EL question- neutral & ground connected

jonblakemore | Posted in Construction Techniques on December 8, 2008 11:21am

I noticed something (actually two things) in a box today that made me question the skill of the electrician who did this.

View Image

First, note that the copper grounding conductor to the screw on the switch has been cut. Was this done so that if an inspector looked at the ground screw he would see a ground wire attached, hoping that he wouldn’t notice it didn’t go to anything? Or am I jumping to conclusions in thinking that this was a shortcut?

Secondly, the matter that made me more concerned is the fact that the neutrals are connected to the grounds. I thought that the main panel was the ONLY place they are to be connected, even subpanels are supposed to have isolated grounds.

This box has three NM cables comin in. Two 14-2 and one 14-3. The 14-3 is using a white insulated conductor as a switch leg, that’s not confusing me (at least I don’t think so). But the neutrals from the two 14-2 cables are tied with a wirenut to all three ground conductors.

Am I correct that this is a big problem?

 

Jon Blakemore

RappahannockINC.com

Fredericksburg, VA

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    Dam_inspector | Dec 08, 2008 11:52pm | #1

    Man, that is soooo wrong...

    I think the sparkie is on meth.

  2. LiveFreeorDie | Dec 09, 2008 12:08am | #2

    I have seen this many times, especially in old houses, in fact in my own house the neutrals and grounds ar in the same neutral bar in the panel. now the mess in that box doesn't speak well of the electrician that did it. As for the ground, what was it accomplishing attached to that screw in a non metallic box?

    1. arcflash | Dec 09, 2008 04:19am | #13

      EGC, equipment grounding conductor. It is a system ground, it does not have to be grounded to a metal box. Its sole purpose is to redirect fault current away from the device. Any color wire can be used as a current carrying conductor (except green) as long as it is re-colored, or "phased". Most electricians use the appropriate colored electrical tape for this.

      Yes, it is a code violation, see NEC 250. It has no equipment ground, and grounded conductors cannot be substituted with grounded conductors.

      A main is bonded once at the first means of disconnect, at the service side, this means that the neutrals and grounds can share a bar and a jumper must be installed between the neutral and ground bars, and the ground bars are to be bonded to the can.

      Like a previous poster, I see a potential electrocution hazard as well. Luck will determine whether or not the breaker trips in time.

      1. User avater
        jonblakemore | Dec 09, 2008 04:23am | #15

        Here's a dumb question. You can have problems if you have 14 gauge wire on a 30 amp breaker, because you may overload the current capacity of the wire before the breaker trips to protect from failure. I would assume this applies to both "hot" and "neutral" conductors, right? What I mean by that is, if you were to use one 14 gauge neutral wire to complete the circuit for two 14 ga. hot wires (on different breakers), you're not going to trip the breaker since the neutrals all go to the neutral bus, but you still have a dangerous situation with the amount of current the one 14 ga. wire could potentially be asked to carry.Am I thinking correctly? 

        Jon Blakemore RappahannockINC.com Fredericksburg, VA

        1. mike585 | Dec 09, 2008 04:51am | #16

          You are right. Amps are amps, whether flowing in the neutral or 2 hot wires. You could exceed the safe current in the one neutral and not trip the shared current source breakers.

        2. arcflash | Dec 09, 2008 05:12am | #17

          Yes and no. Yes on the 30A breaker/14 AWG wire question. #14 is rated for 15A (I think, I hardly ever install anything that small). Firstly, the size of wire you use is dictated by its overcurrent protection, not the other way around. A wire that is that overloaded burns off its insulation and a massive fault ensues. I've never seen one like that, but I could imagine that it would be horrible. The breaker wouldn't trip, and the current would have no where to go. Basically, it would happen like: explosion, fire, death.....not necessarily in that order.

          For the second question, the answer is no. You would be sharing a neutral on two circuits which is perfectly acceptable as long as you don't do it on an arc fault circuit (neutral on an AFCI is monitered by the breaker), and you land both overcurrent devices (breakers) on different phases in the panel, and the wire is sized for the overcurrent device.  The situation you are describing can and might eventually happen if you share phases (I think that this applies less to a single phase system and more so to a three phase system.....but it is still good practice to balance both systems). I think with shared phases you have more potential current for the neutral to carry, and a better chance to ruin the insulation.

