Electrical Tape on Wire Nuts??

GotAll10 | Posted in Construction Techniques on June 10, 2007 06:41am

I thought it was a good idea to support a wire nut connection by wrapping it with electrical tape.  The inspector recently suggested I not do it.  The reason given is that if a connection is loose, the tape may hold it together just enough to keep the wires close enough together to spark.  If the tape were not there, the connection would more likely come loose, calling attention to the problem. 

Comments???

Thanks,

Paul

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Scott | Jun 10, 2007 08:52am | #1

    I've had years of conflicting advice on this, and I know of no code rules on it. I expect it falls in the nebulous category of ‘good workmanship’. I had one inspector insist that all wire nuts be wrapped with tape, and another that was utterly contemptuous of the idea. This really sucks. Lately I've always raised the issue in the first meeting with the inspector so that I know what they expect.

    My latest strategy, which I think is a good one, is to tape all splices that involve stranded wire, including stranded to stranded, and stranded to solid. In my experience stranded wire can cause splices to pop. I extend the stranded wire about 1/8" above the solid before cranking the nut on, then tape. It seems to work well.

    Good luck,

    Scott.

    Always remember those first immortal words that Adam said to Eve, “You’d better stand back, I don’t know how big this thing’s going to get.”

  2. User avater
    Mongo | Jun 10, 2007 08:58am | #2

    I twist the conductors together to start with. Then use a wire nut. Then tape the nut.

    I wouldn't advise depending on just the nut to hold the wires together.

    But I didn't answer your question did I.

    While I understand your inspector's argument, I disagree. If the conductors were not twisted together to start with, and it's just the nut holding the wires together? the nut comes loose, falls off, now you have unprotected hot conductors in the box.

    If the nut were to come loose and the wires became separated, the circuit would still be intermittent. But the tape would at least hold the nut to shield the conductors.

    You want an intermittent light or outlet to let you know that the conductors came loose. Not smoke and fire.

    Redundancy? Hell, I fly jets. I want three hydrualic systems and a back-up flight control system. I'll know when it's broke, I just want to survive the break so I can get the machine fixed.

    Mongo

    1. User avater
      Matt | Jun 10, 2007 03:57pm | #3

      >> I fly jets.  <<

      Hummm... That doesn't sound like something you do for a hobby?

      1. User avater
        Mongo | Jun 11, 2007 05:00am | #21

        Matt, a little of each.I fly one type of jet for a lot of fun and a little pay, the other for a little fun and well...a little pay.

        1. Ragnar17 | Jun 11, 2007 05:28am | #23

          Mongo,

          Are there any threads here about the jets you fly?

          1. User avater
            Mongo | Jun 12, 2007 02:20am | #30

            Not in recent years.We had a few "get to know me" threads where we posted about what we do and what we've done way back in the early daze of Breaktime, back in the '96-'97 time frame. But no, in recent years I've never really gotten into it on these forums. I think Stan pretty much has a lock on the aviation threads with the whirlygig thing he flies.I never opted in on the Tavern when it changed over to private ownership, so I miss out of the off-topic threads that go on behind those closed doors.

          2. Ragnar17 | Jun 12, 2007 06:58am | #33

            I never opted in on the Tavern when it changed over to private ownership

            Yeah, I've stayed out of the Tavern since then, too.  I waste enough time here as it is!  ;)

            I'm curious about the planes you fly though.  Can you briefly tell me what they are?

