I-Joists and bridging
| Posted in Construction Techniques on January 28, 2002 06:50am
While some posts suggest there are extensive discussions of joist bridging, I’m not having any luck locating them using SEARCH.
So; 24×24 garage, 2×6 walls, 14″ IJoists 16″ on center, clear span.
I had thought to use simpson tension bridging (the metal stuff) in two lines at the 8′ mark. Supplier sent the wrong stuff (2″ short), but I’ve got some 1×3 strapping…
Question: would the strapping at normal 16″ centers be sufficient to act as bridging, or should I get the appropriate length briding straps, and use both?
thanks,
-TJ
  1. Mad_Dog | Nov 02, 2001 02:16am | #1
    What are the I joists for?
    1. -TJ | Nov 02, 2001 02:39am | #2
      *Sorry, the I-joists are supporting the 2nd floor - upstairs is gonna be a library. Only walls on the 2nd floor are the gable end wall, and an intermediate wall where the roof pitches change; the roof is framed directly down to the 2nd floor deck (12 in 12 pitch, plus a couple of dormers)-TJ
      1. Mike_Smith | Nov 02, 2001 03:06am | #3
        *if you use a 3/4 subfloor & strap the ceiling , then bridging isn't going to add any thing to the stiffness..if you want to use bridging.. test show that diagonal furring is ok.. but solid bridging is better...b IMHObriding is unneccessary with glued subfloors and strapped ceilings...
        1. Mad_Dog | Nov 02, 2001 03:23am | #4
          *I agree with Mike. Other tests have shown that the bridging did virtually nothing but add squeeks to the floor system.Is the floor carrying the roof in that area where it changes pitch? Seems kind of weak for that with that much span.
          1. George_Roberts | Nov 02, 2001 03:40am | #5
            *You might follow the manufacturer's directions on bridging. They seem to know what they are doing.Your joists span either 23' or 24' it is difficult to tell. You might check the joist sizes also.
          2. -TJ | Nov 02, 2001 05:40pm | #6
            *In response to "Mad Dog"'s question; No, the roof pitch change occurs 4' past the I-Joists, in an area that is 2x10 framed.In response to Mr. Robert's concern over the span and joist size: the free span is 23'9". the joists bear 4.25"+ on 2x6 walls. I've got to trust the sizing, as both the architect and building inspector have signed off on the configuration...-TJ
          3. Mad_Dog | Nov 03, 2001 02:09am | #7
            *Doesn't sound like that will be a problem
          4. Mike_Willms | Nov 04, 2001 06:22am | #8
            *The I-Joists I use (Louisianna Pacific-LPI's) say bridging (a row of solid blocking, actually) isn't necessary but will enhance the floor's performance. A span like that - I'd want to do something to keep the joists from rolling mid-span. Might help in preventing possible drywall cracks in the ceiling. Strapping is good, solid blocking is better (as Mike said).
          5. nathan_wegemer | Nov 04, 2001 09:10am | #9
            *Just a thought, would a ply layer on the bottom of the joist be the ultimate stiffener?
          6. -TJ | Nov 05, 2001 07:31pm | #10
            *I went through all the installation guides for the I-Joists I could locate this weekend, and could find no mention at all about the bridging issue.Thought to check my back issues of FH on the subject, but haven't tracked 'em down yet.Strapping will do me until I can get the fire-rated drywall in (it's a garage, after all). thanks for the helpful responses, as always...-TJ
          7. -TJ | Nov 14, 2001 11:03pm | #11
            *Follow-up:Found the I-Joist installation guide I was looking for, finally.It states: "Mid-span bridging is not required."OK, so not required. Won't hurt to add it, though. I expect to be using 1x3 strapping, as my metal tension ties appear to be 2" too short. (Grrr.)-TJ
          8. nathan_wegemer | Nov 15, 2001 07:01am | #12
            *Could you explain 1x3 strapping? Never seen a joist bay strapped before...I'm guessing bottom chords, perpundicular to joist. Is it three feet long? Wouldn't it require bridging or blocking to nail/screw to?
