Make up air for kitchen exhaust

AXE | Posted in General Discussion on December 7, 2004 08:21am

One thing I dont see a lot of discussion about is making up air for a kitchen exhaust.  I have a spray foamed house and I plan on running the bathroom fans through an ERV.

But we cook a lot (and greasy stuff like stir fry, bacon & eggs, etc.) so I can’t get away with running the kitchen through the ERV.  The hood I’m using is a whopping 715 CFM (at high).  Where is that make up air going to come from?  All gas appliances are sealed combustion so I can’t backdraft anything.  I have tight windows and doors, all plates are caulked, etc. 

Should I just not worry about it and let it be (just won’t get full volume from the hood)?  It doesn’t feel right….I’d like to have a pressure detector in the kitchen and some kind of system that opens a damper and pulls in fresh air (possibly through a heater for the winter)?   Does such a thing exist?

Maybe I could wire into the hood and kick in some make up air into the basement with a grill cut in the floor to allow air to flow from the basement into the kitchen area.  At least I would get some conditioning of the air via mixing with the basement air (most of the basement is my workshop so cold air coming in there won’t bother me all that much).

-MERC

Reply
  • X
  • facebook
  • linkedin
  • pinterest
  • email
  • add to favorites Log in or Sign up to save your favorite articles

Replies

  1. VaTom | Dec 07, 2004 09:14pm | #1

    Doesn't sound like your house will be very leaky.  Any reason you aren't planning a whole house air system? 

    If that's what your ERV is, size the incoming fan larger to slightly pressurize the house, causing leaks to go out.  Much more comfortable that way and would give you some cushion for your intermittent kitchen exhaust.

    That's what we do, very satisfactorily.

    PAHS Designer/Builder- Bury it!

    1. AXE | Dec 07, 2004 09:36pm | #2

      Thanks for the reply.  If I remember correctly, you run your kitchen hood through your HRV right?

      I like the thought of pressurizing the house and I think I'll do that.  Honestly I'll probably need more than one ERV, we'll see how the budget goes.  It still seems like I need something that will match that vent hood, one for one when it is running.  I guess I could just pull out my old EE background and build something.

      I guess I was thinking an ERV or two would be my whole house air system.  I already have a forced air furnace, but I need something to do the air changing.  I just haven't gotten deep enough into that to know what it is yet.

      MERC.

      Edited 12/7/2004 1:50 pm ET by DJ Merc

      1. Hubedube | Dec 07, 2004 09:50pm | #3

         Your ERV or a HRV should have been adjusted when it was installed by an "air flow measure (magnahelic insrument) this measurement ,if done properly by a hvac pro will take into consideration other applances that may be running so as to avoid any 'negative'/ positive pressures within the home, thus the so-called 'make-up air is  drawn from the fresh air intake that the erv/hrv is giving it..

        1. AXE | Dec 07, 2004 10:05pm | #4

          Said ERV is not yet installed.  Are you saying the ERV will be adjusted to provide enough positive pressure such that when running my vent hood it will net out to a positive or zero pressure difference?   Seems like that ERV would be running at a much higher speed than necessary just to overcome the occasional kitchen hood usage.  I think an active system that kicks in when the hood kicks in is a better solution.

          How come HVAC industry just doesn't seem to have it figured out?

          MERC.

          1. Hubedube | Dec 07, 2004 11:37pm | #5

            Ah, but the HVAC industry HAS it figured out.

            Its because YOU aren't up to date on this Technology

             Controlled ventilation systems operate most of the day, and some never turn off. Passive air vents are installed to make-up any air that is nearing a depletion (negative)state,as it would be in the case of this absurd 715 cfm hood.

            what is this ,the kitchen at the waldorf?

             Btw, what type of heating do you have? If its a ducted forced air system, then your in luck if you want to install a few gadgets that maintain a neutral pressure (pressure balanced)thru-out the home, and very economically too.

            Edited 12/7/2004 3:40 pm ET by Hube

            Edited 12/7/2004 3:42 pm ET by Hube

          2. timkline | Dec 07, 2004 11:47pm | #6

            710 cfm fan = kitchen at the waldorf ?

