Electrical Wire Sizing

timc | Posted in Construction Techniques on July 25, 2007 06:24am

I am trying to learn as much about electrical as I can and have what is probably a simple question for many electrians. Could someone explain to me how to interpret the NEC table 310-16 for sizing wire. My understanding is that there is also a separate table for service cable . Which table is it and how do you interpret that as well. Could you give some typical examples of both, for example, with a 200amp main panel what wire would be run to a 100amp sub panel.

thanks

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. pm22 | Jul 25, 2007 07:08am | #1

    I could explain 310.16 to you. So that should answer your question. {0.0}

    Actually, I'm just bumbing this post so I can answer it in the morning. Stay tuned.

    Note: for 100 amp and above, you can use the 75º column.

    ~Peter

  2. renosteinke | Jul 25, 2007 04:44pm | #2

    "Service cable" is ONLY the wire from the power company transformer to your meter .... and even then, that chart only applies for wires strung overhead.

    For a sub-panel, use 310-16. Otherwise .... call a sparky. There's a reason it's called a SKILLED trade.



    Edited 7/25/2007 9:44 am ET by renosteinke

    1. User avater
      BillHartmann | Jul 25, 2007 06:29pm | #3

      ""Service cable" is ONLY the wire from the power company transformer to your meter .... and even then, that chart only applies for wires strung overhead."That is wrong for section 310.15(B)(6).First the NEC has nothing to do with the POCO drop wires or under ground service.They only cover from the serive entrance in.Here is what the code says."(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders For individual dwelling units of one family, two-family, and multifamily dwellings, conductors, as listed in Table 310.15(B)(6), shall be permitted as 120/240-volt, 3-wire, single-phase serviceentrance conductors, service lateral conductors, and feeder conductors that serve as the main power feeder to each dwelling unit and are installed in raceway or cable with or without an equipment grounding conductor. For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s). The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors. The grounded conductor shall be permitted to be smaller than the ungrounded conductors, provided the requirements of 215.2, 220.61, and 230.42 are met."First it only includes single phase dwelling loads.It coverse above ground, below ground cables, and wires in racesways (conduit).And it covers service laterals and feeders from a disconnect to a separate (sub) panel.From the table heading."Conductor Types and Sizes for 120/240-
      Volt, 3-Wire, Single-Phase Dwelling Services and Feeders.
      Conductor Types RHH, RHW, RHW-2, THHN, THHW,
      THW, THW-2, THWN, THWN-2, XHHW, XHHW-2, SE,
      USE, USE-2"SE is above ground service cable.
      USE is underground service cable.
      And the others are wire that needs to be run in conduit.And from the NEC handbook there is some explanatory notes."For the 2005 Code, only editorial changes were made to 310.15(B)(6). If a single set of 3-wire, single-phase, service-entrance conductors in raceway or cable supplies a onefamily, two-family, or multifamily dwelling, the reduced conductor size permitted by 310.15(B)(6) is applicable to the service-entrance conductors, service-lateral
      conductors, or any feeder conductors that supply the main power feeder to a dwelling unit.Section 310.15(B)(6) permits the main feeder to a dwelling unit to be sized according to the conductor sizes in Table 310.15(B)(6) even if other loads, such as ac units and pool loads, are fed from the same service. The feeder conductors to a dwelling unit are not required to be larger than its service-entrance conductors. Exhibits 310.7 and 310.8 illustrate the application of 310.15(B)(6). In Exhibit 310.7, the reduced conductor size permitted is applicable to the service-entrance conductors run to each apartment from the meters. In Exhibit 310.8, the reduced conductor size permitted is also applicable to the feeder conductors run to each apartment from the service disconnecting means, because these feeders carry the entire load to each apartment.".
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      1. renosteinke | Jul 25, 2007 11:12pm | #4

        I think you're bringing in unrelated matters. I see nothing that allows the "service" ampacity table to be used for feeding a sub-panel. For that, the main table is uses (310.16). I believe the OP thinks the wires to the proposed sub-panel are "service" conductors. They are not. They are feeders. The effect of this is that he will need to use larger wire. He will also need a ground wire ... something absent from service conductors. On a more general note, questions such as this one indicate that someone is using the code book as a textbook, or a 'how to' manual, or a design manual ... something specifically proscribed in the introduction.

