Add light off a 20 Amp wire?

Buttkickski | Posted in Energy, Heating & Insulation on May 7, 2007 02:45am

I want to add a light to the corner of my shop. There is a 20amp outlet about 8 feet from where I want my light to be. Can I pull power from that outlet to my switch then to a ceiling light?

Can I use 14 gage wire to do it??

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    BillHartmann | May 07, 2007 02:50am | #1

    Yes, you can add a light.

    No it can't be #14.

    Note, it is generally recommended that you don't have lights on a shop receprtacle circuit because you don't want it to go dark if you overlaod it.

    But I am guessing that this is an addtional light and would not be a problem.

    Also know that a few werid locals don't allow lights on 20 amp circuits and a few other don't allow anything, but 20 amp circuits.

    But both of those are not common and not NEC.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. Buttkickski | May 07, 2007 03:19am | #2

      OK It is an additional light for a corner that is pretty dark at times.So I'll run #12 from the receptacle to a switch to the light.I presume I need a 20amp rated switch, right.That saves me a LOT of work!Thanks.

      1. User avater
        BillHartmann | May 07, 2007 03:45am | #3

        "I presume I need a 20amp rated switch, right."No, you can use a 15 amp switch.The code is not perfect and this is one of the little stange corners.Using #14 would be safe for this, but would not meet code.I am guessing that the thinking is that run could be extended for another receptacle so you want it to be able to handle 20 amps.But the switch is not normally switching anything but a light fixture, which in this case would be less than 15 amps..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. Buttkickski | May 07, 2007 03:59am | #4

          Got it, thanks!

        2. User avater
          xxPaulCPxx | May 07, 2007 05:51am | #5

          What about this:  Wire and extension cord to a surface mounted wall switch, the cable would just be held close to the wall by one of those decorative plastic sheaths (Wiremold makes these products, I think?).  After the switch, the wire from the switch to the overhead light can be encased in conduit as normal.

          Then it would be just like a standard desk lamp... just a little more heavy duty.Rebuilding my home in Cypress, CA

          Also a CRX fanatic!

          1. User avater
            BillHartmann | May 07, 2007 05:55am | #6

            I don't think so. But one would have to read the code carefully.I don't think that cords can be permanately attached to a building surface..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          2. User avater
            xxPaulCPxx | May 07, 2007 06:44pm | #16

            Well, having the light plug into the wall makes it temporary, I would think.

            I had a pair of sconces in a bedroom of the last house I lived in.  Each had a switch on the bulb socket, and a cord to the outlet covered by the decorative Wiremold zipcord cover... what I proposed is based on that.

            How about this then:  Off that outlet he wires a 20amp switch to another outlet that he places on the ceiling.  He plugs a conventional shoplight into that outlet.  Switched outlet - no funny wiring.Rebuilding my home in Cypress, CA

            Also a CRX fanatic!

          3. DanH | May 07, 2007 05:59am | #7

            You're not supposed to use extension cords for permanent wiring.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          4. User avater
            McDesign | May 07, 2007 01:58pm | #8

            <You're not supposed to use extension cords for permanent wiring>

            Right, but what if you get a 25' length of zip cord, and rewire the light fixture just to have a really long cord?

            Forrest

          5. DanH | May 07, 2007 02:01pm | #9

            You can do that in a residence, so long as you're not selling it. Would be tagged by many commercial inspectors, though.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          6. woodturner9 | May 07, 2007 05:02pm | #10

            Wire and extension cord to a surface mounted wall switch, the cable would just be held close to the wall by one of those decorative plastic sheaths (Wiremold makes these products, I think?).  After the switch, the wire from the switch to the overhead light can be encased in conduit as normal.

            NEC says that extension cords are for "temporary use".  It doesn't really define that phrase well, but what you are proposing would not meet code, in my opinion.

            Regarding the 14 guage wire, I find nothing in the NEC that would prohibit that.  Around here, it's fairly common practice.  Perhaps Bill will explain why he views that as a code violation.

