I have Series 200 Anderson tilt double hung windows that are 5 years old and leak. During driving rains the water comes up through the seal where the two windows lock. (in each corner) Then runs down the sides onto my hardwood floors. Naturally Anderson wants to bank my problem on faulty installation. So i’ll go through their check shortly (diagonal measuring) to rule out an installation screw-up. Has anyone ever had this problem with this series windows? Anderson claims that they haven’t heard of this problem. So far 2 of my homes 27 windows I found leak. The other 20 windows would leak onto carpet, will now inspect closer.
thanks,
bri78
I believe it is time for them to send out a representative!
Thanks for all replys. Anderson asked me to check the windows for plumb, put down 132$ on a card, then they'll send a rep. If it's my contractors fault then I'll get charged. If not, then they will not bill. Sounds fair. For me to contact the contractor after 5 years, I'll get better results blowing in the wind. thanks again.
bri78
The contractor comment is NOT always true, try, it may be worth the call.
My guess would be installation- the windows are not set plumb and square. Do you see more light at the sill on one side or the other when you gently push the sash down? Don't lock the sashes when you try this.
Andersen has a great service record, tho. If it is a problem with their window, they'll take care of it. The 200 series isn't their best, but they shouldn't be leaking, either.
After reading frammer's reply, I agree with him.
Do you know where the windows were purchased? If so, call them and ask for the local Andersen service rep to come and look.
If the windows are leaking at the check rail it should still run down the jamb to the sill then out.
If these are 200 tilts, they are bottom of the line for Andersen. There is nothing wrong with them but if they are not installed absolutely perfectly there is no easy fix... other then remove and reinstall correctly. A common problem is called pickle barreled, where the center is bowed out leaving an incomplete seal where the sash meet. In extreme cases, with the sash unlocked, you can grab the lower sash and push it left or right and see outside.
Andersen did have an initial problem with 200's which they can/will upgrade but they would be able to determine if that was the problem over the phone.
On the plus side they should be able to send a tech to your house to determine exactly what the problem is... the down side is, if it's installation they are gonna charge you.
I have seen people do this so many times I couldn't count. Not pointing fingers at the OP, but there's a high probability that could be the problem.
Those windows should always be checked for a perfectly plumb and straight frame on the outside when they are installed.
I have some andersons, series 400? that have this pickle barreling, any ideas what causes it? I installed them years ago and re-installed (long story-had rotted framing).All new windows I buy will be Marvin, even their Integrity line are superior to Andersons, just my opinion.Thanx.AS
Poor installation causes it.
The best window ever made... If installed incorrectly... is no better then the worst window, installed well.
Somehow I think Marvin may not solve your problems.
It is very simple. The jambs tend to bow out in the middle and the window must be carefully installed so that the side jambs are perfectly plumb and straight, with a consistent width measurement from top to bottom.
The easiest way to assure this is to use a level for checking plumb and also for use as a straight edge on the outside of the window when installing it.
When a window ends up with a pickle barrel shape after installation, it is solely the fault of the installer. Most windows come from the factory with some amount of side jamb bowing and it must be corrected when installing the window.
Unfortunately, many hacks just grab a window and nail it in the opening without any regard whatsoever for this problem.
FWIW, I have had many more problems with Marvin windows than I have ever had with Andersens.
I have been educated on your blog concerning window "pickle barrelling". My leaks come in the corners where the double hung windows lock. Speaking with an Anderson rep, his concern for my case was to take a diagonal measurement. And to let him know weather that measurement was whithin 1/8". If my side jams were pickle barreled, the diagonal measurement could still be exact, correct? Assumeing that the side jams bowed alike. The Anderson rep also asked to check if the windows were level but never mentioned the fact that the side jams may be bowed, which could be checked with a straight edge. I'm on the road now, so I can't get much accomplished when I'm not by my windows.
Thanks,
Yes, you could have a window with both of the side jambs bowed out considerably in the middle and still have the same diagonal measurements.
This problem is more common in double hungs, but happens with casements and other styles too.
Hey BoJangles, I have installed 1000's of windows, when the problem is in the corners it does not relate to installation. Probably a factory jig that got out of shape.
As far as more problems with Marvins, at least their factory rep will come to the job and look at it!
I rarely have a problem with an Andersen window and if I do, it is taken care of immediately by the rep from the Andersen distributor.
I see comments like yours frequently and can't believe you get such poor service from the window distributor. The Andersen rep is at our supplier at least once a week. If we have a problem with something, he is at the job and takes care of it pronto! They will bend over backwards to provide good service. It's been like this for the 30+ years I have been installing them. I couldn't be happier with their service here.
I have no complaints about the Marvin rep either. I just don't like their products. Lots of problems with annoying hardware breakage etc.
