HELP ! Electric AC and Electric Heat on at same time (strange: but huge electric bills too).

InventPeace | Posted in Energy, Heating & Insulation on June 25, 2011 12:15pm

I have unit that has all electric heat and air (10kw ).  I keep getting complaints from renters that the bills and deposits are high?

Heres that data fact finding: Took panel off furnace ac unit inside house:

Using Voltmeter:

1. When thermostat is set on  AC  and AC  is actually on and cooling, the heater elements still show voltage on all 4 elements (heat strips ). very strange!     This explains huge electric bills.

2.  I thought maybe the thermostat was bad or wired wrong: I actually took the thermostat off (hunter brand ez clip on/off type)  ; but amazingly all 4 heater elements still showed 167 volts each ac voltage (approx ) with AC on (air conditioner on)  and with the thermostat completely disconnected and in my hand??

I am thinking their is either a bad part in the unit OR someone wired in the thermostat wires inside the unit wrong to start with.

 This is a newer unit installed perhaps 5 years ago new (the guy who installed it was upon reflection a bit off I think, he left a 4-6″ gap around the plenum leading to super heated atitic air ; i had to hire someone else to shore up the gap so that the unit wouldn’t suck in the hot attic air; super negligent, I would be red faced if I did that. ).

     .  In the winter the AC does not seem to run when heat is on;   but in summer when AC is on, all 4 heater elements are showing 167 volts approx .?? 

As a temp solution we disconnected all 4 elements at the elements themselves individually (after  carefully marking which wire goes to what element)  and insulated (taped their ends ).  This means that the heater will not work at all under any circumstances, but the Air Cond still works fine, means we have to either solve theproblem or get used to rehooking the 4 heater elements up every winter and disconnecting them in the spring.

 Has anyone had this problem in the past? 

  One person had a similar problem and replaced the sequencer, but that only seemed to solve part of the problem:    He also said he completely disconnected the thermostat from the wall and all thermostat (24v ) wires were not connected to anything, BUT  the heater STILL  came on, and heated his house in the “mornings” of  summer months??  He said it was always on AC setting in all warm summer months. 

He finally ended up diconnecting 2 of the heater elements and putting the other 2 on a separate circuit breaker to the fuse box, that way he can make sure that “Heater” breaker is off in the summertime!    (in other words he is heating his house with only half power and he says thats works fine since he is in florida and its not excessively cold anyway).      Truth is stranger than fiction !  Strange , Strange, strange !

   Any help would be appreciated, we’d like to work correctly.

We thought about putting a special 4 pole single throw switch in near the furnac/AC unit closet,  to allow the users to be sure the furnace was completely off,  in the summer, and allow ez heat back on in the winter, 

Again any insight into the $$$ expensive problem would be appreciated. As said we know its not the thermostat because we unhooked it completely uninstalled, thus we think it has to be the unit itself. 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. DanH | Jun 25, 2011 04:09am | #1

    First off, how are you measuring the voltage on the heating coils?  Unless you're placing one voltmeter probe on one terminal of the coil and the other probe on the other terminal (vs measuring to ground or some other point) you're very possibly measuring "phantom voltage" of one sort or another.

    If that's not the problem, you need to hire someone who understands the controls. 

    1. InventPeace | Jun 25, 2011 08:02am | #2

      We did that already:

      We had an ac/heat guy out there to look for problems.. he missed the boat.   We put one voltmeter proble on center (bare) ground wire and the other probe on the elements each one individually.. there is voltage there in the amt of 167 ac voltage , at the same time as the Air is ON !  very strange..

      Before you answer thermostat , please read all the data collected and try to tell me in general what you think it might be.. this is the second one I've seen like this,, and the first one was not really solved but worked around.. makes me think that there is alot more out there bankrupting people (with the higher utility rates.).  

      We are wondering about electronic anything anymore with all the power surges, maybe a surge damaged the electronic board inside and is causing this problem.

      Sometimes! ;the Old Ways are the Best Ways.

      . IE FOR sure separate element breaker or manual switch to make sure the elements can never be on unless switch is on. 

       

      Any insight is appreciated!

      1. DanH | Jun 25, 2011 09:14am | #4

        If you measured to the bare ground wire, you measured wrong.

        I am wondering where you get 167V.  Is this building served by 3-phase power or some other setup that differs from the standard 120V/240V residential scheme??

        1. InventPeace | Jun 25, 2011 10:11am | #6

          3 questions

          I measured a regular outlet with the meter and got 125v just to check the voltmeter. 

          1.  Wondering if there were 110 one  terminal of element, and other 110v phase on other end of element,, how indeed do we get 167v to bare ground wire from one terminal of each element?  

