I’m trying to figure out the voltage I am allowed to use with baseboard heat. It seems like most of the heaters for sale are 240 volts. Can I use these with 12 guage wire? I have seen heaters that are 120 volts, and wonder if I should use them instead…..any response greatly appreciated. I wired my own house but I am a little thick when it comes to understanding voltage and watts. Thanks, Hillside
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story

Simple air-sealing measures and spray-applied sealant lower energy bills and increase comfort without the need to tear the house apart.
Highlights
Fine Homebuilding Magazine
- Home Group
- Antique Trader
- Arts & Crafts Homes
- Bank Note Reporter
- Cabin Life
- Cuisine at Home
- Fine Gardening
- Fine Woodworking
- Green Building Advisor
- Garden Gate
- Horticulture
- Keep Craft Alive
- Log Home Living
- Military Trader/Vehicles
- Numismatic News
- Numismaster
- Old Cars Weekly
- Old House Journal
- Period Homes
- Popular Woodworking
- Script
- ShopNotes
- Sports Collectors Digest
- Threads
- Timber Home Living
- Traditional Building
- Woodsmith
- World Coin News
- Writer's Digest
Replies
So if you know the watts and the voltage to find the amps you dived the watts by volts you get amps needed to operate the device.
So if you know the watts the device calls or lets say it is 1300 watts and it operates on 240 volts.
what you do is dived the 1300w by 240v you need 5.4 amp. to make it work right. Now you need to know the distance from the device to the service box so you can figure the size of the wire you need to keep the voltage from dropping
To the calculate wire size try this on line calculators like this one
http://www.elec-toolbox.com/calculators/voltdrop.htm
As you said most heaters are 240 because of the wattage and it keeps the load on the pannel balanced.
But if the size of heater that is need is available in 120 then you can use that. But the wiring has to be bigger for the same wattage (or BTU outputs).
W = V*I (power, watts - voltage x current)
"Can I use these with 12 guage wire?"
Maybe, that depends on the current rating of the particular unit. Might be able to use #14, might need #10 or even bigger.