2 ply header good enough?

alrightythen | Posted in General Discussion on April 12, 2006 07:12am

20’x12′ addition. with bearing 2×6 rafters 4/12 pitch on the 20′ exterior 2×4 wall. window openning is 96″ wide.

Lintel : double 2×10 sound adequate?

can’t make head nor tails of the span tables in code book. anyone know of a span calculator online for headers. Or know if the 2 ply 2×10 will fly.

seams to me last time I did a window that wide I was using a 3 ply. But it could have been 3 ply 2×8..I can’t remember. I know I’ve done big windows with P lams and strandboard before. But guy I’m doing this with was going to go with the 2 x10

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. philarenewal | Apr 12, 2006 08:05am | #1

    What shows on the plans?  ;-)

    But seriously, OK, here's what I think you got -- header under roof and ceiling load with the building width being 20' or less.  For code where i am . . . doubled 2x10 will serve as a header (need two jacks at each end) for a 8'5" span with a snow load of 30 psf or less.  If it snows where you are, this may not work for you.

    Tripled 2x10 (with two jacks at each end) will make it if the snow load hits 50 psf.  More snow load than that, at least where I am you need the engineer.

     

     

    "Let's get crack-a-lackin"  --- Adam Carolla



    Edited 4/12/2006 1:07 am ET by philarenewal

    1. alrightythen | Apr 12, 2006 08:31am | #2

      yeah..I'll have to check the plan more closely....

      cept as you may have guessed..there is no plan. 

      yeah ...for sure the double jacks 

      1. User avater
        RRooster | Apr 12, 2006 09:06am | #3

        In no snow country, my inspector once said, "....an inch of header for every foot of span.......rule of thumb....." 

        Grunge on.

        1. philarenewal | Apr 12, 2006 09:22am | #4

          I like your inspector.  Practical rules that worked for decades are now suddenly horrendously dangerous.  What happened?  Trees -- guess they don't make 'em like they used to.  ;-) 

          "Let's get crack-a-lackin"  --- Adam Carolla

          1. DanH | Apr 12, 2006 06:14pm | #14

            It's inches they don't make like they used to.
            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          2. philarenewal | Apr 12, 2006 06:35pm | #16

            >>It's inches they don't make like they used to.

            Good point.

            Reminds me of a rehab I'm working on.  Young archy specs new 2x12 hem fir (what's common here) #1 or btr joists 16" OC (which would be oversizing anyway, span is 15'8").  More senior guy takes a look at the old existing 3x8s (that really are 3x8) and suggests they stay put.  Guess whose opinion I preferred, plus the older guy is the one actually stamping the plans.  ;-) 

            "Let's get crack-a-lackin"  --- Adam Carolla

          3. User avater
            RRooster | Apr 12, 2006 11:25pm | #24

            LOL

            LOFL

            LOL!!!!!!! 

            Grunge on.

        2. alrightythen | Apr 12, 2006 02:53pm | #9

          I never heard that rule of thumb before. interesting.....so would that mean 2ft or even 3 ft openning would hypothetically be ok with a 2 ply 2x4 as header.

          1. jimblodgett | Apr 12, 2006 04:54pm | #12

            There's a similar rule of thumb for floor joists - 6" span/2x6, 8' span/2x8, 10' span/2x10, etc,

            Of course, there's also an old saying "simple rules for simple fools", but I have always relyed on those beam and joist rules for common house work. Tipi, Tipi, Tipi!

            http://www.asmallwoodworkingcompany.com

        3. User avater
          jonblakemore | Apr 12, 2006 05:58pm | #13

          With all due respect, that rule of thumb is worthless at best and dangerous (possibly even criminal) at worst.As someone else said, does that mean a double 2x4 on edge can act as the header over a 42" window?Or if I need to span 12' in a basment of a house that is 32' wide with three habitable floors and rafters that are supported by a knee wall, can I use a double 2x12?I'm no PE, but I would dollars to donuts that the answer for both is a resounding NO. 

          Jon Blakemore RappahannockINC.com Fredericksburg, VA

          1. philarenewal | Apr 12, 2006 06:18pm | #15

            Hey Jon, I must have had way too much coffee this am, so I got to stir the pot.

            Double 2x4 will span 3'6" for roof and ceiling load on maximum 20' wide building with 30psf ground snow load (under IRC 2003).

