I’m in the process of building a new detached residential garage and I’d like to locate the service entrance at the garage and convert the existing main panel(located on the house) into a subpanel. The existing panel is a 100 amp combo panel; meter and main breaker. I plan on installing a 200 amp combo panel on the garage.
Questions:
1. When the utility Co. pulls the existing meter, do they they provide a cover plate?, if not what should I use?
2. After the existing meter is pulled, do I need jumpers in place of the meter, or do the feeds go directly to the panel lugs?
3. Now, with the house’s panel acting as a sub-panel, does the existing 100 amp main breaker remain in place?, or is it replaced with a new one at the new main?
Thanks in advance!
Replies
*
Anthony,
I can't answer your blanking plate question; in Esatern Montana the meter box is the propoerty of the owner, therfor the owner would have to provide the cover.
The feeds into the sub-panel should feed directly to the main lugs within the box. Don't use jumpers an the meter lugs.
The existing 100A breaker is better of left in place as added safety for the wiring that's "down stream" from it.
I've done a similar upgrade in my home, garage and outbuildings, etc. I'd advise consulting a qualified electrician if you've got any questions. We're allowed to do our own residential wiring on our own property in Montana. That may not be the case where you are.
Good Luck.
*
Chad is correct. You are responsible for the meter, so have your electrician take care of it.
*
Both of the previous suggestions are valid. It's good to keep in mind that the ownership and responsibility for meters and associated portions of the service may vary from state to state and indeed withing local areas of each state.
Another point that should be mentioned is that there are varying laws regarding the homeowner's right to do some portions of the wiring on his/her premises. For instance, several states and municipalities have restrictions on homeowners doing any revision, remodeling or installation of the meter loop (ie: meter socket, riser or underground feeder, main disconnect and distribution panel. This work is required to be done by a duly licensed contractor under permit.
As with most major revisions or modifications, it is best to check with the local authorities to determine what will be allowed.
*
I'm in the process of building a new detached residential garage and I'd like to locate the service entrance at the garage and convert the existing main panel(located on the house) into a subpanel. The existing panel is a 100 amp combo panel; meter and main breaker. I plan on installing a 200 amp combo panel on the garage.
Questions:
1. When the utility Co. pulls the existing meter, do they they provide a cover plate?, if not what should I use?
2. After the existing meter is pulled, do I need jumpers in place of the meter, or do the feeds go directly to the panel lugs?
3. Now, with the house's panel acting as a sub-panel, does the existing 100 amp main breaker remain in place?, or is it replaced with a new one at the new main?
Thanks in advance!