chazas | Posted in General Discussion on April 24, 2007 06:20am

Owner here.

<!—-> <!—->  <!—->

Our windows are Weathershield true divided light casements.

<!—-> <!—->

Within weeks after they were installed, three exterior panes in sashes on the south face of the house cracked with no apparent cause – in the same odd pattern, like an inverted “Uâ€.  Weathershield is replacing these sashes.  They sent 2 of the 3 replacements, though they got lost in our supplier’s warehouse for three months and when they did arrive they were the wrong color.  New ones are supposed to arrive next week.

<!—-> <!—->

Now, another similar crack has appeared in a different sash, also on the south face of the house.

<!—-> <!—->

Clearly, something is wrong here.  Multiple window panes should not just crack with no apparent cause.  I can’t imagine it’s anything other than a manufacturing defect.

<!—-> <!—->

We spent over $70,000 on these windows.  I do not want to be constantly having cracked windows on an extremely expensive house – even if Weathershield replaces them as they break, it would be a huge hassle.  The only foolproof solution I can think of is for them to replace every sash in the house now.  I can’t imagine this will go over too well with our contractor or with Weathershield, and the very thought of it at this stage of construction makes my head hurt.  Any thoughts or other suggestions?

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. peteshlagor | Apr 24, 2007 09:17pm | #1

    Triple pane?

     

  2. Shep | Apr 24, 2007 09:39pm | #2

    What kind of rough opening were the windows set in?

    If the ROs were too small, I could see the shrinkage of the opening as the wood dries as a cause for the breakage.

    Compression of the entire window frame could break the glass.

    Can you remove the interior trim to check it out?

    1. chazas | Apr 24, 2007 09:49pm | #3

      Double pane windows.  The rough openings were not in any way too small - the windows were shimmed into the appropriate places.  This appears to only be happening on the south-facing windows.

      1. User avater
        CapnMac | Apr 24, 2007 10:31pm | #4

        This appears to only be happening on the south-facing windows.

        Sounds like the dreaded (to glassmakers) "thermal expansion."  What may be happening is that the window maker got a bad run of glass from their glazier (whether separate companies/divisions, whatever).  It does not take very much "out of spec" for the frames for the double-pane units to be too tight when made up at the factory.

        The heat coming in fro mthe south heats the outside pane more than the inside one, just like it's supposed to, but there's not enough "give," and the stress has to go somewhere.  Goes into the frame & sash normally; abnormally, it goes back into the glass pane.

        This can be a bit more dramatic when this happens on a 60x120" 300# unit a couple-five stories off the ground . . . Occupational hazard of my occupation not being around (sorry Bubba)

      2. grpphoto | Apr 24, 2007 11:29pm | #6

        Compression of the frame would make the windows hard to open (if they are the type that can open). That's easily checked.George Patterson, Patterson Handyman Service

        1. User avater
          jocobe | Apr 24, 2007 11:39pm | #7

          ....or the Argon, Kyrpton, Carbon dioxide, or whatever is leaking out and ambient air molecules are too large to get back in, leading to spontaneous breakage. Does the glass have a concave reflection when viewed, especially from the outside? Another way to tell is put a straight edge across the face of the glass.

  3. DanH | Apr 24, 2007 11:08pm | #5

    Is there any sort of reflective surface within about 30 feet of the windows that could be focusing the sun on them?

    This inverted-U crack, does it go from corner to corner, or start on the bottom or the sides? Inner pane or outer pane? You say these are true divided light -- what's the pane arrangement and which one is cracking?

    Where do you live?

    So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin
  4. ChicagoMike | Apr 25, 2007 05:22am | #8

    These are called stress crack in the industry. It is described as a spontaneous crack in the glass with no point of impact. The most common causes are glass out of spec from glass manufacturer (Cardinal Glass I believe), too small of a gap in between the glass and the frame it sits in, but the most common cause is the glass installed wrong side out. The Low E coating should be on glass surface #2. There are 4 glass surfaces in a double pane IG. They are counted from the outside in. So the outer surface is #1 the inner surface of the exterior glass is #2 the outer surface of the interior pane is #3 and the interior surface you can touch from the inside is #4. If the Low E is on surface #3, the UV rays from the sun will reflect out to surface #2 and stay in the airspace longer. This will heat up the space, expand the gas or air and then break the seal or the glass. You can test this with a flame. Hold a lighter near the glass about 1/2" away. You will see 4 reflections of the flame in the glass. One flame will be a different color, usually purple. Then you can see if the Low E is on the correct surface. I hope this helps.

