condensation on windows in new addition
jeffrey410 | Posted in General Discussion on December 21, 2008 02:31am
Hello All,
we have had a serious condensation problem with our windows in our house, specifically in the new part of our home built in 2001. We have high end, double hung windows throughout, both in the older log part of our home and in the air tight newer portion.
What is hard to figure out is that the new windows in the older part of our home have hardly any condensation on colder days, while the windows in the new section of our home are almost coated with ice around the perimeter of the windows, especially on the 2nd floor.
Also, the newer addition was built with 2 X 6 exterior walls for added insulation value. On top of that, we added a 1 in. thick polyurethane foam sheets to the outside sheathing before putting on board & batten siding.
Any help in this matter would be appreciated.
Jeff.
  1. sledgehammer | Dec 21, 2008 02:40am | #1
    My guess is the addition is tighter and the moisture is condensing just on the windows, unlike other, less tight areas where it is condensing on everything that has reached the dew point.
    You have a humidity problem.
    google: "Windows do not cause condensation"
    Edited 12/20/2008 6:40 pm ET by sledgehammer
    Edited 12/20/2008 6:43 pm ET by sledgehammer
    1. jeffrey410 | Dec 21, 2008 06:48pm | #10
      thanks for all your replies & interest in our problem. It sounds like we have a humidity/ventilation problem. I will monitor humidity, especially in the newer/air tight part, and look into a small HRV, possibly, to improve things. We have wood burning inserts in the the older part of the house which I'm assuming is lowering humidity when we use them.I'm embarassed to admit that I haven't yet thrown down a vapour barrier on the ground in the crawlspace of the newer addition. I am sure that isn't helping our cause either. thanks again.
  2. Dave45 | Dec 21, 2008 03:29am | #2
    The condensation is due to moisture and the some common sources are:
    1. Bathrooms. Those long, hot, showers generate lots of moisture. Make sure you're running the exhaust fan while you're in there, and let it run several minutes after you're finished.
    2. Kitchens. Cooking also generates a lot of moisture that needs to be removed or it's gonna add to the problem. Use your range hood.
    3. Garden Windows. House plants give off a lot of moisture.
  3. DanH | Dec 21, 2008 03:43am | #3
    Three possibilities:
    1) The humidity is higher in the new part of the house. This can happen in new construction since the drywall and lumber is relatively moist when installed and takes 6-12 months to fully dry out. Plus of course there could be differences in how humidity enters the house, with a shower near the new construction.
    2) It's cooler in the new part of the house, or at least on the new windows, due to poorer airflow through ductwork, etc, or simply something like having curtains on the windows in the new part but not the old part.
    3) The area around the new windows was not properly insulated and air-sealed, and outside air and/or cold is infiltrating into the rough opening area.
    From your description I'd guess #3 first, but would have to see things or ask a lot more questions to be sure.
    The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel
    1. sledgehammer | Dec 21, 2008 04:06am | #5
      There are 100's of reasons for humidity/condensation. The trick is finding it.
  4. JHOLE | Dec 21, 2008 04:02am | #4
    Humidity.
    Remodeling Contractor just on the other side of the Glass City
  5. USAnigel | Dec 21, 2008 07:49am | #6
    First thing is check the humidity level. HD have a small gauge in the garden department that reads temp and humidity. Its with the weather stuff. This will give you a starting point.
  6. user-253667 | Dec 21, 2008 08:01am | #7
    Not to be too sarcastic ,butttttt what is hard to figure out?
    Ancient leaky old logs with no vapour barrier and modern 2x6 with an extra layer.
    You have a ventilation and moisture problem in one and a moisture and ventilation problem in the other.
    The high quality windows throughout illustrate the deficiencies of each type of construction.
    Ventilate the new ( with HRV or ERV )and seal the old  (With Perma chink or whatever).
    Edited 12/21/2008 12:04 am ET by s crough
  7. dude | Dec 21, 2008 03:45pm | #8
    heard that problem discussed on the radio and the recommendation was to open the windows  1/16" and it would go away
  8. Riversong | Dec 21, 2008 06:20pm | #9
    You have a serious moisture problem. You're getting more condensation upstaires becuse warmer (and moist) air rises.
    The old log part of the house may have the same relative humidity level, but the logs have a high moisture-storage capacity and will buffer the RH. You don't have this buffer in the addition.
    Also, the log part is undoubtedly leakier than the new. Leaking air (heating cold air and hence lowering the RH) is what dries out a house in winter. Fewer leaks in the new addition = higher humidity.
    Get a hygrometer to determine the RH level. It should not be more than 40% in winter.
    You need to first reduce the sources. Make sure kitchen exhaust hood and bathroom exhaust fans are used every time moisture is produced.
    If that doesn't work, consider a dehumidifier or a heat-recovery ventilator (small ones are available).
    Riversong HouseWright
    Design *  * Build *  * Renovate *  * Consult
    Solar & Super-Insulated Healthy Homes
    1. homedesign | Dec 21, 2008 07:18pm | #11
      Robert,
      "Winter" is different in Vermont compared to Dallas.
      Many winter days and nights  in Dallas the temp stays above 45 deg.
      What is the outside temperature threshold where 40% Rh(or less) is the goal ?
      I know each house is different..but in general below what temperature?
