Figuring ductwork, CFM, for HRV

johnnyd | Posted in Energy, Heating & Insulation on October 17, 2005 06:59am

I’ve decided to take the plunge and DIY an HRV system.  I mastered and DIY’d radiant floor and super insulation/sealing, but now obviously need some air changes (moisture on windows, last night’s dinner still providing aroma in the morning).  Trouble is there is no ductwork, as I have (and don’t need) no AC.

7000+ HDD;  <1000 CDD climate

I’ve been looking at some of the instruction sheets from “Renewaire” brand HRVs, and it looks like I can run a fresh air supply duct and supply grill on the floor of a central hallway, and a stale intake/grill on the kitchen floor,  but the way the floor plan and access areas work out, the HRV unit itself needs to be about 4 ft from the stale air intake to allow basement  through-the-wall mounting, and the fresh air supply duct will be about 50 ft long. This is a 1600 sq foot house with typical 8′ ceilings through most, but the 24 X 20 living room/great room does have a cathedral ceiling  at a 4-12 pitch.

There is a standard hieght basement under the kitchen, with the rest of the foundation being sealed and insulated crawl space.

The Renewaire techs say this would be an out of balance situation, but I might get adequate air flow if I go to 8″ duct for the long run, and a slightly over-sized unit (130 CFM).  I thought I would use flexible insualted duct for ease of install. though I know I would be paying a friction penalty with flex duct.   How much I don’t know.

I do have good exit fans already, one in master bath off the central hallway, and one in the laundry/bath off the kitchen.

What do you HVAC guys say? Will my plan work…if not what would you suggest?

Thanks.

 


Edited 10/17/2005 12:02 pm ET by johnnyd

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Hubedube | Oct 17, 2005 10:06pm | #1

    maybe I missed it, but what type of heating system do you have in this home ?

    1. User avater
      johnnyd | Oct 17, 2005 10:38pm | #2

      It is radiant floor.  Very successful DIY sandwich with modulating electric boiler at .037/kWH, propane backup, five zones.  Works great except the lack of scorched air leaves me with humidity in the high 40s or  low 50s.  Even low-E windows mist up in cold weather.

  2. Brian | Oct 18, 2005 01:09am | #3

    Talk to VaTom - he built his own HRV...

     

    Treat every person you meet like you will know them the rest of your life - you just might!
    1. experienced | Oct 18, 2005 04:00am | #4

      A truly good HRV system has a supply grille/register in every room in which we spend good chunks of our interior time- bedrooms, den, family room, living room, dining room. Exhaust ports are placed kitchens,  bath or washrooms and possibly the laundry. The idea is to supply fresh air to the areas where we spend time and then it moves through the house to the exhaust ports in the rooms where we create moisture and odours.

      Just supplying to the hall outside bedrooms with closed doors for 8-10 hours overnight does not ensure good air quality and moisture control in those rooms.

      I am not familiar with "Renewaire". Are their systems sold over the counter at hardware stores? If they are, they may be offering the "handyman special" and not an HVAC contractor's version with better controls and more options/modes of operation. These are features that most people don't know they wanted/needed until they see a better system installed and running. I have seen this time and time again in my home inspection business as I explain the lesser systems installed in most "spec" homes to a  potential home buyer. "Why wouldn't they put in a better system??" the buyer asks.  After all, it's about good air quality and your health, why scrimp?

      I installed my first HRV in 1981 and have done about 450 since and  inspected about 1300-1500 for various purposes.

       

      1. Brian | Oct 18, 2005 05:55am | #5

        Experienced, you have quite possibly installed more systems then there are in my entire State of Maryland.  No one I have met knows of HRVs.  (except you genius BTers :-)

        What brand do you recommend?

        Since I have a very open floor plan, I'll probably keep the ducting simple...

         Treat every person you meet like you will know them the rest of your life - you just might!

