I need to add a 220 circuit to my cabin, but there is only 1 circuit slot left. Is there anything I can do that is easier than replacing this panble with a bigger panel? Photo attached.
thanks
I need to add a 220 circuit to my cabin, but there is only 1 circuit slot left. Is there anything I can do that is easier than replacing this panble with a bigger panel? Photo attached.
thanks
Listeners write in about removing masonry chimneys and ask about blocked ridge vents, deal-breakers with fixer-uppers, and flashing ledgers that are spaced from the wall.
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Get home building tips, offers, and expert advice in your inbox
Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.
Start Free Trial NowGet instant access to the latest developments in green building, research, and reports from the field.
Start Free Trial NowDig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.
Start Free Trial NowGet instant access to the latest developments in green building, research, and reports from the field.
Start Free Trial Now© 2025 Active Interest Media. All rights reserved.
Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.
Get home building tips, offers, and expert advice in your inbox
Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.
Start Your Free TrialGet complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.
Already a member? Log in
We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.
Replies
Look at the label on the panel and see if it is rated for 8/16. That is 8 slots and 16 poles.
If so you can replace the two single pole breakers (120 v) with a single tandem breaker.
And you will have to move the 2 pole breakers around so that you have two open slots togther.
That will get you 240.
Not sure what you can do to get 220, other than a big autotransformer.
Thats an FPE 8cct sub panel. Its already got the narrowest breakers FPE makes. In order to get another 220 cct out of it, it MUST be replaced with a larger panel, unless you are willing to "sub a sub" from this panel. (not advisable). It's also only rated for 60 amps, and without a main breaker, it is not allowed to be used for "service entrance" purposes.
locolobo
Emonton, Alberta, Canada
I agree with Bill. Also, considering your picture and the full-ness of the panel, I'd replace the panel. With the wall open as it is, it doesn't get any easier. Consider - you'll have room for future growth...
replace the panel or add a small panel...
Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming
WOW!!! What a Ride!
Forget the primal scream, just ROAR!!!
If you're leaning towards replacing the panel at all, another benefit would be getting a main at the panel. You don't seem to have one in there.
That panel wouldn't pass code where I am for a couple different reasons.
Pull the meter and replacing a small panel like that with a big one (that has a main breaker) would be cake.