Fishing wire through conduit

PenobscotMan | Posted in Construction Techniques on April 30, 2007 07:44am

I’m installing a motion-detector light and will need to conect it via conduit on the house exterior.   I’ve had much experience with romex, little with conduit.  My most recent experience – fished romex through 3/4 conduit, found it hard going, ended up fitting conduit over the cable, which seemed wrong.  So, I am going to need some advice:

1. Total run will be about 15 ft, but I need to make 3 90 degree turns.

2. Should the turns be with those special pull boxes or with the long-sweep pre-bent pieces?

3.  Metal or PVC?  Or that new moisture-tight flexible conduit?

4. Cable or individual wires?  If the conduit is PVC, do I need a ground wire?  If, not, what happens to the ground wire in the romex when I make the romex-to-conduit, inside-to-outside transition?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. JAlden | Apr 30, 2007 08:02pm | #1

    I'm no expert but until someone else comes along.

    Do not use romex, just individual wires. No ground wire if using metal conduit.

    3-90's no problem. I believe code says 360 degrees max. Pre bent or bend yourself.

    Use a pull lube when pulling your wires. Pull them all at once.

    1. User avater
      IMERC | May 01, 2007 09:15pm | #11

      pull the ground wire anyways..
      be safe..Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming<!----><!----><!---->

      WOW!!! What a Ride!Forget the primal scream, just ROAR!!!

    2. highfigh | May 02, 2007 07:26am | #23

      No ground wire is OK if it's for lights but if there are any microprocessors in the device, dirty power is their biggest killer. Sure, the conduit can handle a lot of current but over time, the joints can and do add resistance.
      "I cut this piece four times and it's still too short."

  2. pgproject | Apr 30, 2007 09:41pm | #2

    use thhn wire, no ground needed. run conduit first, push fish tape through, ore use shop vac to suck a string down the emt. attach wires, use lube, pull, easy.

    1. User avater
      BillHartmann | May 01, 2007 02:02am | #5

      "use thhn wire, no ground needed."ONLY IF IT IS METALIC CONDUIT. Even then, if EMT is used many people feel that it is good practice to pull a ground wire and the connection on EMT might work loose."ore use shop vac to suck a string down the emt."Not by itself.You need a "mouse" on the end of the string. A puffed up baggy is often used. Some thing to "seal" the conduit..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  3. grpphoto | Apr 30, 2007 10:03pm | #3

    > Should the turns be with those special pull boxes or with the
    > long-sweep pre-bent pieces?

    I use the long-sweep sections. You might want a pull box at the point where the conduit goes through the wall, or you might install a junction box rated for outside use at that point.

    > Metal or PVC? Or that new moisture-tight flexible conduit?

    I prefer metal.

    > Cable or individual wires?

    Use individual wires.

    > If the conduit is PVC, do I need a ground wire? If, not, what happens
    > to the ground wire in the romex when I make the romex-to-conduit,
    > inside-to-outside transition?

    If you use PVC, you'll need a ground wire. I usually run one even in metal conduit, but it may be overkill. You will make the transition from Romex to individual conductors in a junction box. This box will either be outside, in which case the Romex comes through the wall directly into the box, or it will be inside and the conduit will go through the wall. In either case, you can attach the Romex ground wire to the metal junction box and let the conduit serve as ground. As I said, I prefer to just run the third wire.

    George Patterson

  4. User avater
    maddog3 | May 01, 2007 01:51am | #4

    if you know how to bend EMT without kinking it ... use individual stranded wire instead of solid, it will pull easier for you through those three 90s.
    ..
    but it takes practice to learn how to bend pipe correctly, so you may decide on PVC..which may be the better choice in your situation....since you have mentioned moisture

    if you do decide on EMT, (this would not be my choice )
    don't forget to ream the cut ends before you couple them together and use raintight fittings.

    Good Luck

    .
    .
    .
    ., wer ist jetzt der Idiot ?



