GFCI problems on submersable pump

Stray | Posted in Energy, Heating & Insulation on April 14, 2003 07:47am

Hey folks.  I’m scratching my head over this one…

 

I have a small pond (1,000 sqr’) that I fill via a submersable pump from a nearby stream.  Replaced the weatherproof box next to the stream (that wasn’t so weatherproof anymore) that the pump plugs into, with a new weatherproof box and standard outlet. 

This is in turn is fed from a weatherproof box 50′ away that has a toggle switch and GFCI outlet so I can flip the pump on and off easily.  Toggle switch and streamside outlet was downline from GFCI, so as to be protected. 

GFCI tested out fine (Cheapo pug-in type tyester, with GFCI tripping button).   Plug the pump in, and it trips the GFCI.  Dragged the pump out of the water (unplugged obviously) and checked it over.  No evidence of deterioration on insulation, or anything noticable on exterior.

Have since wired in a regular outlet in place of the GFCI, and all is working fine (as it has for years).

I’m wondering if anything about a submursible pump would cause problems with a GFCI (being underwater and all).  I’ve heard of GFCI’s neusence tripping on circuits with flourecent lights, or other types of interference.  I’d like to have the GFCI on the circuit for obvious reasons.  I’d also like to know if I should throw the pump out ASAP.

Any thoughts appreciated!

-Erik

PS: I have successfullly installed dozens of GFCI’s (interior) without problem, and I’m pretty confident I had this one in correctly.

 

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. frontiercc | Apr 14, 2003 08:04pm | #1

    First things fitst, I am NOT an electrician, but spend a lot of time watching one.  According to him, GFIs can sort of "wear out" over time causing an increase in nuisance tripping.   Issue two is that GFIs don't play well with high initial amperage loads.  While your pump probably does not draw that much power consistently, the start up draw can sometimes trip a GFI, especially an older one that may be getting weak.  (This is the explanation given to me when I asked why everything in the basement of my house is GFI protected EXCEPT for the sump pump).

    I would try a new GFI and see if all goes back to normal.  But like I said, I'm just a guy . . . . . . .  Any electricians might chime in with some more/better info.

    1. Stray | Apr 14, 2003 08:23pm | #2

      Frontiercc,  Thanks for the response.

      The GFCI was a brand new, out of the box, 20amp GFCI that I installed the same time I did the other oultet.

      Your point about startup voltage is interesting though.  In fact, the pump ain't no small little guppy-pond pump, it's more the sump pump variety (discharges a real strong flow out of 2" CPVC pipe, up 20' of head). 

      Not sure what the amperage or GMP is off hand, but I could find out if people think the startup amerage could be the culprit. 

      1. User avater
        johnnyd | Apr 14, 2003 08:46pm | #3

        another point might be that if you unplug the pump everytime you work on it, why does it need GF protection anyway? My understanding is that the GF protection is primarily to protect the USER from becoming a better ground than the EGC (or lack thereof) or neutral in case of a short in the chassis of a handheld power tool that is not double insulated...especially where the user would be located in or near water.

        Brings to mind the time I was shutting off the spigot to a watering trough with a pliers, leaning over an electric fence. Elbow grazed the barb wire.  Never did find those pliers.  GF protection wouldn't work there either...every time the fence would arc the least little bit, the circuit would shut down. High voltage low amps.

        Or a friends grandfather who was electrocuted (died) when he turned on a faulty circular saw while he was standing in water on a driveway.  That was before they had GF protection. (and double insulated tools)

        Chime in here, electricians...

        1. Stray | Apr 14, 2003 11:03pm | #5

          "another point might be that if you unplug the pump everytime you work on it, why does it need GF protection anyway?"

          Well, the pump is pretty much left plugged in all the time.  The pond doesn't hold water real well, plus it pumps it up to a nice little rock "waterfall" that the wife like to look at.  Hence the easy toggle switch on and off instead of crawling through the bushes to plug/unplug it.  I suppose it should be hard wired in, but maybe next week....

          The GFCI is also up near the pond, and convenient for hedge trimmers, etc... to be plugged into, which is also right next to the pond.  If the trimmers fell in the pond, I'd fry all those nice little frogs that were keeping me awake last night.   Hmmm that gives me an idea....  ;~)

          1. User avater
            johnnyd | Apr 14, 2003 11:15pm | #6

            I suppose you could leave the GFCI in and wire the toggle from the non-protected side of the recepticle..then you would still be protected from the hedge trimmers.

