cloudbuster | Posted in Energy, Heating & Insulation on June 26, 2007 05:56am

Hi:  Appreciate any comments as to the benefits of flex duct vs. sheet metal ducting. 

 

Thanks

Cloudbuster

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. jet | Jun 26, 2007 06:04pm | #1

    I do believe that the flex duct can be a 10:1 restriction over ridged pipe. In other words....1 foot of flex has the same restriction as a 10 foot ridged pipe.

    "No doubt exists that all women are crazy; it's only a question of degree." - W.C. Fields
    1. NRTRob | Jun 26, 2007 09:02pm | #4

      2 to 1, I believe, not 10 to one.Flex duct has its place. If the added restriction isn't a problem, then great! for IAQ, flex is usually fine. for A/C, maybe not.it doesn't look very good exposed though. for any exposed ducts we are going to metal.-------------------------------------
      -=Northeast Radiant Technology=-
      Radiant Design, Consultation, Parts Supply
      http://www.NRTradiant.com

      1. Piffin | Jun 27, 2007 06:45pm | #14

        I do almost all remodeling, so I get to tear things up and see the old.Most heat here is hydronic, but I do see the flex on exchangers or for hot air systems and for AC sometimes.It seems that very often the flex duct is crimped or collapsed someplace along the line - maybe a third of the time causing extreme limitations of flow.So it is imperative in my thinking to install carefully in such a way that it cannot be collapsed, but installers seem to have the attitude that the reason for using it is to make their jobs easy and fast, forget about long term effectiveness. 

         

        Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

        1. mwgaines | Jun 27, 2007 08:47pm | #19

          "..but installers seem to have the attitude that the reason for using it is to make their jobs easy and fast, forget about long term effectiveness."

          The difference between profit and professionalism. It seems to be a disease that's plaguing just about every industry in the country these days.New knowledge is priceless. 

          Used knowledge is even more valuable.

  2. User avater
    CapnMac | Jun 26, 2007 06:38pm | #2

    All of the mechanical engineers I know fairly insist on limiting the amount of flex duct used, always prefering smooth-walled ductwork instead.  One I know tries to limit flex runs to under 36" in length, too.

    Now, it occurs to me you may be asking a different question than the way it read.  Are you, in fact, asking about using the high pressure (small diameter) supply lines versus sheetmetal ducting, perhaps?

    Occupational hazard of my occupation not being around (sorry Bubba)
    1. edwardh1 | Jun 26, 2007 06:48pm | #3

      Flex duct is widely used in our area - south carolina because there is no space left for sheetmetal.

      1. Piffin | Jun 27, 2007 06:37pm | #13

        I didn't realize that S Carolina was getting that crowded!;) 

         

        Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

  3. GHR | Jun 27, 2007 03:30am | #5

    Somewhere on the internet are pressure drop and flow diagrams.

    I find that up sizing 1 size is sufficient. And it installs so much easier in tight places.

  4. brownbagg | Jun 27, 2007 03:33am | #6

    sheet metal is noisy.

    1. Piffin | Jun 27, 2007 06:46pm | #15

      quit banging around inside of it!;) 

       

      Welcome to the Taunton University of Knowledge FHB Campus at Breaktime. where ... Excellence is its own reward!

  5. Dave45 | Jun 27, 2007 04:04am | #7

    The only advantage I can think of is that flex can be routed all over the place and sheet metal can't (at least not easily)

    That flexibility carries a penalty in reduced flow so it's a good idea to upsize the flex runs - and/or use it only when necessary.

    1. DaveRicheson | Jun 27, 2007 10:40am | #9

      Have you ever seen flex installed correctly in residential building?

      To be installed correctly it should be stretched tight and supported every few feet with a 2" web strap. Runs should be limited to diffuser and/or return drops only with as short runs possible. The joints should be made with band clamps, not duct tape. Bends in the flex need to comply with the recommended radius for the duct size.

      I work commercial mostly, and seldom see much of the proper installation done  there. Following the manufactures installation instructions are not real high on the priority list when speed, production , and money are the issues. In residential, I have seen a lot more  sh*** work than I have good work in rigid duct, almost zero in good flex duct work.

      The HO and builders save money by using flex because of the "labor savings" factor, but to get adequate system performance, most HVAC  contractor just over size the units a little more. Not much net savings in total cost and it goes negative when you factor in long term energy use.