        1. experienced | Oct 19, 2005 06:43am | #12

          The Venmar brand (a Canadian co. now owned by Broan of Rhode Island) makes some of the  units I would install in my home today (even after fighting  with them all throughout the 1980's). See their website at:

          http://www.venmar.ca

          They have heat wheels and plate type heat exchange mechanisms. The heat wheel is more effective if you air condition a lot. Install the "Ultima" control.

          1. User avater
            johnnyd | Oct 19, 2005 03:42pm | #14

            Thanks much for your comments so far.

            The idea is not to DIY the HRV unit itself, I think the "Breeze" unit itself will be satisfactory.  I'm still wondering about my ducting scheme, which would have a really long duct supplying fresh air to a central hallway, with adjoining rooms recieving fresh air from that grill when the doors are open, which is nearly always.

            That duct will travel through the crawl space to the unit which will be mounted on the interior basement wall, have its inlet and outlet going through the basement wall (PTW foundation easy to cut holes), and recieve exhaust air from a grill directly above it through the kitchen floor.

            There would be other ways to route the ducting, all of them comparatively labor and disruption intensive, which is why I'm willing to compromise a bit on the effectivness and over-size the unit.  But,  will it work at all with that much difference between the exhaust and fresh air duct lengths, or will that fan just be churning away, unable to overcome the inherently un-balanced ducting?.

            A similar situation I suppose would be where a house would have one exhaust fan unit in the attic serving multiple bathrooms and a kitchen, with widely variable duct lengths.  Does the room farthest from the fan unit get the same CFM volume as the room closest to it?

            From having designed and built my own RFH, I know there are certain design parameters (tube length, water temperature, near-boiler piping etc) that if stretched too far from the norm, render the system nearly non-functional,  which is why I'm proceeding with caution on this HRV system.

          2. VaTom | Oct 20, 2005 05:49am | #15

            Digressions, as you know, are common.  <G>

            a really long duct supplying fresh air to a central hallway, with adjoining rooms recieving fresh air from that grill when the doors are open, which is nearly always.

            Why would the air enter those rooms?  You planning an exhaust duct in each one?  I pressurized all my rooms and closets with a fresh air supply.  It pushes air out the doorways to the returns located in our large open space.  You need to think about air movement, it doesn't happen by chance.  Pressure (+ and -) and convection both work well.

            I won't pretend to fully understand your plan.  We have one fresh air run that's 80' long.  It works, but the closer vents get more air, as I planned.

            If you're hoping for someone to give you static pressures and fan capacities, I don't think you have the right forum.  Certainly I'm no expert.  I based our air system on my knowledge of shop dust systems.  Works pretty much the same way except it's much easier when you have 2 movement sources (push and pull) in the house air system.PAHS Designer/Builder- Bury it!

          3. NRTRob | Oct 26, 2005 11:01pm | #16

            I second the choice of a Venmar unit; great fans, we use them all the time. they have balancing dampers, with a magnahelic gauge you can balance the situation as needed.I would wonder about a floor register for supply air though. Supply air will necessarily be cooler than room air, thus having it high off the floor would be best.. even with radiant, there is *some* hot air stratification and this will help prevent any drafty sensations. Don't you dare use ceiling fans with radiant!!!! That's like peeing in the punch at a party!!!Long flex runs should be upsized, yes. Pull the duct tight to minimize frictional loss. If it's a straight run, then perhaps using galvanized wouldn't be much harder though.I would take a hard look at the floor plan and see if there are any places where you can do some creative carpentry to distribute the air a bit better than what you are describing. Perhaps building out the side of a closet wall, for example.-=Northeast Radiant Technology=-
            Radiant Design, Consultation, Parts Supply
            http://www.NRTradiant.com

      2. User avater
        johnnyd | Oct 18, 2005 03:03pm | #6

        A Google search brought me here:

        http://www.positive-energy.com/pages/VentilationWH3.html

        From there you get this:

        http://www.breeze.renewaire.com/ventilation.htm

        I understand the best system would be one which has a supply to every room and and an exhaust from moisture producing rooms.  Fairly easily done where the HRV was a factor during frame-up, or where there's an existing forced air system, but in my case, with radiant floors and no AC, like it or not, the HRV is an after thought.