          It gets quite technical, and it has been explained to me several times, but trying to muddle through a detailed explination (I've tried at Breaktime before) wont help either one of us. Basically, let me get back to you on that, I'll try to remember to ask my journeyman tommorrow. Good question.

          1. gfretwell | Dec 09, 2008 05:25am | #18

            I could tell you where it is legal to have 14ga wire on a 40a breaker but it would start a flame war.
            Think "motor".

            Edited 12/8/2008 9:27 pm ET by gfretwell

          2. User avater
            jonblakemore | Dec 09, 2008 06:40am | #22

            To clarify, I'm strictly speaking about single phase 240v residential service.For the sake of discussion, let's say you have two receptacle circuits with 15a breakers on the same hot bus bar. If I plug two 1,800 watt irons in, one on each circuit, would the neutral not be carrying twice is rated current? 

            Jon Blakemore RappahannockINC.com Fredericksburg, VA

          3. rasconc | Dec 09, 2008 09:25am | #25

            "one on each circuit, would the neutral not be carrying twice is rated current?"

            Yes I believe because it is an inappropriately wired situation.   If different legs the ckts cancel out each other on the neutral.  Same phase they are additive.

            You are describing a multiwire circuit and to be a "correct" multiwire circuit they would need to be on different legs/phases/buss bars, etc.  A common trip breaker is best (/recommended/required?) IIRC to make sure all stays safe and no power is resident on the shared neutral if breaker on one leg is off.

            Not an electrician but believe this is/was correct last time I looked. 

            Supplied with more than a grain of salt (;-0For those who have fought for it Freedom has a flavor the protected will never know.

          4. JTC1 | Dec 09, 2008 03:34pm | #27

            Yes, correct, affirmative.......

            JimNever underestimate the value of a sharp pencil or good light.

        3. brucet9 | Dec 09, 2008 09:40am | #26

          "What I mean by that is, if you were to use one 14 gauge neutral wire to complete the circuit for two 14 ga. hot wires (on different breakers), you're not going to trip the breaker since the neutrals all go to the neutral bus, but you still have a dangerous situation with the amount of current the one 14 ga. wire could potentially be asked to carry."Three wire circuits are connected with one neutral and two hots but the hots are connected to breakers on opposite phases at the panel. Since they are 180° out of phase with one another, when one is at +120V the other is at -120V. When both hots are in use with equal loads, they cancel one another out and the neutral actually carries no current. When the two hots carry unequal loads, the neutral current is only the difference between the two hots.BruceT

      2. LiveFreeorDie | Dec 09, 2008 06:26am | #20

        You are quoting the book and a great explanation, but I have seen some really strange goings on in panels over the years, and in boxes as well. the proper way would have been to nut the neutrals together and the grounds together, but separate of each other. I have found places where ALL the wires in the boxes are black ( circuit wire in conduit ) guess no one ever heard of phasing tape, but it surely happens.

  3. plate | Dec 09, 2008 12:45am | #3

    Yes, you are correct there are clearly code violations here.  For one, as you mention, ground wires (EGC, bare copper in this case) are not suppose to carry current in normal conditions.  They only carry current during a ground fault.  The white wires and the grounds need to be separated.  I notice you say there are three cables, but I only see two ground wires.

    The black wire attached to the switch ground ?????????  I can't imagine why in the world you would do this.  If it truely is being used as a ground wire then it would have to be re-identified with green tape on both ends of the cable.

    Neutrals and grounds get connected in the main panel, but not downsteam (as they are in your case).

     

    1. User avater
      jonblakemore | Dec 09, 2008 12:50am | #4

      "I notice you say there are three cables, but I only see two ground wires."

      One of the copper grounds is connected to the other two with a crimped sleeve. See pic, you can sort make it out.View Image

      "The black wire attached to the switch ground ?????????"