          3. User avater
            Mongo | Jul 27, 2007 08:32pm | #34

            Sorry for the ate reply. I never saw this as an unread message until today.In the USAF I flew T-37s and T-38s in training, and A-10s and F-16s.Got out after the '91 Gulf War.Commercially I've flown B-727s, B-757s, B-767s, L-1011s, and MD-88s.When I was in the USAF I was an A-10 demo pilot for air shows. After getting out I flew a privately owned T-38 in air shows.Mongo

  3. User avater
    maddog3 | Jun 10, 2007 05:02pm | #4

    about the only time I use tape anymore,
    is when I'm making up ..small... motors, the tape is fiberglass though
    other than that it depends on the installer and the wirenuts , the old hard plastic nuts always seemed to be too short to cover the splice ,

    some of the nuts with the wings on them take up more room in the boxes, but tend to be long enough to cover the bare wire

    3M makes some that are two sizes in one ..those are really big but they have a large "skirt"

    I picked up some Ideal "filled " wirenuts the other day and the package instructions suggests a small twist before using one, but no mention of tape

    my personal favorite has always been the Buchanan crimped sleeves..especially outside, it makes the splice permanent !
    so they would have to be cut open if you ever rework that circuit

    .

    .

    .

    .

    , wer ist jetzt der Idiot ?

  4. edlee | Jun 10, 2007 05:58pm | #5

    I dunno.  I've never come across an electrician who tapes wirenut connections for general installations, and no electrician I ever worked for had me do it.  So when I see taped connections (other than on some factory-wired equipment), my thought is that it was not done by a pro.

    When I take them apart, usually there is bare copper exposed outside of the wirenut and somebody added tape to cover it up.  Shoddy.

    FWIW...............Ed

    1. bearmon | Jun 10, 2007 07:31pm | #6

      Friend who is an electrician says the same thing.  If he sees taped wirenuts he figures the homeowner did it.Bear

  5. WayneL5 | Jun 10, 2007 09:05pm | #7

    Code says to install wire nuts according to manufacturers' directions.  The directions don't say to tape.

    Taping makes servicing and changes more difficult.  I don't tape.

  6. Ragnar17 | Jun 10, 2007 09:46pm | #8

    Paul:

    It's an accurate observation that the vast majority of professional electricians don't tape.  That doesn't mean it's not a good idea -- just that the pros don't think it's worth their time.

    I've seen installations in which wires have worked their way out of the wire nuts.  On a few, this led to arcing, and some black marks were visible within the box.  For that reason, I taped when I first learned how to do electrical work (I'm a contractor, though, not an electrician).

    Since that time, however, I've come to the conclusion that the wire nut failures I've seen are more due to faulty installation than to an inherent design problem associated with wire nuts. 

    What I do now is make sure that I keep twisting the wire nuts on until the 2" or so of wires leading up to the nut start to neatly twist around each other.  In this manner, the wires are bound together and the chance of a single wire working its way out of the nut is almost nil. 

    The other thing I do is try to locate the wire nuts in opposite corners in the box.  In that way, there's less chance of them coming into contact with each other.  This isn't always possible, of course, but I do it when it is, and it doesn't take any extra time.

    The only time I'll still tape is when working with multi-stranded wire; for whatever reason, it doesn't seem to work as well as solid when it comes to wire nuts.

    PS: I think the inspector's reasoning leaves something to be desired.  ;)



    Edited 6/10/2007 2:49 pm ET by Ragnar17

    1. mwgaines | Jun 10, 2007 11:02pm | #9

      I have always taped wire nuts. Admittedly, I'm a DIY'er, not a contractor. I think it's more of an asset than a liability to tape the nuts and will continue the practice. I find the inspector's reasoning to be faulty. The best practice would be the one that minimizes the risk of wire movement to begin with. 

      My two cents..New knowledge is priceless. 

      Used knowledge is even more valuable.

      1. Ragnar17 | Jun 10, 2007 11:05pm | #10

        I find the inspector's reasoning to be faulty. The best practice would be the one that minimizes the risk of wire movement to begin with. 

        I agree with you on both counts.