            >>"Or if I need to span 12' in a basment of a house that is 32' wide with three habitable floors and rafters that are supported by a knee wall, can I use a double 2x12?

            Um, no.  You have a point.  Double 2x12 not even close.  In fact under IRC 2003 looks like you need the engineer for that one.  Ain't no ordinary wood that will hold.  For less than what you describe (two clear span floors instead of three), a quadruple 2x12 with three jacks at each end would span 6'0" with a 50psf ground snow load.

             

            "Let's get crack-a-lackin"  --- Adam Carolla

            Edited 4/12/2006 11:22 am ET by philarenewal

            Edited 4/12/2006 11:23 am ET by philarenewal

          2. User avater
            jonblakemore | Apr 12, 2006 09:47pm | #20

            Phil (or whoever you are),You're right, I made my statement too flippantly. See my post to Boss if you want the long explanation. 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          3. philarenewal | Apr 12, 2006 10:01pm | #21

            Not flippant at all.  You made your point.  Sometimes rule of thumb works, sometimes the place would actually tumble.  Makes one think about that.

            Besides, if you can't be flippant, what fun would it be?  ;-) 

            "Let's get crack-a-lackin"  --- Adam Carolla

          4. User avater
            BossHog | Apr 12, 2006 08:07pm | #18

            A rule of thumb isn't an absolute - It's just a starting point. Like if someone comes in here asking if an 11 7/8" LVL will span 20' carrying whatever, I pretty much no there's no chance it will work.If they ask what depth of a beam they need to span a 14' opening, I at least can give them an educated guess. But I would never SPECIFY a beam based on a rule of thumb.
            Did you know...Captain Hook died from jock itch.

          5. User avater
            jonblakemore | Apr 12, 2006 09:46pm | #19

            Boss,That's my point, if rules of thumb are just a good starting point, do they really have any benefit? I'm speaking especially to a "rule of thumb" that has absolutely no information about what loads will be carried.Maybe the guy who first brought the "one inch per one foot of span" rule lives in an area where all the homes are 24' wide ranch houses with no snow load. If that's the case, the rule of thumb is probably pretty decent.The problem arises (and I know you know this) when someone adds a clear span floor trusses and a second story on top of the header that meets the rule of thumb. Now you're grossly undersized.I myself often use the joist sizing rule of thumb, although I am a bit more liberal than JB. I multiply the nominal depth of the joist by 18 and figure that's about the max span allowed. A brief look at the 2003 IRC confirms that this is reasonable with 2x6 through 2x12 joists (#2 SPF, 16" o.co.; L/360, 40#LL & 10#DL).The main difference is that floor joists typically carry the same loading per square foot whereas any two headers in a given home could have a range of 300% (rough guess). 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          6. User avater
            BossHog | Apr 12, 2006 10:24pm | #23

            "That's my point, if rules of thumb are just a good starting point, do they really have any benefit?"

            Sems to me that scentence both asks and answers the question - They're a starting point, but ONLY a starting point.

            In the examples I gave, I said that rule of thumb could pretty much rule out a 12" deep LVL that spanning 20', for instance. The loading doesn't really matter - It just ain't gonna work.

            So I'd say the answer is definitely yes - There is some value in having a starting point.
            Change is inevitable, except from a vending machine.

          7. User avater
            CapnMac | Apr 13, 2006 12:06am | #25

            Maybe the guy who first brought the "one inch per one foot of span" rule lives in an area where all the homes are 24' wide ranch houses with no snow load

            Actually, it's a weird thing--for a material-less, solid, member, the moments & like correspond extremely well with 1" = 1' in span. 

            It's only when the material is significantly weaker, or stronger, for a given section that the rule gets caterwhumpus.  Which is why an engineered "wood" I spans farther than a solid timber of equal length--the strengths of the parts are stronger than cut lumber.  It's also why a high-strength steel section will span farther than a mild steel or iron beam of identical section.

            It gets complicated quick--that's the failing of rules-of-thumb.  Ok, stitch together 3 2xn--they will "act" like a 4x (mostly), but not like a 4.5" wide solid the same depth.  (Making up the length out of big-box rejects 6-8' long won't help any, either.) 