      The picture angle is deceiving, see the edited pic below. The switch is wired correctly, other than the lack of a ground.View Image 

      Jon Blakemore RappahannockINC.com Fredericksburg, VA

      1. plate | Dec 09, 2008 01:14am | #8

        Regarding the ground/black wire on the switch.  Thanks, I'll look closer next time.

      2. woodway | Dec 09, 2008 06:30am | #21

        Cell phone photos are not allowed on Breaktime!

        1. User avater
          jonblakemore | Dec 09, 2008 06:42am | #23

          Not a cell phone, it's blown up (resized).Below is the full res. photo, since you asked so nicely. 

          Jon Blakemore RappahannockINC.com Fredericksburg, VA

          1. woodway | Dec 09, 2008 07:04am | #24

            Thanks. I've seen some sparkies get pretty messy in the box but none that violated the rules. Lots of problems with too many switches controlling one or two lights in the ceiling, then to top it off, they thrown in the Lutron rockers just to make three way/four way circuit a real nightmare to figure out.Actually, sparkies on crack would explain a lot of questions.Thanks again for the clear photo! Edited 12/8/2008 11:05 pm by woodway

            Edited 12/8/2008 11:06 pm by woodway

    2. JTC1 | Dec 09, 2008 12:54am | #6

      >> The black wire attached to the switch ground ?????????  I can't imagine why in the world you would do this. <<

      Look closer, the black is connected to the common terminal of a 3 way switch - not to the switch ground screw.

      Switch ground screw has a small bare copper wire butt under it.

      JimNever underestimate the value of a sharp pencil or good light.

  4. peteshlagor | Dec 09, 2008 12:52am | #5

    That yellow wirenut pushed in to the left - why's a black and a white wire going into that?

     

    1. User avater
      jonblakemore | Dec 09, 2008 04:22am | #14

      "That yellow wirenut pushed in to the left - why's a black and a white wire going into that?"I don't *think* that's a problem (other than the fact that it was not identified as "hot" with tape or a sharpie).That's using all three conductors in a piece of 14-3 cable to get power to another box. The red and black are the two legs on a 3-way switch configuration, and the white is what I have heard called a "white-hot feed" (I'm not sure if that's right, but I've heard the term used). 

      Jon Blakemore RappahannockINC.com Fredericksburg, VA

      Edited 12/8/2008 8:25 pm ET by JonBlakemore

  5. JTC1 | Dec 09, 2008 12:58am | #7

    Neutrals + grounds nutted together?

    Not zactly code but it worked when the hack ran out of wire nuts.

    :-)

    Jim

    Never underestimate the value of a sharp pencil or good light.
  6. sledgehammer | Dec 09, 2008 03:02am | #9

    Good news is it's not a fire hazard.

     

    Bad news is that's a connection that will kill you dead, if you touch the wrong thing.

  7. Waters | Dec 09, 2008 03:20am | #10

    I can't believe a 'real' electrician did that...

    that looks like homeownermess to me.

     

    1. gfretwell | Dec 09, 2008 03:31am | #11

      I agree the homey who did this was confused about where the ground went in a plastic box so he hooked to the neutral. When I see a white and a black under a wirenut is says "switch leg" but in this mess I would want to verify that.

      1. Waters | Dec 09, 2008 04:06am | #12

        First I thought maybe the ground and neutral were both being used for 3 way switch legs... 

  8. Joe123 | Dec 09, 2008 06:22am | #19

    I see the situation of the ground and neutrals tied together as a potential shock issue. 

    As far as breaker tripping goes, it should trip at least as well (and very slightly faster)when the nuetrals and ground are tied together then without the ground and neutrals tied together.  This is so because the resistance back to the panel is less, think of it as higher fault current. 

    As previous posts said, no matter how you look at it, its a code violation.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Fire-Resistant Landscaping and Home Design Details

These defensive details give homes a better chances of surviving wildfires.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump
  • Insulation for Homes in the Wildland Urban Interface
  • An Impressive Air-to-Water Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data