ISOLATED GROUND circuits for computer

toolbear | Posted in Energy, Heating & Insulation on March 27, 2007 05:16am

ISOLATED GROUND circuits for computer

     This for the Gurus of Grounding…

We are doing a remodel and the owner wants four isolated ground circuits in his office.

Does that mean four home runs for four outlets or can one daisy chain the grounds between the four boxes (box to box, recpt. to recpt).?

Cries out outrage?  I suspect this would negate any preceived advantages, but it’s worth asking.

Four more home runs…three AFCI runs, four GFCI, etc. Better get that 40 space sub panel.

The ToolBear

“Never met a man who couldn’t teach me something.” Anon.

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. User avater
    BillHartmann | Mar 27, 2007 05:52am | #1

    Fur getaboutit.

    First if this is not off a sub-panel is does not buy you anything.

    The idea is that in an heavy industrial location you migh have noice on the ground as it goes through several levels of sub-panels.

    But from what I have read the the use of isolated ground to try and fix noise problems from other equipment have not worked. If there is that much noise it is everywhere. And that needs to be fixed.

    Slight different problem, but I work the software to control damping system on ofset printing presses. It consists of a master controller and individual controllers at each printing tower.

    Whenever the presses would run the communications would go down. Each indiviual unit worked ok, but the master could not communicate with any of them.

    They checked and rechecked the ground. I think that they even ran isolated grounds for the electronics and made sure everything else was bonded together.

    Still the same problem.

    So I was sent out to look at it.

    The com was twisted pair differnetial signalling. At one of the terminals a few strands of the standed wire did not get under the screw. The presses running vibrated the wire enough that it would short to the case.

    .
    .
    A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.
    1. toolbear | Mar 28, 2007 06:23am | #18

      Fur getaboutit.

      First if this is not off a sub-panel is does not buy you anything.

      The idea is that in an heavy industrial location you migh have noice on the ground as it goes through several levels of sub-panels.

      These would land on a subpanel in this sector of the house.  What methods do you use to identify noise on a system? 

      (Not that I could on this system at this point.  Most of the old circuits are cut off and more go tomorrow as a french door is going through several runs from the panel.) 

       

       The ToolBear

      "Never met a man who couldn't teach me something." Anon.

      1. User avater
        SamT | Mar 28, 2007 06:53am | #21

        These would land on a subpanel in this sector of the house. 

        Whups, there goes your isolated ground.

        What methods do you use to identify noise on a system? 

        Today, they've probably got "Noise Meters" just for that, but back in the day, one would use an oscilloscope across the outlet. Any noise over about 3% of the supply voltage of the equipment being effected would be suspect. In the case of todays computors, that would be 10% of 5 volts or .5 volts in the frequencies used inside the computor.

        Most computors are relatively proof against supply line noise simply because of the huge capacitors in the power supply bridging from the output voltage leads to ground. This puts any noise to equal potential on the supplied voltages and ground inside the case.

        Open the case on one computor with another running beside it and all bets are off.SamT

        Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

      2. User avater
        BillHartmann | Mar 28, 2007 07:18am | #23

        If you are on T&M and worried about noise install some power conditioners.http://www.solaheviduty.com/products/powerconditioning/Index.htmUnless he is runnin something like a punch press in the basement or maybe a plasma cutter in the garage he is not going to have any noise the bothers computers.But if you are going to put in orange receptacles then I would run the isolated ground wire daisy chained through the 4 boxes. The best thing is to get all of the equipment at the same ground reference..
        .
        A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

        1. User avater
          SamT | Mar 28, 2007 07:47am | #24

          But if you are going to put in orange receptacles then I would run the isolated ground wire daisy chained through the 4 boxes. The best thing is to get all of the equipment at the same ground reference.

          I second the emotion.SamT

          Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

        2. toolbear | Mar 29, 2007 05:51am | #36

          If you are on T&M and worried about noise install some power conditioners.

