Need help wiring an Furnace Emergency Switch
I need to add an emergency cut-off switch for the gas furnace at the top of my basement stairs by code. I but I don’t know how to make the connection. I know it can’t be that hard but I can’t find anything online to help and my electrician is MIA.
As you can see in my diagram, the “Emergency Switch” needs some help. These cannot be 3-way switches.
Replies
The 2 switches are wired in series. Power ( black wire ) goes to the emergency switch. Return from this switch then goes to the master switch. Make sure the white wire is marked as " hot" with black permanet marker or tape.
Your electrician will now how to do this. If you are doing it yourself, it should be inspected.
Update Graphic
Thank you! I think this is what you mean (see UPDATED graphic). It will be inspected along with other plubming issues I just want to get installed before I fire up the furnace for the season. My electrician is out of town it turns out. Just to be clear, I have one switch immediately next to the furnace, this is a second switch at the top of the basement stairs.
Can't make heads or tails of that diagram, but it looks wrong, what I can make out.
Switches have to be in series, so both must be on to energize the furnace. Either one off breaks the circuit.
Question: Emergency switches are not normally used with gas furnaces. Required for oil burners. Is this a local code issue?
Emergency Swtiches Are Requried
Code requires two switches (in a series) for both gas and oil furnaces. My HVAC guy is coming next week but my electrician is MIA. So, I am stuck. Googling two spst in a series (or anything to that affect) gets poor relsults. I'll just wait.
Thanks for the time.
gs
no kidding, an "emergency" switch for the furnace?
Man, glad I'm trying my damndest to retire.
Removed by Original Poster - I meant to reply.
Note that what you need is similar to a "switch leg" for lighting.
View Image
The difference is that instead of the lamp socket you have the existing furnace power switch.
Note that the incoming black goes only to the emergency switch (by means of the white wire painted black). The black wire coming from the emergency switch then goes to the place where the original black wire once connected. No (unpainted) white wire goes to the emergency switch. And, of course, ground wires (not shown above) are all interconnected.
THIS IS IT!
This is what I am looking for. I think I get it. THANK YOU!!!!!
I am too completely satisfied with the answer by DanH.
PT
I'm wondering why your username isn't anywhere close to your email address?