fresh air inlet ‘frosting’

Muteability | Posted in Energy, Heating & Insulation on December 7, 2009 01:45am

Hello,

Had a new 95% efficient furnace installed last month.  Apparentyly, as a code requirement, a 5″ cold air inlet was installed.  We’re now getting our first real taste of winter temps (-20*C forcaseted tonight).  I just noticed that there is frost on the damper and the insulation around it is wet.

When the blower door test was done, I had 5.9 ACH @ 50Pa.  Should be a bit better now since I’ve sealed up a lot, but the windows still suck.  Do I really need a fresh air inlet to my 1950’s bungalow?  Can I just block this off?  If not, how do I keep the insulation dry?

Thanks,

Adam

View Image

View Image

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. BoJangles | Dec 07, 2009 04:39am | #1

    Does your new furnace have combustion air supplied by a PVC pipe that takes air from outside your house?

    1. Muteability | Dec 07, 2009 05:31am | #2

      yes. Intake and exhaust through PVC. Gas hot water is burning room air. Electric stove.

      1. DanH | Dec 07, 2009 05:45am | #4

        OK, I see you have a gas water heater. It needs some combustion air, but the setup you have (I assume that duct is leading into the cold air return) is pumping in more air than you need. The best solution might be to disconnect the duct at the furnace and just leave it to dangle near the water heater. Without the furnace fan to "pump" the air, the water heater will only draw what it needs.
        A society that presumes a norm of violence and celebrates aggression, whether in the subway, on the football field, or in the conduct of its business, cannot help making celebrities of the people who would destroy it.  --Lewis H. Lapham

        1. Muteability | Dec 07, 2009 06:08am | #5

          The old furnace and gas hot water heater ran with out the intake in the past. The house is still pretty leaky.Your comment about the fan pumping in a lot outside air did make me think though. The inlet does go in to the cold air return and I turned the fan from auto to on earlier today. I've probably been air conditioning the house, when the burner's not going. I'll turn the fan back to auto and see what happens.Thanks

          1. DanH | Dec 07, 2009 07:12am | #7

            Yeah, with that arrangement (and a leaky house) you don't want the fan running continuously. The fan creates a mild vacuum, so the duct draws a lot of outside air in, slightly pressurizing the house. If the house weren't so leaky this wouldn't be a problem, but if you were to use an infrared camera on a leaky house with this setup running you'd see jets of hot air exiting from every crack in the house.
            A society that presumes a norm of violence and celebrates aggression, whether in the subway, on the football field, or in the conduct of its business, cannot help making celebrities of the people who would destroy it.  --Lewis H. Lapham

          2. wane | Dec 07, 2009 04:14pm | #8

            you need it, and you don't .. this is a common sense approach to humdity control w/o an HRV, the damper only opens when the furnace is on a suppliments the stale house air w ext air.  It's more $ in the long run than the expense of an HRV and running a motor to power it.  That said it doesn't look like yours is done right, check to make sure the damper swings the right way, check the vent also swings the right way or is just a screen, hard duct the supply line and slope to the o/s ..

             

          3. Muteability | Dec 07, 2009 06:22pm | #10

            The damper is a manual open or closed affair. The inlet is just a screen. Too much humidity is rarely an issue in this climate. The humidifier runs most of the time. The blower door test came out at 5.9 ACH (air change per hour). Caulking around windows and sealing attic penetrations probably brought that down some, but there's still a lot of space for air to be pulled in. I'm leaning towards closing it up.

  2. DanH | Dec 07, 2009 05:42am | #3

    Frankly, I don't know why you'd need the thing in a 50s house that hasn't been extensively reworked to seal it, unless you have other combustion appliances that need the air. (Do you have a gas water heater, perhaps?) Don't know that I'd remove it entirely, but blocking off about 3/4ths of the air intake should eliminate some of the frosting. Also, you should try to seal the area around that damper lever better, to keep moist air in the basement from getting in there.

    A society that presumes a norm of violence and celebrates aggression, whether in the subway, on the football field, or in the conduct of its business, cannot help making celebrities of the people who would destroy it.  --Lewis H. Lapham
  3. BoJangles | Dec 07, 2009 06:46am | #6

    You don't need that thing.  It will freeze you out of your house when it gets cold!

    I would completely eliminate it and plug the hole for good.

  4. rdesigns | Dec 07, 2009 05:56pm | #9

    I doubt if the duct that's giving you trouble was intended for combustion air--instead, it was probably for bringing in outside air to improve indoor air quality, and in your dry climate, would reduce indoor humidity in the summer.

    I believe you could simply close the manual damper for the heating season. Your house is leaky enough to provide all the combustion air you'll need for the water heater and for indoor air quality.

