Best Practice on tying grounds together

globaldiver | Posted in General Discussion on February 18, 2006 12:12pm

I’m roughing in the wiring to my new shop.  I have several 4-position boxes (PVC) which will have a number of 3-way circuits in each.  I can count up at least 8 different ground wires between the three home-runs coming into the boxes, plus the 12/3 runs for the three-way switches.

I’m going to tie all the grounds together and pigtail for the grounds to the switches.  A big wirenut just doesn’t seem the right way to go….so what is the best practice on neatly tying all of that stuff together? 

On a somewhat related issue, I’ve had some of the plastic romex-keeper tabs break entirely off of the back of the box when I put the romex through…..the romex is of course nailed off near the box, but without anything holding it at the back of the box it is a little floppy.  Should I plug around the romex with something in the box?  It just sort of looks wrong…… –Ken

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Link | Feb 18, 2006 12:35am | #1

    First off, I'm not an electrician.

    It sounds to me like you should have a small sub panel with it's own isolated ground tied back to the main panel's ground.  Or maybe I don't understand what you're doing.  I don't like having different circuits in the same box.  I don't think it's against code, I just don't like to do it.  If this is one circuit controlling both lights and outlets, I really don't like that.  And, I think that's against code.  You don't want to be using a table saw, trip the breaker and find yourself in the dark holding one end of a sheet of plywood.

    As for the tabs breaking off, I've just nailed off the romex near the box.  I'd be curious as to what others do.

    1. globaldiver | Feb 18, 2006 01:19am | #2

      This is just a four-gang box; all switches and no outlets.  Not a separate sub-panel or anything like that.

      The table saw (and the other major tools) will be on its own dedicated 220 circuit.

      For the lights, one circuit each for some ceiling mounted can "spot" lights over a work bench; main flourescent lighting (two banks off of one circuit) and a metal halide "low bay" task light (400 watt...and that sucker puts out an amazing amount of light!).

      Overkill on having separate circuits for each lighting type, but I'm leaving room for futher expansion . . .

      With two or even three gang boxes I've just tied all the grounds together and pig-tail to the switches.  In the four gang box, especially with the three-way romex in there, too it just seems a bit messy..... --Ken

      1. Link | Feb 18, 2006 01:57am | #3

        You might try breaking all the grounds up into two groups tied together with another ground pigtail. 

        When I've installed several outlets in a large multi-gang box I've looped all the grounds together with one long ground wire.  But, that was easy because I could wire all the outlets together before I even put them in the box.  Not so easy with separate switches.

  2. User avater
    maddog3 | Feb 18, 2006 01:59am | #4

    what's wrong with a big wirenut ?

    if you're tight for space you could probably use a jumper between smaller bundles......just remember which one is the ground from the panel........
    .
    .
    .
    personally , I don't run Romex, only conduit, so somebody here may have the "best" solution, but a bigwirenut would be my choice...

    that broken plastic thing??
    I wouldn't worry about it..... jam some duct seal in there to keep bugs out

    1. User avater
      Sphere | Feb 18, 2006 02:22am | #5

      Easiest and cleanest I can come up with is twistem all up good and tite, leave or add a long enough strand for the pig tail, and crimp a copper crimp sleeve over the twisted wad.

      If the wad is too big for a standard crimp sleeve, cut off a short hunk of soft copper tubing and cinch it down with channel locks.

      Spheramid Enterprises Architectural Woodworks

      Save a few posts, fill in your Profile, we can help!

      1. FrankDuVal | Feb 18, 2006 05:12am | #10

        Sphere's comment: "Easiest and cleanest I can come up with is twistem all up good and tite, leave or add a long enough strand for the pig tail, and crimp a copper crimp sleeve over the twisted wad."This is what the inspectors here in Stafford County VA want to see in boxes larger than two gang. No green wirenuts for them in large boxes. You can leave 3 long wires for pigtails to three switches, or 4 longs for 4 switches. Or of course one really long one to jump between all switches. These crimp sleeves come in several sizes.As mentioned, read the back of the box inside for maximum number of wires allowed.Frank DuVal You can never make something foolproof because fools are so ingenious.