    Edited 4/30/2007 6:54 pm by maddog3

  5. peteduffy | May 01, 2007 02:11am | #6

    I would just qualify PGProject's response regarding ground:

    If you use metal conduit, you don't need a ground, like he said, BUT only if the conduit is the ground, and you use metal boxes.

    Here in Chicagoland, everything is in metal conduit/EMT, and the piping acts as the ground.  If you have something different, make sure you have something as ground.  It wouldn't be a big deal to run a third wire.  And I like to add a ground wire on exterior fixtures (from the fixture to the box), because screws can corrode and you can lose the ground.

    Bending EMT is no big deal.  Buy a bender, buy some extra pipe (it's cheap), plenty of fittings, and have a go at it.   Assemble your practice pieces, call it art, and sell it.

    Cut it with a hacksaw or Sawzall with a fine blade (rather than with a tubing cutter).  It leaves a much smaller burr to take off.  And be sure to deburr, or you'll nick your insulation and make pulling more difficult than it needs to be.

    (3) 90° bends, 3 THHN wires in 1/2" EMT shouldn't be that difficult.  It would be easier to run a fish tape through and have one person pulling and one feeding.

     

    Pete Duffy, Handyman

  6. pm22 | May 01, 2007 04:07am | #7

    In your case, I would recomend PVC since it is easier to work with and intrinsically waterproof. For sharp, out side bends, use the special fittings known as condulets. You can bend PVC by heating it to about 212º. Do not use 1/2" PVC under any circumstances since it is so hard to pull.

    The special waterproof flexible conduit you mentioned could be LiquidTite. That would solve the bend problems but it is rather sloppy in looks and the fittings are more expensive.

    As for Romex in conduit, the Code is rather unclear, but then it is unclear in a lot of situations. Use individual wires including a green wire.

    Don't forget the clamps. More is better. You need one within 3' of each box and then once every 10'.

    For a 15' run, you should be able to push the wires thru.

    ~Peter

    1. [email protected] | May 01, 2007 07:55am | #8

      I agree, pull a ground. 

      The MGM Grand fire in 1980 was caused by heat in a bad connection in emt used as the ground.  There was short in a box that fed a refrigerated display cabinet, that went to ground through the emt.  Because of the bad connection it didn't pull enough to trip the breaker, but did generate enough heat to start a really big fire. 

      1. PenobscotMan | May 01, 2007 08:01pm | #9

        OK, so I'll use metal (this got most of the votes) but pull a ground to be extra safe.  And individual wires.  Should the ground be a bare wire? I will probably use the pre-bent corners or I may decide to rent a conduit bender.  I did that, years ago, but my local rental place went out of business. 

        I haven't seen the water tight conduit fittings at HD that a poster mentioned.  If I can't find them, I guess that would be an argument for PVC.

        Thanks, guys, for all the help.

        1. User avater
          BillHartmann | May 01, 2007 08:57pm | #10

          I just did this Sunday and used PVC. I like working with it better and it doesn't rust.Now I don't know where you are making the turns. But for going around a corner you need to use a coundit body or the conduit would stick way out. And say runnign vertically and then horizontally up on the wall personally I think that the conduit body looks better, but other might think that the sweep look better.Bare ground wire is more common in larger sizes (for ground electrodes). Typically in #14, 20 I see insulated..
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          1. PenobscotMan | May 02, 2007 02:46am | #16

            Bill, what do you mean by this: "But for going around a corner you need to use a counduit body or the conduit would stick way out" ?   

            What's a "conduit body"?  I definitely need to go around an outside corner.  Do you mean that the radius of the pre-bent sweep is so big that it wil stick out even though the conduit is flat to the wall?  I can't visualize this.  Better go and look at some pieces!

          2. RustyNail | May 02, 2007 02:56am | #17

            Agree with Bill's comments on the Romex.  It IS allowed in conduit... (assuming conduit is sized properly).  That's a point often argued over, but Bill's right. 