        1. User avater
          Luka | Jun 11, 2007 12:02am | #11

          Taking it further...Twist the bare copper together before putting on the nut.Apply the nut. Keep twisting until the wires twist together further down.Tape. (Looking at the top of the wirenut, with the wires on the end opposite where you are, apply the tape clockwise. This opposes the direction the nut would have to turn, to come off.)Now apply one nylon wire tie. About 1/4" down from the nut. Cinch that sucker as tight as you can get it and cut off the excess.(Put more tape around the cut off wire tie, if you are concerned about it cutting someone or something.)IMO When it comes to electrical work, overkill should be standard. And is definately preferable to the 'kill' that may happen otherwise.And yes... I do all the above when wiring inside a motor or other environment where I think there is going to be any constant vibration. Yes, all of it. I didn't just add something because I read it here.I have done this inside outlet boxes as well. Generally I am satisifed there with everything but the nylon wire ties. Except when someone has cut the wires so short that it has been difficult to make the splice. I don't wanna go back and do that one again... LOLAnd recently I went to the crimped sleeves when I installed some baseboard heaters. I musta put a whole roll of tape on just 6 of those connections. LOL Something about all that bare copper giving me the heebies before I started taping.;o)Ok, so I get a bit OC when it comes to splices. Just putting the wirenut on correctly may be enough. But in my OC mind, when standing there doing the job, 'enough'... Is NOT.So sue me.

          Fight fire with water.

          1. User avater
            Luka | Jun 11, 2007 12:05am | #12

            Oh, and I twisted the wires together for about half their available length, when I did the crimps, too.

            Fight fire with water.

          2. edlee | Jun 11, 2007 12:13am | #13

            Why all that?  Why don't you just do it right and solder them?

             

            Ed

          3. User avater
            Luka | Jun 11, 2007 12:39am | #15

            ROFLOLSee Junkhound's response.I've alwys heard that soldered connections are less reliable.

            Fight fire with water.

          4. User avater
            maddog3 | Jun 11, 2007 12:59am | #17

            .." And recently I went to the crimped sleeves when I installed some baseboard heaters. I musta put a whole roll of tape on just 6 of those connections. LOL "Jeff, there are a few different caps for those sleeves , one type is reuseable while the others snap on and have to be cut off http://www.idealindustries.com/wt/CrimpConnectors.nsfsince Ideal bought Buchanan , their copper sleeves are listed as well, including the 4-way crimperbtw, these are the ones I mentioned in my earlier post.

            .

            .

            ., wer ist jetzt der Idiot ?

          5. User avater
            Luka | Jun 11, 2007 01:34am | #18

            Thank you.

            Fight fire with water.

          6. sharpblade | Jun 11, 2007 02:20pm | #25

            >>> I musta put a whole roll of tape on just 6 of those connections.

            You forgot the final coat of liquid tape (comes in 4 oz can with screw-top brush).

            Make sure you slather plenty of the stuff on top of the final tape that covered the plastic strap, that held the previous tape, that covered the wirenut, that held together the bare conductors. Can't be too cautious with them loose electrons.

            ;>)

          7. User avater
            Luka | Jun 11, 2007 10:14pm | #28

            Nah, I'll just use JBWeld or fiberglass gel to encase the whole lot down in the back of the box.;o)I wonder how far we can take this ?=0)

            Fight fire with water.

          8. Scooter1 | Jun 12, 2007 12:58am | #29

            I tape, and color code the tape. Black for hot; Red for switched; White for Neutral. Orange or Blue for a traveler wire in a 3 way switch. I agree that it makes servicing the box a bigger deal. Oh well.Regards, Scooter"I may be drunk, but you're crazy, and I'll be sober tomorrow." WC Fields, "Its a Gift" 1934

    2. User avater
      EricPaulson | Jun 11, 2007 12:45am | #16

      I tape...oh my God I admitted it!

      When spliced in a metal box and especially on dishwashers where there is a lot of vibration and movement and a metal box.

      Our electrician does same. He also wraps the outlets in the backslash for us so the tile guy doesn't get fired up.[email protected]

       

       

       

       

    3. HowardM | Jun 11, 2007 05:24am | #22

      I also slowly twist the wires as you say; and also place in opposite corners if possible.  Yes, I also wear belt and suspenders.

