Bath code question

Henley | Posted in General Discussion on May 10, 2008 11:12am

Reading Cauldwell’s Plumbing book and he lost me.

My understanding was you need at least one GFI by the Sink on it’s
own circuit. Seams like he’s saying you can share it with most anything in the room.

“As long as the Receptacle doesn’t tie in to any other bath, code now allows you to load it up with anything and everything in that Bathroom”.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. McMark | May 10, 2008 11:19pm | #1

    The GFCI should not need to be on it's own circuit.  A bath load is not very great.

    1. Henley | May 10, 2008 11:40pm | #2

      Well it wasn't the load.
      I thought code required it for some safety reason. You can be sure I don't want to pull another wire for nothing.

    2. JTC1 | May 11, 2008 01:00am | #4

      ....a bath load is not very great.......

      until they turn on the heater and the hair dryer at the same time.

      On bath remodels, I like to have two 20A lines into the bath. One for the required outlet and a second for a heat / vent / light unit (either initial install or future).

      Jim

      Never underestimate the value of a sharp pencil or good light.

      Edited 5/10/2008 6:10 pm ET by JTC1

  2. john7g | May 10, 2008 11:52pm | #3

    Not an electrician but I think code says that bathrooms need a dedicated circuit or bath-only circuit that serves multiple baths (aka all baths on 1 circuit with GFCIs somewhere to protect all outlets in the baths).  Lights on the same dedicated circ but not GFCI-ed. I don't like the idea of all baths on 1 circuit when I think about multiple hairdryers running simultaneously. 

    a real electrician will be along shortly.

  3. RalphWicklund | May 11, 2008 02:24am | #5

    Just had a discussion with our city electrical inspector the other day and a reading from the NEC.

    Seems you can have any number of bathroom outlets on a single 20A circuit and if your laundry (washer) is in the same room the washer outlet can be the GFCI and the bath proper can be downstream.

    But if you have a laundry room next to the bathroom, as I did, and the electricians put the GFCI in the laundry room and protect the bathroom from there, it is not allowed.

    1. Henley | May 11, 2008 02:42am | #6

      What about the lights and vent fan?

    2. User avater
      BillHartmann | May 11, 2008 03:18am | #7

      The GFCI protection can be anyplace. Even in the garage or crawlspace. But not receptacles.The code says that a bathroom needs a 20 amp circuit(s) for receptacles.That circuit can feed anything in ONE bathroom receptacles, lights, fan and possible a small heater. Many heaters would require their own circuit.The other option is to only feed the receptacles with the bathroom circuit, but it feed receptacles in multiple bathroom.Without looking the specific spacing you need at least one receptacle by each sink. You can have multiples.ALL receptacles in the bathroom need to be GFCI protected. The code does not specify another other devices that need GFCI protection. But it does require installations to follow manufactures requirments. And some vent fans when installed over a shower or tub require GFCI protection.Also whirlpool tubs require GFCI protection and usually a dedicated circuit. A dead face GFCI is often used for those. I think the same for electric heated floors, but never checked the details on it.About the washing machine."210.11 Branch Circuits Required
      Branch circuits for lighting and for appliances, including motor-operated appliances, shall
      be provided to supply the loads calculated in accordance with 220.10. In addition, branch
      circuits shall be provided for specific loads not covered by 220.10 where required
      elsewhere in this Code and for dwelling unit loads as specified in 210.11(C).
      ...
      (C) Dwelling Units
      ...
      (2) Laundry Branch Circuits In addition to the number of branch circuits required by
      other parts of this section, at least one additional 20-ampere branch circuit shall be
      provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit
      shall have no other outlets.
      ...""210.52 Dwelling Unit Receptacle Outlets
      ...
      (F) Laundry Areas In dwelling units, at least one receptacle outlet shall be installed for
      the laundry.
      ..."A separate circuit and at least one receptale is needed for the laundry area and even if installed in the bathroom it can't be attached to the bathroom circuit.However, if it is in the bathroom then it needs to be GFCI protected. If not in a bathroom (or garage or unfinished basement) then it does not need to be GFCI protected unless it is within 6ft of a sink.BTW, in the "OLD" days (I am guessing be 96, but not sure) the bathroom did not need a dedicated circuit. And GFCI's where relatively more expensive. So it was not uncommon to find something like this. Panel in garage feeds a GFCI for the garage receptacle, then downstream it feeds a couple of bathrooms and then an outiside receptacle..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      1. Henley | May 11, 2008 04:03am | #10