      IMO a poorly installed rigid duct system is still better than 95% of the flex duct systems I have seen in residential construction. Ya, have to beat a rigid duct pretty hard to collapse it, but flex can be smashed by any bufuss arse  working around it or installing it :)

       

      Dave

      1. tuolumne | Jun 27, 2007 03:34pm | #10

        My folks had central AC installed sometime in the late 80's with a foam and foil based rigid duct.  Are products like this still available?  It was certainly of superior insulation value than any flex duct or blanket wrapped sheetmetal I see around today.  The ends were tongue and groove and seams were taped I believe.  The only problem I see was the potential crushing damage during installation.  Has anyone used a similar product recently?  I would be curious to know the cost, pros and cons for our new home construction.

        1. DaveRicheson | Jun 27, 2007 07:15pm | #17

          http://www.specjm.com/airhandling.php?category_id=6

          Duct board is still used. Fairly esay to DIY a project with it if you follow directions supplied with the board.

           

          Dave

      2. Dave45 | Jun 27, 2007 04:01pm | #11

        Dave -

        Do you mean that tossing a coil of flex under the house or in the attic and connecting the ends isn't a proper installation?  Gee, who would have thunk?? - lol

        My first shop dust collection system was made up with 4" plastic flex hose and most of the "collection" was whatever settled on the outside of the hose.  (As a mechanical PE I should have known better, but the hose was inexpensive and it went in fast. - lol)

        I eventually replaced about 75% of the plastic flex hose with 4" sheet metal duct and was amazed at the improvement in performance.

        1. DaveRicheson | Jun 27, 2007 07:36pm | #18

          Many years ago I built a house for a couple I knew very well. I trusted the HVAC contractor to design and install a premium system. He used flex duct runs to all diffuser from the main sheet metal supply and return lines. It all looked good to me, in my blessed ignorance, until the first cold months after occupancy. Two of the four bedrooms were uncomfortably cold, and no amount of raising the T-stat seemed to help.

          Want to guess which side of the load bearing beam they were on?

          Hey it is "flex" right ? It'll squash from a 6" round to a 3x14" oval real easy won't it ? Ya, man, and we don't have no transition ducts on the truck anyhow. Go on Bubba, shove her through thar, and I'll pull er out tuther side.

          Lessons learned the hard way are remember the best.

          Trust and HVAC design/installs aren't mutually exclusive. However they are scare items  in my experience.

          4" flex for  dust collection system? I'm surprised it didn't get sucked into the collection bag after it collapsed on itself :)

           

          Dave

          1. Dave45 | Jun 27, 2007 08:56pm | #20

            Not the 4" flex like is used in dryer vent lines.  The DC stuff is fairly stiff and corregated - like drain line that bends.

      3. MtnBoy | Jun 27, 2007 05:12pm | #12

        Would you mind describing what a quality sheet metal installation would consist of in residential?For my own home I want sheet metal for the central HVAC system. Tied into that system is a whole-house HEPA air filtration unit and an HRV. Furnace is variable speed motor, natural gas fired. The fan stays on all the time to better power the air flow for the HRV and filtration units (if they were stand-alone, they'd both have smaller ductwork).It's the setup I have now and it works fine. There is some flexible duct near the registers, to reduce vibrational noise I guess.

        1. User avater
          CapnMac | Jun 27, 2007 07:06pm | #16

          whole-house HEPA air filtration

          Well, that suggests that the ductwork ought to be sealed to that level, too.  Which is going to likely be brush-on sealer, plus tape over that. 

          Otherwise, it can be a tad inapt to have sub-micron filtering on ducts with millimeter gaps in the joints (or, my personal least-liked practice, only taping the insulation blankets <grrr>).Occupational hazard of my occupation not being around (sorry Bubba)

        2. jtee | Jun 28, 2007 02:41am | #22

          bj,Get a copy of ACCA Manual D (just google it); Every thing you need to know about duct systems. Also, it will save Dave R. a lot of typing :-).

          1. DaveRicheson | Jun 28, 2007 01:08pm | #25

            Thanks.

            I am far from an expert on duct. I have installed a lot of it for commercial  HVAC systems we have added in our power plants. We generally have everything sized and designed by one of our mechanical engineers or suppliers so I don't have to wrap my brain around all the calculations. I have done some shop drawings for the sheet metal shop to use for really simple installs that we self design, but wouldn't even consider doing it for anyone else.

