Floating screws on GFCI…WHY?

Cooper | Posted in General Discussion on November 6, 2005 09:44am

I’m sure this has been asked before, but why are the screws on a GFCI “floating” instead of solidly in place like a regular outlet.  Their so annoying to wire, especially hot.  Anyone know why their built that way?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. MisterT | Nov 06, 2005 01:50pm | #1

    you are not spossed ta wrap the wires around the screw!!!

    there are internal clamps

    strip the wire and poke it in the hole and tighten.

    RTFI!!!

     

    Mr. T.  MOTOL

    "They keep talking about drafting a constitution for Iraq. Why don't we just give them ours? It was written by a lot of really smart guys, it's worked for over 200 years, and we're not using it anymore."
    -- George Carlin

    "I think natural selection must have greatly rewarded the ability to reassure oneself in a crisis with complete bull$hit."

    I'm Swiss!

     

    1. Cooper | Nov 07, 2005 04:08am | #4

      Every contractor I've talked to has always said plugging into the back is not as secure as wrapping the lead around the screw and tightening.  That's not the correct way? 

      As far as doing it hot, it's only 110; it won't kill you just make you mad!

      1. User avater
        dieselpig | Nov 07, 2005 04:22am | #5

        There's a difference between push-in connectors and the ones on a good GFCI.  The ones on the GFCI also rely on a screw whereas the push-ins just rely on a little metal tab.

        Regarding.... 

        As far as doing it hot, it's only 110; it won't kill you just make you mad!

        Well that's just ignorant, lazy, or both.  Sorry, but it's the truth.

         

        1. Cooper | Nov 07, 2005 05:23am | #8

          You turn off the power everytime you wire an outlet?  I can understand doing it if you're going to install a sensitive, expensive dimmer, but a regular outlet, you shut off power?  I'm impressed, but I could swear most of the electrical subs I've seen scoff at turning the power off as "for rookies".  (The tile equivalent of using spacers...)

          I bet you wear a safety harness when you're over six feet in the air!

          Edited 11/6/2005 9:28 pm ET by Cooper

          Edited 11/6/2005 9:30 pm ET by Cooper

          1. User avater
            maddog3 | Nov 07, 2005 05:28am | #9

            well then , .
            ...those tough guys wouldn't work for me."

          2. User avater
            maddog3 | Nov 07, 2005 05:37am | #12

            it's an interesting science experiment though.....something that can MELT steel but not KILL you,"

          3. opie10 | Nov 07, 2005 05:45am | #13

            Only 110?

             

            220+ Volts will throw you off of the circuit (if you are lucky).  110 Volts will grab on to you and hold on....

             

            The only chance you have is if someone saw the whole thing and called 911.

          4. Cooper | Nov 07, 2005 05:51am | #15

            Maybe I've never been shocked properly, but everytime I've been zapped it's felt less painful than a pinch.  Not fun, not something I'd do on the weekends for kicks, but not particularly painful.  I'm not talking about rewiring a double aught power lead to a main service, just an outlet.  Is that so terrible?

          5. esanborn | Nov 09, 2005 04:55pm | #60

            Cooper, As I understand it, the potential for pesonal harm with 110V current is dependant upon two factors: (1) The path the current takes through your body; and (2) The conductivity of the surface(s) you are in contact with. The human body, with a high concentration of salts and electrolites, is a good conductor of electrical current. In fact, that's how much of our neural system works.  If you are in contact with wet or high-conductivty materials, which have a path to ground, you will surely be seriously injured or killed if you short to ground.

            I've had several run-ins with 100-220V current, usually due to expediant field work and or carelessness. Not somthing I would trivialize, even if a few were mere bites.

            I 've worked with a number of electrical contractors and linesmen. I know many of them to be hard-working, profit-minded individuals. Not one of them would consider working hot execept on a most unusual case.

            I think that you'll find the deziens of this message board to be, for the most part, capitalists (even the democrats :o )who are very mindful of profit margins. Being a capitalist doesn't dictate short-sighted risk-taking.

          6. User avater
            maddog3 | Nov 07, 2005 05:55am | #17

            worst shock I ever got ,was from 110 ....put my #### in the hospital ....... that was in 1978 ...Memorial Day weekend.
            I had managed to pull the skin off from both hands and when I came to, the paras were there with the paddles to resuscitate meBTW , Welcome to Breaktime"

          7. Cooper | Nov 07, 2005 05:58am | #18

            Really?  Wow. I can understand that, but really?  I've NEVER, EVER, seen anything like that.  I'm sorry that you were hurt, and I understand that you don't want that to happen to anyone else. 

