Formula or Online Calculator for BTU’s n

CloudHidden | Posted in Energy, Heating & Insulation on March 8, 2004 07:35am

Calculating loads is not particularly easy and not exacting. It’s a lot more than a simple formula. And it takes some educated guesses on the tightness of the construction, for example. 88k v 100k btu is not that big a diff. Just did one with proposals that ranged from <30 to 120!

Ask each the basis of their load calc. Some use the software/formulas and some use experience and/or rules-of-thumb.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    johnnyd | Mar 08, 2004 07:42pm | #1

    Try this:

    http://www.hydronicnetwork.net/hydronic/hea/flashpro.html

  2. User avater
    BillHartmann | Mar 08, 2004 09:03pm | #2

    Here is a pro HVAC software. You can get for home use for $49.

    http://www.hvac-calc.com/main.asp

    It is based on manual J. Ask the different HVAC contractors for a copy of their manual J calculations.

    1. fortdh | Mar 09, 2004 06:43am | #10

      Bill, is that program the same one or close, to the one at http://www.mrhvac.com/manualjshort.htm ? PaulEnergy Consultant and author of Practical Energy Cost Reduction for the Home

      1. User avater
        BillHartmann | Mar 09, 2004 05:58pm | #15

        I have not used the HVAC-calc so I don't know now close they are. But don't think that they are the same (except they both are working to manual J).

        MrHVAC has there own commerical version, http://www.mrhvac.com/products/software/elc/elc.htm

  3. csnow | Mar 08, 2004 09:07pm | #3

    Heat loss is not going to be super precise.  Has a lot to do with the construction details, particularly how airtight the final structure is.  That said, you can probably get close.

    Try this:

    http://www.slantfin.com/he/

  4. DavidThomas | Mar 08, 2004 09:41pm | #4

    "some use experience and/or rules-of-thumb"

    The rule of thumb I like is a very tight, very well-insulated house needs about 0.1 BTU/hr/sq ft/degree F.  Which I used for heat load in my own house.  To wit:  0.1 x 1700 sq ft x 110F (70 inside minus -40F outside) = 18,700 BTU/hour during worst case weather.  I actually acheived a factor of 0.07 BTU/hr/sq ft/degree F by building REALLY tight.  The sq ft are total square footage of the living space, e.g. 1000 downstairs + 700 upstairs = 1700 sq ft in my house.

    Continuing that rule of thumb: use a factor of 0.3 BTU/hr/sq ft/degree F for typical new construction.  Code-required insulation, average workmanship, decent windows, etc.  To use a lower number, you need to be using specific technologies and techniques to make for a better insulated and (more important) a tighter house.

    So a typical, new 2,000 sq ft house with a design temp of 0F would need 0.3 x 2,000 x 70 = 63,000 BTU/hour net from the furnace.

    A factor of 1.0 would be for a early 70's home - some insulation, leaky but you can't actually fly a kite inside.

    A factor of 3.0 would be used for a 100-year-old house - single pane glass, no insulation, leaky as all get-out.

    With a 30-fold range in these factors (and that is appropriate - houses do vary by that much), the naunces come in by deciding how much to bump them up or down for the particular conditions: windows, sheathing, insulation, etc.  And that is where the experience comes in.

    David Thomas   Overlooking Cook Inlet in Kenai, Alaska
    1. User avater
      johnnyd | Mar 08, 2004 10:31pm | #5

      Continuing rule of thumb:

      1600 sg ft house

      Low-E argon filled panes

      12" (settled) cellulose over ceiling rock, 24"C trusses

      ceiling recep boxes taped to poly VB

      All window and door framing-to-jamb gaps foamed and taped

      2X6/16"C (2X8 on North wall) walls with FG batts installed with care with 1/2" foil faced iso on interior, taped at seams, 1/2" drywall

      Conventional recepticle boxes sealed on back (around wires and over un-used clamp holes) with electricians putty, taped on front to foil faced iso

      North side buffered with bedrooms, laundry, mudroom on that side

      3/4s of North wall earth bermed ~ 3 ft up from sill plate

      Double entry exterior door to mudroom to kitchen

      Living areas with South exposure to MN latitude

      FG Batts and poly VB in/on 2x8 PTW crawl space and cellar foundation walls

      Would you consider these details would  get close to or below your 0.1 factor?

