BREAKERS – sizing for a garage sub panel

toolbear | Posted in Energy, Heating & Insulation on February 9, 2009 12:18pm

BREAKERS – sizing for a garage sub panel?

@@@

This remodel is getting a 60a main lug subpanel in the detached garage via a trench. I can’t quote chapter and verse on this, but others can.

What is the protocol for sizing the breakers at the house panel and the garage for the feeder? 60A/2P house side, same garage for the disconnect? Or larger on house side.

I think a 12 space main lug enclosure might be right for the garage. A little room to grow is nice.

The ToolBear

“You can’t save the Earth unless you are willing to make other people sacrifice.” Dogbert

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. renosteinke | Feb 09, 2009 02:06am | #1

    If it's a 60 amp panel, you can't supply it with more than 60 amps. That's a 2-pole 60 amp breaker, feeding a #6 run to the garage. Note that you need to run FOUR wires ... two hots, a neutral, AND a ground.

    Then at the garage, you also get to instal a ground rod. Do not join the neutrals and grounds together at any point.

    As for the circuits in the garage, size tham according to the loads they supply. Ordinary receptacles need to be GFCI protected.

    1. toolbear | Feb 09, 2009 02:16am | #2

      If it's a 60 amp panel, you can't supply it with more than 60 amps. That's a 2-pole 60 amp breaker, feeding a #6 run to the garage. Note that you need to run FOUR wires ... two hots, a neutral, AND a ground.@@@Good to hear. That's what I had in mind - 60a breaker on both ends. garage ground rod and an isolated neutral bus bar in the garage panel.Probably run this in PVC conduit in the trench and transition to rigid where it daylights. Will suggest they run another conduit for any low voltage stuff they might think of later - while the hole is open.
      The ToolBear

      "You can't save the Earth unless you are willing to make other people sacrifice." Dogbert

      1. drh | Feb 09, 2009 07:44am | #7

        If your subpanel is fed by a single branch circuit, you dont need the ground rod as long as you are running a ground wire. See NEC 250.32(A).

        1. renosteinke | Feb 09, 2009 08:32pm | #12

          You are misreading the NEC, and confusing your terms.

          The circuit that feeds a panel is a FEEDER, not a branch circuit. He most certainly needs both a ground rod and a ground wire - in addition to a neutral.

          As for the four-wire feed, I will admit that this opinion was not clear until the 2008 NEC. Poor wording in the NEC left some room to argue that you didn't need all four wires.  That has since been cleared up.

          1. drh | Feb 09, 2009 09:52pm | #14

            I am not misreading. In NEC 2008 250.32, titled "Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s)", the exception to (A) states:"A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non-current-carrying metal parts of equipment."It sounds like his case applies.

          2. gfretwell | Feb 09, 2009 10:07pm | #15

            ... but this is NOT a branch circuit. Go read the definitions in article 100

          3. drh | Feb 09, 2009 10:54pm | #17

            In what situation are you then proposing this exception would apply?Are you saying if he wasn't installing an OCPD (and only a disconnect, which is required) in his garage, this exception would apply?Then a month later he swaps it out with an OCPD (that also can serve as a disconnect), he must install a grounding electrode to be compliant?

          4. gfretwell | Feb 09, 2009 11:27pm | #18

            The exception to the electrode system in a second building was put in to make simply stringing an extension cord out there less attractive. Basically what it says is if you have one branch circuit going to some outlets in a second building you don't need a grounding electrode. You still need a means of disconnect.
            It still must be made clear, if you are feeding a panel you have a feeder. A branch circuit is anything beyond the last panel.

          5. drh | Feb 10, 2009 12:12am | #19

            So in your example of running one branch circuit for some outlets, you would still need a disconnect. A panel that is suitable for use as service equipment is allowed to serve as a disconnect... are we saying that in order for the exception to apply you have to use just a simple disconnect?When I wired my detached garage, I ran a 4 wires (two hots, a neutral and a ground) in a trench from my main panel, off of a 40 amp breaker to a small panel in the garage. I installed two 20 amp circuits in this panel and labeled them both service disconnect. I kept the neutral and the ground separate and did not install a grounding electrode. My inspector passed it with no questions.I understand your point with regards to the definition of a branch circuit, but if it is taken the way you are saying I don't see how you would apply the exception without saying you can't use OCPDs for your disconnecting means.Sounds like there may be some room for interpretation and that you've had it interpreted differently than I have :-)

          6. gfretwell | Feb 10, 2009 04:27am | #20

            You can't have an overcurrent device in the far building as the disconnect and call it a branch circuit. One might argue that if it was a single breaker in a box, not in a "panelboard" and the circuit went straight through (like the box that serves your AC compressor)that was simply a disconnect. It is still technically a feeder between the 2 OC devices.
            In your case you have "a small panel" that splits out 40a to two 20a BRANCH circuits so there is no dispute, the wire you ran is a feeder.

