Bonding ground and neutral in subpanel
NBGT | Posted in Construction Techniques on March 4, 2016 10:56am
Hello,
I’m in the midst of a renovation project, and I have a concern that the electrician has not wired a subpanel box inside the house correctly.  The electrician has installed three panel boxes: 1.) the main box on the exterior of the house, 2.) a large sub-panel box (that feeds from the main box), and 3.) and a small sub-panel box (that feeds from the larger sub-panel box).  The issue that I see is that I think the neutral and the ground are bonded in the large sub-panel box (picture below).  My understanding of installation that conforms to code is for the neutral and the ground to only be bonded at the main panel box.  Sub-panel boxes should have separated neutral and grounds.
Is there any situtation where a subpanel should have a neutral and ground bonded together?
I want to be sure I’m informed before I talk to the electrician about this.
Thanks for the advice!
    Mike_Mahan | Mar 04, 2016 11:59am | #1
    Neutral and ground should not be bonded in a subpanel. It used to be that in a seperate building you could install a new grounding electrode and bond neutral and ground just as in a service. No more. You have to cary a seperate ground wire (which appears to have been done.) and isolate the ground from the neutral. Congratulations on catching this. A good inspector will.
  2. renosteinke | Mar 05, 2016 09:52am | #2
    Where's the Inspection?
    The best party to ask is your local electrical inspector. Let him look overf the entire job and consider the whole picture.
    spclark | Mar 09, 2016 09:46am | #3
    Agree
    that local electrical inspector is your go-to guy for final determination.
    From your description it sounds like your FIRST box would be your meter socket, outside the structure?
    Unusual in most cases to have a main box outside as that's where your main disconnect ought to be located.
    Sub-panels can be anywhere downstream in that or adjacent structures & should NOT have neutral & ground bonded.