I am replacing my boiler with a new high-efficiency boiler. This requires reconfiguring my exhaust.
Two PVC pipes will exit my condo and then be ‘snorkeled up’ to the ‘code’ guidelines. I have a piece of framed lattice about 3.5 feet above grade. Will this lattice work need to be moved?
Replies
Can you use pvc for the boiler vent?
"Put your creed in your deed." Emerson
"When asked if you can do something, tell'em "Why certainly I can", then get busy and find a way to do it." T. Roosevelt
yeah, regular pvc for the combustion air and ppvc for the exhaust.in my jurisdiction.
Yes, PVC will be used for the 'snorkel'.
How far from grade will the upper elbow be?
Could you explain what the concern is with the lattice? Is it a vertical piece against the house to grow vines on? Is it a screen around a deck? Do you want to attach the pipe to the lattice or run up behind it?
I want to know if the existing lattice needs to be moved before the PVC 'snorkel' is installed. My feeling is the the plumbers will just put the PVC where they need to without any regards to what may be in their way or aesthetics. I'm just trying to stay ahead of them. After all, this is just my garden...
So, the question remains how far above grade?
As DanH recommends, check the installation instructions. In general, most manufacturers want the termination to be at least 12" above grade, and there are horizontal clearances from inside corners, windows, overhangs, and ventilation air intakes, whether powered or not.
There should be a diagram of vent clearances in the installation instructions that will make it easy to see what's needed.
Read the installation instructions for the boiler. They will be fairly explicit about distance from various obstructions.
Typically:
a. Vent must terminate:
• At least 6 feet from adjacent walls.
• No closer than 5 feet below roof overhang.
• At least 7 feet above any public walkway.
• At least 3 feet above any forced air intake within 10 feet.
• No closer than 12 inches below or horizontally from any
door or window or any other gravity air inlet.
b. Air inlet must terminate at least 12†above grade or snow line
c. Do not terminate closer than 4 feet horizontally (above or below)
from any electric meter, gas meter, regulator, relief valve
or other equipment.
Great! I know what grade is but what is snowline? I'll bet it's different in different parts of the country...