             

          7. edlee | May 07, 2007 06:05pm | #11

            Regarding the 14 guage wire, I find nothing in the NEC that would prohibit that.  Around here, it's fairly common practice.  Perhaps Bill will explain why he views that as a code violation

            Article 240 - Overcurrent Protection , Section 4(D): Unless specifically permitted ....... the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG and 30 amperes for 10 AWG copper.........

            There are a few exceptions for tap conductors and a list of specific applications relating to things like motors, capacitors, some control wiring, etc.

             

            Ed

          8. woodturner9 | May 07, 2007 06:21pm | #12

            Article 240 - Overcurrent Protection , Section 4(D): Unless specifically permitted ....... the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG and 30 amperes for 10 AWG copper.........

            Good point.  If the breaker is a 20A breaker, then I agree, 14 AWG would not be permitted.

            The OP stated he had a 20A outlet, but did not state the breaker size.  The situation I had in mind was 20A rated receptacles on a 15A breaker - and in that case, 14 guage wire would be OK, because of the 15A breaker.

          9. Buttkickski | May 07, 2007 06:36pm | #14

            It's a 20amp breaker and I'm not changing it.

          10. User avater
            BillHartmann | May 08, 2007 02:40am | #27

            "It's a 20amp breaker and I'm not changing it."A 20 amp receptacle is a waste of money.In residential grade devices only come in 15 amp devices (those are the 59 cent ones).Spec grade (and higher) come in both 15 and 20 amp versions. And with or without backwiring. They start at around $1.75.You would can be the better quality devies in 15 amp versions and save a little money.Unless you have something with a 20 amp plug on it..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          11. edlee | May 08, 2007 04:13am | #28

            Bill,

            "A 20 amp receptacle is a waste of money."

            Well, not exactly.  There's a circuit design issue and a code issue here.

            If you look at Table 210.21(B)(2) you will see that the maximum allowable plug-in load to a receptacle is 80% of it's nominal value.  For a 15a device that is 12a and for a 20a device that is 16a. 

            So when an electrician installs an outlet on a  20a circuit he has to take into account what will plugged into it. For example on a kitchen counter it's not a bad idea to use 20a-rated devices because of the  probable loads that will be attached, possibly simultaneously.  If I'm wiring an outlet that will have an 12a appliance plugged in, then I would certainly use a 20a duplex rather than a 15a duplex which would work but would be maxed out according to Table210 and would be overloaded if someone plugged something else into it.

            The only 120v straight-blade 20a plugs I've come across are in non-residential settings, like commercial production, which use specialized equipment.

             

            Ed

          12. User avater
            BillHartmann | May 08, 2007 05:33am | #30

            "If you look at Table 210.21(B)(2) you will see that the maximum allowable plug-in load to a receptacle is 80% of it's nominal value. For a 15a device that is 12a and for a 20a device that is 16a."Here is what that section says."(2) Total Cord-and-Plug-Connected Load Where connected to a branch circuit supplying two or more receptacles or outlets, a receptacle shall not supply a total cordandplug-connected load in excess of the maximum specified in Table 210.21(B)(2)."I have had too much wine to try and decipher this one.It heavey mixes total with INDIVIDUAL..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          13. User avater
            BillHartmann | May 08, 2007 05:41am | #31

            And also see 210.23(A)"(A) 15- and 20-Ampere Branch Circuits A 15- or 20-ampere branch circuit shall be
            permitted to supply lighting units or other utilization equipment, or a combination of
            both, and shall comply with 210.23(A)(1) and (A)(2).And the Handbook has this comment."A revision to
            210.23(A)(1) clarifies that only cord-and-plug-connected utilization equipment that is
            not fastened in place can have a rating of up to 80 percent of the branch circuit rating
            where the circuit also supplies other loads. Equipment that is fastened in place, whether
            direct wired or cord and plug connected (waste disposers and dishwashers for
            example), is covered by the 50-percent requirement in 210.23(A)(2)."That says that I could plug in a 15 amp load into a 15 amp receptacle on 20 amp circuit.That is where I see many stationary equipment that comes with 15 amp plugs, but should be 20 amp.I have looked on my Jet TS for example and it has a UL motor. And a UL cordset. But the table saw as such is not UL listed..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          14. edlee | May 12, 2007 05:19am | #54

            And the Handbook has this comment.