      2. bigman | Mar 01, 2006 05:08am | #41

        "If the wad is too big for a standard crimp sleeve, cut off a short hunk of soft copper tubing and cinch it down with channel locks." That is not an approved method of making a connection, there is no way I would ever do that......

        The copper barrel crimps (Bucannans) are only approved if crimped with the Bucannan Crimp Tool, not lineman pliers or channel locks.

        It is not a big deal to splice 8 grounds plus a long pigtail for the switches under a wire nut, just leave yourself enough wire to work with. If it is to hard to do split it into 2 wirenuts with a jumper as was previously suggested.

        Have'nt any of you guys ever worked on knob tube wiring or the old style BX??? all the splices are soldered (splices dipped in a lead pot) and taped and they have worked without problems for decades, and this was long before they started soldering electronics.

         

  3. Brian | Feb 18, 2006 02:40am | #6

    I agree with sphere - ground crimps are the standard for this job - with all that 3 wire make certain you aren't overloading your box -- buy a deep one!

     

    Treat every person you meet like you will know them the rest of your life - you just might!
    1. Treetalk | Feb 18, 2006 03:45am | #7

      I used to twist all my grounds together but man its hard bending and shoving it all back into  box as opposed to individual wires crimped or nutted together.

    2. globaldiver | Feb 18, 2006 09:19am | #16

      bought the biggest, deepest one I could, because I knew I'd have a lot of cable in it....

  4. pm22 | Feb 18, 2006 04:28am | #8

    For the grounds, there are several other options.

    One is to use a WAGO connector. WAGO is a proprietary brand but Ideal makes a similar version. Home De Pot sells them. Little plastic things with holes in them. Strip the wire [1/2"?] and plug them in. Almost like backstab but better internal connection. Google WAGO.com. Some of these devices may accept up to 8 wires each.

    If you use conduit you only need one ground wire per conduit. Or you could even use the metal conduit itself as the ground. Legal but conduit, EMT, sometimes falls apart due to heat/cold expansion/contraction.

    On a recent project, I had a 12" X 12" by 6" deep metal box. It had about 38 MC circuits coming in and about 5 3/4" EMT conduits going out. How to tie all those grounds together? I went to the electrical supply house and bought a ground bar for $8. It worked perfectly. With grounds, it is usually acceptable [per listing] to have more than one green wire per hole.

    As for the Romex clamps being broken, I think the Code has you staple ["support"] within 12" of the box but if no clamps them you must staple within 8".

    ~Peter

    The recent Seattle-Tacoma earthquake was all President Cheney's fault.

    1. globaldiver | Feb 18, 2006 09:20am | #17

      Thanks.  I'll look for that connector.

      The problem with a wirenut is if I have individual pigtails I'd have something like 12 wires in one wirenut.....I can get it down to about 9 if I run one long pigtail and daisy-chain to each switch.

      --Ken

    2. globaldiver | Feb 18, 2006 09:25am | #19

      On the cable fixing...I think the current NEC code requires a staple within 6 inches of a plastic box, which I've done.  I'll probably just stuff some putty back in there.  Nothing else it ought to minimize air infiltration (not a huge worry since this is a shop rather than a residence.  --Ken

  5. JohnSprung | Feb 18, 2006 04:36am | #9

    Per G-B, you can get up to six #12's in their #89 or H-2 wire nuts.  Or, you could twist the whole shebang together and solder it. 

     

     

    -- J.S.

     

    1. Don | Feb 18, 2006 06:29am | #12

      waitaminit, John. I thought that soldering was absolutely verboten by code.DonDon Reinhard
      The Glass Masterworks
      "If it scratches, I etch it!"

      1. caseyr | Feb 18, 2006 08:43am | #15

        I thought so also. The AHJ in Contra Costa County, Calif., indicated that soldering of grounds was verboten - the heat from a short might melt the solder and open up the ground circuit.