        I'm just wondering if a single inlet and outlet would still be signifigantly better than cracking a window and leaving the bath fans on.  Especially given that I would like to run one 50' 8" flex duct for the supply and ~ 5' 6" for the exhaust.  I mean, would that kind of a duct setup even work?

        I know it's fairly common to duct a forced air funace with several supplys in each room and ONE cold air return to the furnace.  But there you're delivering heat, and the HRV is simply exchanging air. I also would run ceiling fans on low speed to disturb stratification and spread the fresh air around.

        1. Brian | Oct 18, 2005 04:25pm | #7

          My plan is to pull air from 2 baths and a kitchen on the main level, and return air to the basement, so both levels will be cleared.  My floorplan is rather open, so I think it would be too much to duct every room.

           Treat every person you meet like you will know them the rest of your life - you just might!

          1. User avater
            johnnyd | Oct 18, 2005 04:37pm | #8

            Yes, my plan is open as well, but the basement has an exterior entrance, so is not included in the envelope.  The basement/crawl space is well sealed and insulated as well, though, and since the HRV unit itself is located there, I may be able to get some moderate circulation there as well.

            What has me flumoxed is that with so many forced air systems all over the country, why an HVAC guy that does alot of ductwork doesn't respond to this thread...if only to say that my design will not work and why?

          2. VaTom | Oct 19, 2005 05:37am | #9

            What has me flumoxed is that with so many forced air systems all over the country, why an HVAC guy that does alot of ductwork doesn't respond to this thread...if only to say that my design will not work and why?

            In my area, HVAC guys are only HACs.  I've met exactly one who knew anything about ventilation, and that was because his daughter was asthmatic and had to learn.  Operable windows are considered to have satisfied ventilation code requirements, even though at least half the year most never crack a window.

            As Brian mentioned, I DIYed.  We have 1600 sq ft, but 20,000 cu ft (average ceiling height of 12.5'), which is the far more important number.  What you're looking for is airchanges, preferably at least .5 ACH (air changes/hr).  These will be tiny fans, requiring small ductwork.  I used 5" round (flex) duct and supply fresh air to all rooms and all closets.  It's working just fine, thank you.

            Controlling humidity is another matter.  We monitor rh constantly and act accordingly.  For the remainder of the winter, adding humidity is in order here.  Roughly half the year we dehumidify at least occasionally.  I haven't looked at the climate differences between Va and Se Minnesota in terms of rh, but I don't think we're far apart.  Obviously heating and, possibly, cooling degree-days will differ greatly.

            Phone service, and dialup, was disrupted here for a couple of days, so I haven't looked at the link.  I used aluminum roofing for the heat exchanger core and got nearly 90% efficiency, based on a Popular Science article for an air-to-air heat exchanger.  Our plan is extremely open, which makes air circulation very simple.  I planned for a convection current that worked out even better than I'd expected.  We have 6 fresh air sources, 2 returns, in a 1 BR, 1 BA house.  Guests have often remarked on the quality of our indoor air.

            Hope this helped.

             PAHS Designer/Builder- Bury it!

          3. caseyr | Oct 19, 2005 06:40am | #11

            I have long thought about building my own aluminum HRV.  I originally thought I might TIG weld the thing.  However, given my TIG welding speed (and current quality), I think I will go a different route...

            A couple of questions, if I might, about your DIY HRV - How many partitions of the aluminum do you have in yours.  When you mention "aluminum roofing" did you use the standing seam stuff, if so, did you include the "V's" in your design or just use the flat sections.  Have you had any problem with moisture freeze ups (or anticipate any)? 

            Back in my alternative energy days in college (long, long, ago), some friends tried burying long runs of fairly large diameter pipe in the earth to try and get some cooling of the incoming air from the soil.  They ended up getting a fair amount of condensation and a lot of mold in the pipes so they recommended against others doing this.  Have you checked for mold?  Did you use marine paint on all surfaces that might have some antifungal properties? 