          2. Stray | Apr 15, 2003 04:17am | #8

            "I suppose you could leave the GFCI in and wire the toggle from the non-protected side of the recepticle."

            I'm with you on that...

            I was thinking about doing the same thing.  The outlet by the creek wouldn't be protected, but at least the outlet by the pond (where the 2 year old plays) would be.

  2. MojoMan | Apr 14, 2003 09:32pm | #4

    I once had the same problem: new pump, new GFCI outlet, and the pump tripped it every time.

    Al Mollitor, Sharon MA

  3. booch | Apr 14, 2003 11:37pm | #7

    Get the pump tested by some source or just buy another if you are suspicious. They are cheap enough.

    I'd say the weakest link is the toggle switch. That 2 dollar POS is not waterproof. That could be your leak to ground. Waterproof toggles are dearly expensive. Real waterproof switches like those on military vehicles and other outdoor equipment start at 20 clams each in large quantities. Crack the old one open and see how waterproof it is.

    GFI's measure power to and from the appliance. If there is a path the current can leak, it will show conductivity. Set your VOM on the finest setting you have and ring out the black conductor to the pump to the case of the pump. Do the same for the other components. Since this is outdoors, the wind can drive rain into the body of the components. Possibly the Gfci is compromised by the moisture inside the body of the GFCI. After all there are printed circuit boards inside it.

    BTW is this GFCI of the 3 dollar specials on sale now? If so, it is last years model. The new ones, made this year, are lots more expensive because thay have more features, (I'm stretching to remember but I think conformal coating of the PCB is part of the change) The new ones have some environmental ratings the old style did not have.

    Jack of all trades and master of none - you got a problem with that?
    1. Stray | Apr 15, 2003 04:38am | #9

      "Get the pump tested by some source"

      What kind of outfit to look for?  Local electrician?

      "I'd say the weakest link is the toggle switch. That 2 dollar POS is not waterproof."

      Toggle switch was brand new out of the box as well...

      "Set your VOM on the finest setting you have and ring out the black conductor to the pump to the case of the pump. Do the same for the other components. Since this is outdoors, the wind can drive rain into the body of the components. Possibly the Gfci is compromised by the moisture inside the body of the GFCI."

      Don't have a VOM (But always wanted an excuse to get one).  Wind driven rain isn't an issue fo the pump, since it's sitting at the bottom of the creek.  Not an issue for the GFCI, Toggle, or regualr outlet, since they were all new out of the box. Plus all tested fine before the pump was plugged into the circuit.

      "BTW is this GFCI of the 3 dollar specials on sale now?"

      Not on sale, and actually I paid extra for the 20 amp model (instead of the 15amp rated one you'd typically put in a bathroom).

      I'm leaning to the startup amperage being the culprit, but if the GFCI is rated for 20 amps...is it conceivable that the sump pump could really be exceeding that on startup?

      1. junkhound | Apr 15, 2003 05:43am | #11

        "Don't have a VOM But always wanted an excuse to get one"

        Heck, you can get a chinese VOM off the internet (e.g. Harbor freight) for < $5) which I often do as I forget and leave a bunch (one at a time of course)  lying around someplace.

        BTW, I have zero GFIs in own house (except have a bunch in parts bins in basement), plus have 'heard' even the space station disabled the GFI equivalents due to false/nuisnace trips. Worked in 70's/80's with a guy (Tom Sussman) that was on the NEC panel for GFI, heard from him that the big push was primarily due to mfgs wanting to sell new stuff. Technical literature is split (as one would expect) on the long term benefits of those decisions.

        Signed: A not really so old boy who still tests 120 Vac circuits with fingers, and 9 V batteries with tongue; but, hope to never get across 3kV ever again though!!!!

        1. 4Lorn1 | Apr 15, 2003 07:49am | #13

          Early 70s GFIs didn't have much of a track record. Some of the designs didn't work all that well. By the late 70s, I got these points from a local inspector who has tracked these figures for decades, statistical evidence started to mount. By the 80s all of the studies, many by insurance companies, of numbers of people shocked or electrocuted clearly showed that at a minimum several thousand people have had their lives saved by GFIs.