            This is the trouble with putting span tables into code, too.  The code writer has to "beat" the worst case scenario for their jurisdiction (which could be a fly-by-nighter parting together old apple crates and calling it framing).  The code writers also have a lot of impetus to write "inspectable" code, too.  "Ok, structural header from l to m; has to be at least n of z x at least q deep--done."  Trying to remember if a #1 Hemlock 4 x 8 is "equivalent" tends to get pushed to the side.Occupational hazard of my occupation not being around (sorry Bubba)

          8. Piffin | Apr 13, 2006 12:59am | #28

            " if rules of thumb are just a good starting point, do they really have any benefit?"sure do! A carp with no engineering training who is given a set of plans to build or estimate from should first review it to to see how buildable it is. A fourth to a third of what I've been handed has gone right back withion a day for redesign or confirmation of engineering because I had abasis from which to begin - a reference point to know where something looks rediculous. 

             

            Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

        4. GHR | Apr 12, 2006 07:38pm | #17

          RRooster ---I like your rule of thumb. It is reasonable. It is based on engineering.As I recall the deflection ratio equation looks something like:w/L = constant * L^3/h^3 (H is the beam height, L is the beam length)At least the scaling for the rule is proper.I might differ with you about the proper constant.

        5. JohnSprung | Apr 12, 2006 10:23pm | #22

          > In no snow country, my inspector once said, "....an inch of header for every foot of span.......rule of thumb....."

          I've heard that same rule of thumb, with the proviso that it's for a single story building, or the top floor, and spans up to 12 ft.

          Of course that ain't gonna fly in the sub sub basement of the Empire State Building. 

          What can go very wrong with that kind of rule of thumb is forgetting its limits.  

           

          -- J.S.

           

          1. User avater
            CapnMac | Apr 13, 2006 12:11am | #26

            Of course that ain't gonna fly in the sub sub basement of the Empire State Building.

            Sure it does, we are just missing the variable of width, once we presume a span and depth.

             Occupational hazard of my occupation not being around (sorry Bubba)

  2. Piffin | Apr 12, 2006 10:51am | #5

    You don't say what your snow load requirements are or long long the rafters are

     

     

    Welcome to the
    Taunton University of
    Knowledge FHB Campus at Breaktime.
     where ...
    Excellence is its own reward!

    1. alrightythen | Apr 12, 2006 02:36pm | #7

      we deal with rain where I live. and rafters will be about 18' with truss design web at back bearing wall, which is at 12'. This will well exceed the 2x4 rafter design that has held up actually exceedingly well for past 40 or so years.

      Edited 4/12/2006 7:43 am ET by alrightythen

    2. philarenewal | Apr 12, 2006 04:44pm | #11

      Hey Piffin, just curious.  What difference does it make how long the rafters are?

      "Let's get crack-a-lackin"  --- Adam Carolla

      Edited 4/12/2006 9:47 am ET by philarenewal

      Edited 4/12/2006 11:22 am ET by philarenewal

      1. Piffin | Apr 13, 2006 12:52am | #27

        Well now, say with a ten foot wide window frame, and rafters that are tenn feet long. the load would be for fifty square feet, assumiong a bearing ridge beam or center load bearing wall.But if the rafters are spanning twenty feet over that ten foot window frame, the loading is based on a hundred square feet.In a typical 15# dead load and 40# live load area, 55#/sf for an extra fifty feet is an extra ton and a half of load the header has to bear - about the size of a pretty good sized automobile or a pallet of shingles delivered by boom right onto that spot of the window.That rule of thumb somebody mentioned is a good one - only in moderate snmow areas and when there is no second floor loading also added to the header 

         

        Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

        1. philarenewal | Apr 13, 2006 01:09am | #29

          Ah, I got you now.  Of course.

          The tables I use take building width into account to cover that.  Leads to a lot of oversizing, but at least takes it into account. 

          "Let's get crack-a-lackin"  --- Adam Carolla

  3. User avater
    Matt | Apr 12, 2006 12:26pm | #6

    We use a flavor of the IRC 2000 and the header span table is in the floor chapter. 

    BTW - is this header on the gable end or not? - sounds like not...

    1. alrightythen | Apr 12, 2006 02:48pm | #8

      you are right. If it was gable end I wouldn't be asking.

