Lighting on 20amp circuit

ralphk | Posted in Energy, Heating & Insulation on January 31, 2003 02:47am

My electrical sub has run a couple of 14 guage switchlegs (from the switch to the light fixture) that is being fed by a 20 amp circuit (breaker and 12 guage wire) for outlets.  Is this a real problem? I guess that since a single light isn’t pulling any significant amperage it shouldn’t overheat, but it sounds like it may be a code violation.  Any thoughts?

rk

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. junkhound | Jan 31, 2003 04:52pm | #1

    Make the sub fix it, yes a code violation.

    BTW personal preference is for outlets and lighting to be on separate circuits - e.g., if you trip a breaker with an overloaded outlet or if refrigerator and microwave start at the exact same time, , the lights won't go out also.

    1. ralphk | Jan 31, 2003 05:44pm | #2

      Junkhound-

      That's what I thought.  Actually, with the exception of these couple of lights, everything else is split between lighting circuits and outlets. I was just going through a last check before the electrical / plumbing and framing inspections and found a few things that didn't look right.  I'll definitely have it corrected.  Thanks again.

      rk

    2. JohnSprung | Jan 31, 2003 10:53pm | #3

      I agree as to no plugs on lighting circuits, and I also try to checkerboard the lighting circuits so that adjacent spaces are on different ones.  So if the breaker for the bedroom light trips, the hallway light is still on.

      -- J.S.

      1. billyg83440 | Feb 01, 2003 01:03am | #4

        I have a question. Why go to 14 gauge wire at all? I understand it is cheaper, but the difference in cost between putting lighting circuits on 14 ga. vs. 12 ga. can't really add up to that much? Even in a big house?

        Ok, 2 questions, I read an article last week that recommended upsizing your wire sizes where ever possible. The main reason given was that within a few years you would save enough electricity to more then pay for the upgrade due to decreased line losses. Does this make any sense to you? Seems to make sense to me on a heavily loaded circuit anyway.

        Frankly, I'm grateful all the wiring in my house is 12 ga. minimum. Even more grateful it's not aluminum like my last house. Even more more grateful that the last owner only wired a few things, his work was scary.

        1. espelt | Feb 01, 2003 01:13am | #5

          I just did a whole basement with 12ga.  You're correct, it's just pennies more for the material, but it is WAY stiffer to work with, needs bigger nuts, and for the life of me I can't get two 12ga ground wires attached to the little green ground lug on a switch or plug.  Just my $0.02.

          Eric

          1. MichaelMosel | Feb 02, 2003 01:44am | #10

            Try tying your two ground wires together first with a couple of twists, deep inside the box, low on the wires. Then cut one tail of the two off, and go to the green screw with the one tail you have left. Perfectly legal.

            Edited 2/1/2003 5:45:28 PM ET by MICHAELMOSEL

          2. ScottMatson | Feb 07, 2003 02:06am | #11

            I have just heard from a master electrician that this is no longer acceptable. Anyone have a definite read on this?

          3. billyg83440 | Feb 07, 2003 02:35am | #12

            Not sure if you can just twist them together.

            You can get the green wire nuts with a hole in the end. Do the same thing, but twist all the grounds together back in the box, leaving one wire long. Put the wire nut over the long wire and twist tight then hook the long wire to the outlet. The nut insures the grounds don't come loose.

            My house was wired w/ the ground wires stuck through a sleeve that was crimped tight around them. Not sure this is still legal either, or how much the crimping tool would be.

          4. DaveRicheson | Feb 07, 2003 02:50am | #13

            Crimping bells are still legal, but your inspector may have his own preferance. Luggers cost about $16.00 to $20.00 depending brand and/or where you get them.

          5. billyg83440 | Feb 07, 2003 04:06am | #14

            Thanks, if I did this for a living I'd buy one. As is, I'll spend 15 cents on the green wire nuts, they work well, but take up more space.

          6. Whitman | Feb 07, 2003 04:47am | #15

            Good evening all - Several responses:

            No. 14 conductors are not permitted on 20 ampere circuits that supply lighting and receptacle outlets as per Code. 

            Equipment grounding conductors must be mechanically joined and not just twisted together with one of them landed on the ground screw per Code.  All this takes is a wirenut either the type that has a hole in the end or one that doesn't which would require an additional short length of wire from the splice to the switch or receptacle.  This additional wire does not count as a wire when calculating box fill since it does not leave the box. 

            Also, landing two wires under a screw intended for a single wire is a definite no-no.  Just take a look at the wiring device instructions.  I've never seen more than one wire under a grounding terminal.  Electrical equipment must be installed according to any manufacturers instructions in accordance with Code.

            Regarding lighting connected to receptacle circuits, it seems the forum preference is leaning toward separating the two.  What all should realize that the Code requires, in areas that have not overridden the specific requirement, arc fault circuit interrupters on all circuits serving outlets, lighting, receptacle, smoke detectors, all, that are located in bedrooms.  If two circuits are in a bedroom then two expensive AFCI circuit breakers are needed.  And, if the lighting or receptacle circuits located in one bedroom serves another non-bedroom, then some other portion of the house will be effected.  My suggestion is one circuit per bedroom. 

            Edited 2/6/2003 8:49:36 PM ET by Whitman

            Edited 2/6/2003 8:50:31 PM ET by Whitman

          7. billyg83440 | Feb 07, 2003 06:54pm | #16

            Are AFCI's actually required now? About $70 ea. aren't they?

            I'd only heard that they might start requiring them in the next code reiteration.

            But, when I did wiring it was in the 96 NEC, havn't messed with the 99 one at all.

