GFCI breakers

| Posted in General Discussion on June 16, 1999 11:54am

*
I’m installing a circuit for my wife’s new pottery kiln and have received contradictory information about GFCI breakers. I’m hoping someone can shed light on two questions.

The situation: the kiln is located in an essentially dirt-floored outbuilding (we’ve got bricks on it, right over dirt). The kiln is pure 220 volt (no 110 volt, so no neutral returning to the panel), plus an equipment ground. Due to limited space on the panel, we’d like to use the same circuit for our son’s occasional use of an arc welder (not at same time as kiln). Because of the dirt floor, and because my wife is pretty valuable to me, I’ve been thinking to put in a GFCI breaker. As 50 amp, two-pole breakers are about $100 (as opposed to $9 for a conventional one), I want to be sure it’s the right move. I’ve been told:

1. By a Cutler-Hammer rep that, if there’s no neutral leg returning to the panel, the GFCI feature won’t work, so don’t waste my money. By others, including a contractor and the electrical supply house, that it sure as heck will work as a GFCI even with no neutral returning.

2. That, because of the power surges created by an arc welder, using the welder on the circuit will result in a very early death of the GFCI. Others say it should be ok.

I’m now completely confused and hope someone can help.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Guest_ | Jun 15, 1999 09:18pm | #1

    *
    If you understand how a GFCI works, the Cutler-Hammer rep is correct, but I don't know about #2, as far as power surges go. Arc welders transform AC into DC (AC doesn't arc), so there may not be the surges that would/could trip a GFCI, as with my washing machine's timer and motor. Contact the welder's manufacturer to be sure. You may wish to consider a secondary box that would allow you to have service to both devices, providing 240V to the kiln and 120v (with neutral and GFCI) to the welder, if that's its electrical rating.

  2. TPBosworth | Jun 15, 1999 09:46pm | #2

    *
    Bill:

    I did a bit of research on the Square D website and I believe you can use a 2-pole GFCI breaker for your kiln. It has a white neutral wire in the panel that must be connected to the neutral bus, but it does not need to extend to the load (kiln). The breaker measures the balance across the lines versus the neutral and trips if there's an acceptable level of leakage. Square D part #QO250GFI. I don't know cost.

    I suspect the Cutler-Hammer products have a similar item.

    The addition of a welder for occasional use is a bit dicey because of the distinct possibility of connecting both appliances concurrently - a bad thing. If you're creating a single recepticle to service both - then it's OK. I don't know what type of behavior to expect from the welder on the GFI breaker.

  3. Guest_ | Jun 15, 1999 10:27pm | #3

    *
    AC doesn't arc? Gee, Barry, maybe that's why my welding with my AC only Lincoln welder has been so poor...

    Not that it is really germaine to this discussion, but there are both AC and DC welders that do, indeed, arc. Most of the inexpensive welders (often termed "buzz boxes") are AC welders (including my 225 amp Lincoln welder). Most larger, production welders for steel that I have seen are DC, but aluminum cannot be welded with DC (has to do with aluminum oxide formation). Most welders change whatever input voltage to around 30 volts for the output. My 250 amp TIG (Tungsten Inert Gas) machine requires about 30 amps at 230 volts and the output can be selected for either AC or DC depending upon the requirement of the metal to be welded (this machine allows me to weld up to around 3/8" material).

  4. G.LaLonde | Jun 16, 1999 01:42am | #4

    *
    I agree with what you said.......The breakers are about $70.00 at our local wholesalers. I have never seen a welder hooked to a GFCI so can't comment on that, but if it will work, your idea of using only one receptacle is a good one.

