Gas Dryer Venting Problem

| Posted in General Discussion on December 3, 2003 11:10am

I have checked through messages and am still not certain of which way to go…

I have Gas Dryer in interior laundry room on 2nd floor.  Venting options are:

1. Up through roof, about a 10ft  vertical run with 90 degree elbow at dryer. 4″ galv. pipe through insulated space above plaster ceiling (no attic).  Have seen roof vent from Inovate Technologies, but not sure how well it would work (says recommended for flat roofs and this roof is standard pitched).  Damper would I assume work like standard damper and open under pressure from exhaust air.    a. Any issue for snow blocking vent? (in MA and sometimes heavy snow)  b. Lint on asphalt shingles? c. Proper Flashing would be issue just like any other hole in roof    d. What about moisture in a vertical vent and increased risk of lint accumulating at 90 degree elbow at dryer?

2. Vertical 8ft  and then horizontal 15ft through sidewall and require numerous elbows.  Distance is over limits and would require booster fan & switch ($), plus not be optimal from visual perspective. In other words, option 1 is my preference, but I dont’ want to risk mistake if it has too many problems.  Advice? Thanks, Adam

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. butch | Dec 03, 2003 11:49pm | #1

    I think I'm following you, through the roof w/only 10' of vent run should not be a

    problem w/3 elboes. One elboe at the back of the dryer to transition to vertical and

    instead of this "Inovate Technologies" roof cap use 2 elboes hooked together to

    form a n (shepards hook)at the end of the pipe termination above the roof(high

    enough

    to clear any snow accumalation). For the penetration through the roof , you can get

    a 4" roof  flashing to run your pipe through the roof.  I wouldn't use no damper,

    because it will be a constant  maintanece problem accumalating lint and staying

    blocked open.

    And as far as the lint on the roof if the rain doesn't wash it of you could always wash

    it away with a hose.

     Also use the silver vent tape(not duct tape) and if you use any mechanical

    connections  use rivets instead of screws.

    1. sad | Dec 10, 2003 07:27pm | #2

      Thanks for the advice.  I am now looking at the air inflow for interior laundry room/make-up air.  Can that be just a grill above doorway 12x12 leading into main hallway/staircase area and right next to return grill for 2nd floor air handler?  I had read somewhere on site where someone recommended putting in a dedicated line to outside for make up air, but I don't want to punch any more holes in roof and wouldn't that just make my laundry room very cold in winter?  Also, having just insulated walls for soundproofing, it seems like I am just opening another avenue for sound to travel out into main house? 

      thanks to you and anyone else who can shed some light on this.

      Adam

      1. DavidThomas | Dec 10, 2003 08:23pm | #4

        I would use a grate into the laundry room rather than make another peneration in the building envelope.   Consider the following if you don't want that grate to transmit the sound of the washer and dryer:

        Instead of going straight through with a grate on each side, put a grate high on one side and low on the other.  Use the stud bay as a silencer of sorts.  If you force the sound to bounce off of multiple surfaces, you can reduce the transmission. 

        Note that no penetration should open the framing to a fire hazard.  Sheetrock or block with wood the air passage from the rest of the stud bay.  Check with the inspector, but at most, you'd have to put 5/8" rock on the sides of the studs and fire blocking (2x4s) high and low.

        Once fire blocking is done, you are free to consider acoustical panel or accoustical foam inside the bay to further block sound.  But sound leakage through and under an interior door is probably the bigger source once you've offset the grates.David Thomas   Overlooking Cook Inlet in Kenai, Alaska

        1. johnharkins | Dec 10, 2003 10:45pm | #5

          sad  would cutting 1/2" off the bottom of your laundry room door be a solution?

          we are a busy family of four and  we hang dry just about everything but sheets & towels on wood drying racks  during the day the room is usually open but at night we close it as it will be one of the last to be insulated   --   we use two of those dry z air units ( electrical app 15" diameter) as drying agents      say each one uses the energy of a 40 watt bulb    ciao John

      2. butch | Dec 11, 2003 02:34pm | #10

        As far as make up air is concerned I wouldn't want to punch any more holes in the

        building envelope either.  To bad they don't make (as far as I know) an automatic

        opening and closing cap that would only open when the dryer is running. i'd ck. with

        local building authorities regarding using make-up air from the house instead of

        bringing in outside air. It wouldn't seem to big of a deal with one gas appliance.