          I don't see any heavy equipment.  I think the orange outlet and cover sounded neat, so ...  I keep thinking of a paraphrase of the Wizard of Oz:  You don't need an isloated ground, Sam.  You need an orange cover plate.

          I like the thought of daisy-chaining the lot - cuts down three home runs. The panel is a old Crouse H. 100A meter-main and it needs to go.  Two thirds half height breakers.  No room.  Very cramped wiring gutter.  Saw a big one at HD, but it was a Murray.  Have to find a decent 200a meter main.

          According to the appraiser, this project ('50s) has had a number of electrical fires.  One of the previous owners did a lot of wiring and had some interesting practices. 

          Can't trust anything in the walls that I didn't run.  Out goes the proto-Romex.  Out goes the Romex with nails in it here and there.  Just found a 12/3 with butt splices sitting on a top plate today.  They used one of those El Cheapo crimper/mashers and I could pull one leg apart.  (FWIW - that Harbor Freight crimper does a nice job.  Can't put those splices apart.)

           

           

           The ToolBear

          "Never met a man who couldn't teach me something." Anon.

          1. User avater
            BillHartmann | Mar 29, 2007 03:58pm | #39

            How about Red or Turquoise receptacles.http://www.lutron.com/products/ColorsOfLutron.aspx?pid=Satin&cid=0http://www.lutron.com/products/ColorsOfLutron.aspx?pid=Matte&cid=0http://www.lutron.com/products/ColorsOfLutron.aspx?pid=Metal&cid=0
            .
            .
            A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

          2. toolbear | Mar 30, 2007 05:42am | #40

            How about Red or Turquoise receptacles.

            Saw a merlot there.  Curiously, I had been looking in my Leviton catalog and lusting after the hospital grade toys.  Bright red, custom wall plate: "Do not touch this switch!"

            They have black marble in the Decora series.  Or walnut.  White or ivory is so dull.  Blue surge supressor recpt. - I'll look into those. The ToolBear

            "Never met a man who couldn't teach me something." Anon.

  2. User avater
    SamT | Mar 27, 2007 07:05am | #2

    There is a very very slim chance that the seperate ground might help in a SOHO situation, but it means running the computor outlets to a seperate ground rod and then bonding that rod to the main ground rod.

    Even more effective is to slip an RF choke over the romex as it enters the oultlet box.

    This presumes, of course, that there is a large enough "noisy" load on the same transformer as the building the computors are in. Unless somebody crossed wires inside a microwave and ran its' romex thru the computor outlets themselves, that ain't gonna that much "noise" in a house.

     

    SamT

    Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

    1. User avater
      BillHartmann | Mar 27, 2007 04:41pm | #4

      "that ain't gonna that much "noise" in a house."Need to qualify it, only ELECTRICAL noise.None of these will have any affect on spousal unit noise..
      .
      A-holes. Hey every group has to have one. And I have been elected to be the one. I should make that my tagline.

    2. woodturner9 | Mar 27, 2007 07:04pm | #6

      ran its' romex thru the computor outlets themselves, that ain't gonna that much "noise" in a house.

      In my experience, it's primarily electrical noise caused by flourescent lights, other electronic equipment (such as computers) and ground loops.  You wouldn't think it would be much, but it can be enough to cause problems for sensitive electronics such as computers, radio equipment, and X10 modules.  Often the problem is that the offending equipment is generating more noise than permitted - for example, removing and reinstalling the cover of a computer is often sufficient to significantly increase the noise it radiates, both through the air (i.e. RF) and through the power line (coupled noise).  All those gaskets, filters, and seals are critical to achieving the rated noise performance, and almost insignificant changes to them can have significant consequences.

      For those interested in learning more about these issues, here are a couple of references:

      High-Speed Digital Design: A Handbook of Black Magic, by Howard Johnson

      Noise Reduction in Electronic Systems, by Henry Ott

      Ott is the standard reference in the field, and is probably more readable for most folks, but if you want the detailed nitty-gritty, Johnson will give you that.

