Extending oven circuit w/ splice?

cwtaft | Posted in Energy, Heating & Insulation on July 23, 2002 04:53am

I am remodeling a kitchen and moving the double oven unit and the stove to new locations.  Each is currently fed by 8 ga wire and I would like to splice an additional 15 feet of 8 ga onto each circuit.  Is this a reasonable thing to do?  What is the recommended way of making the splice?  Thanks for your help.

Cyrus

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. BarryO | Jul 23, 2002 05:34am | #1

    Keep in mind any splice must be inside a junction box, which must be accessible.

    Use connectors rated for the application.  For example, Ideal makes a Wing-nut rated for joining two #8 solid or stranded, but their wirenut is rated for two #8 stranded only. 

    1. cwtaft | Jul 24, 2002 05:14am | #4

      Thanks.  What are Wing-nuts?  I bought some copper connectors that look like hollow bolts that the wires slide into.  I assume that wrapping these connections with electrical tape is ok for insulation?  I was wondering about whether soldering would be better or just a waste of time.  I will be making the splice in a square metal box in the attic.

      1. MisterT | Jul 24, 2002 01:23pm | #8

        What are wing nuts!!!!

        Step into the Tavern and have a look around.

        You can't swing a dead cat without hitting at least three!!!!

        Mr T

        Do not try this at home!

        I am a trained professional!

        1. Edgar76b | Jul 24, 2002 05:28pm | #10

          Yeah LoL, like I said wouldn't it be easier for Cyrus, to just buy more wire and make a new run? Safer too

          1. JohnSprung | Jul 24, 2002 10:26pm | #11

            If this is in conduit, going all the way with new wire may well be more cost effective.  The extra wire and time to pull it might be less than the time to make up the splices.  You'd have to know how long the existing run is, and make a judgement call about how nasty the working conditions in that attic are.  If it's Romex, you're stuck with splicing.

            -- J.S.

          2. cwtaft | Jul 25, 2002 04:24am | #13

            Thanks to all that provided advice.  I did strongly consider  making a new home run but getting the new circuits into the existing service panel would have been pretty tough because of the way the existing wires are run.  Where I am working in the attic is very accessible so I don't think it will be too bad.

            Cyrus

          3. archyII | Jul 28, 2002 03:22am | #20

            Sorry if I steal this thead, but do you guys tape all of your wire nut connections?  Do you tape around the terminals of outlets and switches?  When I was much younger I worked in a resturant and part of my job was to help and old electrian (he must have been at least 50yr old and I was 17). He always wrapped his wire nut connections with electrical tape and he would wrap outlet and light switches. He said that it was good insurance and when the place got repainted the exposed outlets/switches would be safe.  I have always done this.  In my new house none of the wire nuts, outlets, switches are wrapped. 

          4. CPopejoy | Jul 28, 2002 05:24am | #21

            ARchyII--

            Yea, some of the real old-timers I worked with--guys who installed knob and tube--could not get past the fact that a wirenut alone can make an adequate splice.  They'd tape 'em up.  A lot of inspectors now think that anyone who tapes wirenuts does it to hide a shoddy job (e.g., bare conductor extending past the skirt of the nut).

            I guess there's no harm in it, but I believe there's really no benefit to it.  I mean, you're wrapping PVC tape on clockwise (looking at the top of the 'nut), right?  So as the tape adhesive starts to soften (like when the splice heats up due to normal current), the stretched tape will start to move, to return to its original length; and it'll "relax" CCW.  If the 'nut is screwed on well, no problem.  But might it loosen the nut?

            On taping around devices, I occasionally do it in an old work situation where there's a metal box and the device is a real tight fit.  But most GFIs not have the terminal screws recessed a little, and clearance isn't a problem with a regular receptacle or a switch.  Taping over the terminal screws may keep a grounding conductor from accidentally touching a hot or neutral.  At least for a while, it will; but eventually, I think the wire will cut through the tape.  I'd rather have the ground fault trip the breaker while I'm there, so I can open up the box and rearrange the wires to address the underlying cause.