            The fan at my sister's home is a Thermador which pulls 1400 cfm.  It is a residential unit that mounts on the side of the house.  Even that wouldn't do squat at the waldorf.

             carpenter in transition

          3. AXE | Dec 07, 2004 11:57pm | #7

            I stand by my assertion that the HVAC industry doesn't haven't it figured out.  Maybe the real answer is that it is figured out, it just costs a lot of money to make it right and therefore few have seen such an implementation.  Where as, for example, you can pretty much install a basic bullet proof electrical system for reasonable cost and commonly available materials, HVAC seems like a whole other world.  I also note that the HVAC trade (people and suppliers) hold their cards close and generally treat me like an idiot when it's obvious that I'm not that clueless, just need some help with a few details.  That is always a red flag that something is amiss with the industry.  But I'd be willing to accept the argument that you can build a wonderful system, it will just cost some money.

            I admit the hood is a little overkill, though maybe not for the wild stir fry nights that I have.  The grease really flys out of the wok.  At any rate, it was the only decent looking hood I could find in 42" width chimney style, so that is what we are using.

            I have forced air which I plan to run 4 zoned for the entire house, provided I can find a reasonable chase to the 2nd story from the basement.  I thought about putting some kind of controller on the furnace blower that would help maintain correct positive pressure in the house zones.  Just need to find said piece of equipment and controller for it.  I'm sure if I strolled into my local HVAC supplier, he wouldn't have any clue what I was talking about.

            MERC 

          4. User avater
            BillHartmann | Dec 08, 2004 01:51am | #8

            You might try asking over here.http://hvac-talk.com/vbb/BTW, you want to ask it in terms of asking that you are learning what it takes to make a good system to help qualify an HVAC contractor.I have not lurked overthere in a while. But in the past they appear to be very helpful, but if it appears that you are doing to DIY HVAC then they will start attacking.There are barametic dampners that will open on pressure differences. But I don't know how they work with a HRV system. Do don't want the dampner to open all the time because of a pressure imbalance from the HRV.But one trick that I saw in FHB is to put the dampner behind the refigerator on the outside wall. That way the heat loss off the refigerator helps temper the air.You can also have an intake fan setup to run when the vent fan is running, but I have no idea how to size it.

          5. Hubedube | Dec 08, 2004 03:12am | #12

             Hvac, as you probably know ,deals with many, many hours  of study and training. Especially , 'AIR BALANCING', its a almost a trade itself.

             Most persons do not have clue about air measure, flow, quantities, cfm, fpm, static pressures, Vol, Vel,duct design ,etc, etc.

             And that is why some dealers put a lid on some information to a diyer.

            As soon as the diyer opens his mouth, a trained person can tell just what level this person is at.

             A lot of hvac adjstments can be very deadly and disasterous if not done precisely.

          6. masterofnon1 | Dec 08, 2004 04:19am | #19

            Speaking of HVAC.  I am sure if you get complicated  . . . well then it can get complicated.  However, I built a 2200 sqft house with my father 30 years ago.  Installed the furance and ran the ducts.   Never had a problem.   Gee size the furnance, run enough heat ducts and don't go short on cold air returns, and . . . .

            Do you really need more? 

            It seems pretty stupid to build an air tight house, and then punch a hole in the wall in order to pull in fresh air with thousands of dollars worth of gear.  And oh yeah, such fireplace smoke from the livingroom into the kitchen.  Brilliant!  And people pay how much for such marvalous systems?

          7. Diamond | Dec 08, 2004 04:41am | #22

            The problem with your leaky house is that you can't control where the air coming into the house will come from. It will probably be coming in through the walls.

            Scenario 1: Summer time and it is hot and humid out, your AC is on,  you turn on your 750 cfm fan, your make up air comes through the leaky walls and will condense somewhere in the wall. Even without your fan on moisture will travel throgh your leaky walls because we all know moisture moves from warm to cold.

            Scenario 2: Winter time moisture will move through your leaky walls from inside to outside and condense somewhere in the wall.

            Scenario 3: Turn on your kitchen fan and your make-up air comes from the garage or your vetilated, unconditioned, damp crawl space.