       

       

      1. User avater
        SamT | Mar 27, 2007 09:24pm | #9

        We usually use 4 guage bare copper.  To reduce the likelihood of ground loops, it's best to route the ground with the cable. 

        I was Roaring at that line. You're worried about ground loops, but you're using bare copper. LOL

        BTW, I've got 9+ years maintaining and repairing military communications equipment. RFI and excess noise is of prime concern in that field.SamT

        Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

        1. woodturner9 | Mar 27, 2007 09:50pm | #10

          You're worried about ground loops, but you're using bare copper.

          Why would you think insulation on a wire would affect ground loops?

          Noise is caused when the ground path and the current path in a loop are different, so that inducing sources affect one path more than another.  That imbalance creates the noise.

          If you only have 9 years experience in the field, Ott may be a little before your time, but it's still the standard in the field.  He explains it in a lot more detail that I can get into here.

          woodturner9

          30+ years experience designing military and commercial communication systems, include ship comm, manpack, DS and FH spread spectrum, telephony......

          :-)

           

          1. paul42 | Mar 27, 2007 10:44pm | #11

            Sometimes real world experience has value.  Not that I'm claiming any - I'm just another design engineer. 

            But the problem with the bare wire makes sense to me anyway.  To avoid ground loops, make sure that the wire is connected to ground in one and only one place - which is a lot easier to do with an insulated wire.

             

          2. DanH | Mar 27, 2007 11:27pm | #12

            Yep, that would be my take -- the ground for an isolated ground outlet should be insulated all the way to the panel.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          3. woodturner9 | Mar 28, 2007 12:54am | #13

            But the problem with the bare wire makes sense to me anyway.  To avoid ground loops, make sure that the wire is connected to ground in one and only one place - which is a lot easier to do with an insulated wire.

            Thanks for your comments.

            Make sense, and probably more of an issue in buildings with metal studs or other sources of metal that could short out.  My residential experience is almost exclusively with conventional wood construction, so that is less of an issue.  Still, there are water pipes, stray nails, and other sources of metal, so insulated wire or zipper tube probably would be a better choice.

          4. DanH | Mar 28, 2007 02:16am | #14

            Certainly the bare ground in standard romex (or plastic conduit) will count as "insulated" from this perspective (not code/standards-wise, but in terms of effectiveness), PROVIDED that it's not allowed to contact other metal items (including other ground wires) along the way.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

          5. woodturner9 | Mar 28, 2007 03:30pm | #25

            Certainly the bare ground in standard romex (or plastic conduit) will count as "insulated" from this perspective (not code/standards-wise, but in terms of effectiveness), PROVIDED that it's not allowed to contact other metal items (including other ground wires) along the way.

            Agreed.  The only issue would be if you want or need the lower inductance of the larger wire - but I can't imagine that would be an issue for residential applications.

          6. User avater
            SamT | Mar 28, 2007 02:35am | #15

            Others have covered my concerns.

            Almost thirty years since I got out of the field of correcting electrical engineers theoretically incomplete work.

            Such incomplete theorys as not including the possiblity that a bare wire may contact another conductor causing its' reactance/length to be different than the parallel conductor it is supposed to be matching.SamT

            Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

          7. woodturner9 | Mar 28, 2007 03:35pm | #26

            Almost thirty years since I got out of the field of correcting electrical engineers theoretically incomplete work.

            Ah yes, the typical technician response - "I don't understand, so the engineer must be wrong".

            There is a reason technicians are technicians, and engineers are engineers.  Techs usually have more "hands on" experience implementing circuits, and can be invaluable in solving issues related to implementations, such as manufacturing issues.  Unfortunately, they don't usually have the theoretical understanding or training, even if they are EETs.

            Engineers, on the other hand, have the training to understand and apply the theory.

            Put another way, engineers understand the "why", techs work on the "what".