            When I installed my shop HVAC I opted to go with  26 ga. metal rather than the lighter 28 ga. used in most residential systems. It starts of quite than the lighter gauge, plus it is easier to work with.

            One of the biggies that I see in residential installs is the lack of sealing of any of the joints. Another is poor or to little insulation on systems installed outside the heating cooling spaces. Drives me nuts when I hear the rational  for such shoddy work from a licensed professional.

             

            Dave

          2. jtee | Jun 28, 2007 09:01pm | #29

            Dave,Whether or not you design a duct system, you know what a good installation looks like, and that's really where the rubber meets the road. A perfectly designed system will perform miserably if it's poorly installed, and the sad fact is that far to many installers are just incompetent. Unfortunately, the only effective recourse the customer has is to educate himself and demand performance testing.

          3. IdahoDon | Jun 29, 2007 04:40am | #32

            One of the biggies that I see in residential installs is the lack of sealing of any of the joints.

            We see that a bunch with the lower 2/3's of hvac installers.  For something that's so easy to do, it's amazing that so many screw it up. 

            Beer was created so carpenters wouldn't rule the world.

          4. MtnBoy | Jun 28, 2007 06:07pm | #26

            Thanks, will do. Any "best practices" ideas beyond what's required?

          5. jtee | Jun 29, 2007 01:45am | #30

            bj,mrsludge (interesting nickname :-) ) raises several good points. An excellent resource is Home Energy Magazine. There's lots of good info in their archive section which is on-line for free, in particular, see issue September/October 1993:
            http://www.homeenergy.org/archive/hem.dis.anl.gov/eehem/93/9309contents.htmlSeveral years ago, when most of the HVAC industry still though duct tape was wonderful stuff, they did well designed test on various duct sealing methods, and proved just how bad duct tape was. Metal foil taped performed pretty well, but mastic is the best. BTW, don't just use your favorite caulk, use real duct sealing mastic (for which several ASTM & UL standards have been established). RCD is one brand that is quite well respected, there are many others these days. Just look on the label for some words about what standards are met.At this point, I think I need to point out that, as important as duct sealing is, combustion safety is far more important. Doing anything that alters the relative pressures in a house (this includes duct sealing) has the potential for causing serious, even deadly problems with combustion appliances, especially naturally vented gas water heaters. A combustion appliance zone safety test is a must, unfortunately, it requires some pricey equipment.
            The Affordable Comfort web site has an on-line copy of the slides used for one of their seminars which are useful to look at, even if you don't get the lecture that went with them:
            http://www.affordablecomfort.org/images/Events/23/Courses/697/DUR_3_CoxCombustion_Safety_Do_No_Harm.pdf

        3. mrsludge | Jun 28, 2007 06:57pm | #27

          bj- if you post on THS at all, I think I responded to some of your system questions a while back (I'm 'thull' over there).

          The best way to tell whether you have a quality duct installation (flex or sheet) is to get a duct blaster test done.  Southface can do this or point you to someone who can.  A tight system should leak at around 0.05 cfm/ft^2 (i.e. 5% based on the square footage of the house). Ideally, I'd want to make clear to your contractor that this is going to be done and that they're responsible for addressing any performance deficiencies. It needs to be contractual, b/c I think the codes in GA aren't going to protect you at all (based on content and lack of enforcement).

          To do this, the duct joints are going to have to be well sealed- all joints mechanically fastened, followed by mastic and/or tape.  I'm not totally clear on what some of the pros do combining foil tape and mastic.  I'm not a pro, and my observation is that the UL foil tape alone may not hold after being subjected to a lot of hot-cold cycles (1 yr in our case). So it seems that putting mastic over foil wouldn't work great if the foil turns loose.

          I ended up having to go back and fix our ductwork after it failed the duct blaster test miserably due to hack HVAC subcontractor (working for hack GC that ended up in a lawsuit).  I DIY'd this mainly b/c we were out of money otherwise and I didn't want to pay to heat/cool the attic.

          I'm a huge fan of Hardcast 1402 butyl mastic foil tape. It's expensive at $28/100', but it's tenaciously sticky, even where I was brushing off accumulated dust to close off the insulation jacket I'd cut to work on fittings.  The butyl backing is the same type of stuff that's widely used for flashing windows/doors/openings these days.

