60A service entrance repair

OneofmanyBobs | Posted in Energy, Heating & Insulation on August 27, 2004 07:41am

Got a cabin out in the middle of nowhere.  No inspections necessary, but I still want things done reasonably to code.  It has 60 amp service.  A 2-pole disconnect with two screw-in fuses mounted outdoors.  All rusted badly.  Inside is the usual mess you don’t want to touch with gloves.  I’ll replace all that.  No problem there.  EMT conduit to avoid rodent problems.  Its very small.  2 rooms and no kitchen or bath. I want 4 circuits.  2 outlet, 2 lights.  No well, heat, stove or anything like that.

Phase one.  Replace all interior wiring.  Run it to the existing disconnect.  Drive a pair of ground rods and run the ground.  I can do all that.

Phase two.  Remove load wires from existing disconnect.  Mount new main panel.  Run new entrance wire to the meter.  Call the power company and have them connect the new entrance wire.

Questions:  Can I run to the meter in conduit?  Existing feed has physical damage from trees, animals, something.  About a 10 foot exposed run from meter to disconnect.  Metal or plastic? What do I use for a disconnect?  Box is totally exposed.  I can make an enclosure around it but would still like something weather tight.  Does this sound reasonable or really stupid?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    BillHartmann | Aug 27, 2004 10:17pm | #1

    The first thing is that I would check with the utility company.

    They will have specs and standard that must be met before they will connect. And they vary by company and parts of the company.

    The code requires a minimum of 100 amp service for "residential" now days. And I don't know what all they have available, but I suspect that 100 amp service is the smallest that they have meters for. So I would plan on that.

    You do not need a disconnect at the meter, it can be "near" where the service first comes inside the building. However, some locals do require disconnects at the meter. They are basically a single breaker pannel and you can get units that combine the meter case with the disconnect.

    If you use a disconnect that the meter then that becomes the "main pannel" where the neutral is bonded to the grounding electrode system. And then the "main pannel" becomes a sub-pannel with isolated neutral and ground bus bars.

    EMT, metallic, intermidate metallic, or PVC conduit can be used between the meter and the pannel.

  2. Stuart | Aug 27, 2004 11:07pm | #2

    Could you answer these questions? It'll help to visualize what you're doing.

    Where is the utility meter? Is it on the outside of the building, or on a nearby pole?

    Is the service to the building overhead, or underground?

    It sounds like your main fused disconnect is on the outside of the building, is the panel there as well, or is it inside?

    At least around here, generally the panelboard is inside the house and includes a main breaker so you don't need a separate disconnect. Some electric utilities require a disconnect on the outside so you have to check that, but the more you have inside the better for resistance to the weather.

    If you're not changing out the meter socket, the utility may well leave the service at 60 amps. If you get a new meter socket and have the utility bring in a new line from their end, the smallest new service they'll supply these days is most likely 100 amps; you can still have a 60 amp panel and main disconnect in the house if you so desire but you may as well go for 100 amps, it'll cost about the same.

    1. OneofmanyBobs | Aug 28, 2004 12:17am | #3

      The meter is on the corner of the building with overhead wires to the pole.  About a 10 foot exposed run to the disconnect.  The meter and socket are pretty new.  An LCD model.  Looks like a 100 amp socket to me.  The drop from the pole is in good condition.  The service entrance wire is 1/0 SER but the sheath is damaged.  Should be replaced.  Everything else dates to maybe 1930.  The utilility here does not require a separate disconnect.  It is very uncommon around here to see the main panel outdoors, but I'd rather keep things similar to what they are if that's possible.  The utility must have thought things looked good enough to connect.

      The fused disconnect IS the main panel.  Two circuits, one on each leg.  Has one 20 and one 30 in it.  No panel or anything inside.  A half dozen assorted pieces of old rusty ungrounded BX and cotton connect to the load side.  Bare wires everywhere inside.  Only one outlet for the whole cabin inside.   That will all go away.  It is classified as an out-building not a living space.  Doesn't need outlets every 6 feet, etc.  Just need 2 in the big room and one in the small room.  Could actually get by with 2 circuits, but would rather do 4. 

      Have not talked to the utility yet.  Do I need to put a 100A panel on 100A service?  Certainly doesn't need it.  A 40A sub is more than adequate but I don't know if I can use that as a main.  The disconnect is about 6 inches from the front door.  A regular 100A panel would look really big and ugly there.

      1. Stuart | Aug 28, 2004 02:01am | #4

        Okay, I get it.  Not much there now, is there?

        Here's a link to the Square D residential panel website.

        http://ecatalog.squared.com/pubs/Electrical%20Distribution/Load%20Centers/Homeline%20Single%20Phase%20Load%20Centers/1100HO9901.pdf

        Look down the page for the model #Q014-8L125GRB, I think it's the sort of thing you're looking for.  It's a small weatherproof panel, about 9 inches wide by 15 inches tall by 5 inches deep, with slots for a main breaker and four to eight branch circuits.  The price listed there is just for the panel, you still have to add the breakers and a ground bar kit.

        Square D is just one brand, you can get similar stuff from Siemens, GE and others.  Just make sure whatever you get is rated for service entrance use. 

        As far as the size of the main breaker goes, if the service from the utility is 100 amps you can certainly have a main breaker smaller than 100 amps if you like, you just can't put in a main breaker larger than 100 amps.

        Also, I'd run the cable from the meter to the panel in a conduit, it will be a lot neater and more durable.