        1. Don | Feb 18, 2006 03:13pm | #20

          Casey: Never got anything from an inspector - my understanding was a fear of corrosion w/i the solder joint or a cold joint, resulting in a high resistance to ground and a resultant danger to people getting across the voltage.DonDon Reinhard
          The Glass Masterworks
          "If it scratches, I etch it!"

      2. r | Feb 24, 2006 06:00pm | #25

        In the 1999 NEC, Section 250-8 says "Grounding conductors and bonding jumpers shall  be connected by exothermic welding, listed pressure connectors, listed clamps, or other listed means.  Connection devices or fittings that depend solely on solder shall not be used."  (For what it's worth, the next sentence bans sheet metal screws to connect grounding conductors).

        One of those fortunate situations where the code is unambiguous.

        1. JohnSprung | Feb 28, 2006 04:46am | #26

          OK, so twist and solder should be OK. 

          Solder is vastly superior to any other way of splicing wire.  That's why we use it in electronics.   

           

          -- J.S.

           

          1. Don | Feb 28, 2006 05:09am | #27

            Johjn: yabut, You have to be licensed to solder electronics. At least for military items. Corrosion in a solder joint is too easy to get for the inexperienced/incompetent.DonDon Reinhard
            The Glass Masterworks
            "If it scratches, I etch it!"

          2. JohnSprung | Feb 28, 2006 11:16pm | #35

            > You have to be licensed to solder electronics. At least for military items.

            I've never heard of that.  NASA in the very early days did have soldering school, and issued certificates.  But their concern was with not nicking too many strands, not using too much solder because of the weight, stuff like that.

            > Corrosion in a solder joint is too easy to get for the inexperienced/incompetent.

            Corrosion is only an issue with acid fluxes.  In electronics, we use rosin core, nobody ever sees any corrosion here.   

             

            -- J.S.

             

          3. Don | Feb 28, 2006 11:51pm | #37

            John: Last I knew, before retiring, was that only qualified personnel were permitted to solder, & you needed a license, essentially like a pressure vessel welder, and you had to periodically be re-qualified. When talking w/ some folks at Honeywell way back in the late 80's that was still the case. I also spoke w/ a woman whose husband had a small business that required soldering military electronics. She was in the process of getting qualified as a solderer.Corrosion may not be a problem, but "Cold joints" are, and that is a real problem. I've done some soldering, building some electronics kits and had problems w/ some cold joints, even using rosin core. I started out back in 1959 in the Nike Air Defense business, and none of the battery personnel were permitted to solder - anything that required a broken joint & re-soldering required that the board go to the next level of maintenance, where they had licensed solderers. Granted, that was back in the days of tubes (You know what they are, I presume - Grin) and a ton of wires, and there were a heck of a lot more individual solder joints. I recall seeing Honeywell manufacturing PC boards in 1990 in Atlanta using a wave soldering machine that got people completely out of the loop. I vaguely recall that on some first generation or second generation PC boards that a repair requiring soldering meant the board was returned to the factory unless it were a combat emergency.DonDon Reinhard
            The Glass Masterworks
            "If it scratches, I etch it!"

          4. JohnSprung | Mar 01, 2006 01:54am | #38

            > Corrosion may not be a problem, but "Cold joints" are, and that is a real problem.

            True, but a problem we can solve.  Cold joints can result from having not quite enough soldering iron for the job.  You just have to get the right tools and use them at the right temperatures. 

            A cold joint can also happen if you don't have things mechanically sound, and want to depend on the solder to hold them.  If they move during cooling, you can get a really nasty cold joint. 

            Cold joints are usually fairly easy to tell by their dull surface, and fairly easy to fix.   

             

            -- J.S.

             

          5. philarenewal | Feb 28, 2006 05:16am | #28

            Uh, I don't know about the best way, but the way required for grounding is exothermic welding or pressure connectors or clamps (or other listed means).  Solder won't cut it because it melts at too low of a temp.