        1. timc | Jul 26, 2007 03:07am | #6

          You're correct, I should be referring to the wire from the main panel to the sub panel as feeder cable instead of service cable (would the feeder not be SER cable though?). I am not an electrician but a G.C. who subs out the electrical. I usually ask the electrician questions but hate to use up all his time answering my questions (or even sounding like I'm questioning his work), As a G.C. I feel I should have a better understanding of the electrical system and use the code not so much as a text book but more of a reference. Even if I were to do the work myself I wouldn't guess which wire to use, that is why I'd like a better understanding of how to size the feeder cable whether it's by using the NEC table or by some other method.

          1. edlee | Jul 26, 2007 02:45pm | #8

            As a G.C. I feel I should have a better understanding of the electrical system and use the code not so much as a text book but more of a reference. Even if I were to do the work myself I wouldn't guess which wire to use, that is why I'd like a better understanding of how to size the feeder cable whether it's by using the NEC table or by some other method.

             

            Well that's a reasonable request. With 310.16 in homebuilding you mainly use the 75-degree column and slide down to the ampacity or wire size you want, copper or aluminum. That will get you either right on the mark or at least in the vicinity and then your electrician can tell you about any derating or other conditions that might apply. The most common is when romex or SER is run inside thermally-insulated walls or ceilings, then you use the 60-degree column.

            To determine feeder sizes for subpanels is more of a calculation based on projected load . Once that's determined then you size your breaker and use 310.16 to figure your wire size.

            Ed

            Edited 7/26/2007 7:49 am ET by edlee

          2. timc | Jul 26, 2007 04:28pm | #9

            Thank you

          3. timc | Jul 31, 2007 11:29pm | #10

            Just confirm wether I'm getting the jist or not.

            Most electricians I've seen on (your average sized residential) jobs don't sit down and do a load calc (or at least I haven't seen them), they seem to be able to look at the size of the project, ask questions and from experience will know what's needed.

            Now, let's say, hypothetically, that there's are 2,000sqft house with an updated kitchen. Let's assume the calcs suggest that a 200amp main panel would be sufficient with room to spare (say for a future hot tub). So for a 200amp main panel there would be 2/0 SE cable from the utility splice to the meter base and the same from the meter base to the main panel. If the main panel feeds a 200amp sub panel the feeder cable will be SE type R 2/0. Or if it feeds a 100amp sub panel it would be SE type R #4 copper.

            Am

          4. edlee | Aug 01, 2007 02:50pm | #11

            So for a 200amp main panel there would be 2/0 SE cable from the utility splice to the meter base and the same from the meter base to the main panel. If the main panel feeds a 200amp sub panel the feeder cable will be SE type R 2/0. Or if it feeds a 100amp sub panel it would be SE type R #4 copper

            I agree that on an average residential job there isn't usually much calculating going on to size a service, at least for a single-family: 100a, 200a, or 320a.

            If you're using SE cable then you're talking aluminum, so according to 310.15(B)(6) you'd need 4/0, not 2/0, for the service entrance.

            For a 200a SUBPANEL off of a larger 300a or 400a service then I guess you'd need to go to a larger size, 3/0 copper or 250mcm aluminum. If you're talking about a 200a panel downstream of the 200a main switch, and that panel carries the entire load of the service, then you can stay with the 4/0 aluminum.

             For the 100a subpanel you'd use 310.16, 75-degree column,  and you will see that you'd need #3 copper or #1 aluminum. Since you said SER then you'd be using the aluminum.

             

            Ed 

          5. User avater
            BillHartmann | Aug 01, 2007 03:17pm | #12

            "If you're using SE cable then you're talking aluminum, so according to 310.15(B)(6) you'd need 4/0, not 2/0, for the service entrance."Unless you are talking about CU. It is available, even it might not be the most commonly used.http://tinyurl.com/277qws"If you're talking about a 200a panel downstream of the 200a main switch, and that panel carries the entire load of the service, then you can stay with the 4/0 aluminum."Even if it does not carry the full load you can still use the smaller load.The downtream cable does not have to be bigger than the servce entrace size.For example you can use one of the combo meter/panesl with 6-8 slots and a main.Feed the AC and hot tube off breakers in the panel and use feed through to a 200 amp panel for the main house loads..
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          6. edlee | Aug 01, 2007 11:25pm | #13

            Bill,

            Sure copper SE is available, but not readily. I imagine it would be a special order, cut to length, with a shipping charge.  Not really the point of OP's queries.

