I think my HVAC system could be oversized. Is this something I should be concerned about?

user-1035959 | Posted in Energy, Heating & Insulation on August 9, 2012 05:11am

I bought my new HVAC system just over 2 years ago. The furnace is a high efficiency natural gas that vents through pvc pipe through the wall. The furnace is rated at 45,000 b.t.u.’s. In the winter, it feels like my house is either hot or cold regardless of where I set the temperature. I try to aim for about 68 in the winter.

My AC is a 2 ton unit with 3 ton evaporator coils. It usually feels either hot or cold in the summer. If I set the temp on the thermostat above 74, it tends to feel a bit clammy. Sometimes I set the thermostat down to 73 or 72 just to get it to run. I’d say most days it probably runs for less than 10 minutes, then shuts off.

I live in Iowa, so I have a mixed humid climate. I also live in a well-shaded area, under 800 square feet of conditioned space. Air tightness is pretty good. I think I’ve sealed up most of the major sources of air leaks and my insulation is fairly good (in the attic at least, not so much in the walls). I don’t notice much of a difference in the running time of the HVAC system before and after some of the insulation/air sealing. It seems to run roughly the same, only the difference is I can keep the temp a little higher in the summer and lower in the winter (but still uncomfortable, either hot or cold).

Am I being too picky here or is this not working out as it should? I’m not sure what else to try. My ductwork is pretty old and poorly done (have a thread about that right now) and most rooms one supply register is in the wall split between two rooms. Would re-doing this just make my system more efficient and possibly more oversized or could it possibly help? Is it possible to put a variable speed fan in that makes the system run slower for longer without having to change out the whole system?

 

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. DanH | Aug 09, 2012 07:45am | #1

    First thing to do is to run the fan all the time.  But it sounds like your system is oversized and poorly balanced.

    1. user-1035959 | Aug 09, 2012 02:53pm | #3

      Good idea. I turned the fan on earlier and it's helping a lot.

      You say the system could be poorly balanced. What does that mean exactly and how can I deal with it?

      Redoing my ductwork is probably going to cost me about a couple thousand dollars. Not sure if it will even help.

      1. DanH | Aug 09, 2012 03:23pm | #4

        Redoing the ductwork may or may not be needed.  Inserting some dampers in the ductwork may help significantly.

        The problem is, you need someone who knows what the heck they're doing, but is willing to use a few tricks of the trade vs insisting on a complete redo.  Finding that someone is hard.

  2. renosteinke | Aug 09, 2012 12:24pm | #2

    2 ton A/C? 45Kbtu heat? Sounds like you have a smaller house, perhaps 1,000 sq. ft. That's a problem.

    The first thing you have to recognize is that it's not just a question of equipment. Then you have recognize how things have changed since the house was built. Finally, you need to understand your priorities and get your facts nailed down.

    Feel hot? Feel cold five minutes later? Maybe the problem is YOU. Hang a few temperature and humidity gages around the house; you'll be amazed how your perception changes while the room stays the same.

    Homes are typically designed with a central system, and everything works off a single thermostat. Alas, houses are not that simple.

    In winter, I suggest setting the central heat fairly low - say, 68 degrees - and supplimenting that around the house with space heaters (I like the oil-filled radiator type for this use). That way, if the wind is hitting one room while the sun warms another, you'll only be adding heat to the cold room.

    Summer is a bit trickier. I expect you'll get the best results if you can vary the speed of your fan, to circulate the air more consistantly. You definitely need a longer run time for the A/C to remove humidity.

    Is your house properly insulated? If it has the original, I'd bet it's time for an upgrade.

    Just as important is your venting. There should be SOME fresh air coming in at all times. This is needed so that the bath fan and range hood actually have something to exhaust. Kitchens and baths add tons of water to your indoor air. Anything that burns - like scented candles- adds moisture.

    Likewise .. what's your roof doing? Improper or blocked attic venting will make the house much less comfortable.

  3. florida | Aug 10, 2012 07:45am | #5

    Generally speaking the condensor and air handler should be the same size. What was the reason for using different sized parts?