Different reps, different parts of the country!
Plus some are AndersEns, some AndersOns. Are we even talking about the same company?
It is an ironic habit of human beings to run faster when we have lost our way. --Rollo May
Do we loose points for bad spelling?
I wasn't really taking either side of it.
Yes they did have bunch of bad glass problems.
And yes, they did make good on the warranties, and even extended for those home that had windows from those runs.
Maybe it was put out on one of those consumer alert bulletins, I don't know. I just happened to have built my in-laws house, so I got an immediate call when the first window started to fog. I followed up with my supplier and they contacted Andersen.
I think it was like one of those automobile manufactures "silent recalls". Fix them if they fail and you get a complaint, fix them if they are in for routine work, but don't every make a public announcement about the problem.
Falls in a gray area. ethically, for me, but then maybe that is one of the reasons I wasn't a very good business person.
come on, are you perfect? I think not!
"I have installed 1000's of windows, when the problem is in the corners it does not relate to installation. Probably a factory jig that got out of shape."
I have seen plenty of factory problems but the nice thing about those is... they show up immediately, meaning... it is impossible to install the unit correctly, saving alot of wasted installion time. I have inspected 1000's of windows installed incorrectly.
Seen plenty myself, even done a few in my time. Factory problems tend to show up quickly, but not alqawy. I recall that Anderson had to replace a bunch of thermopane windows, fogging etc. showed up years later.
I know you used to rep for anderson, maybe when giving advice it would be best to disclose this.
My latest dealings with my Anderson windows. The rep wants measurements. Heck with that. I'll call Anderson in the morning to get someone to my place ASAP. Tonight during a driving rain storm at my place in Lower Mi. It looked as though a river was running on my hardwood floors. Soaked up 9 full size bath towels in 10 minutes from only 1 of the windows. Water wasn't just coming in from the lock area but also from the top seal, different from where I figured it to be from in my earlier investigation. I'm to the point where I don't care if the window was installed without glass, they shouldn't leak that bad. The weird part is, is that I've been in this newly built home for 3 years this September, and I just noticed that they leak, not more than a month ago. Tonight I know of 5 windows leaking from this driving west rain. 2 of them are protected under my porch roof. And honestly, during major snow blizzards during the winter, I never felt a draft. What the heck happened?
Bad Night
Cica 1980-81.
They are still replacing them under a warrenty extension that they intiated themself.
FIL ahd three more fixed two years ago. So far they have done 14 of the 22 casement windows in the house. They runa thermalgram on all of them each time they come out.
I was trying to point out to the former Anderson rep, that his thinking is skewed.
Thank you for pointing out the truth!
I don't rep Andersen windows... It must be voices in your head.
I repair Andersen... and every other window, ever made by any manufacturer.
I specialize in the window repair biz... go figure I know something about bad installations.... Andersen actually calls me to solve problems because of poor installation and frequently they pay me just to keep their name good on jobs that installers had no clue....And what does a fogged piece of glass have even the slightest thing to do with a window installed not per instructions or anything else covered in this thread???
Now back to Bri. You'll notice there is a fin at the top of your 200 window that mates with the sash specifically to stop water. Unless you live somewhere that water travels uphill or you are experiencing no gravity your problem seems to be outside the window. Chances are the installer didn't silicone and waterproof them during installation. My guess is water is running down the exterior wall till it hits the window then going the only place it can.... inside.
Edited 6/13/2008 5:41 pm ET by sledgehammer
It has to do with the fact that some bad products and factory problems do occur with anderson as well as most manufactorors.
Instalation is one thing, it sounds to me like the window may have other problems<G>
That's why we all have opinions... Sounds to me like there is nothing wrong with the window other then the installer thought he knew a better way then the manufacturer.... And the nice thing about Andersen they will inspect it and if they screwed up, they will fix it at no cost to the homeowner.
yep!
Here's the latest on my problem. The Anders(o)(e)n (not sure at this time weather an e or o but I'll leave it at that) rep. showed up thursday. He looked the whole place over thoroughly. He said that he doesn't see how the windows could leak. But he did say that the company has a new seal that he would order and shims for the locking area that would tighten up the locking area. When those parts come in he would then come over to install , then he wants me to put a water hose to the windows. If it was coming in above the window as you may think, wouldn't my drywall be wet somewhere besides at the bottom of the windows where the water has to run off of? That water would have to be in the studded walls, wouldn"t it? And then show up in alot more unexpected places than it has. I hope this rep has the fix. We are talking puddles of water on the floor, not drops. We are talking running water down the insides of the windows, not having to feel to find dampness. The 3 times this has happenen in the past 30 days, were all driving rain storms. Talking with 9 other homeowners in my neighborhood, all having various types of Andersen windows, I was the only one with leaks. Next step may be to use a power washer, something got to get solved soon.