            2.   Are the elements supposed to be 220v across both terminals of each element (110v to each end of each element to get 220v)

           3.  Or are the elements 110V, with one end of elements going to ground, (this was our thinking since it "looks" like one phase coming in feeds 2 elements,  and it 'looks' like  the other phase coming in feeds the other 2 elements .  Of course this is after first feeding into what looks like relays and a sequencer,  also there are light wire connections to electronic board inside.  In other words phase A goes to relay 1 and assoc wiring etc, while phase B goes to another relay and sequencer , it appears. 

          Would this then mean that each element is supposed to be 110v total across its own  terminals?  

          Any insight is appreciated.  

          1. DanH | Jun 25, 2011 10:21am | #7

            The elements are almost certainly 240V elements, with no center connection.  You would read 240V across the two terminals when the element is on, and zero volts when off.

            But look closely at the elements -- likely there is a sticker on them that gives the voltage rating.

            The only way I can think of offhand that you might get 167V is with an open neutral to the power line, but then you'd have light bulbs blowing right and left.

            (How many units in this apartment building?  How is the power fed in -- overhead or underground?  If overhead, how many individual wires are coming in?)

    2. InventPeace | Jun 25, 2011 08:43am | #3

      Again?

      Goodman Manufacturing  co. ELectric AIr/Heat inside unit upright unit,  with horiz fan on top of evaporator pyramid.   

      MODEL#  ARUF 3030 1BA    

      Ok. after re-reading your last post, you are saying there should be a 167vac 'phantom' voltage from ground to heater elements when AIr is on?  That we do not understand, we would think there should be zero voltage from ground to any part of the element. 

      FYI: There are 2 hot wires coming in from fuse box, one seems to run 2 elements the other runs the other 2 heat elements.  They tap off of these somewhere to run fan also. 

      The users manual (limited hookup diagrams) and no diagrams of actual heater element or sequencer or relay connections; 

         If you can help please do.    thanks.

      1. DanH | Jun 25, 2011 09:22am | #5

        Ok. after re-reading your last post, you are saying there should be a 167vac 'phantom' voltage from ground to heater elements when AIr is on?  That we do not understand, we would think there should be zero voltage from ground to any part of the element.

        It's entirely possible that only one leg of the 240V supply to the heater elements is switched, and the other leg is "hot" at all times (when the breaker is on).  Then, if you measure from either leg to ground (or neutral) you'll read a voltage (though how you'd get 167V under any circumstances is beyond me).  [How old is your meter, and is it digital or the type with a needle?  Does it require batteries?]

        There should be two obvious power terminals on the heating element (in addition to a possible ground connection).  You need to measure BETWEEN those two terminals.

        1. InventPeace | Jun 25, 2011 11:01am | #8

          yes we put in new battery and checked on reg 110v outlet.. but its possible we still could have a bad meter.. so we'll check that out.  

          The real PROBLEM is super high AIR COND bills in summer.. to the point ot insanity $500 month on only 1000 sq ft house?  Others have said $360,  deposit was $390 to turn it on last month,  Also you have to remember that the other example with the other guy (see first post), was getting his house heated in the mornings in the summer when he had the selector on Air Cond, and even still heated house when he also completely disconnected the thermostat (hate to think design flaws in HAC units but I was a witness to it as well)l.   In his case it went on for years and he only occasionally noticed it,.  (the ideal was that if its cool on a summer morning lets damn sure not heat the house for any reason, as it will be very hot weather as day progresses);  So he simply disconnected 2 elements, and replaced sequencer with new one, and also put the other 2 elements on a breaker all their own, to isolate them and be abe to turn them off "for sure".  He doesn't have the problem now and simply heats his home on 2 elements instead of 4, also AIr is working great!  THis all makes one think there "MAY" be a design flaw in the HAC business, and it may be more then one co, that is making some wrong assumption about how it will work in summer months.   I hate to say that, but I have seen so many errors, typos, etc in all kinds of equipment that is coming partially or completely out of china that I have to accept its possible.  (Chinese line workers don't read english and do things like put hot where cold is supposed to be on faucets, mislabling things, etc.. and if no one tells them its wrong, they don't fix it. )

                Maybe the circuit board has a problem?

           We'll go back over someday and recheck across both terminals with AIR on, and see what we read. 

            Thanks for your advice! 

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Picture-Perfect Pergola

Built from locally sawn hemlock, this functional outdoor feature uses structural screws and metal connectors for fast, sturdy construction.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Old Boots Learn New Tricks
  • Install Denim Insulation Like a Pro
  • Podcast Episode 691: Replacing Vinyl Siding, Sloping Concrete, and Flat vs. Pitched Roofs
  • FHB Podcast Segment: Roofing on Commercial vs. Residential Buildings

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data