            Cliff

          5. 4Lorn1 | Jul 28, 2002 05:50am | #22

            Had an inspector require that we tape all wirenut connections at a FAA radar site. He claimed that it increased their resistance to vibration. I guess it might help some. Maybe not. Hard to say.

            I have taped connections in cases where there is a history of ants using wave tactics on the circuits. I have seen an entire 10 by 10 by 4 box filled to the top with dead ants. Seems that a single ant and a bit of moisture can get himself fried if the live surfaces are close enough. When the first ant dies it releases a distress signal that attracts his friends. Being single mindedly brave they march to their death while adding to the distress signal. This cycle continues until either the electrical or insect component fail. The tape keeps our insect friends safe and the boxes relatively unmolested.

          6. rez | Jul 28, 2002 06:37am | #23

            That was a really interesting post. Learn something new everyday here at Breaktime.Half of good living is staying out of bad situations.

          7. JohnSprung | Jul 29, 2002 08:20pm | #25

            > I have seen an entire 10 by 10 by 4 box filled to the top with dead ants.

            Perhaps you have an invention here -- an electric ant eliminator.  I can just see the late night infomercial now.  Do you think that if you stepped up the voltage with a transformer you might be able to do roaches?   ;-)

            -- J.S.

          8. User avater
            BillHartmann | Jul 29, 2002 11:44pm | #26

            John

            You might be on to something there.

            In an other forum a friend of mine was saying that ants where attracked to electric fields. He veified this when is well pump stopped and he found the pressure switch not working because it was jam packed with ants.

          9. Scooter1 | Jul 29, 2002 06:12am | #24

            I am old fashioned, and do things the way I was taught. I tape all wire nuts, and tape them with the corresponding tape for the circuit, e.g., black for an unswitched hot line; red for a switched hot line; and orange or blue for other coded hot lines; and white for a neutral line. The tape, if brought all the way onto the wire, holds the wire nut snug and prevents anything from poking up into the wire nut and zapping your connection.

            I also tape the sides of all switches . While this makes it a bit more dificult for a tester from being used on the switch from the outside with probes, it does prevent a short if one is dismantling the fixture without the breaker being turned off and it accidently makes contact with the side of the box, which is only about 1/8th of an inch away.

            Regards,

            Boris

            "Sir, I may be drunk, but you're crazy, and I'll be sober tomorrow" -- WC Fields, "Its a Gift" 1927

          10. archyII | Jul 30, 2002 02:24am | #27

            Thanks for the info.  I will keep taping since it does not take very long and there does not seem to be any downside.

      2. BarryO | Jul 27, 2002 07:00am | #18

        "Wing-nuts" are Ideal's twist-on connector with the 2 little plastic wings on either side. 

        'strange that they're rated differently than Ideal's Wire-nuts; I pointed out that example to make the point that you have to check that what you're using is rated for the application.

        Appropriately-sized split bolts work fine; it's just the extra work of wrapping them, as has been pointed out. 

        1. 4Lorn1 | Jul 27, 2002 07:40am | #19

          For #8 or smaller I would go with wirenuts. By all means carefully read the packaging to make sure you get the right size for your application. I have had good luck with Scotchlock 2s but I think any major name brand, applied with some skill and a little care, would likely perform as well.

          I included the text on split bolts because it was what you had on hand and you had little knowledge of wirenut, wingnuts being a particular brand of wirenut. These simple devices are the work horses of the electrical trade for the connection of smaller conductors. I had assumed, possibly wrongly, that the conductors were fairly large, #8 or larger, when I recommended the preinsulated lug set.

          I'm not sure my text really helps but I'll keep swinging if you keep pitching.

  2. 4Lorn1 | Jul 23, 2002 10:27am | #2

    What BarryO said.