          8. highfigh | Dec 08, 2004 05:05am | #24

            If HVAC was so simple, why aren't there more people in that line? It's not just "put in a furnace, hook it up and have enough ducts". If the ducts are too small, they either won't move enough air or the air that goes through will make too much noise and turbulance. If they're too small, the conditioned air won't get to the destination at the correct temperature. Too many bends and restrictions, laminar flow goes away and you get noise and not enough movement. Most air infiltration comes in around doors and through windows that don't fit well or aren't sealed properly and from leaky walls and holes where pipes, wiring and ducts are not sealed properly and the cold air goes from attics and outside to the heated space. Negative pressure compounds this problem by literally sucking the cold air in. It also draws outside air in through chimneys where exhaust gasses are moving and this brings CO along for the ride. Contrary to some people's opinion, bringing air into a well sealed house to the furnace with an inducer blower does not affect the air in the house. That's combustion air, specifically so the furnace doesn't blow heated air out and suck cold air in. As long as a very slightly positive pressure is maintained, cold air isn't sucked in and people don't die from CO poisoning.
            "I cut this piece four times and it's still too short."

          9. Diamond | Dec 08, 2004 05:24am | #25

            You're right HVAC is not easy, well the H and AC aren't to hard its the V thats the problem. If you are not using sealed combustion appliances you are asking for problems. Your right in that having a negative pressure in your house will suck air into the house, Positive pressure will do the opposite which is bad especially in the winter moisture can condense in the wall.

          10. highfigh | Dec 08, 2004 05:46am | #26

            It's only going to condends in the wall if it can get into it. On a newer home, the vapor barrier should work if nobody added home theater wiring and stuff like that and punched holes in the outside walls. The doors are a more likely candidate for leaking, the windows next if the other plumbing and electrical holes were sealed. Every house will breathe a bit. Some just breathe like a heavy smoker running a marathon. If it's too well sealed, opening and closing doors is just weird.
            "I cut this piece four times and it's still too short."

          11. AXE | Dec 08, 2004 06:06am | #28

            I got rid of my crawlspace and I use sealed combustion appliances.  So I don't have anywhere to draw "bad" air from.  I also sprayed my roof deck to do as much as I could to shut down the stack effect.  Since my walls are spray foamed there is essentially zero air movement through my walls.  So it's going to come from somewhere and I'd rather it not be "by chance" because who knows what hole it will find.

            I think the motorized damper in the cold return will do nicely.  Just need to dig around and find an appropriate part to do that and then figure out how to break into the wiring on the vent hood and open/close the damper with the hood.

            Another choice would be to see if I could come up with some way of mounting the stove top so it had a small gap all the way around and then I could draw make up air from under the stove, draw up and around it, grab the smoke and grease and out the hood.  An 1/8" gap all the way around a 36x30 rectangle is 16.5 sq in, which is about half the cross sectional area of the outgoing duct.  So the air velocity would be about tornado level coming through that gap.  Better come up with something else.

            MERC.

          12. highfigh | Dec 08, 2004 07:16am | #29

            Any heating supply house should carry motorized dampers and there are current sensing recepticles that can turn a second device on when the first causes a spike in voltage, like what is used for dust collectors when another powertool is turned on.
            "I cut this piece four times and it's still too short."

          13. Hubedube | Dec 08, 2004 02:59am | #11

            " you say; your local hvac supplier would'nt  have clue"...

             then go to one that does I,m sure there are some in your area,.

          14. highfigh | Dec 08, 2004 03:17am | #14

            What about a blower that is specifically for bringing air from outside to the underside of the hood and turns on with the hood? That way, you aren't making the whole house cold, and it can't be left on for too long. Do you have a high BTU range, too?
            "I cut this piece four times and it's still too short."

          15. AXE | Dec 08, 2004 03:45am | #15

            I like the idea since the stove top will always be quite hot when the hood is on high, therefore cold incoming air in the area of the hood would not be noticed.  I'll have to give this one some thought.  The stove is a 36" 5-burner with a couple of 15k burners, one 10k and two 8k (I think).

            I also like the behind the refrigerator as suggested, though that might be physically challenging and the architectural committee (wife) might not approve the outdoor grate on the backside of the refrigerator.

            MERC

          16. highfigh | Dec 08, 2004 04:01am | #17

            Since the hood is vented outside, why not bring it in behind the range? If the vent opening has enough area, the incoming air won't be moving too fast and should be fairly quiet. If there's unfinished basement space under the range, that would seem to be ideal. To me, anyway.
            "I cut this piece four times and it's still too short."