          Bumping the radio into the tub with an unwanted wife was a popular plot theme in the 50s. Do it now and your loving wife will likely step out and beat you down with a loofa.

          As with any technology there are limitations. Some things you just don't want to trip off. Freezers and fire pumps for example. Most people who have problems with them are using worn out equipment or do not know how to install them. The only power cords that have problems have nicks or tears in their insulation. These should be retired.

          I was part of a safety program on a large job site. Every week I would inspect all the cords used. At that time they allowed me to shorten, cut out bad sections, and put on new cord caps. I also checked all the tools for proper grounding, faults and intact double insulation.

          In my experience most carpenters stop using a cord only when it cannot be made to run a tool any more. I have seen copper exposed a half dozen places on a 100' cord and a female cord cap that would only run a saw if you twisted it a bit. The carpenter said "It's fine".

          Never mind that it makes the hair stand up in the rain. And might kill you one day. LOL. I used to have to cut them into little pieces to keep them from wandering out of the trash. Carpenters were much happier after I talked the boss into letting me buy a case of 12/2 100' models. As soon as the new cords went out the nuisance tripping of the GFIs stopped. For the price of one serious accident you could buy crates full of cords and GFIs. Cheap insurance.

  4. 4Lorn1 | Apr 15, 2003 05:04am | #10

    The most probable problem is that the pump, being well used and old, has a slight leak in one or more seals. This combined with normal aging of the insulation of the motor windings can allow current to leak to ground. When the leaking current exceeds something close to 15 milliamperes the GFI trips.

    This can be tested, use great care, by disconnecting the ground connections to the circuit and spanning the gap with a meter. For current. This would confirm the functionality of the GFI and the leakage from the pump. If you are not familiar with the tools and techniques needed this is better carried out by an electrician.

    An alternative is to replace the existing GFI and see what happens. You could then isolate portions of the circuit and confirm what piece/s are causing the known good GFI to trip.

    I suspect that the pump is the problem. If it is a model worthy of messing with replacing the seals or rebuilding may be justified. A few times I have had luck opening up the pump, drying it out and resealing it with a rebuild kit or, if needed, silicon sealant, Form-a-gasket or similar.

    Shortening the cord a few inches allows a less worn portion of the cord to make a better seal. Sometimes it works. Other times not. Often you can squeeze out another year or so out of the pump. Seldom is it worth the trouble on anything less than a 1HP industrial model.

    The most common spot to leak is around where the cord goes into the pump body. Particularly if the cord is used to move the pump. Always use a rope rigged to keep some slack in the cord near the pump.

    Having a GFI in this situation is a good idea. Kids and animals like water. A shock with wet hands and standing in water is very dangerous. Be careful. Remember that having an electrician work on it is still cheaper than an ambulance ride.

    1. User avater
      BillHartmann | Apr 15, 2003 06:36pm | #15

      Another thought.

      He said that he tested the GFCI with one of the $3.95 testers. Those use neon light to show that power is on the right conbination of pins and also has a small load (from hot to ground) to test the tripping feature.

      A miswired GFCI can trip with any "load". But I supspect that the test light do draw enough current to trip a miswired GFCI.

      One way of isolating this problem would be to put the pump in the bath tub and power it off the bath GFCI. If that one trips then it is the pump.

      1. Stray | Apr 15, 2003 08:43pm | #16

        Bill,

        Good idea,  I can certainly try that. 

        If the pump trips it in the bathroom however, I'm still not sure if it's faulty wireing or if the pump's startup amps trip the GFCI.  Do you buy into the theory that this could be the cause?

        Thanks,

        Erik

        1. User avater
          BillHartmann | Apr 15, 2003 09:19pm | #17

          "I'm still not sure if it's faulty wireing or if the pump's startup amps trip the GFCI. Do you buy into the theory that this could be the cause?"

          Not exactly.

          A GFCI is NOT AN OVERLOAD DEVICE (unless of course it is part of a breaker). Many people think that high current will trip them. That is not true.