            My girlfriend has been criticizing me for arguing my point, and thinks I'm wrong; that's why she say's I have no friends on this forum.  So I am wrong, and I will never do it again.

            Edited 11/6/2005 10:00 pm ET by Cooper

          8. User avater
            maddog3 | Nov 07, 2005 06:02am | #20

            no wiseguy,
            I was in changing out a damaged panel in a machine shop.like you care"

          9. Cooper | Nov 07, 2005 06:11am | #22

            I honestly am not making fun of you almost dying.  I can be an a$$ but not when someone almost gets killed.  I am sorry that you got hurt. 

            I do wire in new breakers "hot" because there's normally not an easy way to pull power (unless you pull the meter).  I stand on rubber and am diligent about it.

            I was NOT making fun of your accident.  I am sorry that you got hurt.

            I would not change out a panel hot...that would be scary....

            Edited 11/6/2005 10:12 pm ET by Cooper

          10. bosn | Nov 07, 2005 07:54am | #32

            There are sooo many factors involved with whether or not you die when you put yourself into an electrical circuit that it is tough to explain thoroughly, but here is a little more info...

            It only takes milliamps to pass through your heart and interrupt it. If you grab one hot wire and can guarantee that you are not touching anything else,  you are safe.  The circuit isn't "closed" or complete. But if you are touching something that is completing the circuit, like a fridge, a metal door frame, a pipe, your metal watch or ring that is touching something.....

            I've heard that rubber roofing isn't a reliable insulator, because some of it has some kind of metal in it.  (???)

            It only takes about fifty volts to push a few milliamps through your body, but the conditions have to be right.  Ever take a nine volt battery and touch it to your tongue?  You can feel it there, but the nine volts won't push that same current through your whole body because there is to much resistance. 

            In most cases, 110V will easily push enough current to kill you.  But just stopping your heart is not the only thing to worry about.  Electricity flowing through you will also cause internal burns that will harm your organs, sometimes permanently.  So if you survive the initial contact, you may not be out of danger.

            One obvious factor is the path that the current takes through you.  It will take the path of least resistance.  Your finger to your elbow on the same arm won't pass through your heart, one hand to the other will.

             

            Hope this helps.There are no electrons!  It is all made up.  Don't believe it.

            Electricity is made by GREENIES.

          11. Cooper | Nov 07, 2005 08:03am | #34

            Thanks for the technical info.  To your knowledge, do they make a device that can trip ordinary outlets?  Similar to the trip button on a GFCI tester?  That would simplify the task greatly...it makes for a great new tool.

            Thanks again for the info...

          12. highfigh | Nov 07, 2005 11:21am | #35

            The 9 volt battery stings the tongue because the current doesn't need to flow very far. Having said that, the current from a car battery can and will flow through a human body. Years ago, I worked with automotive 12 volt systems and was sitting on the door sill of a car on a hot, nasty, sticky humid day. I was wearing shorts and was in contact with bare metal. It was pretty interesting to feel my leg tingle every time I grabbed a wire that was hot while I hooked up the device.
            "I cut this piece four times and it's still too short."

          13. User avater
            RichBeckman | Nov 10, 2005 06:39am | #69

            "that's why she say's I have no friends on this forum."I suspect 38 posts in 26 months might have more to do with it.And not coming to Fests!Rich BeckmanAnother day, another tool.

          14. MSA1 | Nov 07, 2005 05:35am | #11

            On top of the safety factors would'nt you just feel like a tool to catch a shock in front of the customer. if someone were doing electrical in my house and got a shock it would'nt instill alot of confidence.

            BTW what do you use to keep the gaps uniform on wall tile since its rookie to use spacers? Or do you just make rookies do all the wall tile?

          15. Cooper | Nov 07, 2005 05:49am | #14

            Can't anyone just take a joke?  I swear my crew and I have a good time busting each other's balls.  When I get on this site, I feel like there's a bunch BWC reps pushing some crazy agenda.  Don't get me wrong, I'm all for safety (i.e. protective eye wear, gloves, hearing protection.), but maybe all of you "haters" have all "made it" and forgotten your roots---busting #### and meeting deadlines.  I realize that most of you guys have been doing this for decades, and now are making the big money in the nice parts of town (and I appreciate that you've earned it), but doing everything with a hepa filter and a safety harness, and all the OSHA trimmings, isn't easy to conform with in the lesser markets.....so please lighten up!  (I CANNOT believe that ALL of you guys turn off the power to change an outlet! I can understand if you've got to do several, or if there's a million wires, or if you've got to pull out a metal box and add another gang, but give me a break.  This is the real world, right?)

