Last word on vapor barrier in midwest?
rasher | Posted in Construction Techniques on July 23, 2008 05:41am
I wish I could understand this issue enough to feel confident:
I live in Kansas City, Missouri. We have freezing cold, dry winters with the humidifier blasting away. Then we have suffocatingly wet hot summers with the AC working away to cut the humidity.
I’ve got an exterior wall on my uninsulated house house opened up on the interior side and I’m going to install some fiberglass batt insulation. I also have the siding torn off to reside, so I’m going to install 15# asphalt paper under the siding.
Which side of the wall do I install the paper side of the fiberglass batt?
Thanks!
    shelternerd | Jul 23, 2008 05:55pm | #1
    Paper to the sheetrock.
    But also address the reason you need to run a humidifier in the winter with a blower door and duct blaster test. Your low humidity is created by cold dry exterior air being pulled into the house to make up for hot moist air escaping likely through your ceiling plane. When your furnace warms up that exterior air its relative humidity drops and causes the problems you are trying to address with the humidifier. Cut down on bulk air exchange and you'll reduce your need to run the humidifier and improve year-round HVAC efficiency and indoor air quality over-all.
    All this starts with an energy audit.
  2. Jim_Allen | Jul 23, 2008 05:56pm | #2
    You install the vapor barrier on the warm side.
    If you install it on the cold side, the interior moisture will migrate through the drywall and fiberglass insulation. When it hits that cold moisture barrier it will condense into small beads of water. You've seen these beads on your window panes. The water will run down and create a nice wet condition at the sole plate. It will rot everthing down there. Also, the wet insulation will lose some efficiency.
    1. rasher | Jul 23, 2008 06:37pm | #5
      I know everyone says to "install the vapor barrier on the warm side". However, in the midwest, the "warm side" is to the exterior from June 15 to September 15 and to the interior from November 15 to April 15. So which is it? Vapor barrier to the exterior or interior?And I understand that need for continuous vapor barrier in the form of plastic stapled to the face of studs over unfaced FG batts. However, many owners of 100 year old homes around here swear by blowing in cellulose insulation into the stud cavities. When you do that, where is the vapor barrier?In my particular situation, I am looking at eventually tearing off the existing siding, rewrapping the exterior with asphalt paper and residing the whole house with Hardiplank. At most locations, I can't tear out the existing plaster at the interior to install plastic vapor barrier. With these conditions, is there sense in blowing in cellulose while I have the siding torn off? Or will I be introducing the danger of moisture getting trapped in the wall?
      1. frammer52 | Jul 23, 2008 07:51pm | #6
        I would blow the cellulose and use some vapor barrier paint.
        1. rasher | Jul 23, 2008 08:15pm | #7
          Vapor barrier paint? Isn't all latex some sort of vapor barrier? See, that's why I think the conventional logic about having only one "vapor barrier" in a wall assembly is flawed. I every wall, there are several "vapor retarders" and no vapor "barriers".
          You've got the paint layer. The paper attached to FG batt insulation. The Tyvek or Asphalt paper. The exterior paint. All serve to "retard" vapor permeation, but none are impervious.
          1. DanH | Jul 23, 2008 08:30pm | #8
            Tyvek isn't a vapor retarder to any significant degree.
            It is an ironic habit of human beings to run faster when we have lost our way. --Rollo May
          2. fingersandtoes | Jul 27, 2008 02:04am | #27
            'See, that's why I think the conventional logic about having only one "vapor barrier" in a wall assembly is flawed. I every wall, there are several "vapor retarders" and no vapor "barriers".'
            One vapor barrier or alternative wall assemblies using multiple retardants- what is important is to have a strategy to deal with the moisture that can damage walls.
            You can do this in a number of ways. The one that we use here is to have one vapor barrier (6 mil poly) on the inside to stop moist air from migrating through the wall. The outside is left porous, with gaps in the sheathing and breathable building paper, to allow any moisture in the wall to dry to the exterior.
            It is the conventional approach which is being challenged by approaches using rigid insulation and exterior sheathing as air barriers, or as Matt suggests allowing the wall to dry to the inside. However, if you are content with the fairly inefficient wall that results from batt insulation, this wall assembly is the one most commonly in residential construction, and properly built has few problems.