          7. drh | Feb 10, 2009 05:24am | #21

            Still not clear on a situation where you think this exception applies. You are forced to have a disconnect that is not an OCPD?

          8. renosteinke | Feb 10, 2009 05:41am | #22

            The moment you add any sort of overcurrent device, the wire becoms a feeder. A branch circuit is that wire between the LAST overcurrent device, and the appliance.

            A multi-wire branch circuit has two hots and a neutral, and -again- there is no  overcurrent devices on either 'hot' leg between the source and the appliance.

            For example, one can run a light AND a receptacle circuit to the garage, and not need a ground rod for that garage.

            Or, one can run 220 out to the shed for the welder, and not need a ground rod.

            Add a single circuit to either of those examples, or add any form of overcurrent protection at the garage .... and you need to have a ground rod - in ADDITION to the ground wire back to the house.

            The panel makes all the difference in the world. Otherwise, to use your logig, there's not a building in the country that would need a ground rod - after all, there's sure to be some sort of overcurrent protection at the power company generating plant!

            I suggest that ALL users of the NEC pay particular attention to Article 90. This 'introduction' makes clear that the code presupposes that you already know the trade, and that the NEC is neither a design manual, nor an instruction manual.

          9. gfretwell | Feb 10, 2009 05:57am | #24

            The exception would apply if I ran a single circuit out to the shed, in the shed I had a switch that turned off that whole circuit (and perhaps another switch for the light).
            To expand that to it's extreme, it could be a 20a 4 wire circuit with a 2 pole disconnect switch in the shed and a mix of 120 and 240 volt loads but it is still a single multiwire circuit. You are limited to 20a per leg on this circuit and it would have to be a 2 pole breaker up at the house.

            Edited 2/9/2009 9:58 pm ET by gfretwell

          10. jimjimjim | Feb 10, 2009 01:20pm | #25

            I'm with dfret... and renos...  regarding branch circuit conductors vs. feeder conductors.

            Using your detached garage example (and maybe I'm beating a dead horse here), if we assume your 2 20A circuits are 120V, then the feeder breaker in the main (house) panel only needed to be a 20A breaker.  If its a 40A as you say, then your FEEDER conductors between the main panel and the garage better be bigger than the 12 AWG in the 2 garage BRANCH circuits.

            If I had been your electrician, you wouldn't have a small panel in the garage, the disconnect would have been a 20A rated DPST switch in a small box where the conductors enter the garage.  The 2 hots would be switched.  Your branch circuit conductors (from the house panel) would have been 12 AWG with a 20A (2-pole) branch circuit breaker in the house panel.  You would have 1 multiwire branch circuit in the garage.

            Or if you really ran larger feeders with the 40A breaker in the house panel, then I would have been pounding in ground rod(s) at your garage small panel with the 2 20A breakers.   Your inspector gave you a pass.

            If instead you have 1 or 2 240V circuits in the garage, then your small garage panel is a subpanel and the conductors from the main panel to the garage panel are again FEEDERS.  And your inspector gave you a pass.

             

          11. ChrisComGC | Feb 09, 2009 10:11pm | #16

            Does ToolBear need to consider upsizing the wire size due to voltage drop due to the distance from the house to the garage?

    2. arcflash | Feb 09, 2009 02:53am | #3

      I believe plugs serving permemant loads like large regrigerators do not need to be GFCI, or not easily accessible ones like in the ceiling for garage door openers. Other than that, GFCI all the way, its just safer.

      1. toolbear | Feb 09, 2009 07:26am | #4

        I believe plugs serving permemant loads like large regrigerators do not need to be GFCI@@@As I recall, no. Nor should they be - unless you want your side of beef to defrost when the GFI trips soon as you are out the door on vacation.But then you have to mount a single outlet dedicated to the fridge.The ToolBear

        "You can't save the Earth unless you are willing to make other people sacrifice." Dogbert

        1. gfretwell | Feb 09, 2009 07:32am | #5

          The only exceptions in the 2008 code are ice melting systems and alarm panels.
          All of those other exceptions are gone, including sump pumps and refrigerators.

          1. rasconc | Feb 09, 2009 07:36am | #6

            Darn we are getting so safe.  Are they going to make us wear heavy rubber gloves in rooms without gfci's next?For those who have fought for it Freedom has a flavor the protected will never know.