      Edited 3/8/2004 2:43:38 PM ET by johnnyd

      1. DavidThomas | Mar 08, 2004 10:49pm | #6

        I like the attention to the north-side details - wider wall, buffer rooms.   I like the arctic entry ("airlock") both for the reduced leakage 23.9 hours a day but also to prevent that -20F air spilling in directly from a single door opening.

        I assume you got the foam strip down between the bottom plates and the concrete.  I'd say a factor of 0.12.

        I like to allow cross-ventilation of all sun-exposed rooms and the house as a whole through modest sized windows.  And vertical "cross ventilation" as well to use the chimney effect instead of A/C in the summer.  And, of course, code-dictated egress windows in the bedrooms.  But those egress and cross-ventilation windows can overlap.  After spec'ing good quality windows to acheive the above, I'd make the rest fized-pane.

        I'd go lower is you sprayed urethane on the sheathing all over.  Could be just an inch ($.60/sq ft) and then fill the rest of the bay with FG, carefully as you say.  Then, with your attention to the electrical and lighting penetrations, you're getting towards 0.08.

        Now the biggest remaining hole is the flue pipes for the HWH and the furnace.  If those are direct-vent (and/or the same unit) and you really watch the details on the dryer vent, range hood, bath fans, etc you get down to 0.06-0.07.David Thomas   Overlooking Cook Inlet in Kenai, Alaska

        1. User avater
          johnnyd | Mar 08, 2004 11:19pm | #7

          40883.8 in reply to 40883.7 

          Sounds like I'm doing OK...

          I like to allow cross-ventilation of all sun-exposed rooms and the house as a whole through modest sized windows.  Got it.  And vertical "cross ventilation" as well to use the chimney effect instead of A/C in the summer.  And, of course, code-dictated egress windows in the bedrooms. Got em.  But those egress and cross-ventilation windows can overlap. You bet.  After spec'ing good quality windows to acheive the above, I'd make the rest fized-pane. 24 X 36 awnings on the north, 36X 48 double hungs elswhere, plus three big fixed pane double glass pictures salvaged from "Big Blue" IBM building in Rochester...figuring R 1.5 for those.  Oh, and the ceiling over the south-facing great room is gable, with 2X6 rafters..half of that roof only has R-19, the other half is vallied by additions and has the 12" cellulose.

          Now the biggest remaining hole is the flue pipes for the HWH and the furnace.  If those are direct-vent (and/or the same unit) Probably dual-fuel-rate electric boiler (3.5 cent a KWH) for RFH with DV propane fired HWH through heat exchanger as back-up through details on the dryer vent, range hood, bath fans, etc you get down to 0.06-0.07.

          I'm going to have a pro do a room-by-room heat loss analysis...need rules of thumb like this to keep him honest.

          Thanks.

          1. DavidThomas | Mar 09, 2004 03:45am | #9

            That all sounds good except maybe those double-hung windows. The modern ones do an okay job but they aren't the best sealing windows.

            If you had done the spray foam, then you get so tight, you need mechanical ventilation such as a heat recovery ventilator (HRV).

            With electric rates like that, what part of the Pacific NW are you in?David Thomas   Overlooking Cook Inlet in Kenai, Alaska

          2. User avater
            johnnyd | Mar 09, 2004 05:11pm | #12

            Actually I'm in SE Minnesota, electric utilities (coal fired for the most part) here push 3.5 - 3.7 cents a KWH, with the right to shut you down during periods of peak demand.  You have two meters, one that measures the heating/HW load at 3.X cents, the other at regular domestic rates...8.7 cents here.  They control the switch via radio.