Andersen 200 windows
Hi Sledgehammer
Where are you located? We are having issues with 2 large windows and need them looked at. Built the house 3 years ago.
Originally, thought it was seals....but I can look at the window and see the bowing in the middle. these windows were in 3 sections (12 ft total) and assembled by builder..
I dont know if I can go after builder at this point since its been 3 years.
we are north of Atlanta and really need this looked at.
thanks
Some folks seem to think that all you have to do is slap the unit in the rough opening and nail off the flanges. Superior installation requires shimming between the RO and the unit at all corners and at the meeting rail. Larger units may require additional shims to keep everything solid in the opening. If not shimmed properly, the jambs can bow outward causing sloppy fit and leaks.
Thanks all, I misunderstood the pickle barrel. On the few Andersons it is the SILL that bowed slightly upwards in the middle. The jambs are plumb and have not moved.I'm rushing off to work, but will post a picture later today.Thanks.
A bowed up sill means the window was not set on shims which is in the installation instructions of every Andersen window. You have a header above the window carrying weight down the sides of the window to the foundation. If the bottom corners are not set on shims the sides sink with settlement where the studs and sill under the window with no weight remain the same. Pushing the sill up causing a bow.
FWIW there should also never be shims between the header and the top of the window or door... again because of weight and settlement.
Overall the easiest way is read the instructions... which most throw away because they have been doing it for years and know what they are doing.
One of the funniest I see all the time is Andersen patio doors where the flange says every 3"... DO NOT NAIL.. DO NOT NAIL... DO NOT NAIL... with roofers nailed through it.
Oh and sills also bow because they are brick bound... if you have brick.
The interior structure sinks independent of a brick veneer. The sill catches on the brick and bows... Again this is covered in the instructions, a 1/2" space is required between the brick and the window.
Do you have brick home? Are the windows in question inside a brick opening? If so, this is a common problem. Most brick layers do not leave enough space under the sill to the brick sill for the eventual settling of the house framing. This will almost always "bow" the sill.
The only way to eliminate the problem is to remove the bricks and have them re- laid. I have done this a number of times and it does work. If youe jambs are bowing, a good shim job should straighten that out.As long as GOD makes "bad builders" and rich people... I will have a job
My thoughts exactly!
My experience with the Anderson 200 series is they are going to find some reason that your install is faulty, if you installed them you are out of luck, if you had a contractor install them you might be able to go after them. good luck either way.
Andersen 200 Windows
Haven't been back to this site for awhile but got an e-mail from another Andersen window buyer - still looks like Andersen is selling windows that let the outside in. My Andersen 200 series double hungs are great at letting the sunshine in as well as dirt and snow. Oh well - we just huddle around the fireplace all winter and stick pins in our Andersen rep voodoo doll. Come visit anytime, but bring your own firewood and warm blankets! New advertising slogan for Andersen - "We Let The Outside In!"
Don't believe me - I have photos! Yes, Andersen tried to fix them with upgraded weatherstripping but no success. They verified that the windows were installed correctly and all measurements are plumb and true. Nothing will fix the problem with the windows.
Don't buy Andersen Windows or you will be very sorry!
They design these windows to fail and no amount of 'adjusting' will fix them. Buyer beware! Feel free to contact me for the real story about Andersen Windows.
Arlo Kallemeyn
arlok33@yahoo.com
cell phone 708-439-7316
Our Andersen's are 37 years old. When should I be expecting them to fail?
arlo
"Haven't bee back to this site for awhile.........."
I see you just registered. When you were here last, did you use a different name to post under? Just curious to find your old posts and read up on your andersen problems.
I installed Andersen 200 series windows in my own house in 1987. They were called Narroline back then.
I haven't had a SINGLE leak from them in the 27 years they've been in place.
I followed the installation instructions, added sealing tape over the flanges, checked and double checked everything for square, level, and straight.
I've installed many other Andersen products for customers, as well, without any problem from leaks.
Andersen Series 200 Lock Keepers
We recently purchased a n eight year old home that has all Andersen Series 200 windows. My wife noted a cold air leakage in one window at the lock area. That got me to looking at all the window locks. What I found was that in about half of the windows, the lock keeper was mounted backwards with the locking tangs and the lock ramp to the outside. I could tell the correct manner in which the lock keeper should be mounted because the lock keeper body had recesses for the tapered screw heads.
When mounted backwards, the lock actually would push the upper sash away from the lower sash causing a bowing in the middle of the window on both the upper and lower sections.
Terry
Were these sash painted?
or
Do you surmise that the lock mechanisms were never removed and reinstalled?