    As a safety test, close the damper, close the door to the furnace room while the furnace is running, but with the water heater not firing. Now feel along the bottom of the door to the furnace room from inside the furnace room. If you feel a lot of air rushing into the furnace room under these conditions, there is danger of the water heater backdrafting, and you check further by holding a match at the edge of the water heater's draft hood to see if air is being sucked down thru the flue into the room--the match flame or smoke should be drawn up into the draft hood if the WH is drafting properly.

    I doubt you will see this problem, but if you do, shut off the furnace blower and do the match test again. If it drafts properly with blower off, it means you have an improperly balanced duct system that is de-pressurizing the furnace room.

     

    1. Muteability | Dec 07, 2009 07:43pm | #11

      The damper is already in the closed position, but there's still a lot of air being pulled in. I went outside with the fan spinning and could feel the draw at the inlet from 4 inches away.There is no door to the furnace room. Almost the whole basement has open air flow. There's only one small room with a door. Thanks for the match test idea. I wedged a square of 1/2" rigid foam in the inlet (outside), turned on the furnace fan and smoke is still getting drawn up the hot water tank chimney.Within 30 minutes the frost was melted and dripping to the floor.My return 'duct' is two runs of at most 7 feet of the 16"OC floor joists. No bends The fan is powerful and must have been pulling in a ton of outside air.I think I'll seal it up for the winter and maybe open it for the summer. Nights usually get cool even on the hottest days. I can turn the fan on at night to circulate the cool air.Thanks,Adam

      1. rdesigns | Dec 07, 2009 08:29pm | #12

        "My return 'duct' is two runs of at most 7 feet of the 16"OC floor joists. No bends The fan is powerful and must have been pulling in a ton of outside air."

        This opens another question:  What is the opening into these joist bays? Is it the typical wall grille in the wall of the floor above? If you remove the grille and look inside, you may see that the true size of the opening is just a small cutout of the wall plate, about 3" x 14" at best.

        If so, you likely have undersized return, which would explain why the outside air duct was drawing so hard. Undersized returns are very common, and they reduce the efficiency and airflow significantly, while also shortening the life of the furnace's heat exchanger because reduced airflow results in too-high temperatures across the heat exchanger. It also increases air leakage into and out of, the house, by creating pressure imbalances in various rooms and spaces--some will be pressurized, while others will be correspondingly de-pressurized.

        1. Muteability | Dec 07, 2009 09:14pm | #13

          "What is the opening into these joist bays?"The return inlets are two wall grills on the floor above. They're in the central hallway, pretty much dead center of the house. The opening behind the grill is 5"x27", and open to the joists below(no bottom plate). There is a small grill grate in the basement (8x12 maybe) that has some limited flow back to the cold air duct. Just a few holes in the top plate from the previous home owners reno. It's blocked off at the moment, because I'm replacing the 60's luan paneling with drywall and don't want to suck in the dust. The furnace that was replaced was 53 years old. There's definitely a LOT more air flow with the new blower."It also increases air leakage into and out of, the house, by creating pressure imbalances in various rooms and spaces--some will be pressurized, while others will be correspondingly de-pressurized."I don't know what I can do to fix that.

          Edited 12/7/2009 3:22 pm by Muteability

          1. rdesigns | Dec 07, 2009 11:53pm | #14

            If I understand your description, your return air consists of an opening of 5 x 27, or 135 sq. in.

            That seems very small, but, of course, I don't know the BTU rating of your furnace--my guess is that is will be about 100k. With a high-efficiency furnace, you ought to have about 150 CFM for every 10k BTU's (that would be 1500 CFM for a 100k furnace), and there's no way you'll be getting that much air through your current return air opening.

            The fix may not be all that difficult.

            You can use joist spaces for return air if you seal them well, so you could add more of the type you already have.

            If you heat the basement, you could open a large return air grille in the underside of the return trunk, and then open a pathway for air to get from the main floor to the basement.

             

          2. Muteability | Dec 08, 2009 12:56am | #15

            "If I understand your description, your return air consists of an opening of 5 x 27, or 135 sq. in."It's two openings that size but that's still small by your numbers.80K BTU furnace. The return plenum goes straight up from the furnace an is only the two joist bays.From the pics you can see the cold back of the basement return closed off with core plast. The return for the first floor is above that beam. They are only 2x4 walls so the numbers might be a bit smaller.

          3. rdesigns | Dec 08, 2009 01:52am | #16

            An 80k HE furnace should have about 1000 CFM. Each of the wall returns would need to deliver 500 CFM, which is doubtful, but not impossible, depending on what other restrictions the duct system has.

            If you have access to a manometer, a static pressure test would tell the story. The total external static pressure should not be more than about 0.7, and 0.5 would be better.