             

            "Even if it does not carry the full load you can still use the smaller load."

            Did you mean "you can use the smaller wire?"  If so, then I disagree. This is a common debate about Section 310.15(B)(6) and you and I are apparantly in opposite camps. 

             

            Ed

          7. User avater
            BillHartmann | Aug 02, 2007 06:03am | #14

            Yes, I meant the smaller wire.Here is what the NEC Handbooks says."Section 310.15(B)(6) permits the main feeder to a dwelling unit to be sized according to the conductor sizes in Table 310.15(B)(6) even if other loads, such as ac units and pool loads, are fed from the same service. The feeder conductors to a dwelling unit are not required to be larger than its service-entrance conductors. Exhibits 310.7 and 310.8 illustrate the application of 310.15(B)(6). In Exhibit 310.7, the reduced conductor size permitted is applicable to the service-entrance conductors run to each apartment from the meters. In Exhibit 310.8, the reduced conductor size permitted is also applicable to the feeder conductors run to each apartment from the service disconnecting means, because these feeders carry the entire load to each apartment."".
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        2. User avater
          BillHartmann | Jul 26, 2007 04:50am | #7

          " I see nothing that allows the "service" ampacity table to be used for feeding a sub-panel."It is mentioned twice."For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch-circuit panelboards(s).""The feeder conductors to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors."But those are special cases and not does not apply to his example.
          .
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  3. pm22 | Jul 26, 2007 12:18am | #5

    In their effort to make the NEC as incomprehenisble as possible, the Code making committee created Table 301-16. They could have produced a simple list but that would be too easy. To start with, you have to know what type of wire you're dealing with.

    You should also do a load calculation. [See Article 220.] Just because you have a 100 amp panel does not mean that you necessarily ever be drawing anywhere near 100 amps from it. For instance, if your max is 55 amps, then you can feed it with 55 amp wire [#6] and protect that with a 60 amp breaker. [240-3(b)]

    One thing to note is Article 110-14c. This essentially says that above 100 amps, the terminals are rated for 75*centigrade. Below 100 they assume 60*C. However you can search the device with your Edmund Scientific 1000X microscope and it might say otherwise. So we will assume that you want 100 amps and the breakers are rated for 75*. This means you can use the 75*C column. Except Romex, TW and UF must be from the 60* column. You look down the list and find 100 amps and then to the left and the answer is #3 wire.

    But note the asterisk next to 14, 12 and 10. This refers you to 240-3 which says they don't really mean it when they say in the 60* column that these sizes are rated for 20, 25 and 30 amps respectively. Those double-crossers really meant 15, 20 and 30 amps but its a little more confusing this way.

    But wait... there's more. And that is the wonderland of de-rating. You will notice at the bottom of the table a sub-table labeled "Correction Factors". Since the Code is pseudo-scientific, they realize that as temperature goes up, thhe resistance of the wire goes up so the carrying capacity goes down. So you have to multiply the amperage of your chosen wire by the appropriate factor. For instance, if your wire runs through the attic and the ambiant temperature there is 141*F, then you multiply your 100 amp by .33 and get 33 amps which is no longer good enough so you have to try larger sizes. This is good to know if you are taking an exam. In the field, you would measure the ambient attic temperature in the middle of winter.

    But that's not all. If you carefully read the entire Article 310, you will stumble across Table 310-15(b)(2)(a). This is the famous de-rating mechanism for conduits carrying more than 3 [current carrying] conductors. This trips up many pretend electricians who are really only installers and don't know their own Code or even own a Code book.

    On the surface, it seems simple. You have say nine #14 THHN wires. The de-rating factor for 9 wires is 70%. So you multiply 15 amps X .70 = 10.50 amps. Using 240-3b you could protect this with 15 amp breakers but you can't exceed 10 1/2 amps on any of those circuits.

    But there is hope. Since the wire is THHN, you can start your de-rating with the value in the 90* column. So your calculation is 25 amps X .70 = 17.50. This is okey-dokey, hunky dory and acceptable.

    ~Peter

    "Let me be clear about this. I attached the two black wires to one side of the switch and the two white wires to the other screw." --DIY forum.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Are Single-Room ERVs the Answer?

Learn more about the pros and cons of single-room ERVs.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper
  • FHB Podcast Segment: Are Single-Room ERVs the Answer?
  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data