Heat Pump/Heat Strips Problem?

Nichols747 | Posted in Energy, Heating & Insulation on January 27, 2007 12:50pm

All,

I have a Goodman MFG ARUF061-00A-1B Airhandler with the optional HKR-20C Heat Strips installed in new construction, 2ksf home. 

When running the T-stat in Emergency mode, to activate the heat strips (trying to heat up the house from outside cold temps), the unit will start operation, produce heat, and run for a few hours.  When I come back to check on things hours later, the unit has shut down, and I find that one of the factory installed 60amp breakers that are incorporated into the heat strip unit has tripped. 

When running the unit in Heat mode (running the heat pump function), it will operate constantly without interruption.  The problem is, that with the cold temps, the unit is taking forever to heat the house.  (4 degrees F in 12 hours overnight)

The electrician is going to check his work tomorrow, but the HVAC installer feels that it is not a problem with the unit – he believes that the unit is not getting enough power, causing the breaker to trip.  I know little about electricity, but this doesn’t make sense to me.  Also, there are matching 60amp breakers at the electrical panel, which are not tripping. 

Am I wrong – is a lack of power the possible culprit?  Any other ideas to check out would be greatly appreciated!

Thanks,

AN

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    BillHartmann | Jan 27, 2007 01:30am | #1

    That appears to be a 20 kw heater. And it draws 83.3 amps.

    I don't remember the details of electric heat, but I *think* that you are limited to 60 amps per feed. And you I *think* that you need 125% higher than the load for the feeders and breakers.

    If those I remember correctly then you will need two 55 or 60 amp circuits. And there should be some staging control on the heaters to allow different banks to be feed by separate circuits.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. Nichols747 | Jan 27, 2007 02:23am | #2

      All,

      I believe that the problem has been solved, the wire at the Breaker was not tightedned fully, now is, will see if it trips again.

      Bill, sorry I wan't clear, there are two 60amp breakers going in,  one of them was tripping - my bad.

      I guess that I should change this from a technical Heat Pump thread to a "check the simple connections/solutions" thread.  Hopefully, our problem has been solved.

       

      Thanks again, AN

      1. Nichols747 | Jan 28, 2007 02:56am | #3

        It would appear that I was too hasty to dismiss this problem.  45 minutes after reactivation, the breaker tripped again. 

        The electrician checked his work today, and here is some more information:

        He switched the feeds going into the two 60 amp breakers, ran the system, and the same breaker tripped.

        He says that the only evident difference between the two breakers is that the non-tripping one feeds half of the heat strips, and the tripping one feeds half of the heat strips as well as a circuit board which appears to control the system (powers the airhandler). 

        While he wasn't watching it when it tripped, that side of the setup was drawing 43amps and 245volts for about 35 minutes.

        Any thoughts?I think that this will require a service tech visit - would anyone disagree with me thinking that this must be a problem with the HVAC side, rather than the electrical? Thanks,

        AN

        1. User avater
          BillHartmann | Jan 28, 2007 03:52am | #4

          "While he wasn't watching it when it tripped, that side of the setup was drawing 43amps and 245volts for about 35 minutes."Unless there was a large spike them the problem is in the breakers/panel."He switched the feeds going into the two 60 amp breakers, ran the system, and the same breaker tripped."Switching the LOADS would be much more informative.Unless there is some surge in the load (which switching loads would show) the problem is either a weak breaker or bad connections which causes extra heating on the breakers.The electrican should have checked for that when it tripped..
          .
          A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          1. Nichols747 | Jan 28, 2007 04:03am | #5

            Right about switching the loads, I think that he didn't want to do that, since the breakers are part of a preassembled "plug-in" heat strip set, and he was hesitant to mess with it.  I think that he was concerned about warranty/returnabillity.

            He was going to switch one of the other Siemens 60amp breakers in to see if that one tripped, but the Siemens breakers in the heat strips are dissimilar to the ones in the panel.  Then he was going to switch the breaker positions (tripping to non-tripping) to see if the failure switched, but the screws seem to be covered with some sort of seal/glue.  Another concern about voiding the warranty.

            I think that I need to get an HVAC service tech out - evidently my installer is not a service tech. 

            Thanks for your input Bill, AN

          2. Marc | Jan 28, 2007 05:07am | #6

            It's unusual (especially for a Siemens) but not impossible for the breaker to be defective tripping at a lower current than rated. Convince the HVAC guy to replace the breaker. Good luck

  2. DanH | Jan 28, 2007 06:07am | #7

    It sounds like something's miswired, or the heat strip or breaker is defective. The total load on the breaker should be well under it's rating, so the breaker would only trip if the heat strip shorts out.

    So possibilities:

    1) There's more load on the breaker than just the heat strip -- compressor load is on it and that's causing an overcurrent, eg.

    2) The heat strip is shorting out internally. Not that unlikely, as resistance heat elements move quite a bit as they get hot, and the element could buckle or some such and short out.