            "A revision to210.23(A)(1) clarifies that only cord-and-plug-connected utilization equipment that isnot fastened in place can have a rating of up to 80 percent of the branch circuit ratingwhere the circuit also supplies other loads. Equipment that is fastened in place, whetherdirect wired or cord and plug connected (waste disposers and dishwashers forexample), is covered by the 50-percent requirement in 210.23(A)(2)."

            That says that I could plug in a 15 amp load into a 15 amp receptacle on 20 amp circuit.

             

            Hi Bill,  

            I don't see any relationship between your conclusion and the section/commentary you quoted.

            210.23(A)(2) is about circuit design , i.e. the 50% limitation when sharing fixed equipment and other loads, and is not only about receptacle  loads . It is not particularly relevant to how much current a 15a duplex device can handle. 

             

            ?

            Ed

             

             

            Edited 5/11/2007 10:23 pm ET by edlee

            Edited 5/11/2007 10:27 pm ET by edlee

          15. Buttkickski | May 08, 2007 04:25am | #29

            Uhhh...not sure I follow you; when I built the shop I wired two circuits with 5 receptacles each. Each circuit has 20a receptacles, #12 wire and a 20a breaker. I'm pretty sure I didn't pay any more than $1.75 for each receptacle. Are you thinking I bought something else?

          16. User avater
            BillHartmann | May 08, 2007 05:42am | #32

            Whatever the cost you could have gotten 15 amp rated receptacle of the same quality for less than the 20 amp.(Assuming that you paid "fair market price" and they wheren't surplus from a project or something like that..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

            Edited 5/7/2007 10:43 pm by BillHartmann

          17. Buttkickski | May 08, 2007 03:10pm | #33

            I see what you're saying, but what would have happened when the inspector saw 15a receptacles on a 20a circuit?

          18. DanH | May 08, 2007 04:48pm | #34

            What should happen?
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          19. Buttkickski | May 08, 2007 04:53pm | #35

            I think the inspector should fail the electrical because the receptacles say 15a on them but they're installed in a 20a circuit.

          20. DanH | May 08, 2007 06:48pm | #36

            Show me in the code where that's a violation.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          21. Buttkickski | May 08, 2007 06:51pm | #37

            I don't know... I'm not arguing, I'm asking.

            SO what's the answer? Can someone put a 15a receptacle on a 20a circuit?

          22. DanH | May 08, 2007 11:06pm | #38

            All (UL recognized) "15 amp" receptacles are rated for 20 amps feedthrough, and, as a practical matter, have contacts that will handle 20 amps. (You see more difference in contact quality and current capacity between "lines" of receptacles than you do between the 15 and 20 amp units of the same "line".)So the only significant difference between the two is the T slot on the 20A unit. This is mostly useless (hardly any devices made with 20-amp 120V plugs) except to inform the user that the outlet is (probably) connected to a 20-amp circuit.Code permits 15A receptacles on a 20 amp circuit.

            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          23. Buttkickski | May 08, 2007 11:36pm | #39

            Good, that's nice to know, but the question still stands: would an inspector fail a 20a circuit with 15a receptacles?

          24. edlee | May 08, 2007 11:43pm | #40

            Read my post #16 and look up the Code reference.  What more do you want than that?

             

             

          25. Buttkickski | May 08, 2007 11:48pm | #41

            "On a 20a circuit however, if there is more than one outlet, the devices can be rated at 15a or 20a."

            First, I didn't catch that last sentence of your post 16 because it wasn't addressed to me, sorry. Second, I don't think I have access to the NEC so sorry again. Third, all I wanted was a simple "yes" or "no" answer so please excuse me for asking.

          26. DanH | May 09, 2007 12:40am | #42

            If you want a simple "yes" or "no" you need to be going to a different BBS.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          27. cap | May 12, 2007 01:45am | #44

            O.K., then, here's your answer:

            yes or no

            Cliff

            p.s. or the answer could be:

            no or yes

            C.