            But many techs will always believe they are "correcting" the engineer's "errors".  Most engineers have had to deal with those "corrections" and fix them. I suppose it's just the way of things, and not likely to change.

             

             

    3. toolbear | Mar 28, 2007 06:28am | #19

      Even more effective is to slip an RF choke over the romex as it enters the oultlet box.

           Any particular type of choke?  Off to Radio Shack for one?

      This presumes, of course, that there is a large enough "noisy" load on the same transformer as the building the computors are in. Unless somebody crossed wires inside a microwave and ran its' romex thru the computor outlets themselves, that ain't gonna that much "noise" in a house.

           Then those isolated ground circuits should work just fine.  <g>  A bit of witchdoctoring never hurts.

       The ToolBear

      "Never met a man who couldn't teach me something." Anon.

      1. User avater
        SamT | Mar 28, 2007 07:15am | #22

        Any particular type of choke?  Off to Radio Shack for one?

        What I'ld do. Actually, since I dismantle computors, I'ld just take 'em out of the junk pile. Every computor power supply I've taken apart has one.

        A bit of witchdoctoring never hurts.

        Whaddid I say.

        It will, in fact, knock 3 to 6 decibels off any noise that might be there.

        Add a 0.47 picofarad capacitor across the white and black terminals of the outlet and take another 3 -6 DB off off of any high-freq noise. Radio Shack :)

        None of this "noise reduction" will prevent damage from a voltage spike; they last more than a millisecond! Only a surge protector can do that. Make sure your client understands this before he sues you for a new computor system.

         SamT

        Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

        1. woodturner9 | Mar 28, 2007 03:45pm | #27

          Add a 0.47 picofarad capacitor across the white and black terminals of the outlet and take another 3 -6 DB off off of any high-freq noise. Radio Shack :)

          None of this "noise reduction" will prevent damage from a voltage spike; they last more than a millisecond!

          Just sticking in any old capacitor or inductor is NOT safe design practice.  At least make sure the voltage and current ratings are adequate.  You won't find a suitable inductor in a PC.

          An inductor (i.e. your "choke") CAN reduce the magnitude of a spike - an inductor "slows down" current changes, so the voltage spike can be attenuated by the inductor because the current can't surge (V=IR).  However, it has to be properly sized for that application to be effective.

          A surge supressor in it's simplest form is simply a capacitor between hot and ground and neutral to ground.  A slightly better supressor will use a Metal Oxide Varistor (MOV) - because the response time is better than a capacitor.  A medium to high end surge suppressor will use a pi circuit - a combination of capacitors and inductors - to form a low pass filter to reduce the spike.

           

           

          Edited 3/28/2007 8:50 am ET by woodturner9

          1. User avater
            SamT | Mar 28, 2007 05:27pm | #30

            At least you are a good copy editor. I left out the descriptor "ceramic" as in 0.47 pf ceramic capacitor. And in case you haven't picked up on it yet, I have been talking with ToolBear about that which would impress his client, both of us being aware that none of it is needed.

            Unfortunately, they don't usually have the theoretical understanding or training, even if they are EETs

            Fortunately, this one does. Or did, I literally have forgotten more theory than you been taught.

            I have designed radios and radars, even designed transistors and vacuum tubes. Had to in order to graduate. Then I went into the field and saw what school left out.

            There is a reason technicians are technicians, and engineers are engineers.  Techs usually have more "hands on" experience implementing circuits, and can be invaluable in solving issues related to implementations, such as manufacturing issues.  Unfortunately, they don't usually have the theoretical understanding or training, even if they are EETs.

            Engineers, on the other hand, have the training to understand and apply the theory.

            Sounds like an architect talking about builders.

            But, I'll make you a bet, if I lose, I'll rejoin the Tavern and buy you a beer, if you lose, you go to the tavern and put one in the chiller for me foe the next time I visit there.

            The bet is that I have more hours in electrical theory classes than you do, incuding your lab time and your CE time.

