Fire Extinguishers, and the ADA/ABA

I’m trying to mitigate some issues from an OSHA inspection at work.
I have a quandary due to a conflict between the fire code, and the ADA/ABA.
Fire code requires the maximum travel distance to a fire extinguisher to be 75-feet. And, that the extinguishers be located on the path of travel, which means in the hall ways.
The ADA/ABA does not allow, any protrusion from the wall of passageways, greater than 4-inches, from 27-inches above the floor to 80-inches.
Since the walls are concrete, and the extinguishers, when mounted on the required brackets, extend more than 4-inches into the hallways, I’m at a loss on how to balance the two requirements.
Any ideas?
Replies
Recessed niches for the fire extinguishers.
Or, at the end of a hallway, not along the walls if the distances work out.
Along the path of travel doesn't necessarily mean in the hallways, just on the way to the exit. It might mean hallways if that is the only path to the exit, but it could mean, for example, mounted on building columns in a large, open manufacturing area between work stations and an exit.
How wide are your corridors? seems the pathway would only have to be so wide. I would consult a fire extinguisher cabinet co. and see if they could help you out.
I just helped lay out 20 fire extinguisher cabinets today in a school, but they were all recessed. For mounting heights they were called out 47" to the extinguisher handle.
I have done industrial projects that had extinguishers on brackets in the corridors, and no one took issue with it.
Let us know what happens.
Mike
Small wheel turn by the fire and rod, big wheel turn by the grace of god.
Not sure about your building but doesn't the path of travel include stairways and other spaces connected to the hallways where it might be easier to work surface-mtd. extinguishers into the required clearances?
Jeff
Slab on grade, so no stairwells. The only solution I'm coming up with is to build a cabinet, that runs floor to ceiling, so that blind people with canes, can find the bottom, and know not to run into it. I agree with the ADA/ABA in principle. But, sometimes it can get pretty frustrating trying to balance all the different codes.
Here's a link to Larsen's Mfg's ADA info sheet.
http://www.larsensmfg.com/fire_extinguishers/ada.html
They make a semi-recessed can that projects 4". Any chance of chipping out 2.5" of concrete?
It's possible they might make some type of accessory as this situation must come up on a somewhat regular basis.
Maybe you could just create a pseudo column (I-beam style), with boards on each side of the extinguisher, running floor to ceiling.
As I stood before the gates I realized that I never want to be as certain about anything as were the people who built this place. --Rabbi Sheila Peltz, on her visit to Auschwitz
Here you go.
http://www.safetycenter.navy.mil/photo/archive/archive_301-350/photo339.asp
OVAL Fire Products
Looks like someone has invented an innovative solution to your problem. Check out http://www.ovalfireproducts.com to see their oval fire extinguisher.
Kevin
No need to hide behind a pseudonym, tell us about your invention and the approximate time of release.