             

          28. brownbagg | May 09, 2007 06:27am | #43

            I think the inspector should fail the electrical because the receptacles say 15a on them but they're installed in a 20a circuit.
            that happen to me, it didnt care what it said, it had to have the funny slots. That what happen when wally world lays off the xmas help.

          29. edlee | May 07, 2007 06:42pm | #15

             The OP stated he had a 20A outlet, but did not state the breaker size. The situation I had in mind was 20A rated receptacles on a 15A breaker - and in that case, 14 guage wire would be OK, because of the 15A breaker.

            You're right about him not stating the breaker size........I assumed it when he said there was a 20a outlet. But that's because, I suppose, I know of this section of the NEC:

            Table 210.21(B)(3) - Receptacle Ratings for Various Size Circuits.

            The table shows that with a circuit rated at 15amps, the receptacle rating is to be "not over 15 amperes". So, putting 20a rated receptacles on a 15a circuit is not allowed.

            On a 20a circuit however, if there is more than one outlet, the devices can be rated at 15a or 20a.

             

             

            Ed

             

             

            Edited 5/7/2007 11:44 am ET by edlee

          30. woodturner9 | May 07, 2007 07:07pm | #17

            Table 210.21(B)(3) - Receptacle Ratings for Various Size Circuits.

            The table shows that with a circuit rated at 15amps, the receptacle rating is to be "not over 15 amperes". So, putting 20a rated receptacles on a 15a circuit is not allowed.

            I'll have to dig out the code book when I get back to the office to look up that section - I don't recall that specifically off hand.

            I suspect, though, that they are referring to 20A receptacles - i.e. receptacles designed to accept a 20A plug - as opposed to receptacles rated for 20A but that only accept 15A plugs (i.e. the 'normal' plugs).  Many "15A" receptacles are rated for 20A, and many GFCI receptacles are rated for 20A.  The difference is that they will not accept a 20A PLUG, not that they are rated for 20A.

          31. User avater
            dryhter | May 07, 2007 08:49pm | #18

            I love it when the code books come out in these threads!

          32. edlee | May 07, 2007 10:05pm | #19

            I suspect, though, that they are referring to 20A receptacles - i.e. receptacles designed to accept a 20A plug

            Well, yeah by definition that is EXACTLY what we're talking about.  A receptacle rated at 20a is a receptacle rated at 20a.

            as opposed to receptacles rated for 20A but that only accept 15A plugs (i.e. the 'normal' plugs).  Many "15A" receptacles are rated for 20A, and many GFCI receptacles are rated for 20A.

            I think you're being confused by terminology. Duplex receptacles have their rating printed on them and 15a means 15a.  We're not talking "feed-thru" rating here.

            210.21(B)(3) allows a receptacle rated at 15a to be installed on a 20a circuit, as long as there is more than one outlet. This is "feed-thru" and is in a sense an exception to the general rule, based on load diversity. But the device itself is rated at 15a. 

            15a GFI devices usually say on the back that they are rated for 20a feed-thru. Their rating though in regards to the table and 210.21(B)(1) is 15amps.

            These are the 15a Leviton duplex receptacles I use all the time, even in residential applications. I don't bother with the  residential grade devices. Notice that there is no mention of 20a.

            http://www.leviton.com/OA_HTML/xxlcfbuibeCSrdSrchResults.jsp?cg=&kw=cr15&ds=0&dr=20&st=kw&cpg=0

             

            Ed

             

            Edited 5/7/2007 3:08 pm ET by edlee

          33. woodturner9 | May 07, 2007 10:17pm | #21

            15a GFI devices usually say on the back that they are rated for 20a feed

            OK, but that's not what I was referring to.  A 20A plug has one blade turned:

            http://servertech.com/downloads/Technical%20Notes/notes_pt_cordconectoropts.pdf

            see NEMA 5-20P, for example.  My thought was that they were referring to receptacles designed to accept a 20A plug, but as I said in the other message, after looking at that table I agree with your interpretation, and it seems that is not what they meant.