      1. User avater
        BossHog | Apr 12, 2006 02:57pm | #10

        No way to answer without knowing the loading requirements in your area.
        Usually I would just take off all my clothes and go "whoops, I forgot to draw the curtains". [Caprice Bourret]

        1. alrightythen | Apr 13, 2006 02:52am | #30

          40.0 Live and 15.0 Dead

          1. jimblodgett | Apr 13, 2006 04:47pm | #31

            I was thinking yesterday about the compressive strength of a stud/plate/sheathed wall. There is a certain logic to the argument that header size is largely dependant on the load above it.

            On the other hand, certain sized headers will support as much loading as the wall they are in. So in a sense, as long as there is a positive load path, the wall framing  should be all the information we need to size a header, regardless of what's above it.

            In fact, isn't that the point?  That the header can carry at least an equal load as the wall it's in?

             

              

            Tipi, Tipi, Tipi!

            http://www.asmallwoodworkingcompany.com

            Edited 4/13/2006 9:48 am ET by jimblodgett

          2. User avater
            BossHog | Apr 13, 2006 05:48pm | #32

            I don't see any logic to that at all...
            White people ought to understand, their job is to give people the blues, not to get them. [George Carlin, You Are All Diseased]

          3. DanH | Apr 13, 2006 05:54pm | #33

            It's like you and a friend being chased by a bear.
            If Tyranny and Oppression come to this land, it will be in the guise of fighting a foreign enemy. --James Madison

          4. jimblodgett | Apr 13, 2006 06:21pm | #35

             

            "I don't see any logic to that at all..."

            You don't see any logic to what, Boss?Tipi, Tipi, Tipi!

            http://www.asmallwoodworkingcompany.com

          5. philarenewal | Apr 13, 2006 05:55pm | #34

            In fact, isn't that the point?  That the header can carry at least an equal load as the wall it's in?

            I think I get at what you are saying.  If the header can carry as much as the wall it is in, then by necessity it can carry the load above. 

            Trouble there is it could lead to grossly oversized headers unless the wall was actually carrying its rated load, for very large buildings or very wide openings.

            Where I am a typical 2x4 16" OC stud wall is allowed to carry one clear span floor plus a roof and ceiling (a typical two story building).  The headers on the first floor likewise have to support the same loads.  What's a little wacky is there doesn't seem to be a limit on the width of the floor so theoretically the load on the wall could vary wildly.  I guess the safety factors in wall framing are so high they don't care. 

            For headers, it's different.  The tables (at least where I am) do take into account building width.  A Piffin pointed out, the wider the building, the higher the load on the wall and header.  If we sized all first floor headers for the maximum building width allowable for headers (where I am 36'), the headers would be oversized for narrower buildings.

            The headers on the second floor could be oversized, if sized to support the same load the wall is capable of supporting.  No clear span floor to support.

            OTOH, as a practical matter, maybe it makes no difference as you suggest for most of the headers.  Lets say all window RO in a typical two story building are 3'0".  We size for the widest building allowed (36'0" -- that's what the wall can definitely support).  The headers for the first floor would need to be two 2x6 with two jacks at each end.  The headers for the second floor would need to be two 2x6 with two jacks at each end.  You've convinced me.  ;-)

             

            "Let's get crack-a-lackin"  --- Adam Carolla

            Edited 4/13/2006 11:08 am ET by philarenewal

          6. jimblodgett | Apr 13, 2006 06:27pm | #36

            "If the header can carry as much as the wall it is in, then by necessity it can carry the load above."

            Yeah, that's exactly what I'm asking.

            "Trouble there is it could lead to grossly oversized headers"

            Yeah, in some cases, but when we frame multi storey buildings we increase the compressive strength of the framing on the lower floors, right?  So the header would then be sized to carry the load of THAT wall.

            It's also totally possible that we way overbuild as a common practice and down size our headers to save lumber, I don't know. But I think there's something to this, in a "rule of thumb" kind of way. At least it is interesting to think about.Tipi, Tipi, Tipi!

            http://www.asmallwoodworkingcompany.com

          7. philarenewal | Apr 13, 2006 07:30pm | #37

            I see where you are going.

            The sizing tables are already a digest version of the underlying engineering which leads to oversizing in most cases, but saves a lot of time and aggravation.