          They measure unbalanced currents. And when the motor is starting it draws lot of current so the initial surge might cause some problems with unbalanced currents. But I don't think so and have not really tried to study it or have much experience with operating motors through them.

          I have seen refigerators easly trip the GFCI, but I don't think that has anything to do with the fact that it has motor, but rather the design of the insulation around the heaters and all of the moisture from defrost cycles.

        2. booch | Apr 16, 2003 12:24am | #18

          I don't think the tripping of the gfi is initiated with overcurrent. I run my Tablesaw in the garage off of a 15 A two pole GFI breaker (QO) never a problem.

          You don't have a ground circuit on this pump setup separate from the ground from the GFI do you? The GFI is looking for all current to travel thru it. Any downstream errant ground path will cause it to trip.Jack of all trades and master of none - you got a problem with that?

          1. Stray | Apr 16, 2003 06:13am | #19

            "You don't have a ground circuit on this pump setup separate from the ground from the GFI do you?"

            Nope, no bootleg grounds here...  Just the regular ground wire from panel...thru GFCI...to downline outlet...to pump's grounded plug.

            Thanks,

            Erik

      2. 4Lorn1 | Apr 16, 2003 06:45am | #20

        I use a wiggy for testing. It is handy and while it does not calibrate the leakage needed to trip the GFI it does test the basic function. I used to use a resister, calculated to provide a 10 ma at 120v, soldered into a set of leads as a go/no go test. I would have to dig to find it.

        Some contractors use a tester that is recalibrated regularly, about $600, to test GFIs. They look really sophisticated and the calibration certificate aids in credibility but many of these still use a simple resistor to do what I'm doing with my home made tester, $10 for the leads and resistor, does. A few are a bit more sophisticated.

        The use of the GFI in the bathroom, or kitchen, should work. I wouldn't have thought of that. Carrying a groady pump through the house and messing up a nice white tub usually doesn't go over with most HOs. You might try using the GFI that protects the exterior receptacle, assuming it's not the one your having problems with, and use a bucket.

        1. User avater
          BillHartmann | Apr 16, 2003 07:05pm | #21

          I was not concerned about testing the GFCI in the normal operating mode. Other then measuring the time a simple resistor to draw 6(?) ma should be OK.

          While I don't think that this is the case there are number of times wheere GFCI wire "appears ok", but as soon as a load is pluged in the GFCI trips. For example is a pair of GFCI recpts are used to try to protect downstream recpts on a multiwire circuit.

          That is where the little $3.95 tester will show that it is wired correctly and will trip when the test button is pressed. But the current drawn by the neon indicators might not be enough to show that the GFCI is miswired so that it will trip on any load.

          But pluging in a 100 watt light should do the trick. If it trips then the problem is in the GFCI wiring.

  5. fireball | Apr 15, 2003 06:49am | #12

    Stray,

     I think I'd be suprised if the pump DIDN'T trip a GFCI receptacle.Whenever you have wet cords they're very likely to trip ground fault circuits.When we're doing a commercial building and the roof deck is on ,but the rubber roof isn't on yet,a rainy day becomes wetter inside than outside.All the extension cords laying on wet concrete constantly trip the GFCI receptacles.If we don't dick around tying them up and eliminating the weakest insulated cords,we don't get anything done,because we're going back and forth to the temporary board every 5 minutes.

    I think the only exception for not protecting outdoor receptacles is for snow melting equipment in residential applications.There they want you to use single receptacles that no one can plug anything else into.We do elevator shaft sump pump receptacles that way.And there it CAN'T be GFCI protected so, go figure...

  6. User avater
    IMERC | Apr 15, 2003 08:01am | #14

    Suspect the GFI recept. They give up the ghost just because the can. those cheap testers are natorious for not wrking as advertised.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Mortar for Old Masonry

Old masonry may look tough, but the wrong mortar can destroy it—here's how to choose the right mix for lasting repairs.

Featured Video

Micro-Adjust Deck-Baluster Spacing for an Eye-Deceiving Layout

No math, no measuring—just a simple jig made from an elastic band is all you need to lay out a good-looking deck railing.

Related Stories

  • Fire-Resistant Landscaping and Home Design Details
  • A New Approach to Foundations
  • A Closer Look at Smart Water-Leak Detection Systems
  • Guest Suite With a Garden House

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data