            Edited 7/26/2008 7:08 pm ET by fingersandtoes
  3. DanH | Jul 23, 2008 06:16pm | #3
    Vapor barrier goes to the inside. Inside or outside only becomes an issue farther south (eg, in FL), in areas where you'd commonly see condensation (not just morning dew) on the outside of windows during much of the summer.
    hammer1 | Jul 23, 2008 06:17pm | #4
    Only homeowners use paper or foil faced fiberglass around here. Unfaced batts are the norm with a poly vapor barrier on the inside. Without a continuous and effective vapor barrier, there will be condensation in the wall cavity. Wet insulation looses it's effectiveness and creates the conditions for mold growth or worse. The insulation should fit correctly, without stuffing and make contact with the surface of the drywall.
      Matt | Jul 26, 2008 09:13pm | #22
      >> Only homeowners use paper or foil faced fiberglass around here. Unfaced bats are the norm with a poly vapor barrier on the inside.  <<   Careful how you dole out your good intentions...  We used to use poly vapor barriers here but it went out of vogue because a lot of people felt it caused moisture to be trapped in the wall cavity and cause mold.  This is particularly true since most modern wall sheathings have very low perm ratings.  Right now I'm building some to-be Energy Star certified homes and the certification company (building scientists) are having us use NO vapor barrier - just un-faced bats.  I'm sure your method is good for where you live but this is not a one-size-fits-all issue.
      1. frammer52 | Jul 26, 2008 10:34pm | #23
        Same here, upstate NY>
          Matt | Jul 26, 2008 11:15pm | #24
          same what?
          1. frammer52 | Jul 27, 2008 12:15am | #25
               no vapor barriers
            Matt | Jul 27, 2008 12:58am | #26
            10-4
    rjw | Jul 23, 2008 08:53pm | #9
    I'm with the wet blown cellulose - it's said to eliminate the need for a vapor barrier.
    As someone noted, you need to improve weatherization - cut down on air exchanges.
    Remember Mary Dyer, a Christian Martyr (Thank you, Puritans)
    http://en.wikipedia.org/wiki/Mary_Dyer
    May your whole life become a response to the truth that you've always been loved, you are loved and you always will be loved" Rob Bell, Nooma, "Bullhorn"
    1. DickRussell | Jul 25, 2008 06:15pm | #10
      Wet or dry blown cellulose is not a vapor retarder. It is quite pourous to diffusion of water vapor. Packed densely, it does fill the spaces in the cavity and retards convective air flow far better than a fiberglass batt.In the OP's location, I would avoid use of poly or foil vapor barriers (and vinyl wallpaper) and stick with vapor retarders, to allow some drying through it over time when conditions require it. Latex paint on the inside will provide the vapor retarder, as would the paper on a FG batt. However, most water vapor transport typically via convective transport in the form of air leaks from the warm/moist side into the wall cavity. Sealing up the cavity against such leaks should be done before worrying too much about vapor retarders.Oh, and in the summer, don't run the A/C colder than the dew point of the outside air.Why do we keep getting posts about vapor retarders and barriers? All this has been fairly well hashed over in this forum and elsewhere.
      1. DanH | Jul 25, 2008 06:20pm | #11
        > Why do we keep getting posts about vapor retarders and barriers? All this has been fairly well hashed over in this forum and elsewhere.Because there's no agreement.
        1. rasher | Jul 25, 2008 08:40pm | #13
          Because there's no agreement. Exactly.
      2. fingersandtoes | Jul 25, 2008 06:22pm | #12
        Because we are vapor retards?
      3. frammer52 | Jul 26, 2008 04:46am | #16
        ick as you know this site is filled with both pros and dyi'ers and that's why it must be rehashed.
        That plus many of us have a hard time with this.
        1. DickRussell | Jul 28, 2008 12:40am | #28
          "Dick as you know this site is filled with both pros and dyi'ers and that's why it must be rehashed."I knew right after I hit "post" I shouldn't have added that last line. And right after that I knew how to answer my own question. There are many situations, covering many different climates (cold, hot/humid, and everything between), and involving both new construction and refurbishing older structures. The same principles apply to all of them, but the solutions are widely varied.The nicest thing about this forum and others is that all such issues get hashed over thoroughly, with reasons for and against every "solution." The whole process contributes to furthering the education of all of us in building science issues. Repetition is a good thing, as it leads to more widespread education on the issue. And that is good.(Stepping down off soap box)
          1. frammer52 | Jul 28, 2008 01:00am | #29
            I knew you know that, I figured you had a bad day!