          9. Jerry_Albrecht | Nov 15, 2001 10:07pm | #13
            *I'm building a place with a 23' span and looked at using the 14" I joists. Both manufacturers I talked to said that was no problem. I also used Simpson bridging, wish I hadn't, to hard to keep tight. I'm using 1x3 strapping 16" O.C. on my loft because the rafters are so uneven, they made a huge difference. When I talked to the engineers about the performance of the floor they said bridging isn't required but would reduce the bounce.
          10. Terry_Smiley | Nov 17, 2001 12:51am | #14
            *I've had major arguments about this subject. b Bridging isn't necessary w/I joist.What does necessary have to do with a trampoline floor. I've walked on plenty of new floors that felt horrible. No, they weren't going to collapse, but where's the pride in workmanship, how much does a spruce 1 x 4 cost.i See you got me started!!!Tight floorsTerry
          11. Mike_Smith | Nov 17, 2001 01:06am | #15
            *terry... bridging does so little to improve the stiffness of a floor system that it is next to useless.. if you want a stiffer floor.. increase the framing size..... or reduce the spacing.... or change the subfloor...... or furr the ceiling... but skip the bridging and spend your material and labor budget on something else..b but hey, whadda i no ?
          12. Terry_Smiley | Nov 17, 2001 04:16am | #16
            *MikeIf the old timers used it,(and I'm one) and it worked then, why did it stop working. I've seen the difference. For example, we didn't nail the bottoms of the X's until the sheathing was on. We would walk the floor, jump on it as a test, and then nail the bridging. That's where the rubber meets the road for me, it worked then why did it stop working. Please explain this, please.I'm here to learn.Terry
          13. Mike_Smith | Nov 17, 2001 04:29am | #17
            *it changed when the subfloor became plywood.. the APA did a lot of testing in the late '60's.. and proved that 3/4 T&G ply...glued and nailed .. was stiffer than bridging... also..previous tests had already proved that SOLID bridging was superior to x-bridging in termsn of floor system stiffness...test reports i've seen say T&G, nailed and glued... with a furred ceiling.. is the stiffest system for conventional framing.....most do NOT furr their ceilings..i do..bottom line...skip the bridging and spend your time and money on one of the other floor components...for example:take the cost of bridging out and change your spacing from 16" to 12"..much more cost effective.. and stiffer..or...take the cost of bridging and change your subfloor from 5/8 to 3/4... ordeduct the bridging and glue your subfloor...you get the idea...b but hey, whadda i no ?
          14. blue_eyed_devil_ | Nov 18, 2001 03:56pm | #18
            *Bridging doesn't do anything but make it squeak. Old timers accept everything old as fact. But a lot of stuff was wrong.blue
          15. Terry_Smiley | Nov 18, 2001 06:24pm | #19
            *Blue I don't accept anything as fact until I've seen the results. The example I gave above is fact. The other fact is I like what Mike has to say and I'll try his ideas. Thanks Mike, this is what I was looking for.Terry
          16. blue_eyed_devil_ | Nov 18, 2001 07:34pm | #20
            *Terry, bridging prevents the torqueing of the joists. So does drywall glued and screwed to the bottom of the joist.blue
          17. nathan_wegemer | Nov 19, 2001 01:37am | #21
            *what's the strapped ceiling detail...what's the furred ceiling detail...nathan
          18. Mike_Smith | Nov 19, 2001 02:17am | #22
            *nathan.. strapping & furring are the same thing...in a lot of areas (RI is one) ceilings are furred with 1x3 furring at 16" oc...usually (2) 6d or (1) 8d in each joist...you can shim the furring or not.. it takes out half the error from high joist / low joist in any ceilingbesides making the ceiling stiffer.. it makes the drywall job easier.. it gives you another plane to put blocking in for fancy molding.. or support for lighting...blue contends that screwing & gluing the blueboard / drywall also stiffens the ceiling system.. and this is true.. some think furring ceilings is just a waste of time & money.. but .. what do i care. i've furred every ceiling i've worked on since 1962...it also helps with wiring & plumbing... a lot of things can be run in the 3/4 space the furring makes...some building inspectors want furred blocking every 8' for fire blocking.. some don't...