        Edited 8/27/2004 7:02 pm ET by Stuart

        Edited 8/27/2004 7:05 pm ET by Stuart

      2. fireball | Aug 28, 2004 04:41am | #5

        Sounds like a 6 circuit NEMA 3R panel would do fine.I'd avoid metal conduit from the meter to the panel though,use PVC instead.Before you hit your first overcurrent protection all of the metal portions of the service equipment have to be bonded together,and the code says "Standard locknuts or bushings shall not be the sole means for the bonding required by this section"(250.92B).If you use weathertight EMT connectors or even galvanized rigid conduit you have to use bond bushings because the locknuts,even if driven tight with a hammer and chisel,aren't supposed to be able to handle unfused fault current.It's one of the PITA sections of the code I don't agree with.A metal service mast usually terminates into a threaded hub,and "...threaded bosses on enclosures where made up wrenchtight..."are OK.When you start nippling from the metering equipment downstream in metal it's a lot harder to do correctly.

        Edited 8/27/2004 9:43 pm ET by IBEW Barry

        1. OneofmanyBobs | Aug 28, 2004 05:16am | #6

          I remember now.  Tried to use metal once before.  I couldn't figure it out and the inspector didn't know either, so it got changed to plastic.  Since this is exposed, the protection of metal would be nice but I'll do plastic.   This setup doesn't have a metal mast.  Just some very old tarred cotton copper.  But, that's up to the utility.  If they installed a new meter on it, I guess they think its OK.  Meter socket and meter were replaced maybe 5 years ago.  Nobody was told about it.  It just changed one day.  I'll go to my distributor and see what they have for disconnects.

          1. junkhound | Aug 30, 2004 06:45am | #7

            Never saw a "Barry " post I'd take some exception to before, but "avoid metal conduit from the meter to the panel though, use PVC instead"  in light of your comment on rodent damage would lead me to use metal.

            Have seen squirrels, pack rats,  and mice eat thru PVC for no apparent reason (at least not to me, although I've been refered to as squirrely and a pack rat more than a few times) which is why I'd go with metal.  I've a 4x4 truck I leave at my cabin, and absolutely need to leave the hood up otherwise all the ignition wires and other wires get eaten thru by the squirrels.  If all the PVC is in open air, maybe OK, if any runs thru any nook anyplace the critters could nest, go with metal.

          2. fireball | Sep 02, 2004 06:16am | #8

            Junkhound,

            I like metal pipe too,and galvanized rigid conduit is like the gold standard for installations,but still,I avoid it like the plague ahead of the overcurrent protection.If you have an electrical inspector following the NEC on service inspections,you really have to watch what materials you use.Like I said before standard locknuts are unacceptable.You either have to use threaded hubs or bond bushings,and the way that services are inspected here,the grounding conductor going to the bushings has to be able to carry any fault current the phase conductors can deliver.I of course learned this the hard way.

             Some time ago I did a 1200 amp service on a football stadium using 3 sets of 4" w/600 MCM's.It was really tight quarters where the utility's CT cabinet and the main distribution panel had to go,no room for back to back 4" PVC connectors,so I used rigid all thread nipples between the cabinets.The inspector wouldn't accept it unless I used bond bushings on one side of each of the three nipples,with 600MCM going in between them.Man it sucked.And it was BS too because every bond bushing that size has a 10-24 hole for the lug to attach to the bushing.So which has more ampacity,a copper 600 MCM or a steel #10 machine screw?It's the same thing with the threaded hub that comes with meter bases.You can screw a 2-4"rigid conduit or an EMT connector into it but the fault path connection is still dependant on 4 #10 screws.But that's what is UL approved blah,blah,blah....I even went to the electrician's toolbox website and asked the engineers and inspectors there what they thought and they all agreed that that's what the NEC requires.The moderator said some inspectors allow "grounding wedges" on the locknuts but I've never seen one.

            So anyway,this guy's cabin service wouldn't be that expensive to put together with Myer's hubs or to use bond bushings,if he ever thought an inspection was likely.

            Barry

          3. OneofmanyBobs | Sep 02, 2004 03:12pm | #9

            I'd rather use metal, but you can never get a straight answer from the inspectors here.  They will not give "advice" for liability reasons.  They only look and say accept or reject.  This doesn't need inspection, but I could get it if I wanted it.  Right now the cable from meter to disconnect runs where you can easily touch it.  Only a couple feet off the ground.  If I can reroute it out of reach, plastic conduit would be OK.  If it has to stay exposed like that, I'll do metal.

            There's no ground now.  When I add the ground, does it need to run through the meter socket?  I've only ever done service where the meter was directly opposite the panel.  Then the ground goes through the socket and into the panel along with the feed.  If I can just run the ground into the disconnect rather than into the meter base it would be simpler.

          4. fireball | Sep 04, 2004 07:54am | #10

            Bob,

            Inspectors are probably different with homeowners who may or may not know what they're doing, than they are with the tradesmen whose work they regularly inspect.I know it's frustrating when they clip you and won't tell you why.I used to have to deal with an elevator inspector that was like that.

            I usually work on large commercial jobs with 400-2000 amp services,so there are people here better suited for answering residential service questions.That said,my advice would be if you have a metal water pipe and/or two ground rods,terminate them in the first disconnecting means with the neutral (the grounded conductor).If you use PVC from the meter,you're going to have to run an equipment grounding conductor back to the meter to bond the enclosure.If you use metal conduit with threaded hubs you're OK.If you use regular locknuts you would have to use bond bushings also.That's the way it works where I live.

            Barry

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

A Practical Perfect Wall

Getting the details right for a wall assembly with the control layers to the exterior and lots of drying potential.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast Episode 695: Saving Bricks, Cut-and-Cobble Insulation, and Waterproofing Foundations
  • FHB Podcast Segment: Waterproofing Below-Grade Foundation Walls
  • Midcentury Home for a Modern Family
  • The New Old Colonial

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 333 - August/September 2025
    • A Practical Perfect Wall
    • Landscape Lighting Essentials
    • Repairing a Modern Window Sash
  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data