Ground Rod

| Posted in General Discussion on March 15, 2002 08:31am

*
The ground rod for my house sits in about 1’6″ of soil over bedrock. Is this really grounded? Should I drill and grout the rod into the rock? Or should I add additional grounds? Thanks.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. jim_l | Mar 12, 2002 04:32pm | #1

    *
    I'm not qualified to answer, but I had a similar problem and I laid 3 eight foot ground rods horizontally in different directions as deep as I could.
    I'll also be interested to hear from the electricians reading this board.
    jim

    1. Jeff_Clarke_ | Mar 12, 2002 05:03pm | #2

      *... I suspect they'll tell you that ground rods aren't good for much. Grouting into rock doesn't help since it won't necessarily increase moisture (decreasing resistance). There is a carbon-based backfill material that decreases resistance in difficult (rocky) soils, though.Jeff

      1. George_W._Carpenter | Mar 12, 2002 08:31pm | #3

        *Jeff, currently (ha ha) facing the same problem.The revision to the NEC has three solutions.I'm doing all three, in preparation for the new regulations.1) A ground rod, 8 foot, driven.2) A 20 foot minimum of correct sized ground wire (100A = #6) placed horizontally, in my case under the footings, and bonded to the ground rod.3) Bonding to the copper piped water supply at the point of entry to the residence, then bonding that point to the ground rod/ground wire/panel.GWC

        1. xJohn_Sprung | Mar 12, 2002 11:12pm | #4

          *For tough situations like this where you're up against rock everywhere, the NEC does allow laying copper pipe in trenches to create horizontal ground rods. A really good electrician will have the special test equipment to measure the resistance of your grounding arrangements. If you find one in your area, he may have some experience with similar problem lots. It could be about $100 to get a test and some good advice.-- J.S.

          1. splintergroupie_ | Mar 12, 2002 11:29pm | #5

            *My electrical inspector recommended i ground to the rebar in the footing. This sounded like a great way to get a lot of conductor in contact with a lot of dirt, and quickly.

          2. Wayne_Law | Mar 12, 2002 11:44pm | #6

            *Like the others said, you are probably not grounded properly now. You have to get the conductors in contact with soil that is damp year round. So, as you are looking for a place to run horizontal ground, pick the lowest, wettest spot you can. I don't know your climate, but some suggestions are: put at least a portion of the conductors in the area near your downspouts (assuming you get rain in your area), run the conductors some distance from the house to a low & wet area, or use one of the ground-enhancing chemicals made especially for this purpose. These are poured in the trench when the conductor is installed.Grounding to the rebar is generally not done because the concrete is usually a poorer conductor than if you burried a long enough conductor in the dirt. Also, if you get a lightning strike you could shatter the concrete.It's worth the trouble to get a good ground. For equipment such as electronic surge suppression to work well the ground had to be sound.

          3. Jeff_Clarke_ | Mar 13, 2002 12:31am | #7

            *Grounding to the rebar (bonding the rebar to the building ground) is an NEC requirement in the new code.Jeff

          4. IanDGilham_ | Mar 13, 2002 01:05am | #8

            *I lived for a time in an area of shingle sub-soil, where an effective ground was very difficult and the code requirement there was for a buried 'mat' of copper wire.

          5. splintergroupie_ | Mar 13, 2002 01:23am | #9

            *http://www.pupman.com/listarchives/1995/july/msg00016.htmlSince you are building your house, you have an opportunity now to install a *Ufer ground*. Mr. Ufer developed this technique during WWII for army ammo bunkers. The NEC approves its use for commercial and home grounding systems. In essence, a Ufer ground is just rebar in concrete. When the builder is preparing to pour your slab, make sure all the rebar in the slab is bonded together, either cadwelded or mechanically clamped, before the pour. And make sure to leave a convienent attachment point exposed. A rule of thumb for a Ufer ground is that it takes about 20 feet of 0.5 inch rebar to absorb 8,000 amperes of surge. More is better. The rebar should be embedded in at least 4 inches of concrete.The way a Ufer ground works is through two paths. First it forms a large capacitance to Earth. This is an excellent RF coupling. Second, concrete's ions generally are more conductive than native soils, so you have a large number of virtual resistors in parallel connected to Earth that offer a lower resistance than would a smaller collection of driven rods. Earth is actually a lousy conductor. Most currents are dissipated through Earth by capacitive coupling and arcing from soil grain to soil grain. Concrete is a better conductor since the grains are tightly bound together.Ufer grounds and ground rods.