            Concerning spacers for wall tile:  that's sort of unavoidable, but the master tile setters I now often use pieces of cardboard ripped off the box.  Whenever I've offered to buy spacers, they've laughed their a$$ off....

          16. opie10 | Nov 07, 2005 06:02am | #19

            it is funny... but...

             

            someone sees something like that on here and trys it out... ouch...

          17. Cooper | Nov 07, 2005 06:08am | #21

            BTW, since I am a little ignorant about electric, answer me this: can't you hold the power lead and not get shocked, as long as you're not grounded?  In other words, as long as you don't touch any conductor, aren't you safe? 

          18. opie10 | Nov 07, 2005 06:15am | #25

            that is how you get lucky.

             

            If you feel the buzz... you got a dead-end shock.  The current tried to pass through your body, but couldn't find an exit path  (what I believe the other fellow was referring to as making you mad).  Thank the Lord you were wearing something other than your sweaty socks or grabbed the grounded box.

             

            If it got a good path, it sure won't let go... And man would that hurt!

          19. User avater
            rjw | Nov 09, 2005 12:21pm | #55

            >>BTW, since I am a little ignorant about electric, answer me this: can't you hold the power lead and not get shocked, as long as you're not grounded? In other words, as long as you don't touch any conductor, aren't you safe? PotentialIn asking the question, you make it clear why you've taken the position you've taken.

            View Image

            Sojourners: Christians for Justice and Peace

          20. highfigh | Nov 10, 2005 03:23am | #67

            You can touch a hot lead and not be shocked, as long as you aren't touching the neutral or ground. Or something grounded. Something else to remember, if there are 2 circuits in the same box, the second one is supposed to be from the other phase, which means that if you touch both at the same time, you just got nailed by 220V, not 110V. If you're going to touch a hot lead and ground or neutral, do it with one hand, not one in each. If you do it with one hand, you get zapped. If you touch hot with one hand and neutral or ground with the other, you can die.
            "I cut this piece four times and it's still too short."

          21. MSA1 | Nov 07, 2005 06:13am | #24

            I dont mean to bust any balls. Believe me I havent made it yet. I think i'm getting there but not yet. Yes, I promise, I always shut off the circuit. I have been behind w/ a dead line staring at me and the helper playing hooky, but I will still take the time to kill the circuit.

            I figured the spacer thing was a little tongue and cheek, but I couldnt resist.

          22. Cooper | Nov 07, 2005 06:16am | #26

            Thank you for seeing the lighter side....the comment about tile was funny, too...

          23. User avater
            CapnMac | Nov 07, 2005 11:10pm | #42

            CANNOT believe that ALL of you guys turn off the power to change an outlet!

            That's precisely the attitude that cut off a good source of income for me (being old, but not having "made it").  Texas changed the rules Sep 04, must have a journeyman's license (and/or have one present) for any 110 work.  Means I can't install X-10, dimmers, lighting scene controlers, any of that at all unless I sub it out.  I can't swap or install ceiling fans, either.

            Instead, a DIY homeowner can.  It's still legal to risk/hazard your own house, but you can't hire any experience unless they are licensed electrians (with a lot more overhead & trip charges & whatnot to cover, making for much more expensive house calls).

            I always turn the power off.  No mater if outles, switch, or fixture.  Double check that the box is quiet with a buzzer, too (been surprised a time or two--that "bug" paid for itself several times).

            I use spacers on wall tile, too--but that may be because the fashion in these parts is for whopping big, heavy, wall tile . . . Occupational hazard of my occupation not being around (sorry Bubba)

          24. Cooper | Nov 09, 2005 07:53am | #44

            Texas didn't allow any "grandfather clause" before they changed the rule?

          25. User avater
            CapnMac | Nov 09, 2005 08:04pm | #61

            Texas didn't allow any "grandfather clause" before they changed the rule?

            Nope.  It's a licensing change, so they don't have to.  Work was ok one day, illegal the next.  I know a surprising number of remo/handy people who are still unaware of the change, 13 months later.

            Any house other than my own, I can contract the work out, I just can't perform it.  (Can't have the JM just "on site," either, the work has to be performed "under supervision.")Occupational hazard of my occupation not being around (sorry Bubba)

          26. User avater
            dieselpig | Nov 07, 2005 07:17am | #30

            KMA.