            Thanks, Casey

          4. VaTom | Oct 19, 2005 03:28pm | #13

            Hi Casey.  Sounds like you've been looking into this for awhile.  Congrats.

            Textured corrugated aluminum roofing was what I used, with weather-stripping intended for use with Onduline roofing, which I had around.  Probably still have enough for yours if you're interested.  Then I used sheet metal screws to hold it together.  IIRC, I made a 2'x'2x~8" core.  It was whatever 1 sheet of roofing yielded.  Other than the core and pressurizing the house as Brian mentioned, our airflow is very similar to the below article. 

            On the advice of the article, I made a drain pan plumbed into a house drain.  It never saw any flow so I disconnected it when changing fans awhile back.  My guess is that the only time we'd get inner condensation, summers, is when I was already drying the air with a dehumidifier before the incoming air (now dry) hit the exchanger.  Winters, we add humidity (whenever we fire up the woodstove) and never run the shower exhaust fan.  Icing hasn't been a problem, but this isn't exactly the frozen north.  I also have a few feet of duct in our heated space before the exchanger. 

            We have very humid sunmmers, don't use AC, and are serious about dehumidification.  Monitoring indoor rh tells us when to turn on shower exhaust fan, dehumidifier, whatever's necessary to correct the imbalance.  Automation we happily avoid.  One word of advice, make it convenient to change fans.  They don't last forever.  We got upwards of a decade of non-stop use.  That was muffin, the squirrelcage ones I tried were worthless.  Surplus Center in Nebraska usually has a good selection.  http://surpluscenter.com/community.asp?UID=2003031823141350&catname=electric

            The earth tubes you mention are often a subject on the alternative architecture lists.  Nobody, myself included, has had the temerity to use them in the SE that I'm aware of.  The problem, as you identified, is condensation which will provide an excellent habitat for mold growth.  We get no mold with our simple system. 

            Hait, the guy who wrote the book I followed for our passive annual heat storage (PAHS), believes earth tubes to be an important integral part of the plan.  While we don't get his performance, this is by far the best performing house I've lived in.  His demonstration house was in Missoula.  If we lived in an arid region, I'd have installed earth tubes.  There's a guy in Vermont who's planning on using them, currently trying to figure out flow rate.  Another says he's going to in Missouri but he's not there yet.

            I believe the answer in a humid climate is to either pre-dry the air, use a marine coating inside the tubes, or let the mold grow and treat the air with UV.  The latter is what I'd like to try, but no way am I going to be the canary.  And adding yet another active system is counter to my housing goal.

            By the way, a good friend here is having a small elaborate (expensive) house built.  One HVAC guy told him that all he needed was normal opening and closing of outside doors to ventilate.  He's been through several firms trying to find somebody who knows something about ventilation.  I warned him about talking to somebody (me) who had a little knowledge and wasn't involved with his house.  Can create all sorts of problems.  But he's not DIY, and that's the rub.

            Anyhow, enough of this tome.  And I have a hydraulic line that lost over $100 worth of oil yesterday awaiting me.  Here's the article:

             

             PAHS Designer/Builder- Bury it!

          5. Brian | Oct 19, 2005 06:01am | #10

            I cannot speak for ductwork, but I'd take the cubic footage of your house (probably s.f. x 8 or 9 feet - conditioned area only) and figure how many air changes/hour (ACH) you desire, do the math, and this will give you cfm requirements.

            VaTom, another poster here, recommends a push/pull arrangement on fans with different ratings creating a slight positive pressure in the house.  (e.g. 500 cfm output 650 cfm input)

            My thoughts on ductwork are oversize them so you won't stress out fans or have noise at your registers.  I am in the dark on particulars.

            edit - thanks VaTom - I was typing while you posted

            Treat every person you meet like you will know them the rest of your life - you just might!

            Edited 10/18/2005 11:03 pm ET by Brian

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Custom Built-ins With Job-Site Tools

From building boxes and fitting face frames to installing doors and drawers, these techniques could be used for lots of cabinet projects.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data