      1. DanH | Dec 21, 2008 10:07pm | #13
        40% should be the upper limit is most homes during heating season, to prevent mildew. That limit is good down to roughly 20F, depending on construction. Below that temp the humidity must be reduced to avoid condensation on windowa and condensation within framing.
        1. Snort | Dec 21, 2008 11:11pm | #14
          got plants in the new part?http://www.tvwsolar.com
          Now you see this one-eyed midget
          Shouting the word "NOW"
          And you say, "For what reason?"
          And he says, "How?"
          And you say, "What does this mean?"
          And he screams back, "You're a cow
          Give me some milk
          Or else go home"
          1. jeffrey410 | Dec 21, 2008 11:20pm | #15
            we've got two fairly large potted plants in the master bathroom (north east end of new addition). We've also got our laundry room in middle front of this addition, with no door on it at the moment. I wonder if these two things are a part of the problem?
          2. Snort | Dec 21, 2008 11:26pm | #16
            probably contributors, but I'd get a VB on the crawl space floor... if you have a dehumidifier, you might want to run that down there for a while, both before and after the plastic.http://www.tvwsolar.com
            And he says, "How?"
            Give me some milk
            Or else go home"
          3. jeffrey410 | Dec 21, 2008 11:38pm | #17
            thank you.
            Jeff_Clarke | Dec 22, 2008 02:15pm | #20
            Crawl space open to earth is likely a large part of the problem.
            Brand of windows?Jeff
          5. Piffin | Dec 22, 2008 03:30pm | #21
            "Crawl space open to earth is likely a large part of the problem."exactly!hey guys, my kitchen floor seems to be wet, no matter how ofteen I mop it up, I keep getting my feet wet when I walk in there""Oh, BTW, Perhaps I should mention that I have a leak from under the sink. Do you think that could be the problem?"LOL
          6. sledgehammer | Dec 22, 2008 03:39pm | #22
            No the tile is clearly defective ;-)
          7. HootOwl | Dec 22, 2008 02:51am | #19
            Do you have at least one quality carbon monoxide detector in the house?
            There's always a chance that you're picking up some of this excess moisture from a partially obstructed flue/chimney or a crack/hole in the flue of a gas-fired or oil-fired appliance.  The potential for CO poisoning is not something to take lightly.
          8. arcflash | Dec 27, 2008 05:59pm | #26
            I read up to "vapor barrier in crawlspace" and immediately had to post. I think that might be your problem right there. I'm not sure what your soil is like there, but here it is red clay, and it can hold onto moisture for a really long time. Double up your vapor barrier and tape the seams. Run it up the foundation a bit, and make an airtight joint there as well. Make sure you don't have standing water anywhere within at least six feet of the foundation, and if you do, find a way to remedy it. Run a fan in the crawlspace for a day, and then wait see if the problem goes away. If that doesn't work. Id say start looking for air infiltration. Best of luck!
            Edit: Do you notice the condesation after the dryer runs a bit? I had to re-route my dryer vent run because the installers did a terrible job, I could feel warm air coming out of a switch from the wall behind it, alot of it! Also, buy a timer for the dehumidifier. Set it for when you notice the most condensation. I set mine for the dew point temperature outside, in the morning and late evening.
            Edited 12/27/2008 10:04 am ET by arcflash
          9. jamiep | Dec 28, 2008 04:03am | #27
            turn the humidifier down.
        2. Riversong | Dec 25, 2008 08:46am | #24
          The 40% standard is to prevent condensation. Mold growth requires, in addition to warmth, a surface moisture content for wood of 16%. Wood has an equilibrium moisture content of 16% at 80% RH.
          Of course, continued condensation where drying by diffusion or evaporation cannot occur, can wet wood sufficiently to reach this EMC as long as it remains wet when it's able to warm beyond 50°.
          Design *  * Build *  * Renovate *  * ConsultSolar & Super-Insulated Healthy Homes
          1. DanH | Dec 27, 2008 07:01am | #25
            Other things besides wood mildew, and the problem is not the RH in the middle of the room, but the RH in the corner, or behind the dresser, as well as the RH around the windows.It's a rule of thumb, of course, but 40% is a reasonable upper limit -- an increase above that value will not noticeably improve comfort or reduce human "winter dryness" discomfort, and going above that limit greatly increases the risk of condensation (and associated mildew) in susceptable areas of the structure.
      2. Riversong | Dec 25, 2008 08:35am | #23
        I didn't recall that the OP mentioned his location. He talked about cold outside.
        Many winter days and nights  in Dallas the temp stays above 45 deg. What is the outside temperature  threshold where 40% Rh(or less) is the goal ?
        It depends, of course, on the air and vapor tightness of the structure, and on the outdoor relative humidity. But, by my calculations, with an outside RH of 75%, any outdoor temperature below 40° could be problematic.
  9. User avater
    larryscabnuts | Dec 21, 2008 09:23pm | #12
    Its not the windows. Get a hydrometer and see what your moisture level is in the house. Like someone else sed its moisture in the house has reached dew point temp on the windows.
  10. User avater
    MikeMicalizzi | Dec 22, 2008 12:00am | #18
    Jeff,
    It's not uncommon for windows to get damaged upon installation. Excessive hammering too close to the new windows early on in the project could've very well caused the seals to come loose. Once loose, the gas escapes, the moisture enters. I wouldn't rule it out completely. You'll know for sure once you've tried everything else and it's summer and the windows still have the moisture problem. Just because it's "high end" doesn't mean it was built to last forever...