            You know nothing about me except that I said something you didn't like.  I've been in business for 3 years and am far from having 'made it'.  Flipping a breaker takes all of 30 seconds.  You wanna be a cowboy, be a cowboy.  I couldn't care less.  But it's 'tough guys' like you that pass on bad habits to new jacks by treating 'em like they're babies or something for looking out for their own well being.  I've also noticed that the guys around jobsites that talk the biggest game are also the biggest pansies when the rubber hits the road.

            I bet you wear a safety harness when you're over six feet in the air!

            I don't, but if I did... what would that make me other than a smart business man? 

            Ever here of the Darwin awards? 

          27. Cooper | Nov 07, 2005 07:55am | #33

            You need to learn to chill and not be so critical of others, especially when you're showing your hypocrisy.  You kid me about turning off a breaker, and then proceed to inform me that you frame houses without proper safety equipment?  What's more dangerous: changing out an outlet hot, or walking on a three and a half inch wall plate twenty feet in the air in boots? (And I'm sure it's no picnic in Boston right now).  I love it when someone, like you, chimes in with your safety tips and criticism, and then doesn't even have the integrity to set a good example.  Your crews must laugh behind your back...

          28. User avater
            dieselpig | Nov 07, 2005 02:34pm | #37

            You are absolutely clueless dude. 

            Later.

          29. Cooper | Nov 09, 2005 08:09am | #47

            Uma maldição em você...

          30. User avater
            Luka | Nov 10, 2005 01:58am | #64

            >>>> Uma maldição em você...A curse in you ???Isso é coxo.
            "And, in my humble view, neither Democratic nor Republican party politics has anything to do with lib or con anymore. It's now just pandering to the visceral hatred that's been bred amongst those who refuse to waste their time and energy performing one of the singular most difficult tasks known to man: thinking." -SHG

          31. User avater
            maddog3 | Nov 10, 2005 03:17am | #65

            ........yup"

          32. firedude | Nov 10, 2005 03:18am | #66

            been there, done that, no more - breaker's off or power's off or I don't touch itone big time rule on my job is don't touch wires - chief's aid usually cuts power as soon as possible and the electric co cuts the power at the pole - electricity can "travel" both ways aka backfeed so unless the power's cut, any wires are considered live

            job security - my job, not yours

          33. User avater
            rjw | Nov 09, 2005 12:17pm | #54

            >>most of the electrical subs I've seen scoff at turning the power off as "for rookies". There are bold electricians.There are old electricians.There are no old, bold electricians.

            View Image

            Sojourners: Christians for Justice and Peace

      2. User avater
        maddog3 | Nov 07, 2005 04:33am | #6

        ........As far as doing it hot, it's only 110; it won't kill you just make you mad!you have GOT to be kidding.
        I hope you have your headstone picked out"

      3. MSA1 | Nov 07, 2005 04:35am | #7

        You're confusing spec (good) with stab in (junk). GFI's are the spec type. You insert the wire in the back but it relies on the screw to hold it in.

        The contractors you've talked to are correct, the stab ins are junk.

        BTW wiring devices hot (things like electronic dimmers) not only puts you at risk but you risk burning out the device. Take my word for it. I was working on a circuit that I was sure I turne off. I got a spark and blew out a $70 dollar dimmer. You're right it didnt kill me but the extra $70 did make me mad.

        Edited 11/6/2005 8:39 pm ET by MSA1

        Edited 11/6/2005 8:40 pm ET by MSA1

        1. shod | Nov 09, 2005 08:46pm | #62

          MSA1- If you're concerned over the maximum contact surface of the wire to the terminal on a spec pushin clamp as opposed to taking the time to wrap the wire around the screw to 4 o'clock,

          the wire can be curved to close 90degrees before working it into it's pushin location and tightening the clamp by turning the screw.

          Thus increasing the contact surface of the wire to the terminal area by the added length of the curved portion of wire now entering the opposite side of the entry location past the shank of the clamping screw. 

          If you want to get compulsive about it you can even go more than 90 degrees, but can't see the benefit for the addition PITA labor involved.

      4. User avater
        SamT | Nov 07, 2005 05:31am | #10

        it's only 110; it won't kill you just make you mad!

         

        ROTFLMFAO!!!

        Hey, Cooper, What's yer favorite flower?

         

         

         

        Still laughing.

         

         

         

        Ok, so it's a snicker. WhakinIsay?

