220 V question

MGMaxwell | Posted in General Discussion on June 28, 2009 08:57am

My pump motor is wired for 220 [done by previous owner] with 12 gauge 2 wire i.e. black/white/green. The black and white are both hot and there is no neutral.

I would like to wire a nearby receptacle for 110. I can use one hot leg and the ground, but where/what do I use for a neutral?

Thanks.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. renosteinke | Jun 28, 2009 09:02pm | #1

    You're screwed. Run the right cable and start over. You should also have that 120 receptacle on a separate breaker from the 240 circuit.

    Indeed, since you'll now have more than one circuit, other requirements may also apply. Hiring an electrician might be a good idea.

    1. MGMaxwell | Jun 28, 2009 09:30pm | #3

      Thanks for the rapid reply. Kind of what I thought. Luckily the panel is close by.I just had the electricians out here a few months ago to run power to my garage. Too bad I didn't pick up on this then.

      1. renosteinke | Jun 28, 2009 11:39pm | #8

        As there seems to be a bit of confusion, let me explain my answer a bit more.

        The NEC requires 'detached structures' with more than one branch circuit to have a ground rod. think "separate building = separate lightning target.'

        Clarified in the 2008 NEC, this ground rod does NOT remove the need for a ground wire connecting it all to the ground buss at the source ..... you are also still required to have a separate neutral wire, and to keep the neutrals and grounds separate from each other until you get back to where the power company disconnect is.

        This situation arises whether you get your 120 from the same breaker that feeds the 240 pump, or if you run a separate cable.

        That's why I always tell folks .... run big pipe; some day you might want more or bigger wires out there. Such planning saves you from digging a second time. As you might guess, such advice is almost always met with "but I'm only running a pump, and I'll never want anything else out there." Then the pump guy arrives, and needs 120 for his tools. Oh, well.

        The size of the feeder cable (the wire currently powering the pump) might not be an issue. It might have been possible to supply both the pump and the receptacle using that cable (the electrician does some load calcs to determine this) ... but you're still lacking that necessary neutral.

        Again, in my work there are time where I always run a neutral, even if I have no present need for one; this is one of those times.

        I recently had to deliver the same sort of bad news to a customer: he went to such great pains three years ago to do something in the absolute cheapest way possible - even cutting a few corners - that today even a minor change leads to major expense.

        While there might be some way to 'hillbilly' in something that 'works,' you're still left with an inadequate situation. You just postponing judgement day a bit.

        I do NOT aim this post at the OP personally ..... long time BT readers know just the sort of person I refer to. For them, I want to say 'no, you can't do it - and they can't help.'

        1. MGMaxwell | Jun 29, 2009 12:04am | #9

          Thanks to all that replied. When I had my garage powered up they had to replace my CB panel which is outdoors within three feet of my pump motor. Too bad then I didn't look ahead. I didn't try to do it on the cheap, I just didn't know any better and didn't anticipate what else I might need.If I had wanted to do it cheap I would have run NM under my trailer and only then buried it going to the garage.Off the original topic, I've put more into this 1985 single wide divorce trophy club house than its original worth. Front and back porch with Trex. New carpet throughout. New kitchen cabs and countertops. Total bathroom demo and remodel with cork floors and granite countertop vanity. My son says it's like putting a tuxedo on a pig, but I don't want to build another house with a mortgage that will last the rest of my life.

  2. john7g | Jun 28, 2009 09:16pm | #2

    not an electrician but I've done this a few times

    you need 3 conductors (2 hot, 1 neutral) and a ground run from the main panel to a sub-panel at the pump. Sub-panel should have it's own ground rod.  At the sub-panel install appropriately sized CBs to handle the pump and the 110v outlet you want to run.  receptacle ought to be GFCI. 

    1. JTC1 | Jun 28, 2009 09:42pm | #4

      Huh?

      You suggest:

      1) New heavier home run to main panel with new breaker.

      2) New sub-panel with breakers (possibly reuse old pump breaker in new sub panel, brand / listing issue)

      3) New ground rod (not needed if sub-panel is in the same building)

      4) New cable run from sub-panel to pump.

      5) New cable run from sub-panel to new outlet; requires a new breaker in the sub-panel.

      6) Possible GFCI protection for the new outlet.

       

      What he needs:

      1) New cable run from outlet to main panel; requires new breaker in main panel.

      2) Possible GFCI protection for new outlet.

       

      Why do / pay for steps #1 through #4?????

       

      Jim

       

       Never underestimate the value of a sharp pencil or good light.

      1. john7g | Jun 28, 2009 10:07pm | #5

        under the impression it's run out to a remote location. 

        didn't think about a separate new 110v feed. 

        1. JTC1 | Jun 29, 2009 12:12am | #10

          I suspect this is a submersible pump in the well.

          Hint was in the OP, "12 ga, black, white, green" the hint was the "green" rather than "bare".

          Sounds like that submersible pump wire (don't know the proper name).

          My assumption is a submersible well pump and that the outlet in question is in his basement.

          'Course we all know what they say about assuming..........

          OP does not suffer from TMI.

          JimNever underestimate the value of a sharp pencil or good light.

          1. john7g | Jun 29, 2009 12:27am | #11

            I was assuming (also) wellhouse like we use here where long frosts are not an issue (at least they weren't in the past) and he was looking for a way to add soemthing to add heat during the frosts.  The well house usually includes the pressure switch and pressure tank and a sediment filter.  Many cases original install is done as cheap as possible with only power feeding the pump and no sub panel and the desire to add heat later.  Come to think of it, it's been so long since I've been involved with the no-sub panel set-up I don't remember what they used for a service disconnect at the well head. 

            cheers

            john

  3. JTC1 | Jun 28, 2009 10:25pm | #6

    The pump is legally wired as it sits right now. No neutral is required for a pure 240v load --- if you were to run a cable with a neutral conductor to supply the pump motor, there would not be anywhere to connect it at the pump motor. 2 hots and a frame ground is all there is.

    You simply need to run a new 120v cable to the new outlet, a new single pole breaker will be required at the main panel.

    The new sub-panel, suggested by another poster, will work properly at a greatly increased expense over what you actually need.

    The sub-panel is a good solution only if you are out of space in the main panel and tandem or skinny breakers will not work in your main panel. If the sub-panel is in the same building as the main panel, no additional ground rods are required.

    If you are out of space in the main panel, I would tend to run a new sub-panel with 8 to 12 slots available rather than just a small panel to accommodate your present needs. Probably a 60 or 100 amp sub panel

    GFCI protection is required for the new outlet if it is outside or in a basement.

    Jim

    Never underestimate the value of a sharp pencil or good light.
  4. DanH | Jun 28, 2009 11:13pm | #7

    You don't.

    As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

An Easier Method for Mitered Head Casings

Making mitered head casings is a breeze with this simple system.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data