            By conduit bodies, Bill is referring to LBs, LLs, LRs, and a host of other conduit fittings that can act as a pull point and allow you to sharply make turns (versus the typical "sweep" of a 90deg ell).  Do a Google on "LB" & "Conduit" and you'll see what we're talking about.  Big boxes typically carry LBs... 

          3. User avater
            BillHartmann | May 02, 2007 03:19am | #19

            The conduit body is fitting that has 2 female openings in it. On one the end and the other in the back or right orleft side. Then it has a coverr over it.You don't fish through those. You remove the cover and it becomes a pullt point.Actually the make two other styles. One stright through where you just want to do a pull in the middle of a long run and a T.You need those to make sharp 90 turns. They are needed where you come out of wall and for an outside corner. You can use a radius for an inside corner depending on how it looks to you.http://www.cantexinc.com/p_access1.htm
            .
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          4. PenobscotMan | May 02, 2007 08:08pm | #24

            I know what you mean now -- I was referring to these as pull-boxes.  Thanks again.

        2. User avater
          maddog3 | May 02, 2007 04:02am | #20

          only use an insulated ground wire if you are going to use EMT.. as bare copper will eventually eat a hole on the pipe wherever it makes contact with it
          .

          .

          .

          ., wer ist jetzt der Idiot ?

        3. grpphoto | May 02, 2007 04:51am | #21

          You could probably use bare wire for the ground wire, but I use a conductor with green insulation.George Patterson

        4. User avater
          BruceT999 | May 02, 2007 06:32am | #22

          If you use thinwall conduit, I recommend using compression fittings for weather tightness - HD and Lowe's have 'em. Using pre-bent sweeps is easier than bending conduit yourself. I wouldn't bother pulling a ground wire if you use metal boxes. I have done rehab work in a lot of old houses with conduit and metal boxes and have had no problem with conduit grounds.Be sure to ream the cut ends before putting them together - makes the pull go easier and, with burs gone, you won't risk tearing up insulation. Klein offers a hand tool to ream both inside and outside of 1/2", 3/4", or 1" EMT in one quick operation - available at HD, Lowe's or any electrical supply house - looks sort of like a nut driver.
          BruceT

  7. User avater
    MrSQL | May 01, 2007 11:16pm | #12

    In my opinion (not a pro, but a fair amount of experience), I'd pull the regular romex wire since individual wires will probably be more expensive in shorter lengths. 

    you definately have to use wire lube and pull each section through 3/4" PVC conduit separately; then glue it up after the wire is pulled.

     

    1. [email protected] | May 01, 2007 11:25pm | #13

      A buddy who is a licensed electrician, said it was a code violation to put romex in conduit, and couple of electrical engineers I used to work with all told me that romex does not belong in conduit. 

      I haven't checked the code, but all three were people I have a lot of respect for, so I wouldn't be tempted. 

      1. User avater
        BillHartmann | May 02, 2007 01:10am | #15

        "A buddy who is a licensed electrician, said it was a code violation to put romex in conduit, and couple of electrical engineers I used to work with all told me that romex does not belong in conduit. "Not true.In fact the code calls out the use of conduit (and other options) to guard exposed NM. One common place is in unfinished basements where NM is run down the wall to a receptacle.Now I admit that is a limited application and does not include any turns.But cable can be used in conduit. The problem is that you need to size to be a wire eqivalent to the larges width of the cable. And it is hard to pull..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      2. r | May 02, 2007 03:00am | #18

        refer your 3 friends to NEC chapter 9, Table 1, Note 9, which explains the conduit fill calculation for a multi-conductor cable (Romex) in conduit.

    2. JAlden | May 01, 2007 11:47pm | #14

      You can't glue after the wires are in. The glue has the potential to melt the wire insulation if it drips inside.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data