        SamT

        1. Cooper | Nov 07, 2005 05:54am | #16

          Sam,

          Thanks for seeing the lighter side of an innocent comment.  You make one apparently dangerous OSHA violation COMMENT and there's a feeding frenzy from the Breaktime Remodeling National Socialist Party...

          Edited 11/6/2005 9:57 pm ET by Cooper

          1. User avater
            SamT | Nov 07, 2005 03:13pm | #38

            Cooper,

            T'wern't laughin' at the "dangerous OSHA violation COMMENT." I was humored by the implications of ignorance in the "apparently" part of yer statement.

            I will admit that I was laughing "at you" in my first post. Hopefully to shame you into NOT believing that 110 can't kill.

            However, since reading your replies to the other guys here, it is clear that you have been well taught by a bunch of well meaning old ignoramouses who were just carrying on a tradition of teaching what they were taught.

            Believe me.

            I have 4 years of 40 hour weeks of electrical/electronics school background from the USNavy. I taught the subject for 1 year. I have worked live with everything from 5VDC-60 Amp to 23KV-13KW. I built my first radio from scratch when I was 14yo. I have worked on multimegawatt plants.

            110vac kills more people than all other voltages combined.

            Let me repeat that for emphasis.

            110vac kills more people than all other voltages combined.

            Not because it is the most dangerous, but because of well meaning old ignoramouses who were just carrying on a tradition of teaching what they were taught and that was the wrong thing.

            Yes, I have been zapped by 110. And 1200. And almost by that 23KV-13KW, but that was no accident and is another story.

            Now-a-days I refuse absolutely to work live on anything over 110 and whenever at all possible on 110 itself. My life is worth an extra hours time, expecially when someone else is paying me to take that time. Safety is really cheap compared to the cost of the paperwork ya gotta fill out if ya die.

            If I absolutely must work on 110- live, I first:

            be very, very careful in all steps

            Make sure only one wire at a time is hot

            test to be sure I know which wire is hot

            insulate the surface I'm standing on

            wear insulative shoes

            remove jewlry and other metal from my person

            look carefully for ground paths

            use, inspecting each time, insulated tools

            insulate my off hand

            make sure the arm handling the hot wire is grounded

            push the ground wire out of the way

            cap the return wire

            did I mention be very, very careful and deliberate, and think out each movement before you even twitch

            connect the hot wire

            insulate the hot connection

            finish other connections

            Wipe the sweat off and give thanks that I still can

            Usually quicker to just turn off the stupid breaker and get the drop cord for lighting, which is the only excuse to ever work live. Opening the breaker kills the lights.

            SamT

          2. User avater
            johnnyd | Nov 07, 2005 05:20pm | #39

            FWIW...good point about working the circuit live because it also feeds the light.

            Get one of those headband things with a little light, $10 at walmart.  Work in the dark with both hands free.  Throw out just enough light to wire. Use AA batteries that seem to last forever.  Put it in your "electrical" tool box along with the Klien pliers, testers, etc.

          3. Cooper | Nov 09, 2005 07:50am | #43

            Thanks for taking the time to explain the seriousness of working with 110.  I have never had the guts to work on anything larger live, except adding circuits to a live box.  I have never seen anyone get anything but a zap from 110 (thankfully), and do not want to watch any of my guys (all three) get killed (or ruin my BWC group rating!).

            Is there a tool that will trip a breaker from the outlet, sort of like a GFCI tester?

          4. Cooper | Nov 09, 2005 08:02am | #46

            I must say from the slamming I took on this post that I'm the only contractor in the world that ever changes out outlets hot!  I must have been lucky since I don't wear jewelry, don't sweat much, have insulated tools, use the tester to verify which hot line (if they're are multiple in the box) is hot, and work with care and diligence.  My intention was not to come across "Mr. Macho Sparky", but just to point out that my experience in the field has been that most contractors I know, change out the single outlets hot.  I love this forum for it's information and the contractors who add their experience with wit and humor; I don't like the pompous, holier-than-thou, know-it-alls, that like to eviscerate a comment made in jest....you know who you are...

          5. User avater
            Heck | Nov 09, 2005 08:15am | #49

            Coop, one of the real concerns is that there is an unseen, unheard horde of readers of this forum, with levels of experience from pro to not knowing one end of a screwdriver from another.

            The fear is that someone with absolutely no other knowledge than what they may have gathered from an isolated thread  might attempt to work on a live outlet, because someone here forcefully argued that it was safe  for them.

