How to reduce furnace noise

| Posted in General Discussion on January 2, 2002 08:07am

*
The general noise level produced by my furnace is too loud. I believe the main culprit is just the sheer volumetric flowrate being pushed through the ductwork. The blower by itself sounds normal. The burners put out a good bit of noise, but that is unavoidable I imagine. My house is 1-1/2 yrs old with a Rheem “Criterion II” natural gas forced air furnace. 125,000 btu/hr. Blower is 9.5 amps, 3/4 Hp. I think the blower is capable of 4 speeds, since a table printed on the panel shows the airflows for the 4 speeds. My house is 2700 sf, 2 stories, 10 registers up, 10 registers down, 1 zone.

Whenever my furnace turns on, the blower starts in a slower speed (without flame) for about 45 seconds, then the burners light and the blower shifts to a medium speed for about 30 seconds, then finally shifts to fast speed.

Is it possible to make the blower run at a lower speed? Is it safe (delta-T would increase)? Would the efficiency be changed? How can I accomplish the speed change?

Thanks.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. Tim_Rice | Oct 18, 2001 07:29pm | #1

    *
    Chris,

    What you are hearing when you furnace starts is first the combustion air fan and power exhauster starts. The gas control circuit has a "flow prover" switch that checks to make sure adequate flow is present, then opens the gas valve and starts the burner. At this point no air should be coming out of the registers. Once the burner heats up the heat exchanger to a preset minimum temp (usually about 180 degF) then the furnace blower starts. This limits the amount of cold air that comes out of the duct work at start up.

    The blower that you described should have about a max rating of 2000 cfm @ 0.5" w.c., which is a 5 ton unit. If the furnace is a two stage furnace, the it will operate at a low-fire setting (reduced heat output) with a lower blower speed and hi output on a higher speed. Changing factory set speeds would be il advised for many reasons. Some high end units have 4 speeds that can be set, usually as follows: low-low for contiuous ventilation w/o heat or cooling; low-med- low fired heating; high-med, high fire , max heating, low cooling and high-high for max cooling.

    The causes of noise in a forced air system can be simple or very complex. Starting with the simple, air velocity in the duct work. If the air velocity in the ducts is less than 1500 fpm, it should be fairly quiet. If the velocity is reasonable, then isolating the duct work from "amplifiers" is the next step. Make sure that it is supported and just lying on top of ceiling joists. Wraping the ducts will help some both with sound attenuation and insulation.

    Some layout problems can cause noise as well. Look for any "bull head" tees, tight turns, radical offsets, etc.. If it looks restrictive, it probably is.

    1. Chris_Zito | Oct 18, 2001 09:34pm | #2

      *Tim, thanks for the reply.You're right. The blower only runs at one speed (although it seems capable of 4) and it kicks on after the heat exchanger has reached a certain temperature.All the supply ducts are well insulated and have reasonably uncomplicated flowpaths (no tight turns, etc). I'm pretty sure most of the bothersome noise is from the return plenum, which comes down from the attic, through a framed-in chase, then into the top of the furnace in the garage. The return chase makes a complicated horizontal jog about halfway down the second story wall (a bedroom wall), where the sound level is excessive. I also think the return plenum is undersized, but there's not much that can be done about it now.Would it be safe if a licensed HVAC technician adjusted the system so that the blower ran at a slower speed AND ADJUSTED THE BURNER OUTPUT appropriately? I know the furnace would run longer, but quieter.Is it possible with my particular model furnace?You mention changing the speed is ill-advised for many reasons. What are they?

