ERV/HRV and Combustion air

Ribs | Posted in Energy, Heating & Insulation on October 18, 2006 04:45am

OK this is probably going to get long but here goes.

New boiler put in 3 years ago. House is only about 1500 Sq. ft. English colonial built 1935 near Boston MA. Presently no insulation in walls (plaster). Heat is forced hot water, gravity system converted to forced hot water with 1 zone and circulator when the burner was replaced.

Concern is the boiler room venting (I enclosed it during a basement remodel last year) and overall air quality. Boiler Room is about 11 ft. by 7 ft. and also contains a gas water heater, Furnace is oil. No venting presently but there is a window which could be used to get outside air.

I recently had a home energy audit done and I can get the walls insulated (blown in cellulose) through Nstar contractors for about $2100, estimated savings $400/yr. Nstar also has a rebate program which will rebate 50% of the $2100. So it seems like a no brainer. Attic in the house has about 6 inches of fiberglass unfortunately under a tongue and groove floor (so additional insulation there is a major project) This is also my only storage space as I don’t have a garage. I may go ahead and foam the roof as well given the floor insulation situation up there.

Now the issues. As I’m tightening up the building I’m getting more concerned about combustion air in the basement and indoor air quality overall. During the energy audit they checked the boiler and hot water tank for CO and efficiency, Neither was a problem for CO and the oil burner was running at 86%. I still want to make sure under a constant load and when running more often the boiler is running properly. Last year when I asked the boiler technician about the venting issue he said well let’s see how things work and we can address it if there is a problem (Ahh not the response I was looking for). I’ve switched companies this year and haven’t had anyone in yet from the new place. So before I do.

Questions what is the proper way to ventilate this boiler room as well as the rest of the house? I’ve looked at some ERV and HRV (Aprilaire) units but it seems everything is geared towards a house with a central air setup, forced hot air or installing ductwork throughout the entire house which is not an option (we’re not talking a lot of open closets or wasted space to run new ducts). I figure I could install a unit in the attic for the upstairs bedrooms (in fact we’ve considered this for central air in the future) but there is no way to get the same unit to ventilate the first floor never mind the basement without ripping out walls and such which ain’t going to happen.

so what kind of alternatives do I have? Anyone have any great ideas because I’m really at a loss on this one

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. MartinHolladay | Oct 18, 2006 11:46am | #1

    Ribs,

    First, let's talk about vocabulary.  When one speaks of venting (in reference to a boiler or a water heater), one usually means the venting of exhaust gases through a chimney or flue.  It seems that you're talking about something else -- usually referred to as providing combustion makeup air (that is, fresh outdoor air used for combustion).  You may well be correct that your boiler and water heater need better provision of combustion makeup air.  The trend in the industry is toward sealed combustion units that have ducted combustion air from the exterior.

    Secondly, you should know that neither an HRV nor an ERV is intended as a source of combustion makeup air.  They provide fresh ventilation air, not combustion air.  Manufacturers of HRVs and ERVs specificially note that the units are not intended to provide combustion makeup air.  They are balanced units -- that is, just as much air is drawn into the house as is exhausted from the house -- and therefore cannot and should not be used to provide necessary combustion makeup air.



    Edited 10/18/2006 9:35 am ET by MartinHolladay

    1. Ribs | Oct 18, 2006 04:19pm | #4

      Thanks Martin, I was pretty clear on the terms though not on the use of the HRVERV units. I guess my post was not clear on any of it. I pretty much knew ERVHRV was a balanced unit but I would have thought that combustion air was part of the balanced equation.Thanks for clarifying.Ribs

      Edited 10/18/2006 9:50 am ET by Ribs

  2. Brian | Oct 18, 2006 03:13pm | #2

    A 4" piece of pvc from outside the house terminating near the burner on your boiler and water heater will do the trick.  Less than $100 - solved.

    The windward side of the house would be the best location for the other end of the duct, and should be covered with a screen to keep the critters out. 

    Your appliances will benefit from denser, cool air, and will not depressurize the mechanical room.

    As for the living areas:

    If your house is super tight (difficult on a retro unless you spray foam, and well) you may need an ERV/HRV.  But I personally would wait and see if your humidity levels rise - it may not be an issue.