            The same for other tasks that many of us have taken years to make look easy. While at one time I considered the risks of walking glu-lam ridges 30' up acceptable, I would never state that it was a safe practice.

            Carry on.The heck, you say?

          6. bosn | Nov 09, 2005 08:11am | #48

            There is not such a tool, and it would be a bad idea to short a breaker out on purpose to find it or shut it off.  One reason would be because of the danger when the short occurs: the arc flash and the molten metal flying around.  Another reason is that it is not good for the breakers,  it causes them to prematurely wear out.  Granted, you would have to do it a lot to cause a noticeable failure in most cases, but it is not good for the equipment.

            There is a good circuit tracer made by Ideal that I use frequently to find the breaker if the panel isn't marked.  You plug one part into the circuit and the other you take to the panel and it indicates with lights and sounds which breaker is the one you want to shut off.  It is not fool proof, especially on very old systems or buildings with a lot of electrical interference, but I've found it to be very reliable.  If you need to find the breaker for a switch you can plug it into an adapter that you screw into a light socket.

            It wouldn't hurt to pick up a couple of breaker lockout devices.  They are cheap and the will save you from that one dolt on the job who likes to flip breakers.  He always seams to show up and turn on the one you are working on when you have a hold of the hot wire.  Lock it out and no one can turn it on until you are done.There are no electrons!  It is all made up.  Don't believe it.

            Electricity is made by GREENIES.

          7. User avater
            BillHartmann | Nov 09, 2005 08:24am | #51

            "There is not such a tool, and it would be a bad idea to short a breaker out on purpose to find it or shut it off. "There is. CAP has a breaker test that puts on a calibrated load and monitors when the breaker test.However, it is fairly expensive and the special contactor needs to be replaced after so many tests.BTW, I have not had much luck with using the circuit tracer to find the right breaker. In fact in a house with multiple panels it will often indicate on more than one panel.However, I have found that it is fool proof if you can get the receiver sensitivity set to beep and then start flipping breakers until it stops.

          8. cap | Nov 09, 2005 09:37am | #52

            Bill,

            Hey, you've got a good memory!

            The website for the breaker tester (that trips a 15 or 20 amp branch circuit breaker, safely) is

            http://www.koinstruments.com/

            It's a very useful tool; I use it to test older breakers in residential occupancies.  In commercial and industrial settings, I use it to trip the breaker so I can work on the circuit.  It's easier to trip a breaker and then find it in a panel than to use even a good breaker sniffer.  Of course, I advise the client that a circuit is going to be shut down, so they need to batten down the hatches (as in, make sure equipment in that part of the building can lose power without creating a serious problem.)

            The tester is not cheap, but I can work a lot faster and safer using it.

            As far as Cooper's original post, he must be more careful than I am.  Once upon a time, I occasionally worked 120 branch circuits hot.  Too inconvenient to I.D. the breaker.  As careful as I might be, I'd get bit occasionally.  Finally I decided it wasn't worth it.  Now I just cut the power.  Although they may be inconvenienced, almost all my clients actually feel more comfortable knowing that I'm not working on a live circuit. 

            Of course, you've got to do some testing on energized circuits.  That's different than changing out a receptacle. 

            I figured that Cooper will have to learn his own lesson, and hopefully it won't be a lethal one.

            There are rare occasions when I work a circuit hot, and then I use 1000V insulated tools and 500V gloves, flame-resistant clothing, etc.  What a PITA.

            Cliff

          9. Rich | Nov 09, 2005 10:44am | #53

            I've watched a number of seasoned electricians while doing work at my house or the building I work at.  When working on something such as changing an 120v outlet, they will always work on it hot if finding the breaker is any sort of inconvenience.  Even when I volunteer to go find the breaker for them, they assure me that they work on stuff hot all the time.  Then they go at it with their insulated tools and bare hands.  I would never suggest that a DIYer like myself work this way (I'll spend all day looking for a breaker if I have to.) but the pros I have talked to suggest that this is common for electricians at their skill level.  One old timer even told me about the old timers that he learned from.  Said they used to test a wire by grounding it with two fingers on the same hand.

            I would also add that very few electricians take the time to go back and label a breaker when they make changes.  After spending hours doing a good safe job, why won't they take a minute to label their work to make it easier for the next guy trying to work safe.

          10. DaveRicheson | Nov 09, 2005 02:22pm | #56

            There are rare occasions when I work a circuit hot, and then I use 1000V insulated tools and 500V gloves, flame-resistant clothing, etc.  What a PITA

            Our company safety rules require us to wear PPE when working on anything at or above 240v. That means safety glasses, low voltage gloves, and a nomex flash jacket. We already wear 100% cotton uniforms, so we are pretty much protected from melt burns caused by synthetic clothing.

