Gas Oven – Little help please
GoDadGo | Posted in General Discussion on March 11, 2013 10:05am
Gentlemen / Ladies,
It’s been quite some time since my last visit, please forgive me. In my time of need I must turn to the experts. In short:
Frigidaire gas range ES400
Strong gas odor, but only while in use (oven).
I suspect a faulty part, but which one?
Thank you very much.
Dylan
  1. rdesigns | Mar 11, 2013 01:37pm | #1
    This odor--is it raw (unburned) gas or the odor of combustion gases?
      GoDadGo | Mar 11, 2013 06:36pm | #3
      I think it is combustion gases. But I'm not certain.
  2. dude | Mar 11, 2013 02:47pm | #2
    gas oven
    is it propane or natural gas
    If propane gas in cyl is low
    was something spilled in oven
      GoDadGo | Mar 11, 2013 06:37pm | #4
      The gas is LP - the tank is full.
      Nothing has spilled.
    GoDadGo | Mar 11, 2013 09:13pm | #5
    Additional info
    I found a lot of soot under the flame spread.
    1. dude | Mar 12, 2013 01:46am | #6
      when the oven burner is properly adjusted the blue flame at the burner should have just a little bit of yellow at the tips
      the atr shutter on the end of the burner controls this & is adjustable
      too much soot usually means the flame is too yellow ( not enough air )
    2. rdesigns | Mar 12, 2013 11:16am | #7
      The flame should be blue as dude says. If it's yellow, the primary air mixture can be adjusted.
      The combustion gases may not be exausted fully by the hood--if, indeed you have an exhaust hood that gets turned on when the oven is firing.
      The odor of raw propane is very distinctive, so you probably are correct in identifying the smell as combustion gases.