    1. chazas | Apr 25, 2007 03:58pm | #9

      The windows are not hard to open. I'm in the Washington DC area.The windows actually are not low E (the house is passive solar, we didn't want to block anything), so the wrong-side coating issue shouldn't be a problem.The cracks are primarily in the third floor windows - one on the ground floor, though it's (barely) conceivable that that one is attributable to the alarm sub. The windows are side-by-side casements, four panes to each sash. The cracks are primarily in the bottom pane, though the latest one is one pane up from the bottom. The cracks are in the outer pane. A pic of the window arrangement is below.Sounds as if the most likely issue is the size of the glass used in the manufacturing process. Maybe the issue is occuring mostly on the third floor because of the difference in temperature between the shaded and nonshaded portions of the windows? It didn't happen during our (abbreviated) winter - the one that broke this week was the first problem since last fall, which also would seem to support the expansion theory.We are trying to get a tech from Weathershield out to the site but I don't want to just get dismissed out of hand. Thanks for all the advice - it should help. Any further advice continues to be appreciated.

      Edited 4/25/2007 9:00 am ET by chazas

      1. chazas | Apr 25, 2007 03:59pm | #10

        View Image

        1. DanH | Apr 25, 2007 04:50pm | #11

          What's on the roofs of those bump-outs? Shingles, metal, rubber? Are there heating panels there?
          So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          1. chazas | Apr 25, 2007 04:54pm | #12

            Galvalume standing seam roof - no solar panels there. 

          2. DanH | Apr 25, 2007 05:08pm | #13

            That may be at least partly the problem.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

    2. Wango1 | Apr 26, 2007 07:24pm | #16

      Another possible cause (though D.C. is hardly high altitude) could be collapsed glass. Andersen offers a "High Altitude Breather Tube" option on their windows for those typically headed for Colorado. This allows the window to "fart" when it needs to blow off excess pressure. I wonder if the heat isn't changing the pressure inside and doing something similar.

      I can't believe in this day and age that anyone would put in windows that aren't LowE. There are different types for northern climates and those for southern, making it a no brainer.<$10 a window saves about 25% on energy costs.

      1. ChicagoMike | Apr 27, 2007 04:01am | #17

        Agreed.

        1. oberon476 | Apr 27, 2007 03:39pm | #19

          Chazas,

          <!----><!----> <!---->

          You are very welcome.  I strongly suspect that you have a thermal stress issue with these units – no matter where located – and I also strongly suspect that changing to tempered or heat-strengthened glass should solve your problem. 

          <!----> <!---->

          As I mentioned previously, annealed glass (with an unblemished edge) is “good” up to about 3000psi or so.  Tempered glass is required to be 10,000psi or better by code.

           

          Heat-strengthened glass (although tempered is by definition “heat-strengthened”) is  between tempered and annealed in strength characteristics - being typically somewhere between 6000 and 8000psi.  Heat-strengthened glass is not a safety product (unlike tempered which is a safety glazing), but it is about double the strength of regular annealed and may be a possible option for your situation as well, if you are so inclined.

          <!----> <!---->

          Also, I understand about not wanting to retrofit to LowE.  When I wrote the reply I was at the end of “one-of-those-days” and it does sound like I was apparently carrying some of that into the reply.  I still would always recommend LowE in every possible situation, but the comment about your situation simply wasn’t needed in my reply. 

          <!----> <!---->

          Wango1 and ChicagoMike,

          <!----> <!---->

          In this particular case I would suggest that collapsing glass is not a contributor to the breakage – although it certainly can be in other situations.

          <!----> <!---->

          From an altitude consideration, as you pointed out Wango1, there just isn’t much of change between central <!----><!---->Wisconsin<!----> (where the windows were manufactured) to <!----><!---->Washington<!----> <!---->DC<!----><!----> – certainly not enough to matter concerning breakage of the glass. 

          <!----> <!---->

          Although heat inside the IG can be a problem in certain situations; in this situation the inside airspace of the IG simply cannot heat up enough to be an issue.  While this does sound somewhat counter to what I stated earlier concerning thermal expansion causing the cracks; in essence, it is virtually impossible for the interior of the IG unit to get hot enough to cause the glass to “bow” from interior pressure to the point of cracking because the heat would dissipate (conduction) through the glass and be radiated outward before it could reach the required temperature/pressure. 

          <!----> <!---->

          What you suggest can certainly happen, but not in this specific instance. 

          <!----> <!---->

          Thermal expansion of the glass is the likely cause, in this situation - uneven thermal expansion of the lite (meaning part of the lite is trying to grow while part of the lite is attempting to remain static), can definitely cause cracks in windows – just as described.

          <!----> <!---->

          Chazas, I would suggest that when you look at the crack, from where it starts at the edge of the sash, the crack looks to be exactly perpendicular (90°) to the edge of the sash.

          <!----> <!---->

          Bill, I agree 100%, this is a great thread with loads of very good information in it.

          I have very much enjoyed reading other responses and participating in this one!