            Let's see 97 weeks times 40 hours is 3880 hrs theory and design, plus 71 x 40, or 2840 hours of specific equipment class, but I'm not incuding the equipment classes in our bet. Just the 3880 theory hours. Or we could bet on final GPAs, kick out the highest and lowest and average the rest. But I warn, of the roughly 90 scores in my record, only one was below 95%.

            Did I mention that I also taught some of those classes?

            The Navy schools of 40 years ago are a whole 'nother story than today.SamT

            Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

          2. woodturner9 | Mar 28, 2007 05:45pm | #32

            Let's see 97 weeks times 40 hours is 3880 hrs theory and design, plus 71 x 40, or 2840 hours of specific equipment class, but I'm not incuding the equipment classes in our bet. Just the 3880 theory hours. Or we could bet on final GPAs, kick out the highest and lowest and average the rest. But I warn, of the roughly 90 scores in my record, only one was below 95%.

            In my experience, your level of training and experience is very unusual for technicians.  Good techs such as yourself are VERY hard to find in this day and age.  Just finding a new grad tech who knows how the pins are numbered on an SOIC can be a challenge.  Even with a few years experience, the "kids" don't seem to "get it".  It's the same issues that plague engineering (and many other professions) - the financial rewards aren't there to attract and retain those who do their job well.

            Haven't thought about training hours in a long time.  One could argue that contact hours are different than "training" hours, but I'll stipulate to that. 

            Undergrad: 245 credit hours x 15 class hours per credit = 3675 hours

            Masters:  45 credit hours x 20 class hours per credit = 900 hours (plus the thesis, which is counted as 15 credit hours)

            Ph.D: 45 credit hours x 20 class hours per credit = 900 hours (plus the dissertation, which is counted as 45 credit hours)

            So I guess that totals out to 5475 theory hours in EE.

            I'm not sure grades are a good indicator of ability - I've worked with a lot of 4.0 idiots and far more really sharp B students.

            But FWIW, I did get one B as an undergrad, which dropped my GPA to 3.93.  For masters and Ph.D, grades don't mean so much - everyone gets A's or they don't remain in the program.

            But what the heck - I'll buy anyway.

             

             

          3. User avater
            SamT | Mar 28, 2007 06:10pm | #34

            But what the heck - I'll buy anyway

            Then I guess I'll just have to buy the house a round. When I get there (|:>)

            In my experience, your level of training and experience is very unusual for technicians.  Good techs such as yourself are VERY hard to find in this day and age. 

            Yeah, I went in the Navy in the "Golden Age" of electronic discovery and had an existing background education from a HAM BIL and a pushy mother.

            Just finding a new grad tech who knows how the pins are numbered on an SOIC can be a challenge.  Even with a few years experience, the "kids" don't seem to "get it". 

            I had two techs working for me on a satcom system. One was so smart, he aced all his schools, but couldn't find a blown fuse or change it out without blowing something up. The other barely made it thru school and would never advance in grade, but he could tell you to the day two weeks in advance when something on that contraption would break and exactly what it would be.

            I've known engineers that I would pay to work for and others who thought wrapping ribbon cables in foil tape and stuffing them back into (Intel BLC) computor cases was a good idea. True story.

            Every field of endeavor has people who fit any possible combination of genious and idiocy in their hands and heads. God happened to have blessed me with geniosity in both.

            Anybody who can get a masters and use it in practical ways has my respect.

            BTW, make it a Bud, I've got real plebian tastes.SamT

            Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

          4. DanH | Mar 28, 2007 07:42pm | #35

            The old engineer/tech, doctor/nurse, captain/sergeant argument has been going on for millenia. Practical knowledge vs book learnin'.In my experience, though, the real argument is about arrogance. Both parties tend to arrogantly believe that the other has nothing to offer and discount their opinions. In some cases this is amplified by an "imposter complex" -- the feeling that one is living a lie -- while in other cases (especially medical and military) folks are actually trained to pretend to be sure of themselves when they aren't.IMO, it's important to show a little humility and try to find out what the other party has to offer. This seems to be an ability that skilled leaders have.
            So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

      2. woodturner9 | Mar 28, 2007 03:49pm | #28

        It does sound like it would be helpful to learn more from the client about what they want to accomplish with the isolated grounds.