            Matt | Jul 28, 2008 01:38am | #30
            An annual (for example) re-hashing can be good.  Things change.  New studies are done.  New materials become available.  We all learn new stuff both by reading and via the hard way.  I agree though that the weekly rehashing is just a waste of bits and bytes.
            BTW - I often go back and edit my posts after I look at them "in print".  OTOH, I don't edit them after someone else has commented on my remarks.
            Also, some years ago I asked for a FAQ folder that would be controlled by the man behind the curtain.  You know - how to cut crown, best windows, how to hang a door... etc.  Another brilliant idea trashed by the alternate agendas of corporate America.. ;-)
          3. fingersandtoes | Jul 28, 2008 03:18am | #31
            Yeah, hashing is good. From my point of view probably the most important criterion for evaluating new wall assemblies is how forgiving they are. How will they perform of they aren't installed perfectly, or are modified by future work? Does a little water penetration lead to complete failure? I'd select for longevity over optimum initial performance any day. That's why I'm wary of any new approach until it has been used for a while and had a good hashing.
          4. arcflash | Jul 28, 2008 03:56am | #32
            Well put. There have been alot of "technological" breakthroughs that amount to sh!t, especially in the '70s. I do know that vapor barriers are code in Canada, and codes are enforced to protect people. Believe it or not,your Building Department and inspectors are looking out for you. They are not the enemy. I have learned alot from quite a few of them just by asking questions, and the vast majority are more than excited to answer them for you.
            Houses can't be built like they were 100 years ago anymore. We have used up most of the good resources that people mistake nowadays for good craftmenship. Anyone can build a shoddy structure out of good material and it will still last a long time. So new technologies are now used to supplement the fact that you can't build with 100 year old heartwood anymore. That's the reason why mold lawsuits have gone through the roof. 100 year old heartwood is far more resistant to mold and decay than six year old sapwood pine boards. Its just a fact. Knowing that, if I feel like a roll of Tyvek will protect my house if water gets past the siding, or that a layer of 6 mil plastic will protect the framing in my bathroom, I'm all for it.
            My mom's house was built 90 years ago and is just about ready to fall off of its foundation. The craftsmen of that time didn't believe in footers, apparently. The house is very drafty, and there is mold somewhere in about every area of the house. I like the interior trim details, alot, and the siding appears to be spruce (too yellow to be cedar, and I'm not sure I would recongnize cypress if I saw it, as its not readily available around here) and is holding up pretty well. Matter of fact, the trim and the siding might be the only things holding the house up! I'm not a purist. First and formost, I have to live in a house and feel comfortable, dry, and safe. Secondly, I'll worry about matching architectural details with those of a particular era.
            Its about finding a balance. You want to be energy effecient and prevent water vapor from wreaking havoc at the same time. Its about knowing when to ventilate and when to close up a hole. Don't lose any sleep over it. I think someone said it best when they said "stopping water infiltration is more important than air infiltration". Basically, you just have to go for it. If it doesn't produce the desired result, try it again another way. We are talking about building here, not rocket science!
          5. fingersandtoes | Jul 28, 2008 05:26am | #33
            "100 year old heartwood is far more resistant to mold and decay than six year old sapwood pine boards"
            You should see the fast grown garbage cedar we get now, even though we live on an island of trees. I've used my bare hands to take apart five year old beams - digging through them like I was a superhero!
          6. DickRussell | Jul 28, 2008 07:34pm | #36
            I was thinking more about the OP's situation, refurbishing an old house that had no insulation in the walls. We can figure that likely wind-driven rain has been getting behind the siding and that the windows likely weren't flashed all that well. Fortunately for the house, it also likely leaks air like a sieve. Not so good for energy efficiency, but great for drying out the wood when it gets water inside. Maybe why the house has survived.Now, stuff some insulation in the walls and instant problem - maybe. If the insulation hold water, or retards the free flow of leaking air, then the leaks lead to mold and rot.The OP did say that he will be or has been removing siding, so that gives him the opportunity to insulate, then protect the wall cavity from water problems. I have to think that he will come out better than so many cases where an old house gets insulation blown in through holes, without addressing the issue of water getting in from the exterior.Somewhere else I quoted something from a buildingscience.com article on their site. Summarizing, it said something like don't worry about vapor retarders until you've kept water in liquid form out, and don't worry about insulation until you've addressed air infiltration and controlled water vapor diffusion. (I think I don't have that exactly right, but you get the idea)Edit: here is what it said:
            Today walls need four principal control layers – especially if we don’t build out of rocks. They are presented in order of importance: * a rain control layer
            * an air control layer
            * a vapor control layer
            * a thermal control layerA point to this importance thing here, if you can’t keep the rain out don’t waste your time on the air. If you can’t keep the air out don’t waste your time on the vapor.