        Hey thanks for the thorough reply.
        I saved it for future reference. This is for my house and is pretty basic.
        Two vanity outlets (double sinks-two outlets)
        Vanity lights
        overhead fan/light
        shower light So I'm thinking one circuit should do it. Thanks again Chuck

        1. User avater
          Matt | May 11, 2008 06:10am | #11

          In another thread someone mentioned a NEC code summary book - or similar - no - not "code check"  This one was specifically on the NEC and hopefully isn't of that "for dummies" series...  Anyone know of the book?

          1. User avater
            BillHartmann | May 11, 2008 08:18am | #12

            I am not sure what you are talking about.I have mentioned the NEC handbook. But it is not a summary rather is the NEC code with a bunch of explanitory and background information added.And some one mentioned Rex Cauldwell's book on house wiring. It is a Taunton DIY wiring guide..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          2. User avater
            Matt | May 11, 2008 03:41pm | #13

            How about this book?  Any good? I have electricians do my work so a book on how to wire a house is not really what I need, however it is advantageous for me to know the codes to help avoid mistakes and delays.

    3. MFournier | May 11, 2008 03:53am | #8

      You are stretching it to say any number of outlets, There is a Max allowed on any circuit I would have to look it up to be sure but I think it is 14 outlets per circuit max. And a there are also any number of appliances that could be installed in a bath or laundry that could require or at least recommend a dedicated circuit. Also I am not a fan of feeding lights and outlets on one circuit. Yes it is allowed but that does not make it a good electrical job. And anyone that says a bathroom does not have a large load does not have teen aged daughters. 2 curling irons one flat iron 2 hair driers 2 vanity mirrors with 4 60 watt bulbs each, a radio and electric tooth brush charger a razor charger a cell phone charger. Add all that to the over head light/fan and the whirlpool tub with heater. I would not want all that on a single circuit.

      1. User avater
        BillHartmann | May 11, 2008 04:02am | #9

        The NEC has no limitations on the number of receptacles on a circuit in residential applications. However, some local amendments do limit them.And the breaker is the only limit on the number of portable appliacnes that can be used on a circuit.Bbut for fixed in place appliances cord connected appliacne if it draws more than 50% of the circuit capacity it needs a dedicated circuit. Not sure of the wording on hardware fixed appliances..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  4. MSA1 | May 11, 2008 04:06pm | #14

    Code referring to baths, If there is one bath in the house, the whole bathroom can by on one 20amp circuit.

    If there are multiple baths, the recepticles from the multiple baths can be on the same 20amp circuit (GFCI protected), but nothing else.

    Doesnt matter what the load may be, code wants that recp isolated.

    Also if you are hanging a light or fan above the shower/tub it also must be GFCI protected.



    Edited 5/11/2008 9:07 am ET by MSA1

    1. User avater
      Matt | May 11, 2008 07:53pm | #16

      >> Also if you are hanging a light or fan above the shower/tub it also must be GFCI protected. <<  Is there a certain distance that a light (for example) needs to be away from a bathtub so that it does not need to be GFCI protected?