          6. User avater
            SamT | Mar 01, 2006 04:13am | #39

            Phil,

            Depending on the compound, solder for electrical applications melts between 360*f and 600*f. The Kindling Point for wood is around 660*f.

            Any heat to melt the solder on a well formed soldered connection is going to be coming from a source external to the connection.

            If you're melting the solder, you've got major problems with the rest of your system.

             

            A good soldered connection can be mechanically stronger than the wires it's connecting.

            A good soldered connection has less resistance across it than the same length of the larger of the wires it's connecting.

            However;

            A soldered connection cannot be inspected without removing its' insulation.

            Soldering takes much more skill and training than twisting a wire nut.

            A poor solder job can be more dangerous than a poor wirenut job.

            SamT

            Edited 2/28/2006 8:15 pm by SamT

          7. philarenewal | Mar 01, 2006 05:16am | #42

            Sam:

            I don't disagree with you.  But if the house burns, or someone dies, failure to follow the applicable code is usually considered negligence per se and could be grounds for a criminal charge of negligent hommicide.  If you are doing it for pay, the homeowner's insurance company will also pursue you in subrogation. 

            There is no question that if a ground connection melts solder, there are major problems (the heat source would be current flow through the ground wires, not external).  But what the code is addressing in that specific situation is just that;  something has gone horribly wrong but the ground bonding must be preserved -- if something is that wrong, odds of someone being hurt by an open ground have gone up quite a bit.

            I don't mean to debate the relative merits of one connection method over another.   I'm sure soldering would usually work (I mean really sure; that's how the best knob and tube circuits were run and the ones that were soldered are the ones that won't burn even if disturbed).  The rules for grounding are pretty clear.  I don't make the rules, I just try to follow them.

            As an anecdote, I have been a trouble shooter on more than one system where there were over a hundred amps, on one many hundreds of amps, flowing through a grounding system (insustrial sites, but the principles still apply).  That is not supposed to happen, obviously, but it can when everything else is not done just right.  Anyway, my $.02.

            Best regards,

            -Keith

          8. alanj | Mar 01, 2006 07:03am | #44

            I'm not an electrician but do it once in a while on simple jobs.The book I follow was written by an old master electrician (Knight) who designed the book to aid apprentices in there journeyman test.He says that soldering is fine and sometimes necessary to avoid over-filling a box. A soldered joint apparently is not counted. Which makes sense as there is no wire nut taking up room.I am in Canada, so maybe a Canadian electrician will chime in.On a point of logic, it seems to me that if you have enough amperage and voltage running through a circuit to melt solder, then a wire nut or whatever is not going to save the show!Alan

          9. FrankDuVal | Mar 01, 2006 05:08pm | #48

            "As an anecdote, I have been a trouble shooter on more than one system where there were over a hundred amps, on one many hundreds of amps, flowing through a grounding system (insustrial sites, but the principles still apply). That is not supposed to happen, obviously, but it can when everything else is not done just right. Anyway, my $.02.Best regards,-Keith"You know, but for others this is a reason grounding and neutral conductors are ONLY tied together at one point. The reason this ground current happens is usually because the neutral conductor has been connected to the grounding conductor in two or more places. When this happens, the neutral current now has two paths, both the neutral conductor and the grounding conductor. A parallel circuit. The neutral current is divided by both conductors (current ratio by the ratio of their resistance). So if the circuit is pulling 100 amps of neutral current, and the grounding and neutral wires are the same size, the ground wire will be passing 50 amps! Not a safe situation.
            Frank DuVal You can never make something foolproof because fools are so ingenious.

          10. torn | Feb 28, 2006 05:38am | #29

            Ummmm, I thought the earlier post
            <i>"Connection devices or fittings that depend solely on solder shall not be used."</i>
            indicated that the code specifically excluded twist & solder. Or are you saying twist, then solder, then wirenut? (In other words a mechanical as well as solder connection. I would worry in this case that the wirenut would grab only the solder, and then if the solder melted, the mechanical connection would fail and you'd be in worse shape than if you'd never soldered...)I think the primary reason solder is used in electronics is because it's damm near impossible to fit more than a couple gray wirenuts on a circuit board!! <g>I've never had to deal with the large number of grounds that you're tying together, but it seems like the majority of responses have encouraged crimp splices. I'm curious why you still want to solder, especially given its questionable status in the code?