      1. Tim_Rice | Oct 19, 2001 02:56pm | #3

        *Chris,I don't know if it is possible to modify either the fan speed or the burner capacity of your furnace.The reasons that I would not attempt to modify these parameters is:- I doubt that the equipment has that level of flexibility built into it. Changing motor speeds is not that simple, though I am not an electrician. Most smaller HVAC equipment is direct drive and runs at the speed of the motor. The speed at which motors spin is a function of the electrical service available (60 Hz) and how it is wound and where taps are placed in the windings.-IF it were possible to adjust the speed of the blower, then there would be the issue that you brought up about temperature rise across the heat exchanger. The potential to damage the heat exchanger is a concern, though not that great, really, and voiding any equipment warranty you might have is a definite.-IF you could also reduce the heat output of the burner, all would be OK, but I would bet the cost of such work would be more than the benefit.-If the adjustments were possible and IF the cost was reasonable, then you would still not be addressing the real problem. I believe that you have it pinned down in the return plenum. One way to address this would be to remove the return and replace it with one properly sized. If that is not an option, surrounding it with fiberglass batts (regular R-11 wall insulation) would deaden the sound, maybe to an acceptable level. If access to the duct is not available and you are unwilling to tear into your house to get it, you might be able to reduce the air flow through the system by closing down dampers (if the are installed) close to the furnace. If you do not have dampers in the system, you could (have someone)install them where ducts are accessible. This would also cause the temperature rise to go up.Another option would be to add a new return in the system closer to the furnace so the furnace sees the same air flow (+/-) but the noisy return duct has less air flowing through it.

        1. Tim_Rice | Nov 15, 2001 04:51pm | #4

          *Chris,One more option to consider. Check out your furnace and look for the following: inside the bottom access panel where the blower is located, check out the wiring (shut it down first). There should be 6 wires coming from the blower motor to a terminal block under where all the thermostat wires connect to another terminal block. There should be 3 wires going into the motor terminal block from the controls. A white one (common) a black one (heating blower power) and a red one (cooling blower power) Look at this and note which wires are connected where. The block should have numbers for the 2 colored wires and a "c" where the white wire is connected. If things are as I described, you may be able to change the blower speed.

          1. Bob_Walker | Nov 15, 2001 05:36pm | #5

            *Tim,"Another option would be to add a new return in the system closer to the furnace so the furnace sees the same air flow (+/-) but the noisy return duct has less air flowing through it."Be sure to follow any restrictions on putting returns ina restricted area (i.e., if your furnace is in a "furnace room" or closet, there should not be a return register in the closet to compete with the draft.) I suspect there are intricacies involved here beyong that general rule.

          2. Tim_Rice | Nov 16, 2001 04:12pm | #6

            *With a sealed combustion(one with a PVC piped supply and exhaust) furnace, which I think is about the only option available these days, it is not a concern. With other gas fired appliances, like a water heater with a power vent (not typically a sealed combustion device) in close proximity, the potential exists. Depends on lots of factors, size of the space, amount of ventilation available to the space and proximity of the two. Good advice to follow nonetheless.

          3. David_Daniels | Jan 02, 2002 08:01am | #7

            *1 Duct work might not be sized right . 2 RA grill upstairs might be humming due to air flow remove it see if noise is better. 3 do not adjust blower speed unless you know what your doing 4 for noise the furnace blower compartment can have ductliner installed and the ducts if they are sized for it . 5 canvas connector can be used on the risers and RA connections to keep furnace from rattling duct work

          4. David_Daniels | Jan 02, 2002 08:07am | #8

            *O this furnace comes W / ins . how big our your ducts and metal ductbord or what ?

  2. Chris_Zito | Jan 02, 2002 08:07am | #9

    *
    The general noise level produced by my furnace is too loud. I believe the main culprit is just the sheer volumetric flowrate being pushed through the ductwork. The blower by itself sounds normal. The burners put out a good bit of noise, but that is unavoidable I imagine. My house is 1-1/2 yrs old with a Rheem "Criterion II" natural gas forced air furnace. 125,000 btu/hr. Blower is 9.5 amps, 3/4 Hp. I think the blower is capable of 4 speeds, since a table printed on the panel shows the airflows for the 4 speeds. My house is 2700 sf, 2 stories, 10 registers up, 10 registers down, 1 zone.

    Whenever my furnace turns on, the blower starts in a slower speed (without flame) for about 45 seconds, then the burners light and the blower shifts to a medium speed for about 30 seconds, then finally shifts to fast speed.

    Is it possible to make the blower run at a lower speed? Is it safe (delta-T would increase)? Would the efficiency be changed? How can I accomplish the speed change?

    Thanks.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data