how many amps through knob & tube?

IdahoDon | Posted in General Discussion on December 5, 2008 05:55am

City allows a bag full of 20 amp breakers on a new 200 amp main service to an 80 year old house. 

Knob and tube appears to be as fresh as 80 year old wiring can be, but I can’t help but think most existing wiring would be better off with 15 amp breakers and leave the 20 amp circuits for new 12g wire.

Along same lines, is 14g romex allowed on a 20 amp breaker?  I can’t ever remember 14g on anything but a 15 amp breaker.   The under cabinet lighting I’m building into some new cabinets is being fed with existing 14g wire from a remodel 10 years ago tied into a 20 amp kitchen circuit.

Cheers

 

Beer was created so carpenters wouldn’t rule the world.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. DanH | Dec 05, 2008 06:26am | #1

    14G wiring must be on a 15A or smaller breaker, except in a few very special circumstances.

    In theory K&T is good for whatever the wire size is, but prudence would suggest that you limit it to 15A, especially since you never know if the same size wire has been used throughout a circuit.

    There's generally nothing wrong with using a breaker that's smaller than the wiring would allow -- it gives you a little extra protection against malfunctioning appliances, overloaded extensions, etc.

    The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel
  2. User avater
    SteveInCleveland | Dec 05, 2008 03:48pm | #2

    # 12 = 20 amp

    # 14 = 15 amp

    I wouldn't chance it, especially with some of the crazy older wiring and splices I've come across over the years.

     

     

     

    "Preach the Gospel at all times; if necessary, use words."  - St. Francis of Assisi

  3. frenchy | Dec 05, 2008 05:25pm | #3

    I can't speak for that application but when I tore my house apart the wire size on my knob and tube was over 10 guage. 

    1. DanH | Dec 05, 2008 05:44pm | #4

      The problem is, the feeds to individual outlets are apt to be smaller.
      The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

      1. frenchy | Dec 05, 2008 09:26pm | #7

        I'm not so sure of that.. My whole house appears to have been wired from one spool of wire.   Remember when knob and tube was popular there were far fewer outlets plus most homes were much smaller in size..

         Yep Martha ,We have lights in 3 rooms! Our house is electrified!

        1. DanH | Dec 05, 2008 09:52pm | #9

          The problem is that a sort of primitive romex is often used for the last few feet from the K&T wiring to the outlet. That stuff is apt to be a smaller diameter.
          The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

      2. mrfixitusa | Dec 05, 2008 09:29pm | #8

        I lived in an old house and I remember some of the wiring appearing to be lighter than 14 gaugeIs there such a thing?this was wiring in the walls going to outlets, lighting circuits, etc

        1. DanH | Dec 05, 2008 09:54pm | #10

          They used to play pretty fast and loose with the rules -- and there were no rules. I wouldn't doubt that there are some old circuits on #16. Often the "backbone" would be heavier and the drops would be something light.
          The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

          1. Stuart | Dec 05, 2008 11:11pm | #11

            In my bookshelf I happen to have a copy of the "Minnesota Farmstead Wiring Regulations", effective March 15, 1938 (it's a 20 page pamphlet the size of an index card...a far cry from the codebooks of today.)  This book was used in lieu of the 1937 NEC for rural communities. 

            Anyway, it says that wires shall be 14awg minimum for lighting circuits, and 12awg minimum for appliance branch circuits.  That applies for knob and tube, NM, armored cable or conduit wiring methods.

          2. DanH | Dec 05, 2008 11:59pm | #12

            1938 was pretty late, wiring-wise. Lots of earlier stuff exists, with all sorts of things that would scare the sith out of you if you knew they were present in your house.
            The mark of the immature man is that he wants to die nobly for a cause, while the mark of a mature man is that he wants to live humbly for one. --Wilhelm Stekel

          3. Shoemaker1 | Dec 09, 2008 02:31am | #13

            Hi
            Our first house we bought in 82 it was moved on to the lot in 1917, and planed to tear it down in a couple years and rebuild, nice lot. Well!! l big storm next june and our 628 sg foot of pleasure fell into it to a washed out block crawl space. So the tear down came real soon.
            As we started up to rip the second storey stoop we hit some K+T and it was black in between the wires in many spots. splices into romex were all charred and insulation burned and wires just a hair away from each other in an attic with wood shaving insulation. Showed my friend who was with the local utility. Sort of a dead run to see you hit the main breaker first. Still get the odd chill from that sight.
            I'm not sure but I believe it is against code here in SK. Canada. If you see it! out it goes. That was a ticking time bomb and I'm sure glad mother nature did the deed before the wiring did.Working now on a condo reno, the buried junction boxes and wiring ran in a notch on a studs.
            Todays best was a electrician dam near nicked a gas line with an auger bit. Have you wired in smoke detecters? we a bitch about codes but guess there is a reason for them.
            Regards
            BB

          4. skipj | Dec 09, 2008 10:44am | #16

            Well done man.

            I happen to have the 2006 code right here and K&T ain't in it...anywhere...at all...ever.

