Dust Collecton wiring
rasconc | Posted in Energy, Heating & Insulation on July 19, 2008 11:26am
That “2 hp” dc I have came with 14 ga wire into the switch and from switch to box on motor.  Since it draws 22amps I find that pretty hard to believe.  I have run it on a strong 20 A ckt.  The plug is just a 15 a.  I plan to rewire to 240 but am replacing the wire with some 12 and a 20a plug.  How can they import something like that?
  1. JTC1 | Jul 20, 2008 12:14am | #1
    What does the unit actually draw after start up? In other words what are the normal "running amps" required.
    Measure this on your unit -- or is that the "22 amps" you refer to in your OP.  Forget the initial start-up surge, even if you can measure it.
    That 14ga may be just fine - I would not rip it out just yet.
    Some of those alleged hp ratings are pretty squirrely.
    Jim
    Edited 7/19/2008 5:17 pm ET by JTC1
    1. rasconc | Jul 20, 2008 02:04am | #3
      It was a running 22 amps, not startup.  Using a cheap digital clamp-on.  I have a couple of good old analog ampmeters but that sounds about right.
      After looking more closely the 15A plug was made in Mexico which leads me to believe my BIL's ex partner may have put it on.  No self respecting Chinaman would use a Mexican plug (:-).
    BillHartmann | Jul 20, 2008 01:43am | #2
    The same way that they make similar stuff in the US.
    If you look the unit is not UL approved. And IIRC there is no classification for such equipement except as industrial products and that would be very expensive.
    But if you look most like the cordset is UL approved.
    And the motor is UL approved.
    But not the dust collector.
    And the #14 flexable cord is rated for 18 or 20 amps depending on the
    type of insulation
    But something like that should never be used on a 15 amp circuit.
    I am not concerned about the plug or receptacle. But the common time inverse breakers will carry a large overload for a long period of time.
    Most WW equipment starts unloaded, except for interia, and only had peak loads for a short period of time as a board is being milled.
    But a DC will draw near rated current, depending on the size and lenght of the ducts, for the whole time that it is on.
    So change it over to 240 including replaceing the plug. But the cable is OK.
    1. rasconc | Jul 20, 2008 02:19am | #4
      The cordset does not say anything about UL.  It is printed "vctf 600v 37/0.26mm  2.0mm2 TA Huang (two symbols I do not recognize) 64009 1997".  The wire from sw to motor says 14awg.
      I already replaced the cordset with some older wire I had laying around.  It reads "P.E.C.O 12/3  ST W-A".  Put a quality plug on it and will temp run it on a single 20 amp ckt .
      Plan to put that sub panel we were talking about in but instead of coming off the old fuse panel, going off the newer breaker panel.  I have to look at it to see where I can shuffle a couple of circuits to get a dp breaker in.  I used a lot of the half size breakers and need to recheck the "number of ckt" rating on the panel.  Will probably move one or two of the basement ckts to the sub.
      Thanks,Bob
      Edited 7/19/2008 7:21 pm ET by rasconc
      1. rasconc | Jul 22, 2008 07:07am | #5
        Update; I needed to cut a couple of pieces today so I plugged the dc into a 20 amp gfci on a circuit off the newer panel.  I put the ampmeter on before and after and it was pulling just over 20 amps.  I ran it for about 15 min at it's normal load/pressure, etc.  Felt the wire just before the breaker ( had panel cover off to figure our how I wanted to reland the other circuits).  It was cool as a cucumber.
        Think the final solution will be to extend the old dryer circuit using the fuse block and convert both TS and DC to 240 using a 20A dpst switch for the DC located near the TS which is pretty much central to work area.
FHB Podcast Segment: Roofing on Commercial vs. Residential Buildings
In certain scenarios, flat roofs make more sense than pitched roofs (and vice versa).
  • A Postwar Comeback