          Some detailing I noticed that I had to address:

          -Sealing duct boots to ceiling; you can argue if these really leak under normal operation, but they will during a duct blaster test, which covers registers with sticky film before pressurizing the ductwork. I used caulk where I could (new drywall) and expanding foam elsewhere; ideally, they might have gaskets on the ceiling flange. The boots themselves need either mastic inside or tape on the outside of their joints.

          -Sealing misc openings at air handler; there are a few test ports and switches that will leak at the unit; I just used regular foil tape for these so it could be removed easily if needed.

          -Sealing between the air handler, filter rack, and plenums. It's just a matter of attention to detail to get these boxes all sealed to one another in addition to mechanical connections (screws)

          -Attention to detail on the sheet metal duct- every longitudinal seam and every connection should be sealed. Our hack was less concerned on the return air side and where they were obviously rushing at the end of the job.  On fittings, the adjustable miters should be sealed in addition to the end connections.

          -Flex duct connections; despite specs to the contrary, our hack put in a lot more flex than we said was OK.  Where pieces of flex join together, the regular foil tape seems to have done a lousy job of holding the connections.

          Here's a document on the various tests (blower door and duct blaster):

          http://www.southface.org/web/resources&services/publications/factsheets/22blowdoor.pdf

          1. MtnBoy | Jun 28, 2007 07:08pm | #28

            Yes, thull. Whatever you posted is in my ever-growing files. I always thought that mastic was the best sealant, so I'm likewise surprised to see mention of using it in conjunction with foil tape. I see what you mean about the failure of the tape. I love that aluminum tape, though; it adheres real well.Part of our build includes a duct blaster test; has to meet Amer. Lung Assn's Health House criteria. So I'll verify your numbers and Southfaces's against ALA's.Thanks, once more.

  6. WayneL5 | Jun 27, 2007 06:51am | #8

    Flex duct won't last long, probably 20 years or so.  Leaks like crazy as it gets jostled around during installation.

  7. IdahoDon | Jun 27, 2007 10:54pm | #21

    Properly installed flex results in a quieter and less expensive install for the same performance level.

    Metal duct is used to maximize flow through tight locations and for large volumes in strange sizes such as when maximizing headroom with an overhead duct.

    Duct, flex or otherwise is sized for the flow required so I don't see a disadvantage to the increased size if it fits a location since it's still going to be cheaper than ridgid duct.

    Many will poo poo flex duct, especially 4" as used in bath vents, but I talked our HVAC guys into a run from a basement clear up to a 2nd floor attic, nearly 45' to the roof.  They claimed it wouldn't pull anything, but I simply asked them to humor me.  No, the 100 cfm fantec wouldn't pull 100 cfm's through 45' of flex, but it pulled at least 65% of the others with probably six 90 degree bends, which is plenty for the application when used on a timer.

    Best of luck

     

    Beer was created so carpenters wouldn't rule the world.

    1. davidmeiland | Jun 28, 2007 07:09am | #23

      The AHJ here will allow 4" insulated flex to about 10 feet for bath fans. Longer than that and he wants to see 5", and then not longer than 25 feet.

      1. IdahoDon | Jun 28, 2007 07:19am | #24

        Our mechanical inspector doesn't care what we do with fans that are considered optional.  If it's not an optional item then we have to follow a path that gives a pretty close guestimate of the true cfm output and exchanges per hour.

        It's funny how some get fixated on duct size and pay no attention to the fan attached to the duct. 

        Beer was created so carpenters wouldn't rule the world.

  8. Notchman | Jun 29, 2007 03:49am | #31

    There's been a lot of good info shoved your way, but one thing hasn't been mentioned about flexible ducting.

    I've worked on several older rural homes with retrofitted central heat and those with flexible duct were great habitat for mice, rats and packrats and, in one case, fox squirrels.

    I don't do HVAC but have a good sub who I call to correct these kind of situations.

    But my point is that rodents have an amazing ability to gain entrance to a lot of homes and cabins new and old and if they come across an assessable run of flex ducting, they'll move in immediately and create all kinds of problems.

    IMO, flex ducting should go the way of pre-1970 aluminum house trailers.

     

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Efficient HVAC for a New Build

Self-installing an HVAC system requires a lot of thought and planning.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Podcast Episode 686: Brick Steps, Ground-Source Heat Pumps, and Greenhouses in Nova Scotia
  • FHB Podcast Segment: Efficient HVAC for a New Build
  • Affordable Scans, Accurate Plans
  • FHB Summit 2025 — Design, Build, Business

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data