          2. gfretwell | Feb 09, 2009 10:02am | #8

            When your AHJs adopt the 2008 there really won't be any rooms without some ground fault protection since it is built into the mandated AFCIs at 30ma that will have to be virtually everywhere ... and yes NFPA is out of control.

          3. davem | Feb 09, 2009 04:11pm | #9

            if there is a 60 amp breaker in the main panel feeding the sub, is there a need for a main breaker in the sub panel?

          4. User avater
            BillHartmann | Feb 09, 2009 04:41pm | #11

            "if there is a 60 amp breaker in the main panel feeding the sub, is there a need for a main breaker in the sub panel?"A service to a separate structure needs a disconnect switch. It does not need a overload protection as the feeder breaker provides that.And a main breaker in a sub-panel is the easies and cheapest way of providing the disconnect..
            William the Geezer, the sequel to Billy the Kid - Shoe

          5. renosteinke | Feb 09, 2009 08:36pm | #13

            Here local codes have a major effect.

            The idea of running wires without overcurrent protection all the way to the new panel brings up the 'tap rules,' and I really don't like that idea at all. So, we start with a breaker feeding the wires that go to the new panel.

            At this point, we don't "need' a main breaker at the new panel. Since it's a separate building, however, we need some form of main disconnect - and local rules usually require this to be on the outside of the building.

  2. User avater
    BillHartmann | Feb 09, 2009 04:38pm | #10

    Here is my sizing suggestions on a garage sub panel.

    First add up the NAMEPLATE data on the largest collection of equipment that will be used at one time. If this is a home workshop that might be a TS, DC, some lights and heat/AC.

    In most cases 60 amps is fine.

    Now if there is going to be a hot tub or pool off of this panel then you need to check the sizes of that equipment.

    However, I recommend a 100 amp panel. Commonly available 60 amp panels are usually limited to 8 or more slots.

    100 amp 20 slot pannels are common and cheap.

    Now the feeder breaker can't be any larger than then SMALLEST of the ratings of the feeder wires or the sub-panel.

    So I would use a 60 amp breaker and feeders, but with the 100 amp sub-panel.

    The sub-panel does not need overload protection. It is already protected by the feeder breaker.

    But the building does need a disconnect. And the 100 amp main breaker serves that purpose.

    Now for the ground electrode. This assumes that it is a detached building. If attached it does not need one.

    If this is new construction and the slab/footing are not in it should have a Ufer ground electrode. That is a copper wire burried in the concrete or a connection to the rebar.

    If not then use ground rodS. Unless you have the ground rod tested and it has less than 25 ohms then yuo need 2 at least 6 ft apart. Since this uses special equipment it usually not done and just defaults to the 2 ground rods.

    .
    William the Geezer, the sequel to Billy the Kid - Shoe
    1. toolbear | Feb 10, 2009 05:52am | #23

      First add up the NAMEPLATE data on the largest collection of equipment that will be used at one time. If this is a home workshop that might be a TS, DC, some lights and heat/AC.@@@ They want to sell the place, so we can guess. Worked on a remodel on a 6 mil four floor with elevator and miles of crown molding view home. He had one (1) outlet in the garage. We will do better.In most cases 60 amps is fine.Now if there is going to be a hot tub or pool off of this panel then you need to check the sizes of that equipment.@@@ I doubt that. Not in plans.However, I recommend a 100 amp panel. Commonly available 60 amp panels are usually limited to 8 or more slots.100 amp 20 slot pannels are common and cheap.Now the feeder breaker can't be any larger than then SMALLEST of the ratings of the feeder wires or the sub-panel.So I would use a 60 amp breaker and feeders, but with the 100 amp sub-panel. @@@ OK, makes sense and I like space in a panel. Buy 100, wire to 60.The sub-panel does not need overload protection. It is already protected by the feeder breaker.But the building does need a disconnect. And the 100 amp main breaker serves that purpose.@@@ If I follow this ... get a 100A panel with main breaker instead of a main lug panel. 60A breaker at house side feeding garage thru 100A breaker on garage panel, which serves as a disconnect.Thanks for the input.Now for the ground electrode. This assumes that it is a detached building. If attached it does not need one.If this is new construction and the slab/footing are not in it should have a Ufer ground electrode. That is a copper wire burried in the concrete or a connection to the rebar.If not then use ground rodS. Unless you have the ground rod tested and it has less than 25 ohms then yuo need 2 at least 6 ft apart. Since this uses special equipment it usually not done and just defaults to the 2 ground rods..The ToolBear

      "You can't save the Earth unless you are willing to make other people sacrifice." Dogbert

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Custom Built-ins With Job-Site Tools

From building boxes and fitting face frames to installing doors and drawers, these techniques could be used for lots of cabinet projects.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data