          <!----> <!---->

          <!----> <!---->

          <!----> <!---->

          <!----> <!---->

          <!----> <!---->

          <!----> <!---->

  5. oberon476 | Apr 26, 2007 04:57am | #14

    Chazas,

     

    Glass cracks in order to relieve stress.  Thermal expansion in glass is no problem so long as the glass has (a) room to expand and (b) expands evenly across the surface of the lite. 

     

    Thermal expansion in glass can be a bad idea and can result in stress cracks (a) if the glass is restricted in its expansion and (b) the glass is not expanding evenly across the entire surface.

     

    I am leaning the same way that I think DanH is leaning – it sounds like you are getting uneven thermal stress on the glass possibly caused by reflections from the metal roofs of the two bump-outs combined with shading from the roof line.  

     

    A single crack, without “branching” indicates a low-stress break, or that less than 1500psi was needed to propagate (but not necessarily cause) the crack.   In general, a simple low stress crack requires a flaw in the glass in order to grow.  This type of flaw is often a chip or some other defect in the edge of the glass – a defect that would not be visible when the glass is in the sash.

     

    As a basic rule, ordinary (not heat-strengthened) glass should be able to withstand stress to about 3000 psi without failure.  Temperature-induced stress in glass is generally computed at 50 psi for each degree temperature variation within the lite – so that a difference of only 30 degrees between the warmer and the cooler portions of the glass would be needed in order to produce sufficient thermal stress in order to propagate a thermal stress crack.  Again, with the caveat, that it is highly likely that the glass would have to have a (relatively) significant edge flaw in order to crack at the lower stress level.

     

    Heat reflected from the roof panels onto the glass, unevenly, could very easily create temperature variations well in excess of the 30 degrees difference needed to grow a crack in the lite.  I would strongly suggest that the reflected heat could (and very well might) cause you problems with your window glass in the future. 

     

    The inverted U indicates that the edge of the glass was likely cooler than the center of the lite and that the stress crack was following a line of “least resistance” parallel with the edge of the sash but along the line of heat variation.

     

    One fix might be to use heat-strengthened glass which will have a much greater resistance to heat-related stress than will ordinary annealed.

     

    If you choose that option then I would also strongly suggest that you include a LowE coating in the IGU since clear (uncoated) glass is always less energy efficient than is LowE coated glass.  You are going to lose much more heat than you are going to gain in winter thru that massive expanse of glass, and in the summer your heat gain thru the uncoated glass is going to prove to be a significant expense as you run your air conditioner way beyond what would be needed if the glass was coated. 

     

    Massive expanse of uncoated glass was the passive solar “holy grail” back in the seventies, but in today’s world it is well understood by most energy experts that the correct use of LowE coatings on windows is far and away a much better solution – even in solar heat gain conditions.

     

     

     

     



    Edited 4/25/2007 10:03 pm ET by Oberon

    1. chazas | Apr 26, 2007 04:42pm | #15

      Thanks for your well-considered thoughts.

      The galvalume on the porch roofs below may be an issue - but it's hard to imagine, as the cracks have occurred mostly in the windows between the porches, where there does not appear to be a significant amount of reflected light.  We also had one crack on the first floor.

      My partner (the architect) had already suggested replacing the top floor sashes with tempered glass - glad to see the agreement.

      A digression in response to yours:

      It's a bit too late to switch to low e windows now that they're all up!  Aesthetics prevent having different window glass in different parts of the house.  Anyway, we have 2x6 construction and R-20 Icynene in the wallls, R-48 cellulose in the attic, and very few windows on the east and west exposures.  The sunlight infiltration is very deep into the house in the winter (where it was very comfortable on sunny days, even without the attic insulation in) and drastically reduced the closer we get to the summer solstice, just like it's supposed to be.  With 10 kw of photovoltaic and high-efficiency heat pumps, I think we'll be good to go.  You can't have everything...

  6. BilljustBill | Apr 27, 2007 07:08am | #18

      Chazas,

       You've gotten some great information from some people who seem to know their stuff!!  It's been very interesting!!

       I'd like to pose a concept dealing with the center windows cracking:  With the slanted shiny roof angles from the pop-outs, could it be that these angles are reflecting the sun on the windows as it travels across the sky?

       Having built and learned from an early 80's solar batch water heating project, the rear reflectorhalves were curved in such a way to focus the sun on the side and back of a 40 gallon tank from almost sun up to almost sun down.  Your roof angles seem to reflect  the sun on the far window in the morning, both at high noon, but as the sun angle changes, the heat is reflected to the opposite window for the remainder of the day.

       Maybe covering the outside of windows with some temporary attached aluminum foil would highlight the roof reflected sunlight and help you see any sunlight concentrations.

        Bill



    Edited 4/27/2007 12:23 am ET by BilljustBill

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers

Listeners write in about removing masonry chimneys and ask about blocked ridge vents, deal-breakers with fixer-uppers, and flashing ledgers that are spaced from the wall.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data