     

    Treat every person you meet like you will know them the rest of your life - you just might!
    1. MartinHolladay | Oct 18, 2006 04:32pm | #5

      Brian,

      As Tim's example makes clear, your solution (4" round duct to supply combustion makeup air) would almost certainly be undersized.  This is not a good example of a situation where guesswork is a good idea.  Years ago, an architect I know designed a mechanical room with insufficient combustion makeup air for a three-unit apartment building.  The owners discovered there was a problem after CO detectors were installed in the apartments upstairs.  All the alarms went off, the fire department showed up.  Sure enough, there was a problem. 

      1. Brian | Oct 18, 2006 06:57pm | #8

        Martin - Thanks for your concern, and perhaps my response came off as flippant.  I like Tim's post - the window is already there, and certainly adequately sized - its an elegant solution, though mechanical and not a simple as a dedicated duct.

        And its not that clear.  The 1" clear opening per 1,000 btu is for connection to inside air space in a house with a discontinuous vapor barrier.  The inside space may include several rooms if connected with high and low openings, with each opening providing one square inch of clear opening per 1,000 btu/hr input rating, but not less than 100 square inches each.

        Direct outside makeup air is a different animal - the (requirement drops by a third, or a quarter if any inside air is involved) and we'd need to know the btu ratings of both appliances for the times they would fire together.  The flue outlet sizing would help too.  (See the attached worksheet)

        Additionally, the house will be retro insulated with cellulose, and a blower door test will be the only way to tell, but it will be very difficult to seal the house tightly.  The insulation will be better - air infiltration...I'm not so sure - 38% reduction in air infiltration is what one manufacturer claims - but the older the house, the more problematic.  Even with a world-class cellulose job, he'll likely not suffer depressurization issues.

        Before I did anything, I'd have a $50 CO detector plugged in somewhere - in any house with fuel powered equipment.

        My Bock Oil Fired Water Heater has a 4" makeup air inlet, and a 4" flue.  This was engineered at the factory, and its a 126K BTU unit.  But I'm in an ICF house, so infiltration is minimal.

        I imagine adding any makeup air, in the OP's situation, would be a "belt and suspenders" approach, and a good idea.Treat every person you meet like you will know them the rest of your life - you just might!

        1. Tim | Oct 18, 2006 08:54pm | #9

          The reason I specifcally listed the Codes that require the configuration that I suggested was to hopefully prevent any confusion with a conflicting code such as the UDC. Frankly, I have never heard of this code. If this is the code that apples where you live and work, you have my condolences. It seems, from the worksheet you attached, cumbersome. OTOH, the International Mechanical and International Fuel Gas codes are basically reiterations of the NFPA code requirements for the same type of installations, and is widely accepted accross the country.

          So to be very clear, the 1 square inch per 1000 btu/hr of rated input is for direct supplied outside air to a mechanical room. The requirement that combustion air be provided by mechanical or gravity means is predicated on the "confined space" and "unusually tight" definitions contained within those codes.

          Comparing the venting configuration of a sealed combustion, draft induced appliance to a natural draft appliance with gravity combustiuon air supply is to compare apples to oranges. One is very different from the other. Mistaking that difference could create an unsafe situation.

          1. Brian | Oct 18, 2006 09:58pm | #10

            Comparing the venting configuration of a sealed combustion, draft induced appliance to a natural draft appliance with gravity combustiuon air supply is to compare apples to oranges. One is very different from the other. Mistaking that difference could create an unsafe situation.

            Sure - I thought of that, but I forgot to include it.  My unit is not power vented, however, but the ducting goes directly to the intake.

            I find it unusual that codes vary by a factor of three, and would choose the more generous figures to err on the side of safety.

            From the OP's description of his house, it sounds like he is headed in a good direction - I hope he takes your advice, especially if his room is well sealed.

             Treat every person you meet like you will know them the rest of your life - you just might!

          2. Tim | Oct 19, 2006 12:44am | #11

            "... unusual that codes vary by a factor ...."

            I do business in sevaral midwestern states, and the differences from place to place and state to state, can be staggering. Some codes are extreme overkill, some are just barely good enough. Some make no sense at all. For instance, the building codes in the city of Chicago seem to be soley for the enrichment of the local unions that rule the place, rather than concerned with the health and well being of the citizens.