          11. JohnSprung | Feb 28, 2006 11:32pm | #36

            > <i>"Connection devices or fittings that depend solely on solder shall not be used."</i>indicated that the code specifically excluded twist & solder.

            No, as I read it, it excludes solder without a twist, something that would fall apart without the solder.  Twist plus solder is not "solely" dependent.

            > I think the primary reason solder is used in electronics is because it's damm near impossible to fit more than a couple gray wirenuts on a circuit board!! <g>

            No, it's because solder gets you as close to zero resistance for the life of the system as you can get.  We use it on big stuff, not just boards.  Look at power supplies, power amplifiers, HMI's,  UPS's, etc.  We even solder the lugs onto 4/0 cable. 

            > it seems like the majority of responses have encouraged crimp splices. I'm curious why you still want to solder, especially given its questionable status in the code?

            Because solder is better than crimping.  It covers the whole surface, not just point contact.  It forms an alloy with the copper, turning the  whole thing into essentially one piece of metal.  It gives you the lowest possible resistance, and therefore the least heat. 

            Somebody else mentioned corrosion.  Try to corrode a solder joint, and it'll work until you corrode thru the wires.  Do that with a crimp, and it'll corrode between the wires and fail far earlier than a solder joint. 

            Bottom line, code should not forbid better methods and require worse ones.   

             

            -- J.S.

             

  6. IdahoDon | Feb 18, 2006 06:28am | #11

    Back home our standard for grounds is twist em together and add a crimp ring.  Neat, tight, easy, works good.

    Around Boise I've seen a number of various things including an electrician that just twists all the grounds and leaves them as is with no mechanical connection.  It's surprising that our tight-ars inspector didn't call him on that one.

    Not an electrian, but stayed at a Best Western last night.

    Don

     

    Beer was created so carpenters wouldn't deliver the morning paper.

    1. User avater
      maddog3 | Feb 18, 2006 06:49am | #13

      hey I tought the smart guys stayed at Holiday Inn.......;>)

      1. IdahoDon | Feb 18, 2006 07:12am | #14

        They probably do.  Hey, never said I was smart.  :-) 

        Beer was created so carpenters wouldn't rule the world.

    2. globaldiver | Feb 18, 2006 09:22am | #18

      And since my friendly Boise inspector is *closely* inspecting my work since I'm not an electrician....I have to be spot on.

      Actually, he's been pretty good to work with so far.  --Ken

      1. IdahoDon | Feb 23, 2006 06:34am | #21

        And since my friendly Boise inspector is *closely* inspecting my work since I'm not an electrician....I have to be spot on.

        Once again our Boise electrical inspector has been driving us crazy.  We have him stop by to explain exactly what he wants for a strange situation.  It then takes us three additional inspections for him to finally quit adding additional crap.

        The kicker was, once he wasn't available and another inspector was covering for him.  There was about $500 of hardware that he didn't think was required but the other guy did. 

        We went from the detached garage to the house and into a new addition with a new pannel.  Between the original grounds and the new grounds we have about a half dozen grounds and one guy said a 7th--a uffer ground was required in our situation, the other guy said no.

        Electrical inspection on new service--power company lineman waiting for the inspection to clear to move connection--inspector said it won't happen today, then approves it 5 minutes later.

        Oh the games we play.  :-)

        1. globaldiver | Feb 23, 2006 07:36am | #22

          I wonder if we have the same one.  Jack?  --Ken

          1. IdahoDon | Feb 24, 2006 07:17am | #23

            Handlebar mustache?

            Edited 2/23/2006 11:29 pm ET by IdahoDon

          2. globaldiver | Feb 24, 2006 07:56am | #24

            Nope.  Cleanshaven. 

