Grounding Rod

kazm | Posted in General Discussion on July 9, 2007 04:42am

What size grounding rod should be used for a 200 amp service entrance? 1/2 or 5/8 copper clad?

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. MSA1 | Jul 09, 2007 05:14am | #1

    I've never heard that question before. I think I always use 5/8". I dont know why though.

  2. DanH | Jul 09, 2007 05:47am | #2

    You don't use a rod, you use a "system". The rod may be part of it.

    So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin
    1. kazm | Jul 09, 2007 06:00am | #3

      We are planning on several ground rods connected with #4 copper. Plus the "ufer" attached to the footing which I haven't quite figured out yet. Our local supplier who the electric company said would get us all the right supplies for a new service entrance supplied us with about 9/16 ground rods. We read in the code that 5/8 is required. Is the local supplier doing everything under code?????

      1. User avater
        BillHartmann | Jul 09, 2007 08:39am | #5

        If you have a ufer ground then code does not require a ground rod.However, if you have metalic water supply lines, with the underground part at least 10 ft long then it must also be used as a ground electrode.However, local amendments and/or the power company rules might be different.Or they might be handling out old sheets that show ground rods because a ufer was not used..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

  3. User avater
    Luka | Jul 09, 2007 08:23am | #4

    You don't say where you are. Fill out that profile !

    Here, when I put in 200 amp service the grounding system required was two, ten foot 5/8 common rebar. 6 feet apart from each other. And a separate 1/4" solid copper run to each from the ground buss.

    I made it twelve foot rebars. And sunk all but about 4 inches of each.


    Yeh... That'll work.

    1. kazm | Jul 09, 2007 04:53pm | #6

      I am in Wyoming. We are sometimes about 20 years behind the rest of the country. The grounding rods are required at the service entrance. However we are told the local inspector will not pass inspection without the connection to the foundation rebar.

      1. User avater
        BillHartmann | Jul 09, 2007 05:53pm | #7

        Here is the requirement (2005 NEC) for the ufer."(3) Concrete-Encased Electrode An electrode encased by at least 50 mm (2 in.) of
        concrete, located within and near the bottom of a concrete foundation or footing that is in
        direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or
        zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of
        not less than 13 mm ( 1/ 2 in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare
        copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be
        bonded together by the usual steel tie wires or other effective means."This is some commentary about the ufer."Section 250.50 introduces the important concept of a ``grounding electrode system,'' in
        which all electrodes are bonded together, as illustrated in Exhibit 250.21. Rather than
        total reliance on a single grounding electrode to perform its function over the life of the
        electrical installation, the NEC encourages the formation of a system of electrodes
        ``that are present at each building or structure served.'' There is no doubt that building a
        system of electrodes adds a level of reliability and helps ensure system performance
        over a long period of time.
        This section was revised for the 2005 Code to clearly require the inclusion of a
        concrete-encased electrode, described in 250.52(A)(3), in the grounding electrode
        system for buildings or structures having a concrete footing or foundation with not less
        than 20 ft of surface area in direct contact with the earth. This requirement applies to
        all buildings and structures with a foundation and/or footing having 20 ft or more of 1/
        2 in. or greater electrically conductive reinforcing steel or 20 ft or more of bare copper
        not smaller than 4 AWG. However, an exception does exempt existing buildings and
        structures where access to the concrete-encased electrode would involve some type of
        demolition or similar activity that would disturb the existing construction. Because the
        installation of the footings and foundation is one of the first elements of a construction
        project and in most cases has long been completed by the time the electric service is
        installed, this revised text necessitates an awareness and coordinated effort on the part
        of designers and the construction trades in making sure that the concrete-encased
        electrode is incorporated into the grounding electrode system."The picture shows a ufer ground.I am also concerned about how to keep the ground electrode conductor safe before getting the foundation and walls finished. If this is a slab and/or shallow footings it would not be that bad.But if you have basement or crwalsapce construction with footing 4-8 ft underground then I think that it woudl be difficult for keep the conductor protected.What I would want to do is to use tied up turned rebar. Then tie that to the rebar in the foundation. And mount a box in the foundation so that when the forms are stripped you have access to the rebar and you can make connections afterwards.But I would pass that by the inspector first.Here is the ground rod requirements."(5) Rod and Pipe Electrodes Rod and pipe electrodes shall not be less than 2.5 m (8 ft)
        in length and shall consist of the following materials.
        (a) Electrodes of pipe or conduit shall not be smaller than metric designator 21 (trade
        size 3/ 4) and, where of iron or steel, shall have the outer surface galvanized or
        otherwise metal-coated for corrosion protection.
        (b) Electrodes of rods of iron or steel shall be at least 15.87 mm ( 5/ 8 in.) in diameter.
        Stainless steel rods less than 16 mm ( 5/ 8 in.) in diameter, nonferrous rods, or
        their equivalent shall be listed and shall not be less than 13 mm ( 1/ 2 in.) in
        diameter.""250.53 Grounding Electrode System Installation
        FPN:See 547.9 and 547.10 for special grounding and bonding requirements for agricultural
        buildings.
        (A) Rod, Pipe, and Plate Electrodes Where practicable, rod, pipe, and plate electrodes
        shall be embedded below permanent moisture level. Rod, pipe, and plate electrodes shall
        be free from nonconductive coatings such as paint or enamel.
        (B) Electrode Spacing Where more than one of the electrodes of the type specified in
        250.52(A)(5) or (A)(6) are used, each electrode of one grounding system (including that
        used for air terminals) shall not be less than 1.83 m (6 ft) from any other electrode of
        another grounding system. Two or more grounding electrodes that are effectively bonded
        together shall be considered a single grounding electrode system.""(G) Rod and Pipe Electrodes The electrode shall be installed such that at least 2.44 m (8
        ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m
        (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an
        oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is
        encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in
        a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be
        flush with or below ground level unless the aboveground end and the grounding electrode
        conductor attachment are protected against physical damage as specified in 250.10.""250.56 Resistance of Rod, Pipe, and Plate Electrodes
        A single electrode consisting of a rod, pipe, or plate that does not have a resistance to
        ground of 25 ohms or less shall be augmented by one additional electrode of any of the
        types specified by 250.52(A)(2) through (A)(7). Where multiple rod, pipe, or plate
        electrodes are installed to meet the requirements of this section, they shall not be less than
        1.8 m (6 ft) apart.
        FPN: The paralleling efficiency of rods longer than 2.5 m (8 ft) is improved by spacing greater
        than 1.8 m (6 ft)."And a drawing show the orientation of ground rods..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. kazm | Jul 09, 2007 06:53pm | #8