            Your other points are well stated. Though I had no confusion with any of them, and hopefully didn't convey such. I've never just twisted ground wires together w/o a wire nut. Wouldn't trust it even if it was allowed.

          8. User avater
            BillHartmann | Feb 07, 2003 08:46pm | #17

            The 99 code says that effective 1/1/2002 that all 15/20 amp recptacles in bedrooms had to be protected by arc faults.

            I dont' have the 2002 version of the code, but I think that it was changed to read all outlets, including lighting and wired smokes.

            Of course it depends on if your local has adopted the 99 or 2002 version yet. And I have heard that some locals with the newer versions are passing on the new requirements for the time.

          9. billyg83440 | Feb 07, 2003 09:13pm | #18

            Interesting. I've never seen an arc fault.

            Read a good explination of how they work once, but don't really remember it. The article suggested they may soon be required, but reccommended people wait as they were still unreliable and tended to trip when they shouldn't.

            Probably read this 4-5 yrs ago.

            How expensive are they for a 15 or 20 amp breaker? Sounds like you might need 10 or more of them for a house.

          10. User avater
            BillHartmann | Feb 07, 2003 09:41pm | #19

            I am not sure of the price, maybe $50-70.

            No, you should be able to get by with 1-3 in the typical 3-4 bedroom house.

          11. edlee516 | Feb 08, 2003 03:20am | #20

            Single-pole 15's/20's Cutler-Hammer or SqD Homeline are costing me $31.95 wholesale.  $68.57 for a 2-pole 15a.   'course I mark-em up :)

            Ed

          12. Englishbuild | Feb 08, 2003 11:47pm | #24

            Hi,

            We wire the homes with each bedroom on its own circuit , lights and receptacles. Why do we do this? 1. Because if a circuit in the bedroom trips it only takes out the lighting in that bedroom and the receptacles in that bedroom.  Each bedroom has a switch within reach of the door to activate hall light. 2. With todays electricals needs, hairdryers, curling irons etc. being used in the bedroom more and more. We feel this is a standard that best suits our clients.  We also zone the lighting so if any circuit trips only that zone will lose lighting. We also put the smoke detectors on their own circuit because in the event that a receptacle or light would arc or short and the breaker would trip after the short started a fire the smoke/fire alarms would still be functional.  We use detectors that have a light on when the circuit is closed. The electricians like this method, the homeruns are easier to layout and wiring schematic is neater and easier to read.

            Sincerely Yours.

            Dave

          13. edlee516 | Feb 08, 2003 03:25am | #21

            "I can't get two 12ga ground wires attached to the little green ground lug on a switch or plug."

            Espelt   - 

            When I read that it made me spit out my beer ....it's so un-selfconsciously wrong it made me laugh  :-)

            Peace and love dude, and stay away from electricity.  PLEASE.

            Ed

          14. espelt | Feb 08, 2003 08:31pm | #22

            I got it together right, eventually.  I guess that's why I'm having the basement permitted and inspected (most people around here don't).  Although I'm a Civil Engineer and have worked in construction, I'll be the first to admit I don't know everything.  Eric

          15. DaveRicheson | Feb 08, 2003 11:42pm | #23

            Article 210.12 (B)  NEC 2002

            All branch circuits that supply 125-volt ,singe phase, 15- and 20-amp outlets installed in dwelling unitbedroom shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.

        2. User avater
          BillHartmann | Feb 01, 2003 01:32am | #6

          There are two good reasons for using #14 on lighting circuits, at least in some cases.

          Lighting circuit often have 3 way or 4 way switches and sometime multiple ones in one gained box. That makes for a lot of box fill. Specially as in the job that I was doing it was surface mounted metal boxes. You don't have lots of choice in box size.

          When retrofiting circuits it is a lot easier to fish #14, specially 14-3.

          1. billyg83440 | Feb 01, 2003 01:50am | #7

            Thanks to all.

            I should have thought about the box fill, fishing, and stiffness issues. Never enough volume in boxes. Especially if forced to use a specific type or size.

            Still, I will use 12 ga.. Even if it doesn't help w/ line losses, I prefer it. 14 ga. just seems cheap after getting used to 12. Kinda like using particle board for drawer sides in a nice oak cabinet.

          2. junkhound | Feb 01, 2003 04:14am | #8

            When I was young and relatively foolish and even when romex was 5X the price as now in infaltion dollars, I put 12 Ga everywhere. 

            As I got older, all of the previous comments about the ease of using 14 AWG vs 12 AWG came into play fast, besides, is there anyone here who lights a ball field or something (e.g. - MJ crop<G>) that needs over 15 A on lighting circuits.

          3. fireball | Feb 01, 2003 04:59am | #9

            Using more circuits w/14's is a much better alternative than using 12's for every thing.If you use 12 for everything you're going to have either too many boxes or too many code violations.

            Edited 2/1/2003 11:59:53 PM ET by IBEW Barry

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Finding the Right Fixer-Upper

Get expert guidance on finding a fixer-upper that's worth the effort.

Featured Video

How to Install Cable Rail Around Wood-Post Corners

Use these tips to keep cables tight and straight for a professional-looking deck-railing job.

Related Stories

  • Guest Suite With a Garden House
  • Podcast Episode 688: Obstructed Ridge Vent, Buying Fixer-Uppers, and Flashing Ledgers
  • FHB Podcast Segment: Finding the Right Fixer-Upper
  • Keeping It Cottage-Sized

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 332 - July 2025
    • Custom Built-ins With Job-Site Tools
    • Fight House Fires Through Design
    • Making the Move to Multifamily
  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data