I’d like to run PVC conduit from the bottom of my meter base to a L-type conduit body and then thru a concrete wall into the garage where my load center will be located. Can I use SE cable for this short run or should I use non-jacketed cable since its inside conduit? This is 200A service in new construction.
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
This spray-foam sealant from Great Stuff offers mess-free, 6-in. coverage.
Featured Video
How to Install Exterior Window TrimHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
Looks like nobody wants to answer your question. Around here, you would not be allowed to use SE cable..but why would you want to anyway?
Unless it is for a commercial use, you would be required to use 2/0 copper in three individual lengths. (3/0 for commercial use.)