      One caution: Be sure NOT to twist too hard.  I did this and one of the wires broke just outside  the cap spring and not noticable until taking off the cap. Could not figure out why my table saw would not work; checked everything twice and then found the break.

      After twisting wires inside the cap; I also pull on each wire to be sure it is fully captured, and complete

    4. User avater
      Matt | Jun 11, 2007 01:50pm | #24

      >> It's an accurate observation that the vast majority of professional electricians don't tape.  That doesn't mean it's not a good idea -- just that the pros don't think it's worth their time. <<

      And as Luka says, they twist the wire nut until it twist the involved wires together down the insulation too in addition to the fact that they already twisted the bare conductors together with their pliers.  One additional point is that what I see is they use their Clines (electrician pliers) to twist the wire nuts on tight.

      I tape but here, in NC I am not allowed to do any electrical work (at work) since I don't have an electricians license, nor do I work for an electrician.  They pretty have it set up so you really can't get the license unless you do a multi year apprentiship.  Sure, I could wing it on a few things, but if there was ever a prob I'm sure the first thing that would happen would be that I would loose my GC license.   So, in 99% of the situations I have my electricians do whatever.

      1. WayneL5 | Jun 12, 2007 04:01am | #31

        Klein.

        http://www.kleintools.com/

      2. fingersandtoes | Jun 12, 2007 05:38am | #32

        I agree with Matt. Most Electricians I've seen use pliers to twist the conductors first, then trim the ends to equal lengths. They use pliers to secure the nut and twist the insulated wires.

        If you do all that right, what's the tape for? The only time I use tape is to label wires, or occasionally to hold wires on overhead fixtures together while I am hanging them.

  7. junkhound | Jun 11, 2007 12:16am | #14

    Dont use wire nuts, twist and crimp.  I use the ideal crimps with the rubber boot over them.

    In own house, even soldered the crimps -- even though mil-std-217 says a soldered crimp is less reliable than a crimp. That however, is due to often poor workmanship on soldering or mistaken use of acid flux;  mine soldering is always perfection however <G>.

  8. pm22 | Jun 11, 2007 03:58am | #19

    The only time I've been told to use black phase tape with wire nuts is in motors. Other than that, seeing tape on wire nuts is a sure sign of do it yourselfer at work.

    I pretwist solid wire with linemans pliers. For stranded, it doesn't seem to matter except that it seems to help hold the wires together until I can get the cap on.

    One post brought up the electrician who insisted on stranded wire. It may be easier to pull but is harder to push. But more importantly, it is harder to make the connections to the receptacle screws. The little strands tend to mush out.

    Note: I do wrap tape around the receptacles. Tape should be rated for 600 volts.

    ~Peter

     

    1. markusda | Jul 27, 2007 08:55pm | #35

      when you say you wrap tape around receptacles, are you meaning you wrap it around the entire device, such that one continuous wrap will cover the screw heads and bare copper from the wires?  I do this on outlets as well as switches.  be it for tile guys or whomever, it helps prevent someone getting lit up if they *accidentally* poke into the box with a conductor - screwdrivers being the most guilty conductor

  9. twincoach | Jun 11, 2007 04:52am | #20

    I not an Electrician but I play on on TV. at work we tape all motor connection  1/4 hp to 300hp IE 480 v 3 phs. general lighting and outlets no tape just twist the wire until it has 3-4 turns below the wire nut. we do tape the side  of all outlets and switches and I just put on an addition on the house inspector said to tape all outlets amd switches but nothing about splices. I have seen motor splices that have vibrated the wire nut right off the wire with out tape

    ps chemical plant we make glue

  10. GHR | Jun 11, 2007 08:03pm | #26

    Wire nut instructions do not say to use tape. Using tape may be a violation of the listing.

    1. rasconc | Jun 11, 2007 09:38pm | #27

      I doubt that, if it said "not to tape" then it would be wrong.  Just my opinion though.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data