            That means every time we pull the cover off a panel we have to "dress for the occasion". Open up a 3000 amp switch gear and we add a face shield and hard hat to the costume.

            The whole routine is a royal PITA, but since the policy was established in 1996, we haven't had any hot contact injuries. We did have one broken hand from a fuse blow out in a motor control center, and that incident could had been worse if the electrician had been standing in front of the switch (we stand to one side when energizing a switch).

            We go way beyond what OSHA and most electrician consider safe practices. Not surprising the, that we have the best safety record for a utility company in the country.

             

            Dave

          11. User avater
            maddog3 | Nov 09, 2005 02:37pm | #57

            Dave, I don't know if I ever posted this here, it seems appropriate......... don't you think?
            BTW, I snapped this picture in the Spring ..2001"

          12. DaveRicheson | Nov 09, 2005 04:29pm | #58

            That is a 10.0 on the pucker factor scale if I am on site.

            Got a story to go with it?

             

            Dave

          13. User avater
            maddog3 | Nov 09, 2005 04:50pm | #59

            Yes,
            the short version.....during some equipment testing.....This is a peaker BTW....an air break was closed on a 345Kv line backfeeding into the plant. through two transformers and then into this 5Kv gear.....prior to the testing, the 5Kv feeder cables from the smaller AUX transformer were disconnected in that cabinet , shoved above a barrier, and a temp feed was re-connected.I was the Start-Up GF for the electricians,
            so I was " witnessing " this latest testThe cables that had been placed above the barrier were not insulated only isolated, so when the switch was ordered closed
            ,and after being told to not worry about it, the obviously shorted cables blew up about twenty feet from where I was standing.
            That picture was not taken with a tele photo lens"

          14. bosn | Nov 09, 2005 11:01pm | #63

            Bill, Ideal has improved the circuit tracer.  The old one with the sensitivity dial was a PITA to work with.  The new one auto adjusts.  If you have all your breakers in the same area, it is easy to pass the receiver over all of them two or three times until the tester decides which one (or two or three) it likes the best.  Its a huge improvement on the old tester and the new one is now a pretty reliable tool.There are no electrons!  It is all made up.  Don't believe it.

            Electricity is made by GREENIES.

          15. User avater
            BillHartmann | Nov 09, 2005 08:20am | #50

            "Thanks for taking the time to explain the seriousness of working with 110. "Just a reminder, if you work on residential receptacles it ain't 110 volts.It is 120 volts, which is even worse.

      5. highfigh | Nov 07, 2005 06:11am | #23

        It won't kill you? BS! It's called 'high voltage' because it CAN kill. The NEC codebook definition of low voltage is "no lethal voltage present". In order to reduce the risk of death, make sure that wherever you come in contact with the voltage, it's the same area that goes to ground or the load. NEVER touch hot with one hand and the load or ground with the other side of your body. It doesn't take much to stop a heart.You think they make GFCI's to protect the electrical equipment in the house?"I cut this piece four times and it's still too short."

        Edited 11/6/2005 10:13 pm by highfigh

        1. opie10 | Nov 07, 2005 06:24am | #27

          they say, "volts that jolt, but it's the mils that kills"

          a person can take thousands of volts (as with a Vandegraf generator to make your hair stand on end) but a few mili-Amperes passed through your body can screw up your biological signals and stop your heart.

          standard electrical theory states that it is the load that determines the amount of current passing through the circuit.

          if... you are the load, it presents almost a low resistance because we are mostly water.  The current can spike, like a dead short.  The current could theoretically build until the resistance increases (all of the water is dried from your cells and your flesh is burnt). 

          I wouldn't want to think about the thousands of Amperes that would work out to being. 

           

          very, very good point about GFCI's

          Edited 11/6/2005 10:28 pm ET by opie10

          1. Cooper | Nov 07, 2005 06:29am | #28

            I've heard the horror stories about guys working on poles, and having their legs blown off...is that true?  I've always thiought that was urban legendesque remodeling tales to scare the new guys...

          2. opie10 | Nov 07, 2005 06:34am | #29

            nope... so true...

            truth is scarier than fiction

             

            think about it... what would happen if your arced a screwdriver across 110?  it would eat it for lunch (aka. plier or screwdriver welding).  Same thing happens to your body.  elctricity goes through your body and finds the least resistance exit point into the pole.  Meanwhile it has boiled off all of the water in your cells at such a rapid rate that the water (now a gas) explodes the cell structure as it expands.