            -----------Hopefully the OP will be reinstalling the windows, with sill pans or flashing and side & head flashing, using a good wrap, all properly lapped, and maybe even using a rainscreen of some sort under the new siding.
            Edited 7/28/2008 12:41 pm ET by DickRussell
          7. rasher | Jul 28, 2008 10:25pm | #37
            Thank you for the informative response. Here's where I am right now with a little siding repair job that got me thinking about this:1. Tore off junky 100 year old wrecked wood siding. Tore off asphalt paper. 1x8 solid wood sheathing looks good, a little spot rot at some portions of the "sub-water-table". The one window I worked around looks good (I completely renovated all of the windows inside and out last year), no rot at the head or sill. All in all, I think the house has been pretty effective at keeping water out.2. I epoxied the spots at the "sub-water-table" that were showing a bit of rot. Didn't look too bad to me, really.3. The windows all have a built up cornice at the top. This cornice is basically a 4/4 x 3 board that is sloped at the top edge, nailed from the top through the top edge of the head casing, and has "ears" that extend past the edges of the casing about 3 inches on each side. I know from repainting the house a few years ago that most of these cornices have metal "L" flashing that protects the top face of the board and goes up under the siding.4. What I did on this one window that I worked on this weekend (which is one of a couple that didn't have the flashing) was cut a peice of 3" x 4" "L" profile galvanized and nailed the 4" leg to the sheathing and the the 3" leg perfectly covered the top face of the cornice.5. Took a can of low expanding spray foam and filled in at the bottom edges of my walls where the subfloor hit the studs, where the floor framing hit the stone foundation, and any other holes I could get.6. Took 15# asphalt paper and started at the bottom edge of the sub-water-table and worked my way up. Most of the existing casing and corner trim, window sills, the window cornice, and other trim all had enough of a gap between it and the sheathing that I was able to get the edges of my asphalt paper about an 1" or so underneath the trim. Asphalt paper goes over the top of the metal flashing I installed at the window cornice.This is where I'm at now.What I'm planning to do:7. Cut a new 1x8 water table trim peice with a modified window sill trim board (replicating the existing trim) on top to create a large drip edge. This peice nails through the new asphalt paper to the "sub-water-table".8. Take a peice of galvanized "L" flashing and flash the top face of this large drip to the face of the new asphalt paper. Then get a strip of "peel-and-stick" and tape over the top edge of the flashing to the asphalt paper.9. Install fiber-cement siding per mfr. specs. I don't have the room to install this on furring strips, but Hardie specs say installation right over asphalt paper is fine.-----------------------------------------------That leaves me with a decent rain control layer on the exterior of the building (rain control). Most of the air infiltration is fixed (air control).What I'm contemplating now is a DIY foam insulation like Tiger Foam. I'm doing this project a little bit at a time as time and $$$ allows, so I can't afford the setup charges every time an insulation contractor would need to come out. Tiger Foam allows me to buy the foam kits I need and install myself. Now generally, the plan would be to shoot in foam from the exterior prior to asphalt paper, but I didn't have time this time. I do have the plaster removed to the lath on the interior, so I think I'll install the foam from the interior and I'll be able to keep a close eye on how it fills.Anyway, the foam would then serve as the primary air control and also vapor control and thermal control, right?Any opinions or suggestions?
          8. arcflash | Jul 28, 2008 11:17pm | #38
            Wew! Thats alot to wrap my little 'noggin around. From what it sounds, you have it WELL under control! Its like the previous poster said, worry about the water first, then the air infiltration, then insulation. I don't have the poly spray in my wall cavaties, but if I could, I probably would. I've heard that it is great stuff(get it?)!
            I've got a little advice for the air infiltration issue. Your ceiling. Climb up into the attic and seal every penetration with caulk or foam. You'll see some savings on your bill, and you'll worry a little less about the condensation issue. The attic is hot in the summer, the hot air mixes with the conditioned cooler air and produces vapor. You'll likely see mildew or water stains around light boxes and other ceiling penetrations. Not to mention, you don't really smell that vapor in the air like you would an unsealed house. Other than that, you seem to have the exterior under control and it is way more important, by far.