    1. cliffp | Jun 16, 1999 01:48am | #5

      *Bill--A GCFI (I'm going to call it a GFI) works by comparing the current in the supply and return conductors. For a conventional GFI in the States, if the current is different by more than 6 mA, the GFI must open the circuit within a few seconds (5 to 6).For most of the 120V branch circuits on which GFIs are installed, the supply conductor is the "hot" or "phase", and the return conductor is the neutral (actually the 'i'groundedi'i') conductor. In a 240 V circuit, there is no neutral, but there is a return conductor--it's just the other phase conductor.So, a GFI breaker designed for it WILL work in a 240 V circuit.I suggest the question you ask yourself is, what is the potential for someone to come in contact with an energized part of the kiln? Is the frame made of metal and is it grounded? Are the electrical controls & splices in a grounded metal box? Is there any way (even failure of two levels of electrical insulation/isolation) for a person to provide a current path to ground? If the answer is an easy 'yes', then go for the GFI.Major appliances (washing machines, electric dryers & range/ovens, etc.) are NOT protected by GFIs. This is because they usually have some leakage current, more than 6 mA, that would trip a common GFI. (It's not because of the nature of the motor's current draw or the timer). When properly grounded, there's a low impedance path for the leakage to get to ground, so there's little chance of the current taking a path through someone.If you do want to install a GFI, look into one with a higher trip point; they are commercially available in the States. In fact, in Europe, GFIs are set to trip at a higher current and time than 6 mA & 6 seconds, which is an extremely protective standard. I believe it's between 12 and 15 mA and all I remember is it's more than 6 sec. One commercial GFI is settable--6, 12, or 30 mA trip. It's a 240V job, and it's not a breaker/GFI.On the arc welder issue--pick a GFI breaker (can't go wrong w/Square-D) and call the manufacturer. Get the technical people on the line. They'll be able to tell you. Also they'll confirm the fact the you can protect a 240V circuit with a GFI. But I bet that you'll be able to use the weldeer. The GFI is just a current comparator; I don't see how surges of current would kill it.Good luck with the pottery.

  5. Bill_Houghton | Jun 16, 1999 11:54am | #6

    *
    I'm installing a circuit for my wife's new pottery kiln and have received contradictory information about GFCI breakers. I'm hoping someone can shed light on two questions.

    The situation: the kiln is located in an essentially dirt-floored outbuilding (we've got bricks on it, right over dirt). The kiln is pure 220 volt (no 110 volt, so no neutral returning to the panel), plus an equipment ground. Due to limited space on the panel, we'd like to use the same circuit for our son's occasional use of an arc welder (not at same time as kiln). Because of the dirt floor, and because my wife is pretty valuable to me, I've been thinking to put in a GFCI breaker. As 50 amp, two-pole breakers are about $100 (as opposed to $9 for a conventional one), I want to be sure it's the right move. I've been told:

    1. By a Cutler-Hammer rep that, if there's no neutral leg returning to the panel, the GFCI feature won't work, so don't waste my money. By others, including a contractor and the electrical supply house, that it sure as heck will work as a GFCI even with no neutral returning.

    2. That, because of the power surges created by an arc welder, using the welder on the circuit will result in a very early death of the GFCI. Others say it should be ok.

    I'm now completely confused and hope someone can help.

  6. Guest_ | Jun 16, 1999 11:54am | #7

    *
    Just installed a G.E. brand 240V GFCI and it had instructions for both applications. With or without a neutral. If there is a neutral then it is connected to the breaker where it is labled "load neutral". If there is no neutral involved and the application is strictly 240V then all that is required is to connect the white pigtail supplied and made into the breaker to the neutral bus. The point is that a load neutral is not "required" for it to work properly.

    As far as the arc welder on a GFCI I do not know.

    If a Cutler-Hammer is the panel you have and thats the breaker you need, I would call back and ask another rep.

    glenn

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Simple and Discreet Countertop Power

A new code-compliant, spill-safe outlet from Legrand offers a sleek solution for a kitchen island plug.

Featured Video

Video: Build a Fireplace, Brick by Brick

Watch mason Mike Mehaffey construct a traditional-style fireplace that burns well and meets current building codes.

Related Stories

  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations
  • A Closer Look at Smart Water-Leak Detection Systems
  • Guest Suite With a Garden House

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data