Electrical Question – Grounding EMT in basement applications

NBGT | Posted in Construction Techniques on March 1, 2016 11:57am

Hello,

I’m adding several outlets in my basement and want to have the Romex run in EMT along the walls (basement walls are concrete block).  I’m planning on putting the outlets (GFCI protected) in metal boxes.  The romex will be run along/through the joists.  Therefore, the EMT will not be run all the way back to the electrical panel.  Since the EMT will not be run all the way back to the electrical panel, I cannot ground the EMT at the electrical panel.  Would it be sufficient and within code (NEC 2014) to only ground the EMT through bonding with the ground wire in the Romex at the metal box were the outlets are installed, or do I need to run a ground wire from the top of the EMT to the electrical box somehow?

Thank you for your advice.

-N

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. DanH | Mar 01, 2016 02:38pm | #1

    In that case you are using EMT for physical protection of the romex, not as standard EMT-style circuit.  For short lengths I'm thinking code does not require the EMT to be grounded at all, and grounding at one end should be sufficient in other cases.  (Unlike an EMT-based wiring system, you're not using the EMT as a ground wire.)

    Of course you can dodge the question by using plastic conduit instead.

    Don't forget to use appropriate bushings at both ends of the conduit -- you can't have the romex come straight out of the cut-off EMT without a bushing.

    1. NBGT | Mar 01, 2016 05:08pm | #2

      Thanks, DanH.

      Plastic may be the better/easier way to go in this case.

  2. renosteinke | Mar 01, 2016 06:45pm | #3

    You MUST Ground EMT

    .... And do it several times!

    What you are doing is 'changing your wiring method.' Here's how you do that.

    You have the Romex end in a box, using the proper connector.  In the box you will install a green 'pigtail' that connects to the back of the box. This short wire is needed in every box, and will be connected to your ground wires at every box.

    You connect the EMT to the boxes, using the appropriate fittings. The EMT is grounded by its' connections to the boxes..

    In the EMT you run proper, separate, green, black, and white wires. It's a fine point, but you're not allowed to run Romex itself in the pipe, or to use the wires from within the Romex.

    The boxes are attached to the walls, and the EMT is also fastened to the walls (within 3 ft. of each side of each box, and no more than 1- ft. between supports). Use "industrial" covers for your switches and receptacles, since this is exposed work.

    1. DanH | Mar 01, 2016 07:15pm | #4

      I'm pretty certain you are wrong.  There's a difference between using the EMT wiring system (I forget the "official" name) and simply using metal conduit to protect romex from damage (which is often required by code in various situations).

      1. renosteinke | Mar 02, 2016 06:48pm | #5

        EMT + Boxes = Wiring Method

        Which is quite different from using a few inches of concealed pipe to protect a cable.

        1. DanH | Mar 02, 2016 07:11pm | #6

          He's talking about running romex all the way from the breaker panel to the GFCI outlets.  He's not converting wiring methods.  The EMT is used purely for physical protection, as required by code when in an exposed location of a inhabited area.  This is done all the time.

          Are you saying there's some code limit on the distance that romex can travel in such situations??

          1. gfretwell | Mar 03, 2016 12:24am | #7

            There is nothing wrong with running Romex in EMT if you are not exceeding the fill but you have to compute fill using the widest dimension. That ends up making the cable a pretty big conductor.

          2. renosteinke | Mar 03, 2016 06:39pm | #8

            I Disagree

            The OP said he didn't want to run EMT all the way to the panel. That's not a problem, you can change your wiring method all the time.

            He then went on to describe metal boxes, and the pipe being on the face of the wall. That's a change in method, plain and simple. Were he to just have the Romex pop out of the pipe, enter the box, than go back into the pipe .... that's a violation, no matter how you look at it. The solution is to properly change your wiring method.

            What if he used plastic boxes? Same issues- plus, plastic Romex boxes are not designed for attaching pipe. The proper way to do this is to as i described - change your method.

            Greg's comment about wire fill also sheds some light on the issue. Since Romex typically requires a 5/8" hole, that in turn suggests that the smallest pipe you can use is 1".  I suspect that's not what the OP has in mind.

            Article 100 is pretty clear .... the wiring method used must provide mechanical protection for the wires, protection suitable to the application. From the OP's description, "sleeves" won't cut it. There are also requirements that the cables be protected from cutting and abrasion - something that can't be provided by the simple end of a piece of pipe.

            I am aware of only ONE place in the NEC where such sleeving is called for: when the cable passes through the framing from one floor to another. Note that the context of that requirement makes clear this is for a situation where the sleeve is not accessible later.  That's quite a bit different from tacking your pipe to the wall and pushing the cable through it.

            I also draw attention to Article 90, which makes plain that you're supposed to learn the trade BEFORE you open the code book. It's not a design manual, instruction manual, or substitute for competence. I also note that every place that licenses electricians requires several years of experience in the trade first .... simply passing the test, attending a seminar, or 'related' knowledge  is not enough.

          3. DanH | Mar 03, 2016 08:27pm | #9

            From my old (1981) code book, Article 336 (Nonmetallic-Sheathed Cable), section 6 (Exposed Work):

            The cable shall be protected from physical damage where necessary by conduit, pipe, guard strips, or other means.

          4. gfretwell | Mar 03, 2016 09:59pm | #10

            In the 2014 334.15 (B) says

            (B) Protection from Physical Damage. Cable shall be

            protected from physical damage where necessary by rigid

            metal conduit, intermediate metal conduit, electrical metallic

            tubing, Schedule 80 PVC conduit,

            250.86 goes on to say

            Exception No.2: Short sections of metal enclosures or

            raceways used to provide support or protection of cable

            assernblies from physical damage shall not be required to

            be connected to the equipment grounding conductor.:

            "Short" is not defined. They may want bushings on each end of these sleeves.

            OTOH if you make up the EMT in metal boxes with the proper connectors and pull your Romex through it you are perfectly legal and a lot safer. It probably works put cheaper too by the time you buy romex connectors and bushings. 

  3. miltonE | Sep 01, 2021 08:29am | #11

    Yes, you have to ground EMT, but are you planning on doing this all on your own? If you're not fully confident about this task, maybe consider calling a professional.

    https://www.electricianstcatharines.ca

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data