    2. roofdoc | Dec 10, 2003 07:33pm | #3

      Several manufactors make roof jacks or vents just for dryers of exhaust fan.If I am not mistaken I think GAF even makes them to gowith their roof systems

      1. butch | Dec 11, 2003 02:25pm | #9

        Doc,I'd be interested to see what your talking about.  Do you have any links or more

        info. Inquiring minds want to know. Butch

        1. roofdoc | Dec 11, 2003 03:14pm | #12

          In response to your request try http://www.gaf.com/content/document/20502.pdf or simply http://www.gaf.com  you will find more than one product that can be used for your installtion.

          Reading some of the posts I really think that b pipe is overkill.The straight up and out is about best way to deal with it,I used to take care of a condo complex that had long vertical runs installed through the garage attic space,they used to plug up with lint and then cause condisation to form on the outside of the pipe,was the roof leak that only happened when the dryer was on

  2. jsvenson | Dec 11, 2003 04:04am | #6

    sad,

        If you are talking venting the cumbustion fumes (as I think you are) and not the lint, I would think you would have to use B-vent, not just sheet metal vent. It is also known as MetalBestos. It is a double walled vent to reduce the outer metal temperature.

        This would not have a damper on it unless it was electrically opened with a safety device to prevent combustion if the damper fails. After it exits the roof it takes a special b-vent cap to help prevent downdraft. You should not use the box type vent intended for bathroom exhaust fans!

        The two safety issues that this system addresses are CO fumes and flue temperature (sp.FIRE!)  These should not  be taken lightly. Make sure your system is safe and to code if you are determined to do it yourself!

         I'm not trying to pass myself off as an expert in gas dryers (I have never installed one) but I have installed many other types of gas and wood funaces,stoves and fireplaces and I do know not a winter goes by that I don't hear of fires and deaths resulting from improperly vented gas appliances.

    John Svenson, Builder, Remodeler, NE Ohio (Formerly posted as JRS)
    1. DavidThomas | Dec 11, 2003 04:31am | #7

      "venting the cumbustion fumes (as I think you are) and not the lint"

      But all natural-gas fired clothes dryer vents combustion fumes (N2, O2, CO2, Ar and CO in order by %) with excess air and whatever lint the dryer didn't catch, right?  I have never seen a separate lint vent.

      In most of the combustion equipment in a house (HWH, furnace, boiler), the flue gases are (should be) the combustion products of an slightly lean mixture - a few percent O2 and very low CO.  Equipment can be out of adjustment, poorly tuned and discharge higher than average CO, for sure.

      But the excess air used in a clothes dryer keeps the temperatures much lower than a HWH, boiler, etc.  Hence, things like plastic anti-critter screens are rountinely installed on dryer vents that never would be used on high-temperatures exhausts.

      Clothes dryers certainly cause houses to burn down at times, and I suspect they can cause CO deaths (although I don't recall any recently). 

      But before going to the (not required by code) MetalBestos route, I would, in order of importance:

      1) Keep the run as short and straight as possible

      2) Use aluminium tape designed for that purpose (not, "duct tape" or, quack, "duck tape").

      3) Use rigid (not flex) metal ductwork only.

      4) Use pop rivets instead of screws to snag less lint.

      5) Aluminium tape the length of the seam of each piece of ductwork.  OF COURSE you tape the junction of one section to another!David Thomas   Overlooking Cook Inlet in Kenai, Alaska

      1. jsvenson | Dec 11, 2003 06:51am | #8

        Thanks for the info on gas dryers. They are a rarity in my area, and I have never had to deal with one.