          9. sisyphus | Jul 28, 2008 05:55am | #34
            I agree, there is nothing like the passage of time to test a technique. What I find most informative is what is revealed when repairs or renovations etc. cause a wall to be opened up and reveal it's secrets.
          10. arcflash | Jul 28, 2008 05:59am | #35
            I feel you there, bro. That's about the best part of it all.
      4. arcflash | Jul 26, 2008 05:32am | #17
        DickRussell nailed it. It doesn't matter what your climate is, warm air always tries to find cold air to mix with and produce vapor. Otherwise, heat rises. Basically, you just have to isolate the two extremes. Let the hot be hot, and the cold be cold, by themselves. Find the areas in your home that are on both ends of the spectrum, and isolate them so they don't mix. Do whatever it takes: caulk, expanding foam, paint, insulation, pipewrap, extra lumber, whatever. Close up the pathways that allow the two extremes to meet. But like one poster said, heat is a tricky little devil, if it can't use air to travel, it will just radiate on through.
        To clear up some of the confusion, latex is not a vapor barrier. Oil-based paint is. And also like someone said, a vapor barrier is not as important as air infiltration to prevent condensation.
        I like that one fella's piece-meal approach. Start from the outside and work your way in. It is much easier to tell what works and what doesn't from the exterior because that is where the problem is originating from anyways.
        Also, don't forget to check your HVAC system for leaky ductwork and the like. Tightening up your ductwork will save you money, and possibly prevent a problem before it even starts.
        1. Sasquatch | Jul 26, 2008 06:09am | #18
          Speaking of leaky ductwork...
          Today, I went to the Legends shopping center west of KC.  We had dinner at Ted's Montana Grill.  During the meal, we noticed moisture falling down on our table.
          After we had eaten, I walked back to the bathroom to wash my hands.  I almost tripped and fell (only had one brew!).  I noticed that the floor was buckled up in several  (about 20) places, as much as one inch, on my way to the men's room.
          Also, I saw several large water spots on the floor on the way back to my table.  On top of that, I looked up at the ceiling and noticed that water was raining down on the hardwood floor along the entire 30-40 foot trip from my table to the men's.
          I don't have to tell the BT members here what was buckling up the floors.  I waited for a chance to talk to the manager after paying for our dinner.
          He thanked my for my input and told me some big guys were there trying to figure out what was causing the problem.
          I don't think this needed any "big guys".
          1. frammer52 | Jul 26, 2008 06:20pm | #19
            Big guys include common sence?
          2. DanH | Jul 26, 2008 08:00pm | #20
            Cents when?
            BillHartmann | Jul 26, 2008 08:08pm | #21
            "I don't think this needed any "big guys"."Sure it does.There are 2 ways.First 'big guys' can stand on the buckled floor and hold it down.The other is that 'big guys' and go to the GC and say "Viny sent me to tell you to FIX THIS"..
  6. JohnT8 | Jul 25, 2008 11:48pm | #14
    Would the Mooney wall work in your situation?  In which case you wouldn't have to worry about a vapor barrier.
    http://forums.taunton.com/tp-breaktime/messages?msg=65624.1
    "A little 'enthusiasm' and all problems seems small!"
  7. Sasquatch | Jul 26, 2008 04:10am | #15
    I live just across the border in KS.  I fully understand the problems you are encountering and considering.
    If you were building a new home, you could take one of the many theories that apply to this climate zone and build well.
    When you are remodeling, you have to deal with what someone else created.  Each particular wall element has different issues regarding the original theory of vapor barriers that was used, the technology available at the time, the adherence of the contractor to the design, and the quality of the construction itself.
    As you dismantle the house, you will be able to see how good the results of the original construction were.  If the framing is in good shape and there is no apparent problem, say on the southern exposure, your main consideration will concern any desire to improve energy efficiency.  If it worked, you can always leave it alone, or you can enhance what is there.
    If you find a problem, you should be able to determine what happened and from that you will know what to do.
    On my current home, I categorize the walls according to directional orientation, sun and weather exposure, overhangs, and so on.  My plan is to work in sections of wall, floor by floor, getting each section right.  Once you have the exterior wall coverings removed on a section, it is not that much extra work or expense to remove the drywall on the inside.  Then you can apply your best theory.
    In any case, this process is far less expensive and far superior to having someone apply a layer of insulation and vinyl over what you have and replace all the windows.