             

  4. User avater
    shelternerd | Dec 05, 2008 06:11pm | #5

    Our old place up in Maine (in the family since 1788) we upgraded the panel with arc fault breakers feeding juice to the old Buss Fuses so that as the wiring continues to degrade we at least have some assurance that when they go sparky on us they'll shut themselves off. One circuit did so when the house was un-occupied in the middle of the winter two years ago and we just let it be dead rather than tear up the house looking for the fault. I just left a bad fuse in the suspect circuit with tape on it saying that the circuit was bad and went on. It's a really old farmhouse and we don't really need all the outlets to be live if the alternative is spending a ton of cash or burning the house down.

    m

    ------------------

    "You cannot work hard enough to make up for a sloppy estimate."

  5. VMackey | Dec 05, 2008 07:24pm | #6

    The standard logic I've heard from a number of trusted electricians is knob and tube is safe if all is in good condition, not covered, and fused with a 15a breaker.

    So I agree with your thoughts to keep the existing on 15a's and leave the 20a for the new 12g wire. It's nice if you can kill the existing recepticles and make them all new 20a. Lighting circuits usually work fine with the existing 15a K&T. Vic

  6. cap | Dec 09, 2008 03:46am | #14

    Don,

    You recall right: 14 gage copper wire, 15 amp breaker (or fuse).

    You can protect a 12 gage circuit with a 15 amp breaker, and that's a very good idea for old houses.  It's what I do when replacing the old panel in an old house:  protect the branch circuit wiring with a 15 amp breaker, even if it's an AWG 12 copper conductor leaving the panel.  You never know if some yahoo has extended a 12 gage circuit with #14, or for that matter, 18 gage zip cord.  Or phone wire--no kidding, I've seen that.

    The NEC has always required that 14 gage copper wire be protected at no more than 15 amps (except in some uncommon situations, like motors that have a heavy startup current, and you wouldn't see this in old houses).  Again, that doesn't mean that uninformed people didn't put a 20 amp fuse or breaker on a 14 gage circuit, to keep the fuse from blowing/breaker from tripping under overload, or extend a circuit with wire too small.

    Generally, the wiring in old houses ( circa 1890 to 1950) that were wired by professional electricians was done very well.  The NEC came to exist within the first few years of electricity being installed in houses.  People were rightly scared of electricity--not that it was any more dangerous than gas, or kerosene for lighting, mind you, but it was new--and the electricians of the time typically were very good craftsmen.

    Also, in very old houses, knob-and-tube wiring was typically set up with one  neutral shared by two circuits.  In the earliest days, this was in houses with 30 amp, 120 volt service.  The neutral was fused as well (usually for the lighting circuits, and at 15 amps), so that if the sum of the current on the two circuits exceeded 15 amps, the neutral fuse would open the circuit and protect the wiring from overloading.  This worked because the loads were usually very light (only a few 40-watt or 60 watt lamps on one lighting circuit at any given time), and so an overload of the shared neutral was rare.

    In the 1920s, as electrical appliances became common (toaster, waffle iron, mixer, electric fan), the loads on circuits increased.  Consequently, people over fused (or by passed the fuse with a penny) the neutrals so as to not be inconvenienced, and there were fires.

    So, some time in the late 1920s, , the use of a fused neutral (called the grounded conductor, for you semanticists) was prohibited in new construction.  Shortly prior to thehis change, sometimes a 10 gage copper conductor was used for the shared neutral, and was not fused.  I don't know if this was allowed by the NEC, but I've seen it often enough (and in different areas), to think that it was.

    This was also when 240/120V, 60 amp services started to be used for houses, so the shared neutral circuits (called Edison or multiwire circuits) didn't require a fused neutral.  With the two hot conductors coming off the different legs of the 240/120V service, the neutral carries the difference in the current of the two, not the sum (as with a 120V service).

    From a practical standpoint, anyone who upgrades wiring needs to know a lot of history, or they can get things really messed up (as in, "burning the house down" messed up.)

    Cheers,

    Cliff

     

  7. brucet9 | Dec 09, 2008 10:35am | #15

    "The under cabinet lighting I'm building into some new cabinets is being fed with existing 14g wire from a remodel 10 years ago tied into a 20 amp kitchen circuit."

    I was called out to fix dead kitchen outlets in a condo. The tenants complained that they couldn't make toast and coffee until it was fixed. There was also an electric grill and a toaster oven.

    The outlets were actually plug mold installed under the cabinets where tile back splash covered the wall right up to the cabinets. I traced the problem back to a duplex outlet upstream from the under-cabinet plug mold. Wires were 14ga. Half of the duplex outlet's plastic body had melted, forming plastic stalactites. Somewhere in the wall behind all that tile the 14ga was spliced to a 12ga wire from the original 20A kitchen circuit.

    BruceT

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Making the Move to Multifamily

A high-performance single-family home builder shares tips from his early experience with two apartment buildings.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • A Classic Paint Sprayer Gets a Thoughtful Refresh
  • Podcast Episode 692: Introduction to Trade Work, Embodied Carbon, and Envelope Improvements
  • FHB Podcast Segment: Embodied Greenhouse Gas Emissions and the Building Codes
  • Old Boots Learn New Tricks

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2025
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data