        If they are primarily concerned about power line transients causing damage, there are "whole house surge supressors" that are installed at the panel to protect the whole house.  There are some pretty expensive units out there, but in our testing, the $20 units that look like a large cylindrical capacitor work as well.  They mount on the side of the box, and if they take a large enough hit, they absorb it, but the case ruptures and drops "sand" on the floor - which is the indication they need to be replaced.  However, it's rare to get that big a transient in residential applications (I have never seen it), so normally they just work fine forever.

        1. toolbear | Mar 29, 2007 05:58am | #37

          It does sound like it would be helpful to learn more from the client about what they want to accomplish with the isolated grounds.

          It would, but he is off to London on business - and we hope to get a few facts on the ground in his absence to slow the changes.  Or put the bathroom complex on casters.  It's moved around enough on the plans.

          Foolish moi - asked if he wanted a isloated ground for the computer.  He figured one on each side of the office would work just fine. 

          We'll chain them together and see about running it to the panel rather than the sub.The ToolBear

          "Never met a man who couldn't teach me something." Anon.

          1. woodturner9 | Mar 29, 2007 03:22pm | #38

            We'll chain them together and see about running it to the panel rather than the sub.

            If you are going to daisy chain them, there is probably not much benefit to running them back to the panel instead of the subpanel.

            The engineer in me cringes when we talk about daisy chaining them.  Daisy chaining increases the inductance and more significantly, the number of connections.  From a pure engineering standpoint, it's much less effective.

            FWIW, that's one reason why the NEC requires the system ground to be a single, unspliced wire - because in the case of a lighting strike or other fast, transient ground fault, the impedance of a connection becomes significant.

            However, that really means less effective at higher frequency.  So if you are seeing 1 pS transients, maybe even 1 nS transients, it might make a difference.  In practice, transients are normally 1 mS or longer - 1,000,000 times slower.

            So, in practice, daisy chaining them should be fine, unless the house is subject to some very unusual conditions (like sitting in the near field of a broadcast antenna, or something like that).

             

          2. toolbear | Mar 30, 2007 05:46am | #41

            So, in practice, daisy chaining them should be fine, unless the house is subject to some very unusual conditions (like sitting in the near field of a broadcast antenna, or something like that).

            Nothing in the area like "Radio Noventa - Cinquenta Milliones de Potencia" (sic) - kids around there probably had three arms.  No lighting the fluor. tubes without wiring them up.The ToolBear

            "Never met a man who couldn't teach me something." Anon.

  3. woodturner9 | Mar 27, 2007 03:40pm | #3

    We are doing a remodel and the owner wants four isolated ground circuits in his office.

    Does that mean four home runs for four outlets or can one daisy chain the grounds between the four boxes (box to box, recpt. to recpt).?

    Yes, that's what it means - a separate, distinct ground wire from each circuit run directly back to the common ground point (usually the service panel).

    It's helpful to make these large wire - you want the lower impedance to get the maximum benefit.  We usually use 4 guage bare copper.  To reduce the likelihood of ground loops, it's best to route the ground with the cable.  We zip tie the ground wire to the NM-B every foot or so, to ensure that the ground stays physically close to the hot so we don't get ground loops (which introduce noise).  Alternatively, "Zippertube" may be a more practical option if the wallboard is up and you have to pull cable.  This is a "sleeve" that opens up to install the wire, then zips up to essentially for a single cable.  It's also available with a good braided ground in the sleeving.  Down side is that it is kind of expensive - $5 to $15 a foot (and that is WITHOUT the cable).

    This will function as a safety ground (and thus meets NEC), but the primary benefit is for equipment protection and reduced electrical noise.