    3) The breaker is getting warm and tripping, due either to a bad connection in or at the breaker, or due to heat from the heater elments getting to the breaker, possibly because a cover is missing or misinstalled.

    A pure resistance element will not draw more current due to low voltage -- it will draw less as voltage is reduced. So low voltage would only be a problem if the compressor or some other motor load is also on the breaker.

    So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin
    1. Nichols747 | Jan 28, 2007 07:36am | #8

      Thanks for the pointing me in the right direction(s).

      The breaker that is tripping is the one which powers the air handler "Squirrel Cage"/fan, which will run for days as long as the heat strips are not on.

      It is mounted (from the manufacturer) on the heat strip kit, though not on the metal plate oposite the strips, it does get warm, and will not reset for about fifteen minutes.  After that, it resets just fine. 

      Thanks again, any more ideas are appreciated.

       

      Andrew

      1. ponytl | Jan 28, 2007 08:21am | #9

        any time i've had a problem with a goodman unit... their 1-800 tech  people walked me thru every test & function and always came up with an answer on the phone... arranged for replacement parts local for me to pick up... or sent em out next day...

        i can't say a bad thing about em...

        p

    2. Nichols747 | Jan 28, 2007 10:39pm | #13

      DanH,

      The outside unit (Compressor?) is on a seperate 50 amp breaker, seems to run fine when the system wants it to.

      In regards to the breaker heating up from the heat coils, when it trips, it is warm to touch, but not at all uncomfortable to touch.  Could this be enough to cause the failure? Any ideas on how to isolate the breakers? (they come preattached to the heat strip unit)

      Sure apppreciate the information,

      Andrew

      1. User avater
        BillHartmann | Jan 28, 2007 10:53pm | #14

        The question is the breaker generating the heat because of problems in the breaker/connection, is it normal heat, is it heat from the heating elements.What is the tempature of this breaker verse the other one when both are drawing current.I am assuming that the heating elements are staged by the thermostat? or by time? you want to have both running and then see how hot the two get.THERE IS NOTHING IN THE ELECTRICAL SUPPLY THAT COULD BE CAUSING THESE SYSMPTOMS.Also that the breaker can't be reset for 15 minutes certainly indicates that the "breaker" is getting way too hot..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. Nichols747 | Jan 29, 2007 12:29am | #15

          Bill,

          Good point, the non-tripping (good) breaker is next to, but closer to the heat strips.  They are the same temp to touch, which is the same temp as the rest of the components/metal in that area. 

          Thanks for the good info, I guess I need to the the General Contractor to get this resolved with the HVAC guy/a service rep or tech.

          Sounds like I may not be the only person with this problem, hopefully I can get some resolution.  Andrew

  3. blutz | Jan 28, 2007 07:25pm | #10

    This is my first post as I am a interested LURKER but the subject is of concern to me as well. I have the same unit and my heat strips have cause the internal air handler breakers to fry on THREE occasions. I am currently on heat strip module #4 ($200 +/- a pop) every time I use emergency heat. I have even changed the thermostat to a simple mechanical unit to avoid any auto switch to emer. heat and use it only as normal heat pump. Installer blames everything but probable cause of faulty unit design.

    I have asked if Goodman has issued a field fix or bulletin regarding problem but no response. I wanted you to be aware that this is more than problem with your install or individual module but design flaw of some sort. 

    I hope some of you more talented and aggressive tradesmen will pursue this to some sort of conclusion. You guys are great to learn from and hope this will be one that strikes home for me as well.

    Lurking Bob 

     

    1. jesup | Jan 28, 2007 09:52pm | #11

      Go to HVAC-Talk.com; Goodman is not highly regarded if I remember. Cheap, though.

    2. Nichols747 | Jan 28, 2007 10:34pm | #12

      Bob, thanks for the info, I guess you haven't had any luck coming up with a solution eh?  I am working with an installer who is not a service tech, not sure if this is common, but he keeps pushing the discussion towards an electrician problem.  This doesn't seem to be the case. 

      Since you know what the strip kit looks like, can you confirm that you have the same failure:  Unit runs in emergency mode, running heatstrips, blowing hot air, for 30min-a couple of hours, then the breaker which runs half of the strips and powers the small circuit board and airhandler.  The entire unit is warm to the touch, and the breaker will not reset for about fifteen minutes, then is able to reset, and runs again the same. 

      Have you found a solution that works?  Is Goodman willing to warranty these problem kits? 

      Will go to HVACTalk to see if there is a solution or some more guidance. 

      Thanks All,Andrew

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

A Classic Paint Sprayer Gets a Thoughtful Refresh

The Titan Impact X 440 offers great coverage with minimal overspray.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Fine Homebuilding's Author Guidelines
  • Podcast Episode 693: Old-House Hazards, Building Larsen Trusses, AI in Construction
  • FHB Podcast Segment: Finding Hazardous Materials in a Fixer-Upper
  • A Classic Paint Sprayer Gets a Thoughtful Refresh

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data