             

          34. edlee | May 08, 2007 12:45am | #24

            I get what you're saying. 

            There probably are 120v 20a straight-blade receptacles that will accept ONLY a 20a plug, i.e. blade turned.  But what I'm used to seeing, at least for in-wall devices, is the combination, i.e. rated at 20a but has both neutral slots so that it will take 15a or 20a plug.

            Nice talking with you............Ed

          35. User avater
            BillHartmann | May 08, 2007 02:33am | #25

            "These are the 15a Leviton duplex receptacles I use all the time, even in residential applications. I don't bother with the residential grade devices. Notice that there is no mention of 20a."Those same device are available in 20 amp versions.I would have to look up the some of them, but the CR15's are available in CR20's.But I have never seen anything with a 20 amp plug on it. Although some woodworking tools should probably have them. Some one did tell that they did see one on some resturant equippment.AFAIK ALL 15 amp UL DUPLEX receptacle are rated for 20 amps load. That is why you can use them on 20 circuits. That 20 amps can be any combination of feed througn and/or loads connected to the 2 15 receptacles. For example 2 10 amp loads. Or a 15 load plus 5 amp feed through.Here is a links showing both the plug and receptacle configuration for NEMA straight blades.http://www.systemconnection.com/downloads/PDFs/NEMAPlugReceptacleConfigurations.pdfBoth 120 and 240 15 amp plugs will plug into their corresponding 20 amp receptacles.I don't think that the same follows for the 120/240 or 277 or 3 phase circuits..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          36. woodturner9 | May 07, 2007 10:13pm | #20

            The table shows that with a circuit rated at 15amps, the receptacle rating is to be "not over 15 amperes". So, putting 20a rated receptacles on a 15a circuit is not allowed.

            After reading the actual code section, I agree with your interpretation.  While I couldn't find any clarification of what they mean by "rating", it certainly seems a simple reading of that table would be the common interpretation.

            Sorry for adding to the confusion.

          37. MikeHennessy | May 07, 2007 06:21pm | #13

            Well, he CAN legally run 14 wire, so long as he changes out the breaker for a 15A one. Otherwise, it's against code.

            Mike HennessyPittsburgh, PA

  2. pacificsbest | May 07, 2007 11:18pm | #22

    I still cannot understand using 15a breaker OUTLETS (with 14 g wire) as opposed to 20a breakers (with 12 g wire).

    Who knows what someone may plug in the outlet later? Say work is being done in the area of a 15a with 14 wire, someone plugs in a heavy load power tool, another person turns on a hair dryer on the same curcuit.

    Ok, the 15a breaker trips, soon enough if you are lucky.

    Isn't this a hazard waiting to happen???

    Well, Guess I have to learn how to do THAT, now!
    1. Buttkickski | May 08, 2007 12:23am | #23

      Huh?

      I have a 20a outlet with #12 wire and a 20a breaker. All I am doing is pulling a light off of that circuit. What's wrong with that?

    2. User avater
      BillHartmann | May 08, 2007 02:37am | #26

      "I still cannot understand using 15a breaker OUTLETS (with 14 g wire) as opposed to 20a breakers (with 12 g wire).Who knows what someone may plug in the outlet later? Say work is being done in the area of a 15a with 14 wire, someone plugs in a heavy load power tool, another person turns on a hair dryer on the same curcuit.Ok, the 15a breaker trips, soon enough if you are lucky.Isn't this a hazard waiting to happen??? "No hazard.And you still have the possibility of overloading. If you have more than one receptacle each one could, in therory, be drawing 15 amps. For the basic duplex receptacle that is 30 amps.If you have #14 wire and 15 amp breaker the breaker will open and protect the circuit the same as if you had #12 wire and 20 amp breaker..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  3. cap | May 12, 2007 01:50am | #45

    But seriously, if it's a 20 amp circuit (has a 20 amp breaker), then, NO you can't use 14 gage wire.  The maximum overcurrent protection allowed for 14 gage wire (except in certain instances like for some types of fixed in place, hard wired motors) is 15 amps.