          6. CaseyR_ | Mar 13, 2002 01:26am | #10

            *Grounding to footing rebar is the preferred method of grounding in my county even though, as far as I know, they haven't adopted the new code yet. The rebar needs to be bare or zinc coated and at least 20 feet in length. Copper wire can also be encased in concrete if it is not smaller than No.4 and is at least 20 feet in length. An alternative grounding electrode can also be a "ground ring" of not less than No. 2 copper wire that surrounds the building in direct contact with the earth and is not less than 20 ft in length. Plate grounding electrodes are also described in the code as being at least 2 sq.ft. in direct contact with the earth and of a prescribed thickness depending upon the metal used. The device xJohn mentions is usually referred to as a "megger" (as in megohms). The resistance between two ground rods a set distance apart (20 meters?) is measured. An acceptable ground is not supposed to exceed 25 ohms. If the resistance is greater than 25ohms, then multiple grounding electrodes are to be used.There are other types of grounding systems including electrolytic ground rods in which an electrolyte is used which seeps into the ground to lower the ground resistance. I have no first hand experience with this and I would assume that these are only used in critical industrial situations. As my text book says: "So far, the resistance to ground of the grounding electrode at a residence has not been that big a jproblem. It may become one in the near future as the "Smart House" becomes more and more a reality..." Electrical Grounding, 5th Edition Ronald P. O'Riley, 1999, p55. Of course, I am not a licensed electrician, so discount all of this information accordingly...

          7. bungalow_jeff | Mar 13, 2002 06:42am | #11

            *Thanks for the replies. Since this is a 100 year old house, we can eliminate rebar in the foundation as an option. I think the copper ground pipe in a trench is my best option to explore. When we had the service upgraded to 200A the electricians complained when the inspector insisted on replacing the ground connection to the water line. I'm glad they sucked it up and made the connection. The idea popped in my head at work. I am designing a rail tunnel with a traction power substation over the track area. The power guys want to connect ground plates in the substation down to a wire mat under the box, connected to rods drilled to the rock. They were very adamant about grounding down to the rock, which is why I thought maybe a long rod drilled into the rock would work. Mainly, it made me realize that spring gardening can practically kick the rod out of the shallow soil.

          8. bake_ | Mar 13, 2002 07:44am | #12

            *We are allowed to use ground plates now, they are approx 2'x 2' galvanized plates you bury 3' deep.cheersbake

          9. bungalow_jeff | Mar 13, 2002 03:17pm | #13

            *That's another good option. I'll probably stick with the long pipe since I need to trench along the foundation to add drainage.

          10. George_W._Carpenter | Mar 13, 2002 05:18pm | #14

            *Jeff, if you can, go with two 10 ft. sections of copper pipe, bondyour ground wire to both with bronze "bugs". This should provide the 20 ft min. of horizontal conductor, and be relatively corrosion resistant.Avoid copper to steel/iron connections.-gwc

          11. bungalow_jeff | Mar 13, 2002 07:54pm | #15

            *Thanks GW,Now I look forward to reading the responses to the lightning rod post by David Lechel.

          12. Erich_Muschinske | Mar 14, 2002 08:05am | #16

            *My military electrical installation manuals talk about putting in ground systems on rocky mountaintops. The conditions are thin soil over bedrock. The usual way of getting a good ground for lightning protection is to lay out a ground grid around the building. As a previous post said, the object is to get less than 25 ohms, 10 ohms is the desired maximum. This is usually measured using a Vibraground, via the fall of potential method. An electrician that builds radio sites would probably have the equipment to do the measurement. Also your local phone or power utilities will also have the equipment.

          13. Steve_77 | Mar 15, 2002 02:28am | #17

            *Checkout Feb.94 , JLC. (Not a answer to the question , but useful )!

          14. 4Lorn | Mar 15, 2002 08:31pm | #18

            *An electrical contractor from your local area, especially one that does commercial grounding, should be able to help you out. Grids are good but if your location is elevated and the soil doesn't hold moisture they can be a waste of money. There are chemicals that can be added around the rod or in a hollow, typically copper pipe, ground rod. These chemicals are selected to both absorb water and help with conduction much the way common salt , the original chemical used, would. Unfortunatly salt can be toxic and corrosive in the amounts used. Grounding to the rebar in a slab or footing does much the same thing as concrete tends to absorb and hold water even in relatively dry conditions. But even this doesn't work well in extremely dry locations. In difficult locations and where it is critical to have low grounding resistance. I have seen a well sunk for the purpose of grounding. Of course a steel pipe sunk several hundred feet to get to the ground water level, the mother of most good grounding, doesn't come cheap.If it is just a home your grounding the actual ground resistance might not be important. Lightning protection is largely a matter of relative resistances. The lightning want to go to ground and will take the easiest way. Making sure that your grounding system is substantially better grounded than the stuff you wish to preserve is more important than the actual ground resistance. Greatly simplified; if your metal roof is 40 ohms and the surface of the earth around your house is 30 ohms and your lightning rod and ground rod is 25 ohms the lightning will tend to strike the lightning rod. Talk to a local contractor. The one you want will be familiar with your soil conditions and should be able to give you sound advice and some options at a nominal price.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data