          19. George_Roberts | Nov 19, 2001 02:37am | #23
            *Everyone has their own opinions of bridging. Most of the differences reflect their good and bad practices.Poor bridging will not help a floor. Good bridging will.Bridging does 2 things. It prevents twisting of the joists and it distributes loads over several joists.People used to build to 1/240 deflections and nail boards. Now people design to 1/480 of less deflections and glue plywood. Bridging is less needed now.I personaly use bridging on ceilings. It prevents the joists from moving as I walk over them in an attic.
          20. blue_eyed_devil_ | Nov 19, 2001 07:44am | #24
            *George, I would assume that the tests were done with the same quality installation.blue
          21. michael_garvey | Nov 27, 2001 04:28am | #25
            *Gotta agree with Mike. I just spent an afternoon ripping down bridging mid-span between my Louisianna Pacific-LPI's. GC's first job with I-Joists-he was a dimensional man. Span is 19' on 16" centers. He used cut I-joists to solid block about midspan. The moaning and groaning from every step on the floor above drove me to destruction! I only wish I had done it a year ago! Now it really is a "silent" floor. Don't have any tests to back me up, but customer satisfaction is up 100%.
          22. blue_eyed_devil_ | Nov 27, 2001 01:46pm | #26
            *That's what I've been saying Michael...bridging=squeaks!I wouldn't let anyone put any in my house. I'd tear it out before it was boarded!blue
          23. Boss_Hog | Nov 28, 2001 12:59am | #27
            *I personally think 24' is too far to span with anything 14" deep. I really don't like to go over about 21' - I don't care what the span charts show. Increasing depth increases stiffness. Decreasing spacing increases strength. If the floor is stiff enough to begin with, blocking and bridging aren't necessary.
          24. blue_eyed_devil_ | Nov 28, 2001 05:53am | #28
            *Hear! Hear! O' Master Spanner!Right on Ron! If bridging was so good, why don't we just eliminate the joist, and just install the bridging?!blue
          25. doug_hubbard | Nov 30, 2001 05:54am | #29
            *I've used I joists for about ten years and nary a problem. Never had to bridge at midspan.Long as I give the supplier accurate demands for the floor it works. Didn't used to strap- but since reading up here I do frequently. Easier to get a better looking drywall job and stiffer floor.Solid bridging every 1/3 span glued and nailed makes for a stiff floor. I will retro blocking in older homes to take out the bounce.In general I don't bridge I joist.
          26. Matthew_Steadman | Jan 23, 2002 07:15am | #30
            *Mike,Do people actually use 5/8 as subfloor? What about adding LVLs every 4 to 6 feet? It seems like that would be the best way to stiffen up an over-spanned TJI system. It would cost a bit though.
          27. David_Onkels | Jan 27, 2002 06:00am | #31
            *DO NOT OVERSPAN. FOLLOW THE MANUFACTURER'S SPECIFICATIONS. DO NOT BRIDGE. DON'T TRY TO SAVE NICKELS AND DIMES! You could use 14" TJI Pro 550's at 16" O.C. and have a nice floor. Do that.
          28. George_Roberts | Jan 28, 2002 01:55am | #32
            *Let me understand this.Every manufacturer of floor trusses recommends strong backs, this is real good bracing.Most of you are saying I- Joists don't need bracing.I suspect that the truss manufacturer's are right. Some Canadian firm makes real good I-Joist bracing.Put in bracing and put it in right.
          29. blue_eyed_devil_ | Jan 28, 2002 06:50am | #33
            *George, every set of manufactured joists that I have used, have a very specific mid span brace specified. It has never specified cross bridging. I do what I'm told....blue