    With an oversized A/H the fan won't run long enough to dehumidfy the air before the thermostat is satisfied and cuts off the condensor. Here in humid south Florida we would probably have installed a 1 1/2 ton unit in your house to make sure the A/C ran long enough to get the humidity out.

    1. user-1035959 | Aug 10, 2012 12:35pm | #6

      Is it somehow possible to go with a variable speed fan? I know I have a 2 stage furnace.

      1. DanH | Aug 10, 2012 12:40pm | #7

        Generally not possible to swap in a variable speed motor, without replacing the furnace.  It may be possible to adjust the speed of the fan, though, between one of several fixed speeds that it might support.

        1. user-1035959 | Aug 10, 2012 10:50pm | #8

          Ok

          DanH wrote:

          Generally not possible to swap in a variable speed motor, without replacing the furnace.  It may be possible to adjust the speed of the fan, though, between one of several fixed speeds that it might support.

          I'm having the company that installed my system out next week. I hope that there's something that can be done. I don't know if there are different fixed speeds for the fan. My impression is that there are only two (2 stage furnace?). I'll talk to them and see what they say. Not sure I can trust them at this point, however. I may be on my own.

    2. Tim | Aug 24, 2012 01:45pm | #15

      The reasons

       one would select different coil/condenser combinations is to match the S/T ratio and tailor the capacity of the system to the load.

      An "oversized" (in relation to the condensing unit capacity) evaporator coil will result in a greater (percentage of the total load) latent capacity, and can get a little more out of a marginally sized ACCU. An "undesrized" evaporator with have a higher sensible capacity, in relation to the total capacity. Also, capacity can be "trimmed" with a smaller evaporator coil. These practices are not common in the residential market.

      Most of the time, evaporator coils are selected based on what's on hand, what's the cheapest and/or what fits.

  4. davidmeiland | Aug 10, 2012 11:38pm | #9

    Did the installer

    do any sort of load calcs when they installed the equipment? Did they come up with room by room airflow requirements and then measure the actual airflow to each room? Did they do a duct leakage test or any duct sealing? Was external static pressure checked?

    The mismatch between the indoor and outdoor coils is a bit unusual,  but some equipment specs allow for this. That should be checked.

    The point above about the A/C running too short is important. If it blows a bunch of cold air on you and then shuts off without dehumidifying the house enough, you will be uncomfortable.

    Where is the ductwork... in the basement, the attic, in the conditioned space?

    It is really hard to get this sort of stuff solved. Many HVAC techs don't know how to do it.

  5. user-1035959 | Aug 11, 2012 08:08am | #10

    I'm not sure what load calculations and/or testing they did. I was only present for part of the evualation/bid. They have an A rating with BBB so I thought I could trust them. I reckon there's not much they will be willing to do for me 2 years after the install.

    It sucks because we are usually either hot or cold when the hvac is running (winter or summer).

    1. DanH | Aug 11, 2012 08:41am | #11

      Unfortunately, BBB rating means little.  It only reflects how many complaints have been filed against the company, and only relatively severe complaints are counted, and only after "mediation".  (And, after all, how likely are you to file a complaint against the company?)

  6. cussnu2 | Aug 14, 2012 11:20am | #12

    It sure sounds like it is way oversized.  You can certainly spend a bunch of money with the company or someone else but you may be just as well off balancing the system yourself....and by that I don't mean fancy load calcs and airflow measurements.  Shut the supply vents closest to the thermostat and open the ones farthest away.  Its simple, its fast and with a little adjustment you will find the best mix for you to be comfortable.

    My Forced air furnace is not dead center so I completely shut the vents in two bedrooms and a bathroom that are closest to the furnance and force more air to the second floor and other end of the house despite these rooms being on the south side of the house.  Those rooms still get enough blow by out of the vents to keep them comfortable.  Dampers just off the supply line are the "real" way it should be done but then you have to head down (or up as they case may be) to adjust the dampers if the change in seasons cause you to need more or less in those rooms.  For example, in the winter, I still keep the vent shut in the bathroom unless the kids are taking a bath.  We open it up then to make it nice and toasty.