      1. User avater
        BillHartmann | May 11, 2008 08:59pm | #17

        "404.4 Wet Locations
        A switch or circuit breaker in a wet location or outside of a building shall be enclosed in a
        weatherproof enclosure or cabinet that shall comply with 312.2(A). Switches shall not be
        installed within wet locations in tub or shower spaces unless installed as part of a listed
        tub or shower assembly.""406.8
        ...
        (C) Bathtub and Shower Space Receptacles shall not be installed within or directly over
        a bathtub or shower stall.""410.4 Luminaires (Fixtures) in Specific Locations
        (A) Wet and Damp Locations Luminaires (fixtures) installed in wet or damp locations
        shall be installed so that water cannot enter or accumulate in wiring compartments,
        lampholders, or other electrical parts. All luminaires (fixtures) installed in wet locations
        shall be marked, ``Suitable for Wet Locations.'' All luminaires (fixtures) installed in
        damp locations shall be marked, ``Suitable for Wet Locations'' or ``Suitable for Damp
        Locations.''
        ...
        (D) Bathtub and Shower Areas No parts of cord-connected luminaires (fixtures), chain-
        , cable-, or cord-suspended-luminaires (fixtures), lighting track, pendants, or ceilingsuspended
        (paddle) fans shall be located within a zone measured 900 mm (3 ft)
        horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall
        threshold. This zone is all encompassing and includes the zone directly over the tub or
        shower stall. Luminaires (lighting fixtures) located in this zone shall be listed for damp
        locations, or listed for wet locations where subject to shower spray."And from the handbook discussion."A revision of 410.4(D) clarifies that securely fastened luminaires installed in or on the
        ceiling or wall are permitted to be located in the bathtub or shower area. Where they
        are subject to shower spray, the luminaires must be listed for a wet location.
        Luminaires installed in the tub or shower zone and not subject to shower spray are
        required to be listed for use in a damp location. GFCI protection is required only where
        specified in the installation instructions for the luminaire.
        The intent of 410.4(D) is to keep cord-connected, chain-hanging, or pendant luminaires
        and suspended fans out of the reach of an individual standing on a bathtub rim. The list
        of prohibited items recognizes that the same risk of electric shock is present for each
        one.
        Exhibit 410.1 illustrates the restricted zone in which the specified luminaires, lighting
        track, and paddle fans are prohibited. This requirement applies to hydromassage
        bathtubs, as defined in 680.2, as well as other bathtub types and shower areas. See
        680.43 for installation requirements for spas and hot tubs (as defined in 680.2) installed
        indoors."Fans would only be controlled by the manufactures installation requirments..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. User avater
          Matt | May 11, 2008 09:51pm | #18

          Thanks Bill.  The text was a little confusing, but the picture made it pretty clear.

        2. MSA1 | May 11, 2008 11:11pm | #19

          Thanks Bill.

  5. renosteinke | May 11, 2008 07:18pm | #15

    If you are only powering the receptacles in the bath, one GFI and one 20 Amp circuit can cover all the bathrooms.

    If you are also supplying the light, fan, etc., with that same circuit, every bath needs its' own 20 Amp circuit.

    Bathrooms are graced with such power for one reason: hair dryers. It might be for only 10 minutes a day, but that circuit is very heavily loaded.
    Call it a difference between the sexes. Men might have a shaver, even an electric toothbrush. Women, on the other hand, have that hair dryer, curling iron, illuminated make-up mirror, and heaven knows what else.

    1. Henley | May 12, 2008 12:35am | #20

      First off thanks for all the info from everyone.

      My plan is to run a single circuit for the one bath (20 amp). Gfi at
      the panel.
      Two gfi outlets for vanity ( I know redundant but it looks official)
      and then one fan/light, two vanity lights, and one shower light.
      Any future baths will be on their own circuit. I think that covers it right?

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers

Listeners write in about removing masonry chimneys and ask about blocked ridge vents, deal-breakers with fixer-uppers, and flashing ledgers that are spaced from the wall.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Keeping It Cottage-Sized
  • Townhouse Transformation
  • Mortar for Old Masonry
  • Grout-Free Shower Panels

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data