            In order to qualify, you need to have an automatic alternate source of heat, like a propane space heater, or HWH that switches over to heat when they shut you off.  Some high mass systems qualify for the dual fuel rate, as they expect the slab to have enough risidual heat to outlast a peak period shut down.  I think baseboard resistance that's on domestic also qualifies.  That might be the cheapest up front way (and maybe long term) to go, as baseboard resistance units are cheap, and you could keep them set at minimum temps so they might not even cut in during a few hours of peak demand shut down.

            We'll also have a small wood stove for ambiance and backup heat in the living area.

            I think 3.5 cent KWH electricity is roughly equivalent to 75 cent/gallon propane....a price we haven't even been close to for awhile.

            Payback to the utility is a larger, more dependable load.  BIL is on this, says only time he gets shut down is during first cold snap as they ramp up generating.  He has all baseboard resitance on dual fuel,  and conventional propane HVAC for backup.

            Anyway, I sized the service entrance to this house to handle a heating load, to keep my options open.

          3. User avater
            CloudHidden | Mar 09, 2004 05:37pm | #13

            >Some high mass systems qualify for the dual fuel rate, as they expect the slab to have enough residual heat to outlast a peak period shut down.

            That's a wonderfully enlightened view! Glad to see it being recognized. We have similar rates off-peak, but there's no shut-down capability, just on and off peak times. Saves about 100/m.

          4. User avater
            BillHartmann | Mar 09, 2004 05:56pm | #14

            Here (just outside Kansas City) are biggest load is AC and we have seasonal rates.

            The first 600kwh is 6.93 for both winter and summer. For 8 months of non-summer the next 400 kWh is 3.74 and all above that is 3.1. Now that is if you have primary electric heat. It is about 10% higher if you don't.

            The sumemr base rate is the same, but then rates for higher usage increase rather than decrease.

          5. User avater
            johnnyd | Mar 09, 2004 07:33pm | #16

            Just talked to them about dual fuel...they require 6 - 8 inches of SAND underneath the slab, on top of the insulation, to provide a larger heat sink.

            Also came up with an idea to kill two birds with one stone:

            Install a 30K BTU/hr electric boiler (they have modulating boilers) as the primary radiant floor heat (RFH) source, and circulate its output through a heat exchanger in a propane water heater (like the Bradford-White Combi-Core). Under normal winter circumstances, the electric boiler would be consuming 3.5 cent/KWH electricity, heating the heating fluid to ~120 degrees for the radiant floor, and also indirectly heating domestic hot water. When the demand for both domestic HW and RFH hot water is great, the propane would kick in to pick up the slack.  It also would automatically kick in if peak demand shut the current to to the boiler, and satisfy the requirement for an automatic back up.

            So I would be able to heat both domestic and RFH water with relatively cheap BTUs during the winter and also take advantage of quick recovery during a long hot shower...and just shut off the electric boiler (or flow to the RFH system) during the summer and use propane when the off peak rate goes up to 5 cents/KWH. Depending of course on what the price of propane is at any given time.

            This would also leave me open to potentially heating domestic hot water with solar panels during the summer.

            What do you think?

          6. DavidThomas | Mar 09, 2004 09:01pm | #18

            >>"qualify for the dual fuel rate"

            >"That's a wonderfully enlightened view!"

            Yeah, took a while to get here on a residential level. Germany has had radio, remote-controlled water heater for 30 years. And time-of-use pricing. My F-I-L wrote his Economics PhD thesis on demand pricing at a time when US phone calls were priced the same regardless of time of day. And if the lines got busy mid-day, they just built more lines.

            David Thomas   Overlooking Cook Inlet in Kenai, Alaska

          7. edwardh1 | Mar 10, 2004 01:47am | #20

            I think some of these hvac calc programs ignore/can not handle open cathedral ceiling and 1 1/2 rooms like cathederal ceilings in homes where there are two units

          8. fortdh | Mar 09, 2004 07:13am | #11

            John, Give the utility room(washer/dryer) its own air supply if you can.