            Ther is no reason to not digest the sizing tables even further, if you don't mind more oversizing (which I don't think is a real problem 'cause lets face it, except for tract builders, keeping track of an assortment of different headers can be more time and trouble than just sizing them alike, even if that does oversize them most of the time).

            Here's a first go at it.  All headers are doubled 2x's.  Typical two story single family residential building, with bearing exterior walls framed 2x4, 16" OC.  Maximum building width is 28'; maximum ground snow load is 50 psf.

            2x4 will span 2'3".

            2x6 with double jacks will span 3'4"

            2x8 with double jacks will span 4'2"

            2x10 with double jacks will span 5'1"

            2x12 with triple jacks will span 5'11"

            Except for the 2x12, it would work (under the limiting conditions described) if you said always double the jacks and span in feet is half the depth in inches (up to 5' opening).  Could you live with that?

            To really boil it down, make all headers doubled 2x10 on double jacks for up to a 5' opening (again assuming 28' max bldg. width, 50psf max snow).

             

            "Let's get crack-a-lackin"  --- Adam Carolla

            Edited 4/13/2006 12:36 pm ET by philarenewal

            Edited 4/13/2006 12:42 pm ET by philarenewal

            Edited 4/13/2006 12:44 pm ET by philarenewal

          8. JohnSprung | Apr 13, 2006 10:06pm | #38

            > The sizing tables are already a digest version of the underlying engineering which leads to oversizing in most cases, but saves a lot of time and aggravation.

            And so does the rule of thumb.  Consider that this one is good for a maximum span of 12 ft.  Take the price of two 2x12 by 12 ft., subtract from that the price of two 2x10 by 12 ft.  At $150/hour, how much of an engineer's time can you get for that?  Probably not enough to solve the problem, and even if you do engineer it, there's no guarantee that the answer will be the cheaper header. 

             

            -- J.S.

             

          9. alrightythen | Apr 13, 2006 10:20pm | #39

            Do you really use double jacks on all your openings? that is 2 jacks plus your king studs making a three ply? I didn't realize doubling the jacks on most stuff under 6' was something necessary or desired.

            Maybe I am missing something that you were trying to point out. a lot of basic header situations, it is the deflection we are dealing with and not so much the actual bearing. So having 3 plys for most small header situations seems a waste to me.

            *footnote... I checked with the in house engineer at my local lumber yard to see about getting the beam sized. Got a beam schedule indicating the use of  3 1/2" x 9 1/2" timber strand. with bearing of 1 1/2" at either end. My buddy whom I'm doing the job with wants to go with 2x 12" if 2 x 10" isn't good enough. Now I don't know if the lumber yard is trying "push" the more expensive TJI product. But for $37 more bucks than 2x 12" I told my buddy to go with the timberstrand ... .in the end he still gets the better product.

            and by the way....in spite of the schedule I will be doubling the jacks.

            Edited 4/13/2006 3:23 pm ET by alrightythen

          10. philarenewal | Apr 13, 2006 10:29pm | #40

            >>"Do you really use double jacks on all your oppenings?

            No.  What I was getting at is an interesting idea that Jim suggested maybe it would be possible to boil down a header size that is as strong as the wall it is in.  So, if you got a 2x4 stud wall, use X as a header and go.

            It kinda works.  Very interesting idea.

            Anyway, I'd definitely go with what your lumberyard engineered.  They know your snow loads and I assume exactly what you've got going on in your building.  Double jacks won't hurt anything for sure.  IIRC, you don't get much snow.  Must be coastal BC.

            My better half is from Nova Scotia.  Her folks are still in I think it's near St. John or anyway not too far from Frederickton.  They get SNOW.

             

            "Let's get crack-a-lackin"  --- Adam Carolla

            Edited 4/13/2006 3:37 pm ET by philarenewal

          11. alrightythen | Apr 13, 2006 11:14pm | #41

            yup, lowermainland/Fraser Valley plenty of rain. We got lots of mountains around us that get snow ( actually ... even the local slopes seem to be getting less and less snow)

            anyway....ok what do you think then about the 16" oc vs 24" oc framing then. It seems FHB likes to run these articles that push for 24" oc framing and I think there are a lot of supporters for it as well. ( the 'more insulation' issue gets brought up.) personally I still prefer 16"oc 2x6 construction. 

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data