    I will add that if the circuit is run in aluminum, common in this area, that a trip to an electrical supply house for some anti-oxidant compound and a set of preinsulated lugs, saves on time, that are rated for aluminum may be the ticket. If you don't have one a small stainless steel brush, looks like Rambo's toothbrush, will help and are available on the isle with the welding equipment in the big box.

    Brush or scrape off any excess oxides. Apply the anti-oxidant thickly and brush again. Wipe hands and apply a final coat just before you insert the conductors into the lugs. Tighten the lugs and do your final stapling or do something else for a few minutes. Recheck the lugs for tightness as the aluminum will tend to creep. Don't over tighten.

    Be sure to use proper connectors where the cables go into the box and don't forget to install a cover. You probably knew this last part but I see this sort of obvious failure to get it right at least once a week.

    1. MisterT | Jul 23, 2002 11:57pm | #3

      What 4 and barry said but turn off the power!!!!

      TDo not try this at home!

      I am a trained professional!

    2. cwtaft | Jul 24, 2002 05:16am | #5

      Fortunately these circuits are copper and not aluminum.  Thanks anyway.

  3. Edgar76b | Jul 24, 2002 05:34am | #6

    I'm no electrician, but why not just buy the entire length of wire and replace with a new home run. why mess with a  splice and a box etc. It might not be cheaper, but it will be a better job. Why mess around? Every connection creates resistance and the entire length might be important too. How long is the run? like I said I am not an Elec. maybe you should ask one.

    Does code really allow splicing , that size circuit?



    Edited 7/23/2002 10:41:03 PM ET by Edgar76b

    1. 4Lorn1 | Jul 24, 2002 06:57am | #7

      Insulating those split bolt connections will be the biggest chore. Rubber tape, electrical putty and high quality insulating, electrical, tape are available at most supply houses and some big boxes.

      I start by packing the hollows and deep recesses with electrical putty to keep the splice from breathing. This is less important in a dry location but a good practice. Then tightly wrap the bolts with rubber tape, the type with a backing strip not normal electrical tape, paying particular attention to any protrusions or points that may threaten to puncture any insulation. Build up a little better than 1/8" of tightly wrapped rubber tape. The connection should look much more ball like if this is done properly. 

      Finish off by actually insulating, everything before this is just set up to keep the bolt from cutting the insulation, the connection with a high quality tape. I use 3M Super 33 for the final layers it is tough and stretches well. Try to get at least 3 layers, I go for 4 or 5, of this tape tightly wrapped smoothly and evenly  to the entire split bolt. I tell my helpers that they should be able to hold the live joint under water without fear of getting shocked. Plan to use about half a roll of each type of tape on each connection. I use a little less, depending, but more, within reason, won't hurt. Don't scrimp but try to make it neat and even.

      To finish the application use your dykes to cut the tape several inches after where you would finish. Don't tear it or touch the sticky side. Let this flag relax for few seconds and then wind it into place without stretching it or touching the sticky side of the tape. Polish the final edge with a thumbnail. Failure to do this final step correctly causes many joints to slowly unwind in time.

      You could avoid this mess, it's not that bad after the first one, by using the set of preinsulated lugs mentioned before. They are quicker and easier but still care must be taken to make sure the insulation is not pressed against the wall of the box when the connections are stuffed in.

      Edited 7/24/2002 12:01:13 AM ET by 4LORN1

      1. User avater
        rjw | Jul 24, 2002 02:33pm | #9

        "electrical putty "

        Is that the same as anti-oxident?

        1. 4Lorn1 | Jul 25, 2002 04:22am | #12

          Electrical putty looks like, and may actually be, common duct seal or rope putty. It should be available at any good electrical supply house in blocks. It won't add much to your connections seeing as that the box will be high and dry. I wouldn't worry too much about it in this case. I mention it only because it improves reliability of bolted connections that may be under water so IMHO it wouldn't be good to discuss bolt insulation without a mention of it.