  7. cynwyd | Feb 28, 2006 07:12am | #30

    I've used bugs for this type of connecting.

     

    http://www.foxelectricsupply.com/content/products/ProductDetail.asp?qsCatID=24629&qsProductNo=8H

    1. FrankDuVal | Feb 28, 2006 07:19am | #31

      Bugs? Around here thems is split bolts.Frank DuVal You can never make something foolproof because fools are so ingenious.

      1. en2ohguy | Feb 28, 2006 08:04am | #32

        Cable clamps/split bolts  same/same here too...bugs is a new one one me...just out of curiousity...are these switches single poles?  if so, since when do we attach ground?   leave the incoming ground extra long, after running it to the box screw twist it up with the rest and clamp 'em, then pigtail as needed off the long tail of the incoming....

        1. FrankDuVal | Feb 28, 2006 08:20am | #33

          The switches need to have a ground wire attached when screwed to a plastic box.Frank DuVal You can never make something foolproof because fools are so ingenious.

    2. philarenewal | Feb 28, 2006 08:22am | #34

      We call 'em bugs in Philly too.

  8. booch | Mar 01, 2006 04:49am | #40

    Ring em out. It is 20 minutes out of your life and the grounds need to be identified to the circuit. It is a slippery slope to calling all common's the same too.

    The commons in my old house were mixed as well. When you get that tingle on a dead circuit and then find 27 to 50 volts on the common you have to wonder.

    It isn't that hard. Just take your time. Oh yea, pitch the plastic and go for steel or at least get replacement plastic boxes. They are only 97 cents each. The steel ones take more abuse in a shop

    Jack of all trades and master of none - you got a problem with that?
    1. globaldiver | Mar 01, 2006 07:02am | #43

      In other words, you'd say don't tie the grounds in a box together?

      1. booch | Mar 01, 2006 07:31am | #45

        Yes tie em together but sort out the circuits. The wiring plan sounded pretty murky in the first paragraph of your original description.

        We all know the white and the green / bare copper go to the same place in the main load center---eventually. My point is there are quirks that make them unequal potentially. Examples are a GFI circuit, secondary load center, or just plain shoddy wiring cobbled together from the source to the box you are working on.

        It's sort of like washing your hands after going to the bathroom. yea, you probably won't die or even get sick but chances are some day something can happen that isn't good.

        I just flash back to my old house and a circuit that should have been dead wasn't. All because someone tied together the common from a different circuit. Nothing to die from but not good practice either.Jack of all trades and master of none - you got a problem with that?

        1. globaldiver | Mar 01, 2006 07:44am | #46

          The wiring plan is clear enough (to me anyhow).  Probably just a little sloppy on how I described it.

          The biggest issue for me was looking at all the three way wires coming in a 4 gang box....and wanting to manage the conductors to get a "good and workmanlike" installation.  --Ken

          1. booch | Mar 01, 2006 05:04pm | #47

            I appreciate the issue. I have one memorable 3 gang box with two 4 ways in it. Wire tags (brady brand) were a great help. Still it consumed hours of work.

            The best help was the different type of wirenut I switched to. I have stepped away from the std wirenut twist on type. Instead I use the Wago, Buchannan or Ideal 'push nut' type of wire connector.

            Std wirenuts get applied to a twisted tumid collection of like conductors. After the nut is applied this is like bending a curtain rod and tucking it back in the back of the box. (broken plastic box tabs sound familiar?) If you use the pushnuts you instead have 4 or more wires all straight and parallel connected at the end. Now when you try to tuck it in the box you have a very bendable structure. it tucks much easier and assembles much faster.

            Electrical supply houses have one or all types in house. The only real issue is that they (pushnuts) don't like the fine strand wire like is found on light fixtures. There is some hard to decipher legend that describes the number of strands per ga on the pushnut box but suffice it to say that solid wire is best.Jack of all trades and master of none - you got a problem with that?

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Simple and Discreet Countertop Power

A new code-compliant, spill-safe outlet from Legrand offers a sleek solution for a kitchen island plug.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data