        I thought it would be good to bring up, because when I see DIY, gas, and venting, all in the same post, red flags go up.

        BTW, I've been to Kenai, and Soldatna. Beautiful country. I've also made it on down to Homer a couple of times, once for a halibut charter. What an experience that was! The sight seeing was the best, the fishing was just a bonus! (Shipped home 80 lbs. of halibut-never thought I could get tired of it, but it took a long time to consume, even after giving some of it away)

        John Svenson, Builder, Remodeler, NE Ohio (Formerly posted as JRS)

        1. DavidThomas | Dec 11, 2003 11:30pm | #14

          "80 lbs. of halibut-never thought I could get tired of it, but it took a long time to consume"

          At least it keeps well frozen for a long time - a year or better if vac-packed.  Salmon you gotta use in a few months.  Salmon is great smoked (I do 2/3s of mine that way), but you can also smoke halibut and serve it on crackers or in omelets.  In addition to backed and grilled, frozen frozen halibut goes very nicely in some casseroles.  Got a friend up here who does great halibut enchiladas.

          But I shake my head when I see tourists in Kenai or Anchorage checking (and paying for excess baggage) on six 70-pound boxes of frozen fish.  Do they have any idea how long 420 pounds of fillets will take to eat?!  Even for their whole extended family?  2 halibut and 20-30 sockeyes are all we need each year and that's in a no-red-meat house.David Thomas   Overlooking Cook Inlet in Kenai, Alaska

          1. jsvenson | Dec 12, 2003 01:28am | #16

            Dave,

                   420 lbs.-unbelievable. I really did get a little tired of the halibut, but I guess I didn't realize it preservrd that long frozen. The casserole sounds delicious, I wish I would have thought of that. Had most of it baked, broiled or grilled.

                  I've got family in Palmer and Anchorage, next time I come up I'd like to look you up. It probably wouldn't be for a couple of years. I've got kids in college. Maybe when I'm down to one. 

                  Maybe an Alaska-fest someday? Bet you could get some of those Oregon & Washington Breaktimers up there!

            JohnJohn Svenson, Builder, Remodeler, NE Ohio (Formerly posted as JRS)

      2. sad | Dec 12, 2003 05:55pm | #17

        Thanks for all the advice.  Here's what I was recommended to do by a sheet metal/ducting contractor:

        1. Gas dryer exhaust vent to 90deg. shallow clearance duct attachment = 2 90deg's

        2. 4" 90 deg elbow to straight run of about 11' of 4" galvanized rigid duct. = 3 90's

        3. Capped clean out T installed low in straight run to permit vacuum house cleaning as needed.  Joints sealed with "Duct Butter" sealant and taped with silver duct tape. Pipe wrapped in fiberglass batt insulation

        4. Straight duct terminates at underside of roof where it attaches to rectangular flat aluminum flange with attachment for 4" duct.

        5. 4" hole in roof and hooded aluminum roof jack/vent made by Lambro which has damper activated by air flow and at very end a critter screen (not fine mesh).  Vent properly flashed and sealed.  Hooded vent/jack is another 90 degrees = 4 90 deg's

        Anything seem out of place here or suggestions for improvement?

        thanks again to all.

        Adam

        1. butch | Dec 13, 2003 05:59pm | #18

          Everything sounded fine up to step 4? I wish I could see this Lambro roof jack your

          talking about. Any kind of screen or damper in this WILL be a constant source of lint

          accumulation. Hopefully you'll be able to access from attic to clean.

        2. User avater
          BillHartmann | Dec 13, 2003 06:43pm | #19

          Each 90 elbows count as 5 ft of straight pipe.

          Looks like you are right at the maximum recommended run 25 ft. Plus transistion or two.

          You might want to make allowance to add a booster fan if the drying is slow.

          Or up as much as you can, specially the elbows to 5" pipe.