    Somebody else is going to tell you that for maximum efficiency you need to do all this bull and more but we are talking about an EIGHT HUNDRED SQUARE FOOT HOUSE.  All the extra efficiency in the world with a precisely sized and exact system will never save you the money you spend getting there NOW THAT YOUR SYSTEM IS ALREADY IN.  Getting it done right in the first place is a different story.

    1. davidmeiland | Aug 16, 2012 12:36am | #13

      I dunno

      Seems like a good HVAC tech could check him out in an hour or two for small money,

      Of course, actually FINDING a good HVAC tech who does it right is the trick, so I like your approach too. He could install a Magnehelic 2001 on the blower cabinet to keep an eye on static pressure as he plays with the grille dampers.

    2. user-1035959 | Aug 17, 2012 03:34am | #14

      Talked to them today and he suggested that we lower the fan speeds when I get the furnace tuned up next month.

       I will see how well this helps and post the results. Hopefully it doesn't cost me efficiency of the system.

      With my small, tight well-insulated house in a shaded area it shouldn't cost that much to cool/condition in the summer but it does. I have to turn the temp down to 74 or 73 to get it to run. We're cold in the house, but it's more comfortable than being hot and humid.

      A couple of ductless mini splits probably could heat and cool this entire house on their own 95% of the time. Knowing what I know now I wish I had explored that.

      Thanks for all of the feedback. I'll post again with the results after I have the system adjusted.

  7. Tim | Aug 24, 2012 02:08pm | #16

    Basic problem

    with your furnace is that it is the smallest capacity commonly available (some offer a 40MBH in 80% AFUE lines) and still, at rough guess, 50% too big. Same goes for the AC setup, but it could have been selected more appropriately. With less than 800 SF conditioned space, mild environment , heavy shade and good contruction, no conventional central type forced air system will be properly sized. This is a delimma that would take a sharp tech to address.

    All basic furnaces of modern design/construction (single stage, multi-speed) have 4 "built-in" speeds, one speed is used for heating air flow and one is used for cooling air flow. In your case, I would use the lowest speed possible for heating and the next lowest speed for cooling. These are typically "adjustable" by taps on the fan control board.

    The ductwork has little to do with the efficiency of the system. That is pretty well set by the design of the equipment. Poor ductwork can affect the effectiveness greatly, though. Better distribution and more consistent air flow/delivery will result in better comfort.

  8. Clewless1 | Sep 16, 2012 04:27pm | #17

    I didn't read all the posts ... my 2 cents. Oversizing causes comfort problems and is energy inefficient. <1000 sqft and 2 tons of cooling. Wow. Oversizing causes the compressor to short cycle ... just as you pointed out. Remember, you only have peak cooling a very small percentage of the hours. The rest of the time, the oversized unit has a much lighter load and so it short cycles. This is energy inefficient. It also causes comfort swings between delivering cool/cold air to nothing.

    Oversizing also shortens the life of the equipment substantially. 

    No you're not being too picky. The installer may have not actually sized the system or didn't do a very good job. He may have arbitrarily sold you an oversized unit. Many installers think they might be doing their clients a favor (and avoiding comfort complaints because of possible undersizing) if they just through a large unit at you.

    Well shaded and under 800 sqft tells me maybe a ton might work (although I'm not certain about the latent load). I sized a ton for hot dry climate (design temp 107) for about 1300 sqft unshaded. 

    Someone suggested maybe a two speed or variable speed fan ... without the right compressor, this may not work well for cooling ... it's important to have air flow to have the right supply temps. Low flow means even lower supply air temps (e.g. 47 degF). This doesn't work well.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

Scaled to Suit the Site

This thoughtfully designed home preserves the character of its neighborhood while maximizing space for a growing family through careful attention to scale, rooflines, and material choices.

Featured Video

How to Install Exterior Window Trim

Learn how to measure, cut, and build window casing made of cellular PVC, solid wood, poly-ash boards, or any common molding material. Plus, get tips for a clean and solid installation.

Related Stories

  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring
  • FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity
  • Tools and Gear for the Moms Who Get it Done
  • An Easier Method for Mitered Head Casings

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data