            However, you could do a simple test to see if the main floor is being pressurized:  Assuming you have a door separating the main floor from the basement, close that door while the furnace blower is running, and, standing on the basement side of the door, feel for airflow under the door. If there is much of a breeze coming thru, it means that the main floor supplies do not have adequate return pathways, and that the air is pushing into the basement.

            Another useful and simple test is to check the temperature rise across the heat exchanger, which is done by measuring the air temp at the supply plenum and the return plenum after the burner has been running for 5 minutes or so--if, say, the return side was 70 and the supply was 150, the rise would be 80, and that is too high according to most manufacturers, who want the rise to be in the range of 35 to 75. High temp rise = too little airflow. The temp rise can also be used to get a fairly accurate estimate of the total CFM. I can give you the formula if you feel that would be useful.

          4. BoJangles | Dec 08, 2009 03:42am | #17

            Not to worry....with that air inlet hooked up, he will be lucky if he can get his supply temp up to 70* when it is cold out. 

          5. Muteability | Dec 08, 2009 04:50am | #18

            "Each of the wall returns would need to deliver 500 CFM, which is doubtful, but not impossible, depending on what other restrictions the duct system has. The only restriction would be the filter, which is only a low cost FG (MERV 1 or 2??) "The total external static pressure should not be more than about 0.7, and 0.5 would be better"I do have access to a digital manometer. What is the test set up and what units of measure is the .5 to .7 you refer to? My flow meter only goes to about 120 LPM and has a 1" round inlet. Won't be much use for ducts.I'll be out of town until Thursday, so all testing will need to wait until then.Thanks

          6. rdesigns | Dec 09, 2009 05:57pm | #19

            The values of 0.7 and 0.5 refer to "Inches of Water Column" (IWC). A digital manometer will likely have a scale for IWC, as well as one for Pascals--250 Pascals = one IWC.

            You want to know the total static pressure (resistance) for the system. You need two readings to get this: the supply side and the teturn side. For the supply side, insert the probe in a small hole that you drill between the furnace outlet and the AC coil, being VERY careful not to drill into a refrigerant line. The return measurement is taken at a point in between the filter and the furnace. The sum of these two is your total static pressure for the system.

            If the supply was 0.25, and the return was 0.35, that would be a total of 0.6, which is slightly high, but not a problem. If you find the total to be much more than about 0.75, you could have airflow reduced enough to cause the heat exchanger of the furnace to overheat, or the AC coil to have insufficient airflow.

            You should be able to get the manufacturer's blower chart, which will corellate static pressure to CFM. The higher the static pressure, the lower the airflow, or CFM.

            In Calgary's dry climate, combined with its high elevation, you need much higher cooling airflow than the standard 350-400 CFM per ton of AC that is correct for sea level and high humidity. You should have at least 450-500 CFM per ton of AC to correct for the less-dense air and lack of humidity. (a "ton" of AC capacity = 12,000 BTU's.)

          7. Muteability | Dec 11, 2009 10:48pm | #20

            rdesigns,

            I hope you see this in the new format. I've had a bugger of a time finding things.

            I don't have AC installed, so drilling in to the coil is a non issue.

            So if I understand correctly...

            With the fan running on high,

            I drill a small hole after the filter, insert the tube attached to the digital pressure meter and I will see a negative pressure.

            I then drill a hole on supply side (the plenum right above the furnace?) insert the tube and I will see a positive pressure.

            The difference between the two should be around 0.5 IWC.

            I might give that a try this weekend. Getting back after three days with the fresh air inlet loosly blocked has resulted in the frosting disappearing and the moisture in the FG insulation drying up.

            I did try the closing the basement door with the fan running and could not detect any flow from the first floor to ground floor, even with the smoke from an extinguished match.

            Thanks again for all the help. If I can figure out a way to email directly. I'll try that.

          8. rdesigns | Dec 14, 2009 11:22am | #21

            New format = bad, but that's
            New format = bad, but that's another problem.

            Since you don't have AC, much of what I was concerned about is not really a problem, and frankly, I was wondering why you'd need AC in Calgary--its summer design temperature is only 80 degrees, meaning that it's warmenr than 80 only 1% of the time.

            Lower airflow on heating is not as critical as on cooling. Low heating airflow is mainly a concern when the temperature rise exceeds the manufactuer's acceptable range, which is quite large, 35-75 degrees being common. So the thermometer test I mentioned earlier is adequate to show this.

            If the temp rise is within limits, the only other question is: are certain spaces or rooms not adequately heated by the time the t'stat is satisfied and shuts down the system?

            If so, it means insuffient airflow to that space. The first thing to check is return air: is there unrestricted return from that space? If so, then the supply branch is the next thing to check, along with air balance for the whole system.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Old House Air-Sealing Basics

Look high and low to find and plug air leaks that cost you money and comfort.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data