             

            It litterally blows your legs off

          3. DaveRicheson | Nov 07, 2005 02:26pm | #36

            Opie10 is right about high voltage severly wounding and maiming linemen. i know several of them.

            High voltage as defined by OSHA is 600v and above. PPEs must be worn when working at or above that voltage.

            Someone also mentioned milamps being capable of stopping your heart. That is the reason you are putting in the GFCI s. They interupt the circuite when detect a difference incurrent between the hot and neutral.

            As far as you not turning off a breaker to wire in one device, that is your call, but it is not a good practice. I have worked as an electrician for a utility company for over 20 years now, and been bitten by 120v and 277v (single phase) many times. Each time it was because I violated a company safety rule, because I got lazy and was in a hurry. Being macho has nothing to do with it. Being in a hurry and thinking that you have the skills to keep from scewing the pooch does.

            Maybe 4Lorn1, CAP, or Bill Hartman will chime in here. Bill is an EE, CAP and 4Lorn1 are master electricians with tons of knowledge to share with you,...if you are willing to take it.

             

            Dave

          4. User avater
            JeffBuck | Nov 09, 2005 07:59am | #45

            buncha chicks ....

             

            Jeff    Buck Construction

             Artistry In Carpentry

                 Pittsburgh Pa

          5. User avater
            EricPaulson | Nov 10, 2005 05:11am | #68

            kinda reminds me of the j box thread don't it?It's Never Too Late To Become What You Might Have Been

             

             

             

            [email protected]

          6. User avater
            JeffBuck | Nov 11, 2005 07:47am | #70

            yeah, but that was about breaking the law ...

            this one is about good clean fun ... like zapping yerself every now and then.

             

            like I did on Tues ... a coupla times.

            Jeff    Buck Construction

             Artistry In Carpentry

                 Pittsburgh Pa

      6. bosn | Nov 07, 2005 07:32am | #31

        BS!  50 volts will kill you.There are no electrons!  It is all made up.  Don't believe it.

        Electricity is made by GREENIES.

      7. User avater
        Soultrain | Nov 07, 2005 08:26pm | #40

        As far as doing it hot, it's only 110; it won't kill you just make you mad!

        A 12V car battery can kill you under the right conditions.  There are so many variables to contend with.  Your body's resistance to current, moisture in the air, impedence of the conductor you are dealing with, ect.  You can be killed by as little as 20 mA if the current is traveling through the right part of your body.

        Under MOST environmental conditions you could get away with contact, however, you don't have control over humidity levels, and many other things that could make you a nice conductor.  It's better to show a little healthy fear than to be dead because you didn't take 2 seconds to switch off the breaker.

  2. User avater
    maddog3 | Nov 06, 2005 04:32pm | #2

    ......Their so annoying to wire, especially hot.....

    I'll bet they are, ...why is the power ON?

    "
  3. Jemcon | Nov 06, 2005 05:03pm | #3

    What Mister T said. If you buy the better outlets in supply houses not the 49c ones at HD they are the same way. Alot of people think the hole on those are pushins which there not. Pushins are only on the chaep outlets.

    And why are the hot, just kill the breaker. 

     

     

     

    Headstong, I'll take on anyone!

  4. Snipes | Nov 07, 2005 10:15pm | #41

    So you don't think a simple 110v circuit can kill you. It's a 15A circuit, and it only takes 0.07A to kill you if you 'happen' to be grounded or touch something to ground yourself. After 0.02A you won't be able to let go if you wanted to because the electrical impulse will cause your muscles to tighten their grip. Hey man, go ahead and work on it live, 'cause you're cool. I prefer to roll the dice at the casino. I think I'll be a rookie and stand back and watch you for entertainment.

    Breakers protect the wire from catching fire, GFCIs trip at 0.005A to protect you from catching fire (and dying).

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper

Listeners write in about ventilation and radon control and ask questions about tightening basement garages, ventilation solutions, and safer paint stripper.

Featured Video

Builder’s Advocate: An Interview With Viewrail

Learn more about affordable, modern floating stairs, from design to manufacturing to installation.

Related Stories

  • Design and Build a Pergola
  • Podcast Episode 689: Basement Garages, Compact ERVs, and Safer Paint Stripper
  • FHB Podcast Segment: Are Single-Room ERVs the Answer?
  • Fire-Resistant Landscaping and Home Design Details

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data