WHERE GROUNDED. Of courese they where plugged in either.

    And I wented to Lowes and I saw hundreds and hundreds of the metal boxes that where grounded. And load centers that where grounded, and water heaters that weren't grounded. But of course there was not thing connected to them. But based on your "LOGIC" they should have a separate ground.

    If this scheme of not using the ground on a receptacle, but rather running a separate ground wire is go great then the inspectors must require it on all equipment. Cut the ground pin off the refigerator, dishwasehr, clothes washer, etc and then run a separate ground wire.

    And I want to know where this "good ground" is that you are running the dryer to?

  7. User avater
    BillHartmann | Nov 02, 2006 01:11am | #49

    "It's not a modification to the code at all, just an interpretation of NEC with a bit of "local flavor"."

    The only local "flavor" must be in the moonshine that the inspector is drinking.

    That is nothing in the code that allows anything like you claim.

    "It's actually pretty common in the midwest."

    Well "midwest" is not a very specific location. There are several states in the Midwest.

    One of which is IL.

    The code in varies to Chiago, which as I understand it is there completley own code.

    One of the village in the Chicago are use 1990 NEC, with mods to require conduit for most wiring to outstate areas that has no codes at all.

    "Didn't you ever wonder why when you buy a dryer, the pigtail is sold separately, while when you buy other appliances, the cord comes with it?"

    No I did not know that at all.

    It is very simple. The NEC allows 3 wire connections for existing installations that have appropriate 3 wire branch circuits.

    And requires 4 wire connects for new branch circuits or existing 4 wire branch circuits.

    1. mrfixitusa | Nov 02, 2006 06:06am | #50

      Would it work to use the 10-2 your have to add extra circuit and outlets in your house? Seems like with older houses they all need more circuits. Especially in the kitchen.My son has electric guitars, amplifiers, huge speakers, etc etc and when their band practices they have three guitars and a drummer. I think they are pulling a lot of juice.My son thinks his equipment for his guitar alone is 7-8 amps.I may need to run heavy circuit and use 10-2 wire for all their music equipment.^^^^^^

       

      S N A F U (Situation Normal: All Fouled Up)

      1. tab1 | Nov 02, 2006 06:21am | #51

        It would work if I needed other circuits. Just don't, at least at the moment. <g>

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Mortar for Old Masonry

Old masonry may look tough, but the wrong mortar can destroy it—here's how to choose the right mix for lasting repairs.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels
  • FHB Podcast Segment: Hand Tool Sharpening Tips
  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data