    Edited 3/27/2007 12:08 pm ET by woodturner9

    1. User avater
      SamT | Mar 27, 2007 05:00pm | #5

      ROARSamT

      Anyone who doesn't take truth seriously in small matters cannot be trusted in large ones either. [Einstein] Tks, BossHogg.

    2. toolbear | Mar 28, 2007 06:32am | #20

      Yes, that's what it means - a separate, distinct ground wire from each circuit run directly back to the common ground point (usually the service panel).

      I had best update my panel plan to show four more home runs.  The ToolBear

      "Never met a man who couldn't teach me something." Anon.

  4. woodway | Mar 27, 2007 08:16pm | #7

    What does he/she mean by isolated ground? Ask the owner just what they want to accomplish and then you'll ahead of the game. I've run into more than one computer savvy owner, that dug deep into some obscure computer magazine or serious conversation with an electrical engineering friend, only to come away with completely harebrain grounding/bonding ideas.

    1. DanH | Mar 27, 2007 09:09pm | #8

      A point with regard to computer or entertainment equipment: With any grouping of interconnected equipment it's vitally important that all equipment be connected to the SAME ground. More important than having a "clean" ground is not having ground potential between the units.
      So convenient a thing it is to be a reasonable Creature, since it enables one to find or make a Reason for everything one has a mind to do. --Benjamin Franklin

    2. toolbear | Mar 28, 2007 06:16am | #17

      What does he/she mean by isolated ground?

      I think it is a style points issue.  Those orange outlets are rather dashing, and it might work.  I was expecting one for the office, but he got the pen and one became four.

      He also wants phone drops by each can.  I though that was what cell phones were for.  I am looking for a large structured wiring panel for all that.

      He is off to London and we want to get stuff in before it gets moved around, again. 

      Whatever, it's T & M. 

       The ToolBear

      "Never met a man who couldn't teach me something." Anon.

  5. renosteinke | Mar 28, 2007 02:57am | #16

    "A little knowledge is a dangerous thing."

    "Isolated ground" means separate from the ground path provided by the conduit. When you are using romex and plastic boxes, ALL of your circuits are "isolated grounds."

    There have been various reasons given for IG circuits in the past; most of these ideas have failed to accomplish anything. IBM, who are mainly the ones guilty of starting this, has since backed away from the concept.

    Simply put, a number of electronic things (surge suppressors are but one) use the ground wire in their operation. What matters is that there is a good, low impedance ground path back to the panel.

  6. jrnbj | Mar 28, 2007 05:01pm | #29

    All the replies seem to be assuming that there is an existing problem with noisy power circuits.....not that I'm any kind of expert, but I've never heard of a little AC noise affecting a typical office computer setup. Typically the spec. is for dedicated circuits, which makes sense-you don't want some bozo blowing the breaker & loosing all your data on a shared circuit. Isolated ground seems like gold plated specification to me....

    1. paul42 | Mar 28, 2007 05:29pm | #31

      The isolated ground seems gold plated to me as well.

      Just add in a whole house surge suppressor and use a decent UPS - problems solved.

      1. woodturner9 | Mar 28, 2007 05:46pm | #33

        A UPS is likely to be a far more satisfactory solution to the client's concerns, based upon what we all speculate are his "real" issues.

         

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity

Learn about different approaches to making updates and repairs to older homes with historic charm.

Featured Video

A Modern California Home Wrapped in Rockwool Insulation for Energy Efficiency and Fire Resistance

The designer and builder of the 2018 Fine Homebuilding House detail why they chose mineral-wool batts and high-density boards for all of their insulation needs.

Related Stories

  • Podcast Episode 684: Masonry Heaters, Whole-House Ventilation, and Porch Flooring
  • FHB Podcast Segment: Repairing an Old Home While Maintaining Its Integrity
  • Tools and Gear for the Moms Who Get it Done
  • An Easier Method for Mitered Head Casings

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 81%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data