          It would occupy the air space that would breath as atmospheric or environmental pressure changes. In these cases the pressure, given enough time, can cause failure of the insulation and allow the connection to be filled with water. This causes corrosion, heating and electrical leakage.

          The anti-oxidant, looks like grease, won't hurt a copper to copper connection, it is vital in any connection involving aluminum, but is not necessary unless the split bolt manufacturer recommends it.

          I realize that my explanation was long and probably made it seem more complicated than it really is. I didn't mean to scare anyone off. Split bolts with hand wound insulation are a time honored solution with a long history of reliability that give an electrician a chance to show off his/her skills. The preinsulated lugs are faster, easier and adequate but being a romantic I still , sometimes , use the bolts. With practice it is not unreasonable to completely insulate a split bolt in 2 to 4 minutes including a final inspection. The second one you do will likely take half the time of the first. Get good at it and you may enjoy the process.

          1. User avater
            Luka | Jul 25, 2002 05:03am | #14

            To make a splice in 10 ga, I did the following. (This was a splice that was to be in the middle of about a 70 foot run, outside. Not to be stuck in a wall somewhere.)

            I cut one long, one medium, and one short leg on the ends of the 3 wires comprising the two cables to be spliced together. Making sure that there was a long and a short of white and a long and a short of black. The greens were both the medium size.

            I cut back the insulation far enough that I was able to twist the wire ends around each other, leaving one single, twisted leg about 3 and a half inches long. I then folded that leg, (just the bare copper part), several times, until I had a knot of copper. Crimped it down tight.

            I wrapped this with a couple of nylon wire ties, to prevent it from ever unbinding. I use the really thick, tough nylon wire ties. Not the cheesy kind that you can break just looking at them.

            I wrapped that in about 20% of a roll of electrical tape. Yes, I ended up with three very large knots in there. And this is why I made the alternating lengths. When I was finished, I had a bundle that, when laid together, was only a little more than one third as thick as it would have been if all three 'knots' had been in the same place along the length.

            I then wrapped all three together with pipe tape. Much thicker than electrical tape, and made to resist the weather. Used a LOT of that tape.

            I then wrapped it solid, one wire tie at a time, from one end of the bunch to the other, with the nylon wire ties. Alternating the 'head' of the tie, 180 degrees from each other, every time.

            Then folded a "Z" into the wire, and flattened it up to itself, and wire tied this together. (To keep the whole thing from ever being able to be pulled apart.)

            Now looking like a small log.

            I then slipped a piece of pvc pipe down over the whole thing. I filled it to the halfway point with 100% silicone sealant. Then wrapped that end up tight with the pipe tape, and wire tied everything so it would never unwind or pull loose. Repeated for the other end, and was done.

            The end result looked a lot like some kind of plastic sausage. No water will ever get into it, and you would pull the actual cable itself apart before that splice would ever be pulled apart.

            I was told afterward that the only thing really wrong with my approach was filling the sausage with silicone sealant. Apparently the sealant can degrade the wire, because of a chemical it puts off when curing. If I ever do it again, I will use rope putty instead.

            Quittin' Time

          2. 4Lorn1 | Jul 25, 2002 05:13am | #15

            I hope your kidding.

          3. MisterT | Jul 25, 2002 01:08pm | #16

            Luka ,

            By the time an electron gets through that many twists and bends, it is gonna be SOOO dizzy it won't know whether its positive or negative!!

            TDo not try this at home!

            I am a trained professional!

          4. User avater
            Luka | Jul 26, 2002 01:41am | #17

            4LORN1...

            When have you ever known me to be serious ? For that matter, when have you ever known me not to be serious ?

            ; )

            Mr T,

            All I cared was that for as long as I used it, those electrons still remembered that they were electricity.

            : )Quittin' Time

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized
  • Townhouse Transformation

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data