        3. DavidThomas | Dec 13, 2003 10:06pm | #21

          "Pipe wrapped in fiberglass batt insulation"

          A nice and helpful step, not common.  Helpful to keep the temperature up in the duct work so you don't get condensation in the duct work.   Wet lint gets stuck to the inside of the dutwork.  Dry lint keeps moving.David Thomas   Overlooking Cook Inlet in Kenai, Alaska

    2. butch | Dec 11, 2003 02:41pm | #11

      We never use double wall vent(use galv. rigid pipe) because that in itself creates a

      fire-hazard.  The reason being that lint accumualtes between the two pipes creating

      a potential fire hazard. I always leave 1" clearance around any penetrations.

  3. Rockbeare | Dec 11, 2003 05:53pm | #13

    Interesting discussion.  I did a full renovation on a couple of 19th. century stone buildings over the last couple of years and, with rubble walling up to 22" thick, installing vents just wasn't very practical.  In both cases, the owners went with my suggestion to install electric dryers imported from Europe as the condensation is 'caught' in a removable drawer.  Yes, the cost was higher but they are much more efficient (and the Inspectors agreed!)  Maybe, as we now have gas-fired boilers (as they have had in Europe for over 30 years) with balanced-flue vents, there are gas dryers out there with the same system?

    Rockbeare

    1. DavidThomas | Dec 11, 2003 11:32pm | #15

      "my suggestion to install electric dryers imported from Europe as the condensation is 'caught' in a removable drawer"

      And, if there's a long heating season, you might as well kept those BTUs (and some leaked moisture?) inside the house.  But in the cooling season (what's that? - hah!), I'd want a big operable window in the laundry room to dump the heat.David Thomas   Overlooking Cook Inlet in Kenai, Alaska

  4. djohan | Dec 13, 2003 09:58pm | #20

    My personal experience with dryer vents is that elbows dramaticly decreases airflow.  In the instrucion book for my Maytag gas dryer, it states that runs of up to 25 feet with four inch rigid pipe are allowed.  Our run was 16 feet with two 90 degree bends.  After a few months, my wife noted one day to me that it was taking up to two hours to dry a load of bath towels.  I called Maytag help line and they said that according to their specs, all was right and that I should have the unit checked to see that the fan was running the correct speed.

    Anyhow, after a lot of checking that produced nothing, I decided to route the vent through the side of a cabinet and out the adjoining wall.  The total run with flex tubing was just under five feet.  The same load of laundry now drys in under 30 minutes.

    So....keep the runs as short as possible and use sweeps in the turns when you have to make the turns at all.  Take the most direct route.  I would advise against using an outlet in a horrizontal or sloped position that was designed for a verticle installation.  It is very possible that he amount of airflow will be to small to keep the flapper open, and may result that the dryer will vent into your living space.

    1. DavidThomas | Dec 13, 2003 10:14pm | #22

      "After a few months. . .it was taking up to two hours. . .(after installing) flex tubing of five feet the same load of laundry now drys in under 30 minutes."

      But that the problem worsened over time, makes me think of something instead of, or rather in addition to, the long duct run.   The air flow/velocity may have been too low in the 16 feet plus 2 elbows.  Allowing lint to fall out, moisture to condense, then more lint to fall out.  It kind of snowballs because as the flow decreases, more lint is deposited.

      You might have been able to restore performance by snaking the 16 feet run with a duct cleaning brush.  But your installation of a shorter run is a vastly better solution that will involve little future maintenance.  Higher air flow, drier air in the duct because it doesn't cool as much.  Little lint deposition.  Better drier perfromance and less energy consumption.

      Shorter is always better.  Contrary to all those spams I get about adding inches.David Thomas   Overlooking Cook Inlet in Kenai, Alaska

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

A New Approach to Foundations

Discover a concrete-free foundation option that doesn't require any digging.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Old House Air-Sealing Basics
  • A Drip-Free, Through-Window Heat Pump
  • Insulation for Homes in the Wildland Urban Interface
  • An Impressive Air-to-Water Heat Pump

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Old House Journal – August 2025
    • Designing the Perfect Garden Gate
    • Old House Air-Sealing Basics
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data