          17. AXE | Dec 08, 2004 04:04am | #18

            Would this vent be a flapper type or something that closed by gravity when the hood is off?

            MERC

          18. Diamond | Dec 08, 2004 04:21am | #20

            If you put the make up air close to the stove it will short circuit and not work properly. Put a motorized damper into the cold air return ducted to the outside. Have it wired so it will open when you turn on your kitchen fan. The air coming in will be filtered by your forced air system and all the make up air won't be coming from one area. Stirling makes an erv that will measure the outside pressure and makes the inside pressure the same, It takes this measurement every ten min. so it wouldn't work for make-up air. I would avoid keeping your house under a positive or negative pressure you want it to be the same inside as outside.

          19. PhillGiles | Dec 08, 2004 03:12am | #13

            Well, in my limited experience, if you get an installer through the gas company, he's likely to be wedded to a fairly simple technology, probably somewhat behind the times. If you find an installer through one of the high-end suppliers who deal with big stoves and appliances, you may be a lot happier.Your recovery unit should be sized/tuned to allow for the maximum amount of exhausted air, that should include any open fireplaces (some people still do this !) and hoods..
            Phill Giles
            The Unionville Woodwright
            Unionville, Ontario

          20. Mooney | Dec 08, 2004 04:36am | #21

            I shut down a resturant that was drawing negative pressure through sewer traps. It would also have comne through a vented gas device.

            I have done quite a bit of inspection work with state inspectors and have learned a little . Ive worked out a few problems like you have now.

            The only way to "effectively do it ", is to bring in make up air when the hood is running . No biggy. Run a wall vent or from a roof vent a 4 to 6 inch pipe or flex line with incomming air via an inline fan switched to come on when the hood is on. when the hood is off , so is the incomming air. It would be best to make the incomming opening close to the draw so that temperature in the room is not afffected.

            Commercial type 2 or 3 hoods allow the same make up air in them . But you can make it your self.

            Tim Mooney

      2. VaTom | Dec 08, 2004 02:17am | #9

        If I remember correctly, you run your kitchen hood through your HRV right?

        Your memory serves you well.  And for your cooking, I'd reroute the ductwork.  But unless you have a tiny house, you can plan for removing that amount of air for 20 minutes without making a major incoming leak. 

        2 ERV's?  How large is your house?  Take a look at your volume and see if your exhaust fan will be significant.  If you have 40k cu ft, I can't imagine you would notice your fan's intake. 

        We have 20K cu ft that we're changing, .5ACH.  I don't think your exhaust would make much difference if I upped the intake fan a few cfm.  Our exhaust fan is a recycled one, no idea of cfm.  It works very well with our over-sized hood.  I did, for the inspector, have it bypassing our heat exchanger.  Wasn't a problem.  The change was primarily for my peace of mind.  Sounds like you have a similar desire. 

        Clearly you can have a fine tuned system with multiple parts and get something more efficient than ours.  Payback on the system will be never and I'd be very surprised if a visitor could tell the difference.  PAHS Designer/Builder- Bury it!

        1. AXE | Dec 08, 2004 04:00am | #16

          My house volume is about 41k cu ft, spread over three floors, including basement workshop and storage room.  Top two floors are living space and are about 27k between them.  So if I run a 715 CFM fan for 20 minutes that would produce 14k cu ft of exhaust or about 0.3 air changes / 20 minutes = 0.9 ACH.  That seems pretty significant to me.  I sure would feel better if I knew where that volume was coming from.   I guess like I said before if I don't provide a make up air path it will just choke the cfm down to what it can do.

           

          I was planning on two ERVs because of the issue of chasing even more ductwork between the floors.  I still haven't fully come to grips with what a good ERV installation looks and feels like so the design is still in flux.  I'm not planning on closing up anytime soon so I have some time to give it some thought and play around with it.  Since I'm chasing an HVAC feed and return to the second floor, maybe I can tie into that somehow though I read the JLC article and they said tying into a furnace ductwork doesn't make the best ERV installation.  Might be good enough for me though.

          I think I'll go mill about at hvac-talk.com.

          MERC.

          1. VaTom | Dec 08, 2004 04:51am | #23

            So if I run a 715 CFM fan for 20 minutes that would produce 14k cu ft of exhaust or about 0.3 air changes / 20 minutes = 0.9 ACH.  That seems pretty significant to me.