    This is one of the most basic aspects of branch circuit wiring.

    Anyone who thinks it's OK is very dangerously misinformed.

    Cliff

    1. Buttkickski | May 12, 2007 02:20am | #46

      well now hold on Tex. I may not be an electrician but I do understand the basic theories of electricity. I'm pretty sure that single light I intend to add is never going to draw 20 amps therefore 14g would be safe FOR THE LIGHT ONLY, but not legal according to code.

      1. cap | May 12, 2007 02:45am | #47

        Well there Pilgrim...

        You have a point, with the way you're wiring the circuit.  What happens when someone adds more ligthing load, downstream of your undersized wire?  O.K., not likely, I'll grant you.

        But, and this is a big but, the branch circuit conductors have to be protected not just against overload, but also against faults.  A fault, for instance, like a line-to-ground short.  The 14 gage wire, according to the Code-making panels, is not adequately protected by a 20 amp overcurrent protection device (OCPD).  Not enough copper in the wire to carry the considerable current before the breaker trips, the wire heats up, maybe a fire starts.

        I've often wondered how much heating is allowed in a properly sized conductor under either max overload or fault current.  But whatever the value, be it heat produced or temp rise under some plausible worst-case conditions, some body (UL, NFPA, or a contract testing lab to one of them) has done the tests and some engineer has drawm a line as to what's safe and what's not.  And the Code-making panels have debated and decided that 15 amp OCPD and no greater is safe for 14 gage wire.  And of course there are some exceptions.

        I'm thinking there's no point to get into what might be safe but not Code compliant.  In a bigger sense, there have been a lot of third-world buildings that have fallen down and burned down, because some builder made his own decisions as to what's safe. 

        So I don't mean to insult your intellegence.  It seems like we're slaves to Code requirements, and that's not a bad thing.  Could we get away with doing a lot less in some instances, and not have a life-safety problem?  Probably.  But why the heck go there, when the difference is a bit of 12 gage wire vs 14 gage?

        Peace,

        Cliff 

        1. User avater
          BillHartmann | May 12, 2007 02:58am | #49

          "But, and this is a big but, the branch circuit conductors have to be protected not just against overload, but also against faults. A fault, for instance, like a line-to-ground short. The 14 gage wire, according to the Code-making panels, is not adequately protected by a 20 amp overcurrent protection device (OCPD). "Objection in the court.But you are are allowed to do with with taps and motor circuits. And the breaker will protected it against faults.As I said earlier I think that the main reasoning is that some will will see #14 and think that then can extend the circuit with #14 and then you have problems with overload protection..
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          1. DanH | May 12, 2007 03:14am | #52

            I liked my reason better. And technically #14 CAN handle 20A (it's in one of the NEC charts), it's just a "special case" (footnote to the chart) to limit it to 14A, probably because it's used in the type of circuits most likely to be abused.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          2. cap | May 12, 2007 03:24am | #53

            Scheist, Bill!

            Yes, you're right.  So is it the Copper Development Association that influenced the CMP to limit 14 gage copper branch circuit condictors to 15 amp OCPD, except in some specific circumstances?  Sell more copper that way, maybe?

            Cliff

        2. Buttkickski | May 12, 2007 03:12am | #50

          Oh, I totally agree with you and the code for those very reasons. I just wanted you to know that I know what kind of wire is needed to handle 20a.Thanks.

      2. DanH | May 12, 2007 02:50am | #48

        The main concern is for the bozo who removes the bulb and replaces it with one of those outlet plugs, then hangs his toaster and microwave off of that.
        So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

        1. Buttkickski | May 12, 2007 03:13am | #51

          I agree and I'm using 12g as BillH and the code told me too.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Outdoor Lighting

Lighting up an exterior isn't just about ambiance— it's also about code compliance. Here is what the code says about safety and efficiency when it comes to outdoor lighting.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Design and Build a Pergola
  • Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper
  • FHB Podcast Segment: Are Single-Room ERVs the Answer?
  • Fire-Resistant Landscaping and Home Design Details

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data