125 Amp Sub Panel
jimhanley | Posted in General Discussion on January 27, 2013 11:29am
I am a finish carpenter who builds furniture in his spare time. After many years I am building my own shop just off the main house. I am installing a 125 amp sub panel and need to make sure I use the correct wire size, conduit size, and junction box. This will all be done in copper. The junction box is because I am feeding a second sub panel of the main. Thanks to all in advance.
  1. gfretwell | Jan 27, 2013 12:38pm | #1
    The 125a sub panel should be using three 1 gauge copper conductors with a 6 gauge grounding conductor (4 wires total)
    Some AHJs might let you get away with #2 since 115 is not a standard size breaker.
    I would run this in 2" PVC to make it an easy pull. You can squeeze it in 1.5" but if you are going very far you might have quite a tug.
    Use a pretty good size junction box if this is going to have another big feeder in it. A 6x6 Carlon box is a reasonable fit because it gives you enough room to handle the #1s but bigger may be better.