            And it will be, if you don't plan for that make up air with a pressurized system.  See how simple it is?  Size your fans.  With that size volume you have significant latitude.PAHS Designer/Builder- Bury it!

          2. AXE | Dec 08, 2004 05:57am | #27

            Yes I think I see where you are going now.  I'm glad I asked the question and I will contemplate for a while and see what I can come up with.

            Thanks -MERC

  2. SEBDESN | Dec 08, 2004 02:26am | #10

    Crack the window when you have it cranked up to 10...I have a 1200 cfm (unit on the roof), and a gas restaurant type grill on the peninsula. When its up to 10, I crack the window.Its only at 10 when the grill is on,and smoking however,otherwise its not a problem. The d-mn thing will suck the smoke from the fireplace in the front room all the way to the kitchen.Dont ask how I know that.. 

  3. cabman | Dec 08, 2004 07:24am | #30

    I didn't read all 30 posts, so maybe this has been covered, but does building code come into play?

    Around here a fan that big requires not only make up air, but warm air.

    I have seen inline fans installed, switched to the fan speed control, and vented behind a fridge.

    Just a thought.  Darren.

    1. user-66767 | Mar 23, 2006 02:32am | #31

      I just figured out how to do this.

      A current sensing relay (Aprilaire A50, an HVAC part, $30) installed on the wire powering the exhaust fan will close a 24 volt circuit.  You will need a 24 volt transformer and a Honeywell power operated damper.

      I installed this on my return air duct which exhausts directly behind the range.  It goes on when the fan goes on and provides enough makeup air directly from the attic to prevent backdrafting down the chimney or other such annoyances.

Log in or create an account to post a comment.

Sign up Log in

Become a member and get full access to FineHomebuilding.com

Video Shorts

Categories

  • Business
  • Code Questions
  • Construction Techniques
  • Energy, Heating & Insulation
  • General Discussion
  • Help/Work Wanted
  • Photo Gallery
  • Reader Classified
  • Tools for Home Building

Discussion Forum

Recent Posts and Replies

  • |
  • |
  • |
  • |
  • |
  • |
View More Create Post

Up Next

Video Shorts

Featured Story

FHB Podcast Segment: Efficient HVAC for a New Build

Self-installing an HVAC system requires a lot of thought and planning.

Featured Video

SawStop's Portable Tablesaw is Bigger and Better Than Before

The 10-in. Jobsite Saw PRO has a wider table, a new dust-control port, and a more versatile fence, along with the same reliable safety mechanism included in all SawStop tablesaws.

Related Stories

  • Podcast Episode 686: Brick Steps, Ground-Source Heat Pumps, and Greenhouses in Nova Scotia
  • FHB Podcast Segment: Efficient HVAC for a New Build
  • Affordable Scans, Accurate Plans
  • FHB Summit 2025 — Design, Build, Business

Highlights

Fine Homebuilding All Access
Fine Homebuilding Podcast
Tool Tech
Plus, get an extra 20% off with code GIFT20

"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Fine Homebuilding Magazine

  • Issue 331 - June 2025
    • A More Resilient Roof
    • Tool Test: You Need a Drywall Sander
    • Ducted vs. Ductless Heat Pumps
  • Issue 330 - April/May 2025
    • Deck Details for Durability
    • FAQs on HPWHs
    • 10 Tips for a Long-Lasting Paint Job
  • Issue 329 - Feb/Mar 2025
    • Smart Foundation for a Small Addition
    • A Kominka Comes West
    • Making Small Kitchens Work
  • Issue 328 - Dec/Jan 2024
    • How a Pro Replaces Columns
    • Passive House 3.0
    • Tool Test: Compact Line Lasers
  • Issue 327 - November 2024
    • Repairing Damaged Walls and Ceilings
    • Plumbing Protection
    • Talking Shop

Fine Home Building

Newsletter Sign-up

  • Fine Homebuilding

    Home building tips, offers, and expert advice in your inbox.

  • Green Building Advisor

    Building science and energy efficiency advice, plus special offers, in your inbox.

  • Old House Journal

    Repair, renovation, and restoration tips, plus special offers, in your inbox.

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters

Follow

  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X
  • Fine Homebuilding

    Dig into cutting-edge approaches and decades of proven solutions with total access to our experts and tradespeople.