          This isn't the first time I have received needed information from you. Thanks. This is a do it yourself project my husband and I are working on but we are detailed oriented and know how to read and comprehend. We will do some studying on the information you forwarded. We have received valuable comments and information from all the folks at Breaktime and I am sure there will be other questions as we go along.

  4. renosteinke | Jul 09, 2007 11:28pm | #9

    The size of the service has absolutely nothing to do with the size of the ground rod.

    Of greater concern to you are A) your local codes B) local soil conditions and C) how difficult it will be to drive the rod.

    Around here, we are required to use a 10' rod. Since the ground is quite rocky, this means a 5/8 copper clad steel rod is preferred.

    1. FastEddie | Jul 10, 2007 12:35am | #10

      Just finished a bank branch in Roanoke.  Freestanding 4300 sf building.  We used 3 @ 20 ft 5/8" copper ground rods, spaced ina triangle with 30 ft sides, connected by cad welded 4/0 bare cable.  That should do the trick."Put your creed in your deed."   Emerson

      "When asked if you can do something, tell'em "Why certainly I can", then get busy and find a way to do it."  T. Roosevelt

      1. User avater
        BillHartmann | Jul 10, 2007 12:43am | #11

        Why no ufer.Should be lots of footings for a building like that..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

      2. User avater
        maddog3 | Jul 10, 2007 12:45am | #12

        those "deltas" are pretty much standard on commercial work around here heavy industries bond every beam with 500MCM ....

        .

        .

        ., wer ist jetzt der Idiot ?

  5. AzDiscDog | Jul 10, 2007 01:39am | #13

    When I re-did the service on my house, I used 2 5/8 copper clad rods. Mostly I wanted the thicker rods to make it easier to drive them. Price difference is minimal, or at least it was for me.

    Spaced 'em 6' apart and tied them with #4 cu, if I recall correctly. Also tied it back to the house's water supply (mostly to make the inspector happy).

    They need to be buried 12" under as well. I ran #4 in plastic conduit between the two rods in case someone ever digs in that area in the future.

    Glen

    1. brownbagg | Jul 10, 2007 02:05am | #14

      I install three 5/8 rods ten feet apart. I failed my inspection by my wally world electrical inspector because I had more than one rod. so I drove the other two below ground. and passed

      1. User avater
        SamT | Jul 10, 2007 04:49am | #15

        failed my inspection by my wally world electrical inspector because I had more than one rodHenh! Henh! henh! Idjits.SamT

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Summit 2025 — Design, Build, Business

Join some of the most experienced and recognized building professionals for two days of presentations, panel discussions, networking, and more.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Podcast Episode 691: Replacing Vinyl Siding, Sloping Concrete, and Flat vs. Pitched Roofs
  • FHB Podcast Segment: Roofing on Commercial vs. Residential Buildings
  • Preservation and Renewal for a Classic
  • A Postwar Comeback

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data