  3. Tim | Oct 18, 2006 03:39pm | #3

    First, combustion air supply and general ventilation (i.e. fresh air for air quality in the living spaces) must be treated separately. An HRV/ERV for general ventilation is always a good idea. 200 cfm will give you 1 air change per hour (ACH) and will provide all the fresh air you will need.

    You said that you have a window that opens directly into your mechancial room, right? The best way to provide combustion air into a confined space would be to use the window, fit it with some duct and a motorized damper. The International Mechanical Code and The International Fuel Gas Code both require 1 sq inch of opening per 1000 btu/hr (for both appliances) of input. Say your boiler if 75K and your WH is 40 K, that is 115 sq in required. That could be done with a 16x8. A 24v, spring return motorized damper is readily available from Honeywell and DuroDyne. You would need simple controls to open the damper whenever the WH or the Boiler were firing. You mention a furnace. I assume you mean your boiler. As you tighten the house, you can create a condition where the inleakage is reduced to the point (I don't know what exhausts you have) that you could back draft (the WH and boiler have no power vents, right?) either WH (more likely) or the boiler (less likely, but possible). The manner I suggest is "by the book" with the addition of the requirement that there be two openings, one within a foot of the ceiling and one within a foot of the floor. Usually the jacket and piping heat losses are more than enough to keep the room from freezing, but it is a concern, especially if the damper sticks open.

    1. Ribs | Oct 18, 2006 04:49pm | #6

      Thanks Tim, those numbers from the code are exactly the type of thing I was looking for. I plan to have the new service guy in from the new oil company and wanted to ask him about the equipment you mention from Honeywell and durodyne (I had a quick look on line and couldn't find them). I'm guessing he will know how to hook it up so it opens when the boiler or WH fire (although based on the last guy won't count on it).Yes when I said furnace I meant boiler. No neither the WH nor the boiler are powervented. You said "The manner I suggest is "by the book" with the addition of the requirement that there be two openings, one within a foot of the ceiling and one within a foot of the floor." Do you mean the these two openings are in addition to the 1 sq inch of opening per 1000 btu/hr (for both appliances)? I found what I think is a good diagram of this but don't really understand the use of the ventilation air? It looks like the 1 inch/1000btu/hr is combustion air and the other two openings are for ventilating the utility room. Why do this if the units are not putting out any CO (all going up the chimney)?My sister had her house done last year by a contractor and fully inspected. They have two registers about 6 inches by 10 in the wall into the living space and were told that was sufficient (I'm guessing these are for ventilation). No allowance at all for combustion air besides that.Thanks again

      1. Tim | Oct 18, 2006 05:25pm | #7

        What I meant by the two openings is an "expansion" of the requirement of 1" per 1000 btuh. In other words, if you take my example, you would provide the 16x8 (min) opening into the space, using a duct with two openings in it, one near the floor and one near the ceiling. Each opening in the duct would be full size, 16x8.

        In a mechanical room of the size and equipment that you have in your house, providing the code required combustion air will suffice for any ventilation requirements as well. In a large commercial mechanical room, an additional 0.05 cfm/ft2 is required. Usually using outside air for cooling far exceeds the requirement.

        If you look here http://www.durodyne.com/products/durozone/durozone.pdf you can see the catalog that has the dampers in it.

        Edited 10/18/2006 10:35 am by Tim

  4. drafthunter | Dec 06, 2020 06:25pm | #12

    Great thread. Wonder what current thoughts are. I’m in the process of tightening up my house. Unfortunately because of COVID, blower tests aren’t allowed in my area at the moment. So I have no idea how tight the house will be.

    My primary heat is a Mitsubishi Hyper Heat multi zone ductless system. I usually run a Peerless oil fired boiler as a secondary system in the basement. It has a 6” duct exiting to flue into chimney. There is a window in the room, but I cringe thinking of letting all that cold air in.

    What if I were to run an HRV just for the basement with positive pressure and supply fresh air to the utility room, or is there a way to have the HRV go into boost mode when the boiler is firing? Still a no no?

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Vintage Sash Windows Get an Energy-Efficient Upgrade

Low-e storm panels improve the energy efficiency of these old sash windows without changing their classic look.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • From Victorian to Mid-Century Modern: How Unico Fits Any Older Home
  • Designing the Perfect Garden Gate
  • Vintage Sash Windows Get an Energy-Efficient Upgrade
  • Design and Build a Pergola

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data