    Start Free Trial Now
    • Facebook
    • Instagram
    • X
    • LinkedIn
  • GBA Prime

    Get instant access to the latest developments in green building, research, and reports from the field.

    Start Free Trial Now
    • Facebook
    • YouTube
  • Old House Journal

    Learn how to restore, repair, update, and decorate your home.

    Subscribe Now
    • Facebook
    • Instagram
    • X

Membership & Magazine

  • Online Archive
  • Start Free Trial
  • Magazine Subscription
  • Magazine Renewal
  • Gift a Subscription
  • Customer Support
  • Privacy Preferences
  • About
  • Contact
  • Advertise
  • Careers
  • Terms of Use
  • Site Map
  • Do not sell or share my information
  • Privacy Policy
  • Accessibility
  • California Privacy Rights

© 2025 Active Interest Media. All rights reserved.

Fine Homebuilding receives a commission for items purchased through links on this site, including Amazon Associates and other affiliate advertising programs.

  • Home Group
  • Antique Trader
  • Arts & Crafts Homes
  • Bank Note Reporter
  • Cabin Life
  • Cuisine at Home
  • Fine Gardening
  • Fine Woodworking
  • Green Building Advisor
  • Garden Gate
  • Horticulture
  • Keep Craft Alive
  • Log Home Living
  • Military Trader/Vehicles
  • Numismatic News
  • Numismaster
  • Old Cars Weekly
  • Old House Journal
  • Period Homes
  • Popular Woodworking
  • Script
  • ShopNotes
  • Sports Collectors Digest
  • Threads
  • Timber Home Living
  • Traditional Building
  • Woodsmith
  • World Coin News
  • Writer's Digest
Active Interest Media logo
X
X
This is a dialog window which overlays the main content of the page. The modal window is a 'site map' of the most critical areas of the site. Pressing the Escape (ESC) button will close the modal and bring you back to where you were on the page.

Main Menu

  • How-To
  • Design
  • Tools & Materials
  • Video
  • Blogs
  • Forum
  • Project Guides
  • Reader Projects
  • Magazine
  • Members
  • FHB House

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Podcasts

  • FHB Podcast
  • ProTalk

Webinars

  • Upcoming and On-Demand

Popular Topics

  • Kitchens
  • Business
  • Bedrooms
  • Roofs
  • Architecture and Design
  • Green Building
  • Decks
  • Framing
  • Safety
  • Remodeling
  • Bathrooms
  • Windows
  • Tilework
  • Ceilings
  • HVAC

Magazine

  • Current Issue
  • Past Issues
  • Magazine Index
  • Subscribe
  • Online Archive
  • Author Guidelines

All Access

  • Member Home
  • Start Free Trial
  • Gift Membership

Online Learning

  • Courses
  • Project Guides
  • Reader Projects
  • Podcast

More

  • FHB Ambassadors
  • FHB House
  • Customer Support

Account

  • Log In
  • Join

Newsletter

Get home building tips, offers, and expert advice in your inbox

Signing you up...

This site is protected by reCAPTCHA and the Google Privacy Policy and Terms of Service apply.
See all newsletters
See all newsletters

Follow

  • X
  • YouTube
  • instagram
  • facebook
  • pinterest
  • Tiktok

Join All Access

Become a member and get instant access to thousands of videos, how-tos, tool reviews, and design features.

Start Your Free Trial

Subscribe

FHB Magazine

Start your subscription today and save up to 70%

Subscribe

Enjoy unlimited access to Fine Homebuilding. Join Now

Already a member? Log in

We hope you’ve enjoyed your free articles. To keep reading, become a member today.

Get complete site access to expert advice, how-to videos, Code Check, and more, plus the print magazine.

Start your FREE trial

Already a member? Log in

Privacy Policy Update

We use cookies, pixels, script and other tracking technologies to analyze and improve our service, to improve and personalize content, and for advertising to you. We also share information about your use of our site with third-party social media, advertising and analytics partners. You can view our Privacy Policy here and our Terms of Use here.

Cookies

Analytics

These cookies help us track site metrics to improve our sites and provide a better user experience.

Advertising/Social Media

These cookies are used to serve advertisements aligned with your interests.

Essential

These cookies are required to provide basic functions like page navigation and access to secure areas of the website.

Delete My Data

Delete all cookies and associated data