            Otherwise, it will suck out side air in where ever it has to, and exhaust conditioned air. Often, a duct to the attic, with filter, will allow warmer air than outside air to be used. If dryer is gas fired, you have some specific codes to follow for confined space appliances. With a super tight house like David's, you have to be very careful to provide enough combustion air and avoid back drafting.

            I am working on a design now that will have the air lock foyer, east wall buffered with non heated storage/cedar room, walled to non conditioned utility room.

            Closed cell poly foam sprayed in all walls with fg behind that and exterior of sheathing will be 3/4" foil foam board. Attic will also get 1" foam spray. Foyer, stairs to 2nd story and all upstairs will be isolated from rest of house with french doors so that up hvac system not needed unless company staying with us.All hvac, duct work to be in conditioned space and air tight. Advise either returns in rooms that will have doors closed, like bedrooms, or bridge vent to a room or hall that has the return. That way, you won't be pressuring a room with no air escape except to the outside, if using forced air system.

            Being in mid-Atlantic,summer humidity a problem, so refrigerator will have condensate drain, and shell formed by cabinents around the dish washer and built in ovens will have low volume exhaust system.

            Shower drain on master shower will have a GFX heat capture pipe.

            Hope some of this helpful to you. PaulEnergy Consultant and author of Practical Energy Cost Reduction for the Home

          9. User avater
            rjw | Mar 09, 2004 07:55pm | #17

            Paul

            >>If dryer is gas fired, you have some specific codes to follow for confined space appliances. With a super tight house like David's, you have to be very careful to provide enough combustion air and avoid back drafting.

            I've never been able to find how to include dryer requirements (I figure either gas or elect will draw air from the house and contribute to neg pressure) in coming up ith the air supply requirements? Is it a manufacturer spec?

            Or is a straight BTU calc - at least for the gas?

            _______________________

            Tool Donations Sought

            I'm matching tool donors to a church mission to Haiti - we're shipping a bus converted to a medical facility in (now it looks like) April and can fill it with clothes, tools and all sorts of stuff needed in that poorest of all countries. A few hand tools or power tools can provide a livelihood for an otherwise destitute family. Please email me if you have tools to donate.

            Thanks to Jeff and David and Jim and Rich and Steven and Mark and Jason and Shep and Jen and Mike and Joe and Bill and Ken for their offers!

            Several donations have arrived! Thanks and God bless!

          10. fortdh | Mar 10, 2004 12:50am | #19

            Bob, the water heater installation manual and our local inspector both say to total the Btus in the confined space of all the gas utilizing equipment in that space. Then you go to the chart for supply air source and whether horizontal or vertical supply duct. Typical is 1 sq inch per 4000 Btu direct vent to outdoors, two vents, one high (12" from ceiling, other low, 12" from floor). Each must supply the sq inches required, not a total of the two, and grille, louver interference must be accounted for. Horizontal supply is double in size.

            Now the weird part is what you alluded to, the cfm of the dryer, and in my case, the cfm of the WH power vent. When both running, there is a lot of neg pressure in the room. With the dryer operating, you could expect pilot flue gas to be pulled back through the dryer flue, but with the sq. inches satisfied, there does not seem to be a problem.

            So, bottom line, total Btus rule. I think a house with multiple dryers in a confined space with a standing pilot WH could have a problem with back draft. PaulEnergy Consultant and author of Practical Energy Cost Reduction for the Home

  5. fireball | Mar 09, 2004 01:24am | #8

    Drugrep,

    I bought the HVAC program linked in Bill Hartmann's post last week and it's great.It gives you good background on equipment sizing and can help size your duct runs too.I did a heat loss/gain on my own house, and then had two contractors that sell Carrier and Trane products over for estimates.They were both "rule of thumb" B.S. artists.Do yourself a favor and go to the HVAC Talk Forum before you buy.

    Barry

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Hand Tool Sharpening Tips

Learn how the pros keep their hand tools sharp without breaking the bank.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Podcast Episode 690: Sharpening, Wires Behind Baseboard, and Fixing Shingle Panels
  • FHB Podcast Segment: Hand Tool Sharpening Tips
  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data